Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Sun. Nov. 25, 2018 6:38 am

I really do believe it’s just changing where the ash motor gets its power from, it needs to come from the combustion fan, not a big deal to change if it’s not currently wired like this. Save your money and we’ll cross that bridge when you get it home and see what it does..

On a side note, with a temp sensor on the bottom of the hopper, there’s pretty much no chance of a hopper fire.

 
lzaharis
Member
Posts: 2365
Joined: Sun. Mar. 25, 2007 8:41 pm
Location: Ithaca, New York
Stoker Coal Boiler: Keystoker KAA-4-1 dual fuel boiler
Hand Fed Coal Boiler: former switzer CWW100-sold
Coal Size/Type: rice
Other Heating: kerosene for dual fuel Keystoker/unused

Post by lzaharis » Sun. Nov. 25, 2018 8:46 am

The sky was not falling on me, I figure that if even after begging Keystoker to come up here they were unwilling to help me even after I offered to put them up in a hotel and pay for their meals they were still going to stick me for 75 dollars and hour plus travel time something is wrong with that picture.

I remember reading at least one account of a hopper fire in both a keystoker and an AHS unit.

Does your axeman unit still have 2 single aquastats?

 
User avatar
hotblast1357
Member
Posts: 5657
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Sun. Nov. 25, 2018 9:14 am

lzaharis wrote:
Sun. Nov. 25, 2018 8:46 am
I remember reading at least one account of a hopper fire in both a keystoker and an AHS unit.
With the sensor on the hopper it won’t happen.


 
User avatar
Rob R.
Site Moderator
Posts: 17979
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Sun. Nov. 25, 2018 9:26 am

BodyshopPat wrote:
Fri. Nov. 23, 2018 10:18 pm
From what I am hearing my 260 wont have mode 1 and 2,,, is mine going to be prone to the booms or exactly what is the mode 2? I will try to digest what you tell me , since my unit will not have a timer it has the thermocouple correct?
A quick call to AHS will answer a lot of your questions. Based on the serial number of your unit, they will be able to tell if any upgrades are available (or recommended).

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Sun. Nov. 25, 2018 10:09 am

lzaharis wrote:
Sun. Nov. 25, 2018 8:46 am
I remember reading at least one account of a hopper fire in both a keystoker and an AHS unit.
That may have been forum member 'Yanchee' a long time ago. I believe he may have been the one who inspired AHS to install the snap switch on the bottom of the hopper. I think he turned his ashing switch off and forgot to turn it back on.

Thinking of this, if you must turn your ashing switch off in order to haul out the ash tub for emptying, please also turn the fan switch off. Then when the ash tub is back in place turn both switches back on.