Post by StokerDon » Tue. Jun. 21, 2022 7:01 pm

Retro_Origin wrote:
Mon. Jun. 20, 2022 8:21 pm
For sure. What were your findings with changing fan speed? Just ramp up time?
The fan speed sets the BTU output of one of these boilers, nothing else.

Unfortunately, all of my fans speed data was done with an Axeman fan. I am currently running an AHS fan and insulated fan plate. The AHS fan is different and will not easily relate to my Axeman fan data.

I am running a fan speed of 1460 RPM (Stock AHS is 1725 RPM). All that really tells me is that it is running at less than 130,000 BTU's.
IMG_0002.JPG
.JPG | 330.7KB | IMG_0002.JPG
IMG_0003.JPG
.JPG | 332.4KB | IMG_0003.JPG
-Don


 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sun. Jun. 26, 2022 8:59 pm

It's HOT! And HUMID!!!
IMG_0003.JPG
.JPG | 264.2KB | IMG_0003.JPG
IMG_0001.JPG
.JPG | 360.7KB | IMG_0001.JPG
Over the past 7 days;
Fan reading, 2363.4 - 2345.4 = 18.0 hours of fan run time, 2.57 hours per day.
Ash reading, 1346.8 - 1334.3 = 12.5 hours of ashing, 1.8 hours per day, 69% of fan run time.
IMG_0002.JPG
.JPG | 332.9KB | IMG_0002.JPG
39.5 pounds of pretty rocky crappy looking ash.
IMG_0005.JPG
.JPG | 456.6KB | IMG_0005.JPG
I know that Gofer is in there sweat'in!
IMG_0004.JPG
.JPG | 331.8KB | IMG_0004.JPG
Current settings,

Fan RPM = 1460 RPM (Stock AHS is 1725 RPM)
Auger speed = 4.31 RPM (Stock is 8.05 RPM)
Grate cycles per hour = 15.11 (Stock AHS is 34.18)
Pounds per hour = Estimated ??
Aquastat = 165*F (Inkbird), ON/OFF, Hysteresis = 5*
Anthrastat = 120*F (Inkbird), Hysteresis = 0.3*
Low flue temperature cut off = 160*F, Hysteresis = 0.1*

-Don

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sun. Jul. 03, 2022 7:30 pm

Happy Fourth Of July!!!

This is about the latest we have run the Axeman. Through Spring and into Summer now. It is running perfectly and in the past it has had serious problems in warm weather. One of the differences this year is we are not running bottom of the bin coal loaded with fines. I guess in the Winter fines are no big deal for the Axeman, but in the warm weather it's puffbacks and outfires. I haven't heard a puffback yet! :o
IMG_0001.JPG
.JPG | 366KB | IMG_0001.JPG
Over the past 7 days;
Fan reading, 2379.6 - 2363.4 = 16.2 hours of fan run time, 2.31 hours per day.
Ash reading, 1357.8 - 1346.8 = 11.0 hours of ashing, 1.8 hours per day, 68% of fan run time.
IMG_0002.JPG
.JPG | 326.2KB | IMG_0002.JPG
33.5 pounds of rocky looking ash.
IMG_0004.JPG
.JPG | 428.7KB | IMG_0004.JPG
Time to order more coal for that Gofer. We can probably fit 2 more tons in there. I need to get it ordered before the price goes up later in July.
IMG_0003.JPG
.JPG | 494.8KB | IMG_0003.JPG
Current settings,

Fan RPM = 1460 RPM (Stock AHS is 1725 RPM)
Auger speed = 4.31 RPM (Stock is 8.05 RPM)
Grate cycles per hour = 15.11 (Stock AHS is 34.18)
Pounds per hour = Estimated ??
Aquastat = 165*F (Inkbird), ON/OFF, Hysteresis = 5*
Anthrastat = 120*F (Inkbird), Hysteresis = 0.3*
Low flue temperature cut off = 160*F, Hysteresis = 0.1*

