Zone Loop Friction Head and Circulator GPM Calculator

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Thu. Jan. 10, 2019 11:57 am

McGiever wrote:
Thu. Jan. 10, 2019 11:24 am
No need for permanent gauges to be installed...just install these ports and then only move stem or prob gauge(s) around to measure as or when needed:

https://api.ferguson.com/dar-step-service/Query?U ... _ID=166137
Good idea! The greatest precision comes from using the same gauge to read PSI on the inlet and outlet sides of the circulator. Unless you are really lucky, no two gauges ever seem to read exactly the same.

 
User avatar
Rob R.
Site Moderator
Posts: 17979
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Thu. Jan. 10, 2019 12:01 pm

I go by the method suggested earlier....if the house and showers are warm enough the flow must be adequate.

If I wanted to, I can look at the GPM display on my Alpha circulator. I have only looked at it a few times but it seems accurate based on the pipe sizes and what I would expect.

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Thu. Jan. 10, 2019 12:17 pm

Rob R. wrote:
Thu. Jan. 10, 2019 12:01 pm
I go by the method suggested earlier....if the house and showers are warm enough the flow must be adequate.

If I wanted to, I can look at the GPM display on my Alpha circulator. I have only looked at it a few times but it seems accurate based on the pipe sizes and what I would expect.
I get what you're saying, and that Alpha display is nice, but one needs 2 separate readings from 2 separate locations to be able to do the math calculations to obtain results through any given pressure dropping point in loop or circuit...such as through a coil, exchangee or other component to know actual performance..
Last edited by McGiever on Thu. Jan. 10, 2019 12:21 pm, edited 1 time in total.

 
User avatar
Rob R.
Site Moderator
Posts: 17979
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Thu. Jan. 10, 2019 12:18 pm

That is why I go by the first method.


 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Thu. Jan. 10, 2019 12:20 pm

Here is a method by which to use a single pressure gauge to measure both inlet and outlet side pressure on your circulator. Close the gauges outlet side valve and open the inlet side valve to read pressure on the suction side of the circulator, and visa-versa.

PSI.pdf
.PDF | 10.5KB | PSI.pdf

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Thu. Jan. 10, 2019 12:26 pm

Rob R. wrote:
Thu. Jan. 10, 2019 12:18 pm
That is why I go by the first method.
Thanks, good to know.

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Thu. Jan. 10, 2019 12:32 pm

lsayre wrote:
Thu. Jan. 10, 2019 12:20 pm
Here is a method by which to use a single pressure gauge to measure both inlet and outlet side pressure on your circulator. Close the gauges outlet side valve and open the inlet side valve to read pressure on the suction side of the circulator, and visa-versa.


PSI.pdf
Nice for simple flow calcs where getting the temp reading is not needed for any BTU calcs...like with coil or exchanger.
But then maybe this is getting a bit beyond the scope of this thread...