I am installing a water to air heat exchanger in my plenum. Currently we have the air conditioning coil in the plenum above the furnace.
In your opinion how close can the two coils be together? I cannot find any info online, so I figured I'd ask the experts.
Anyhow thank you for your time.
Frank
-
Frank F
- Member
- Posts: 208
- Joined: Sat. Apr. 07, 2018 8:48 pm
Post
by Frank F » Sat. Oct. 27, 2018 9:12 am
Check out my pic
-
swyman
- Member
- Posts: 2355
- Joined: Mon. Apr. 13, 2015 9:50 pm
- Location: Blissfield, MI
- Stoker Coal Boiler: Axeman-Anderson 260M Leisure Line AA-220 Boiler (FOR SALE)
- Coal Size/Type: Lehigh Pea
Post
by swyman » Sat. Oct. 27, 2018 9:21 am
Mine is as close as I could get it so I don't miss any branches but left room to work.
-
swyman
- Member
- Posts: 2355
- Joined: Mon. Apr. 13, 2015 9:50 pm
- Location: Blissfield, MI
- Stoker Coal Boiler: Axeman-Anderson 260M Leisure Line AA-220 Boiler (FOR SALE)
- Coal Size/Type: Lehigh Pea
Post
by swyman » Sat. Oct. 27, 2018 9:22 am
Didn't have room to put above A coil.
-
Frank F
- Member
- Posts: 208
- Joined: Sat. Apr. 07, 2018 8:48 pm
Post
by Frank F » Sat. Oct. 27, 2018 9:29 am
swyman wrote: ↑Sat. Oct. 27, 2018 9:22 am
Didn't have room to put above A coil.
Nice. I'm hoping to use one but if I have to get two smaller ones one for each trunk I will.
-
swyman
- Member
- Posts: 2355
- Joined: Mon. Apr. 13, 2015 9:50 pm
- Location: Blissfield, MI
- Stoker Coal Boiler: Axeman-Anderson 260M Leisure Line AA-220 Boiler (FOR SALE)
- Coal Size/Type: Lehigh Pea
Post
by swyman » Sat. Oct. 27, 2018 9:39 am
I like your insulated duct. Wonder how much of a difference that would make in my house?
-
Frank F
- Member
- Posts: 208
- Joined: Sat. Apr. 07, 2018 8:48 pm
Post
by Frank F » Sat. Oct. 27, 2018 10:53 am
swyman wrote: ↑Sat. Oct. 27, 2018 9:39 am
I like your insulated duct. Wonder how much of a difference that would make in my house?
I was fortunate that it was there when we bought the house. Not sure if it will be as easy to work with as metal. I'm a little worried about the strength difference when mounting the coils. Figured I'll have to make some brakets to mount them to cieling or something rigid.
-
swyman
- Member
- Posts: 2355
- Joined: Mon. Apr. 13, 2015 9:50 pm
- Location: Blissfield, MI
- Stoker Coal Boiler: Axeman-Anderson 260M Leisure Line AA-220 Boiler (FOR SALE)
- Coal Size/Type: Lehigh Pea
Post
by swyman » Sat. Oct. 27, 2018 11:40 am
Frank F wrote: ↑Sat. Oct. 27, 2018 10:53 am
I was fortunate that it was there when we bought the house. Not sure if it will be as easy to work with as metal. I'm a little worried about the strength difference when mounting the coils. Figured I'll have to make some brakets to mount them to cieling or something rigid.
Oh, I thought it was sheet metal with insulation over it?
-
Frank F
- Member
- Posts: 208
- Joined: Sat. Apr. 07, 2018 8:48 pm
Post
by Frank F » Sun. Oct. 28, 2018 8:35 am
Could I put the heat coil in top of the furnace, and put the air coil (A-frame) on top of that?
Structural wise seems to make sense.
-
swyman
- Member
- Posts: 2355
- Joined: Mon. Apr. 13, 2015 9:50 pm
- Location: Blissfield, MI
- Stoker Coal Boiler: Axeman-Anderson 260M Leisure Line AA-220 Boiler (FOR SALE)
- Coal Size/Type: Lehigh Pea
Post
by swyman » Sun. Oct. 28, 2018 8:43 am
Frank F wrote: ↑Sun. Oct. 28, 2018 8:35 am
Could I put the heat coil in top of the furnace, and put the air coil (A-frame) on top of that?
Structural wise seems to make sense.
Looking at your setup I would think that would be ideal but there will be others on here that know better than me!
-
coalkirk
- Member
- Posts: 5185
- Joined: Wed. May. 17, 2006 8:12 pm
- Location: Forest Hill MD
- Stoker Coal Boiler: 1981 EFM DF520 retired
- Hand Fed Coal Stove: Jotul 507 on standby
- Coal Size/Type: Lehigh anthracite/rice coal
Post
by coalkirk » Sun. Oct. 28, 2018 10:21 am
Mine is in the return before the air handler and works fine.
-
Frank F
- Member
- Posts: 208
- Joined: Sat. Apr. 07, 2018 8:48 pm
Post
by Frank F » Sun. Oct. 28, 2018 10:55 am
coalkirk wrote: ↑Sun. Oct. 28, 2018 10:21 am
Mine is in the return before the air handler and works fine. heat exchanger.jpg
Great idea. That opens up even more options! Dang it to many decisions. That would be much easier than moving the air coil.
-
dcveem3
- Member
- Posts: 89
- Joined: Sat. Jan. 20, 2018 6:44 pm
- Location: NorthWest York Co, PA
- Stoker Coal Boiler: Someday!
- Hot Air Coal Stoker Stove: Harman Magnum (temp basement duty)
- Other Heating: Propane/Heat Pump
Post
by dcveem3 » Fri. Nov. 23, 2018 5:47 pm
I vote return like Kirk did. If I had a single return, I'd do the same.
Don
-
Pauliewog
- Member
- Posts: 1824
- Joined: Mon. Dec. 02, 2013 12:15 am
- Location: Pittston, Pennsylvania
- Hot Air Coal Stoker Furnace: Alaska 140 Dual Paddle Feed
- Baseburners & Antiques: Fame Rosemont #20, Home Stove Works #25, Glenwood #6, Happy Thought Oak, Merry Bride #214, Sunnyside, Worlds Argand #114, New Golden Sun , & About 30 others.
- Coal Size/Type: Stove, Chesnut, Pea, Rice / Anthracite
Post
by Pauliewog » Fri. Nov. 23, 2018 10:57 pm
The cold air return duct would be my first choice too.
Paulie
-
ziggy87
- Member
- Posts: 311
- Joined: Sat. Oct. 25, 2014 11:22 am
- Location: Halifax, Pa
- Stoker Coal Boiler: axeman anderson 130
- Coal Size/Type: Pea
Post
by ziggy87 » Fri. Nov. 23, 2018 11:47 pm
It should not matter how close to the A coil it is because your plentium temp will not be above melting point of a plastic drain pan on A coil. I would put it between the furnace and the A coil. I usually leave 2-4" gap when I install them. Avoid the return side if you can. If you install on the return side it must be after the air filter.