-Don

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sun. Jul. 10, 2022 7:11 pm

Heading into the hottest part of the year now. Still no problems.
20220710_150528.jpg
.JPG | 425.9KB | 20220710_150528.jpg
Over the past 7 days;
Fan reading, 2396.7 - 2379.6 = 17.1 hours of fan run time, 2.44 hours per day.
Ash reading, 1370.2 - 1357.8 = 12.4 hours of ashing, 1.8 hours per day, 73% of fan run time.
20220710_150609.jpg
.JPG | 675.4KB | 20220710_150609.jpg
41.5 pounds of rocky ash. A little more fan runtime and ash this week. I don't know why.
20220710_150726.jpg
.JPG | 1.1MB | 20220710_150726.jpg
Gofer action.
20220710_150639.jpg
.JPG | 648.9KB | 20220710_150639.jpg
Current settings,

Fan RPM = 1460 RPM (Stock AHS is 1725 RPM)
Auger speed = 4.31 RPM (Stock is 8.05 RPM)
Grate cycles per hour = 15.11 (Stock AHS is 34.18)
Pounds per hour = Estimated ??
Aquastat = 165*F (Inkbird), ON/OFF, Hysteresis = 5*
Anthrastat = 120*F (Inkbird), Hysteresis = 0.3*
Low flue temperature cut off = 160*F, Hysteresis = 0.1*

-Don

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sun. Jul. 17, 2022 7:16 pm

Not enough time to do a proper update this week.

The only change is the Stack Temp Inhibit setting. I lowered it from 160 to 150. It takes about 5 minutes for the stack temp to get up to 160 and the fan only runs for 10 to 15 minutes. I was getting behind on ashing. This seems to have helped a lot.
20220717_114614.jpg
.JPG | 807.9KB | 20220717_114614.jpg
20220717_114526.jpg
.JPG | 766KB | 20220717_114526.jpg
20220717_114543.jpg
.JPG | 787.1KB | 20220717_114543.jpg
Current settings,

Fan RPM = 1460 RPM (Stock AHS is 1725 RPM)
Auger speed = 4.31 RPM (Stock is 8.05 RPM)
Grate cycles per hour = 15.11 (Stock AHS is 34.18)
Pounds per hour = Estimated ??
Aquastat = 165*F (Inkbird), ON/OFF, Hysteresis = 5*
Anthrastat = 120*F (Inkbird), Hysteresis = 0.3*
Low flue temperature cut off = 150*F, Hysteresis = 0.1*

-Don

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sun. Jul. 24, 2022 7:07 pm

Again, not enough time to do a proper update. But, it's Summer so it doesn't much matter. :D
20220724_154642.jpg
.JPG | 752.5KB | 20220724_154642.jpg
20220724_154721.jpg
.JPG | 478.2KB | 20220724_154721.jpg
20220724_154812.jpg
.JPG | 1017.7KB | 20220724_154812.jpg
20220724_154834.jpg
.JPG | 626.5KB | 20220724_154834.jpg
Current settings,

Fan RPM = 1460 RPM (Stock AHS is 1725 RPM)
Auger speed = 4.31 RPM (Stock is 8.05 RPM)
Grate cycles per hour = 15.11 (Stock AHS is 34.18)
Pounds per hour = Estimated ??
Aquastat = 165*F (Inkbird), ON/OFF, Hysteresis = 5*
Anthrastat = 120*F (Inkbird), Hysteresis = 0.3*
Low flue temperature cut off = 150*F, Hysteresis = 0.1*

-Don

 
User avatar
Retro_Origin
Member
Posts: 914
Joined: Sun. Feb. 21, 2021 7:46 pm
Location: Schuylkill county
Stoker Coal Boiler: 1957 Axeman Anderson 130
Coal Size/Type: Buckwheat / Pea

Post by Retro_Origin » Sat. Jul. 30, 2022 8:55 pm

Don, what would you say is the most advantageous 'non stock' upgrade you made to this beast? You've got so much info here...


 
User avatar
freetown fred
Member
Posts: 30293
Joined: Thu. Dec. 31, 2009 12:33 pm
Location: Freetown,NY 13803
Hand Fed Coal Stove: HITZER 50-93
Coal Size/Type: BLASCHAK Nut

Post by freetown fred » Sat. Jul. 30, 2022 9:30 pm

Plus a couple$$$$$$$$$$$$$$$$$$$$$$ :)

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sun. Jul. 31, 2022 7:21 pm

Retro_Origin wrote:
Sat. Jul. 30, 2022 8:55 pm
Don, what would you say is the most advantageous 'non stock' upgrade you made to this beast? You've got so much info here...
Mostly, the mods I made are "Nice To Have's" rather than anything needed.

I would like to think that the insulated fan plate improves efficiency by keeping more heat in. But I have no proof of that.

The best thing you can do with one of these is match the heat output to the load, this will give you the best efficiency. I did this in very much the same way listed in the 1953 Burau of Mines report.

The Axeman is the most modifiable, tinker-able stoker boiler out there. So naturally, I tinkered, modified and Hot Rodded the heck out of mine! :lol:

Back to business...
IMG_0001.JPG
.JPG | 377.7KB | IMG_0001.JPG
Over the past 7 days;
Fan reading, 2445.7 - 2429.9 = 15.8 hours of fan run time, 2.26 hours per day.
IMG_0002.JPG
.JPG | 420.3KB | IMG_0002.JPG
39.5 pounds of rocky looking ash.
IMG_0003.JPG
.JPG | 443.3KB | IMG_0003.JPG
Current settings,

Fan RPM = 1460 RPM (Stock AHS is 1725 RPM)
Auger speed = 4.31 RPM (Stock is 8.05 RPM)
Grate cycles per hour = 15.11 (Stock AHS is 34.18)
Pounds per hour = Estimated ??
Aquastat = 165*F (Inkbird), ON/OFF, Hysteresis = 5*
Anthrastat = 120*F (Inkbird), Hysteresis = 0.3*
Low flue temperature cut off = 150*F, Hysteresis = 0.1*

-Don

 
User avatar
Retro_Origin
Member
Posts: 914
Joined: Sun. Feb. 21, 2021 7:46 pm
Location: Schuylkill county
Stoker Coal Boiler: 1957 Axeman Anderson 130
Coal Size/Type: Buckwheat / Pea

Post by Retro_Origin » Sun. Jul. 31, 2022 8:55 pm

Haha, that wasn't a sneaky probe to find out what my first alteration is going to be (if any!) but rather if you had seen any major differences. 8-) 8-)

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sun. Aug. 07, 2022 7:49 pm

We've made it into August, and still going!
IMG_0001.JPG
.JPG | 347.2KB | IMG_0001.JPG
Over the past 7 days;
Fan reading, 2462.7 - 2445.7 = 17.0 hours of fan run time, 2.43 hours per day.
IMG_0002.JPG
.JPG | 344.4KB | IMG_0002.JPG
Lots of rocky looking ash.
IMG_0003.JPG
.JPG | 465KB | IMG_0003.JPG
Current settings,

Fan RPM = 1460 RPM (Stock AHS is 1725 RPM)
Auger speed = 4.31 RPM (Stock is 8.05 RPM)
Grate cycles per hour = 15.11 (Stock AHS is 34.18)
Pounds per hour = Estimated ??
Aquastat = 165*F (Inkbird), ON/OFF, Hysteresis = 5*
Anthrastat = 120*F (Inkbird), Hysteresis = 0.3*
Low flue temperature cut off = 150*F, Hysteresis = 0.1*

-Don

 
User avatar
Retro_Origin
Member
Posts: 914
Joined: Sun. Feb. 21, 2021 7:46 pm
Location: Schuylkill county
Stoker Coal Boiler: 1957 Axeman Anderson 130
Coal Size/Type: Buckwheat / Pea

Post by Retro_Origin » Sun. Aug. 07, 2022 9:11 pm

Don I'm so proud of you for running this thing through the summer. You're far enough away from coal country to justify shutdown...but your principles hold fast...jolly good show....

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sun. Aug. 14, 2022 7:21 pm

The only principal I have go'in on here is I don't want to live without hot water! :lol:
20220814_161846.jpg
.JPG | 566.7KB | 20220814_161846.jpg
Over the past 7 days;
Fan reading, 2478.2 - 2462.7 = 15.5 hours of fan run time, 2.21 hours per day.
20220814_161915.jpg
.JPG | 753.7KB | 20220814_161915.jpg
Fan run time per day is pretty low but the ash is mostly cooked, not burnt coal.
20220814_161959.jpg
.JPG | 1.2MB | 20220814_161959.jpg
Where did all the coal go?
20220814_161931.jpg
.JPG | 802.6KB | 20220814_161931.jpg
Current settings,

Fan RPM = 1460 RPM (Stock AHS is 1725 RPM)
Auger speed = 4.31 RPM (Stock is 8.05 RPM)
Grate cycles per hour = 15.11 (Stock AHS is 34.18)
Pounds per hour = Estimated ??
Aquastat = 165*F (Inkbird), ON/OFF, Hysteresis = 5*
Anthrastat = 120*F (Inkbird), Hysteresis = 0.3*
Low flue temperature cut off = 150*F, Hysteresis = 0.1*

-Don

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sun. Aug. 21, 2022 8:06 pm

Another 7 days...
IMG_0001.JPG
.JPG | 367.8KB | IMG_0001.JPG
Over the past 7 days;
Fan reading, 2494.2 - 2478.2 = 16.0 hours of fan run time, 2.29 hours per day.
IMG_0003.JPG
.JPG | 458.9KB | IMG_0003.JPG
One, just about full, heavy ashpan.
IMG_0004.JPG
.JPG | 397.2KB | IMG_0004.JPG
Where did the coal go???
IMG_0005.JPG
.JPG | 330.5KB | IMG_0005.JPG
I lowered the ashing temp to 110 degrees to see if it helps.
Current settings,

Fan RPM = 1460 RPM (Stock AHS is 1725 RPM)
Auger speed = 4.31 RPM (Stock is 8.05 RPM)
Grate cycles per hour = 15.11 (Stock AHS is 34.18)
Pounds per hour = Estimated ??
Aquastat = 165*F (Inkbird), ON/OFF, Hysteresis = 5*
Anthrastat = 110*F (Inkbird), Hysteresis = 0.3*
Low flue temperature cut off = 150*F, Hysteresis = 0.1*

-Don

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sun. Aug. 28, 2022 9:08 pm

We're at the end of August now!
20220828_114926.jpg
.JPG | 812.7KB | 20220828_114926.jpg
Over the past 7 days;
Fan reading, 2512.5 - 2494.2 = 18.3 hours of fan run time, 2.61 hours per day.
20220828_114914.jpg
.JPG | 857.4KB | 20220828_114914.jpg
Ash looks a little better and lighter this week.
20220828_114943.jpg
.JPG | 979.8KB | 20220828_114943.jpg
Still got coal left so I guess we'll keep on go'in!
20220828_114954.jpg
.JPG | 601.3KB | 20220828_114954.jpg
Current settings,

Fan RPM = 1460 RPM (Stock AHS is 1725 RPM)
Auger speed = 4.31 RPM (Stock is 8.05 RPM)
Grate cycles per hour = 15.11 (Stock AHS is 34.18)
Pounds per hour = Estimated ??
Aquastat = 165*F (Inkbird), ON/OFF, Hysteresis = 5*
Anthrastat = 110*F (Inkbird), Hysteresis = 0.3*
Low flue temperature cut off = 150*F, Hysteresis = 0.1*

-Don