Post by StokerDon » Tue. Jan. 12, 2021 1:13 pm

swyman wrote:
Tue. Jan. 12, 2021 6:43 am
That ash pic with stock settings is exactly what mine looks like. I take that as my boiler is running as it should.
Pretty much. You could possibly get a little more complete burn if you made it run a little longer per day.

Time to get that hour meter hooked up! :D

-Don


 
User avatar
hotblast1357
Member
Posts: 5661
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Tue. Jan. 12, 2021 1:29 pm

Have you ever weighed the coal going into this?

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Tue. Jan. 12, 2021 3:10 pm

StokerDon wrote:
Tue. Jan. 12, 2021 1:11 pm
Looks like it would be 50 pounds per day at a fan speed of 1293.75 RPM (12% ash) Vs. 57.8 pounds per day at a fan speed of 2875 RPM (15%ash). The math says we saved 7.8 pounds per day. That's probably a little optimistic though.

I couldn't resist doing a little more tinkering though. I put a 2.5" pulley in place of the 3" pulley. The new fan speed is 1078.13 RPM. We'll run it like that for a few days to see what happens.

-Don
At some juncture the flapper won't pull in during the fan cycle.

 
User avatar
dbsuz05
Member
Posts: 191
Joined: Thu. Nov. 28, 2013 8:09 am
Location: Central Pennsylvania
Stoker Coal Boiler: Axeman Anderson
Hand Fed Coal Boiler: Burnham 23"

Post by dbsuz05 » Tue. Jan. 12, 2021 5:45 pm

I would have thought you’d save more coal than that. Up to 25 lbs maybe.
You have done a thorough job to reduce consumption and try to do even better than factory!

 
User avatar
StokerDon
Site Moderator
Posts: 7502
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Tue. Jan. 12, 2021 6:37 pm

lsayre wrote:
Tue. Jan. 12, 2021 3:10 pm
At some juncture the flapper won't pull in during the fan cycle.
Your correct Larry. Once we get under 1300 RPM on this unit, the door is prone to hang open on a re-start if there is a good fire going. It's not much of a problem if it's been off for more than 10 minutes.
hotblast1357 wrote:
Tue. Jan. 12, 2021 1:29 pm
Have you ever weighed the coal going into this?
Yes, but not during the Winter, only Spring and Summer.
dbsuz05 wrote:
Tue. Jan. 12, 2021 5:45 pm
You have done a thorough job to reduce consumption and try to do even better than factory!
Thanks!
But to be fair, they designed it to put out 130,000 BTU. I just optimized it to run under 60,000 BTU. As Rob stated earlier in this thread, by making the stoker run for longer periods of time, we have moved it further up the efficiency curve.
Of course this will all fall apart when it gets warm out. :oops:

-Don

 
Jkohanski
Member
Posts: 257
Joined: Mon. Nov. 25, 2019 11:11 pm
Location: ringoes, nj central west jersey near pA border
Stoker Coal Boiler: ahs s260
Coal Size/Type: pea
Other Heating: fuel oil
Contact:

Post by Jkohanski » Tue. Jan. 12, 2021 8:17 pm

Ditto with swyman, the fast setting ash looks just like my stock ahs 260.

 
User avatar
StokerDon
Site Moderator
Posts: 7502
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Fri. Jan. 15, 2021 6:31 pm

4 days of running the "Super Low & Slow" settings with the fan at 1078.13 RPM.
IMG_7406.JPG
.JPG | 371KB | IMG_7406.JPG
IMG_7407.JPG
.JPG | 342.2KB | IMG_7407.JPG
Over the past 4 days;
Fan reading, 118.9 - 71.8 = 41.7 hours of fan run time, 11.775 hours per day.
Ash reading, 74.7 - 51.6 = 23.1 , hours of ashing, 5.775 hours per day.
IMG_7411.JPG
.JPG | 378.9KB | IMG_7411.JPG
27 pounds of ash. Ash looks good with some big clinkers. There are some rocks, probably due to the mild weather we are having.
IMG_7408.JPG
.JPG | 367.8KB | IMG_7408.JPG
IMG_7409.JPG
.JPG | 474.8KB | IMG_7409.JPG
Coal usage by ash weight estimate. Ash is closer to 12% than 15%.
12% = 225 pounds, 56.25 pounds per day. 5.39 pounds per fan hour.
15% = 180.00 pounds, 45 pounds per day. 4.32 pounds per fan hour.
18% = 150.00 pounds, 37.5 pounds per day. 3.60 pounds per fan hour.

Back to the original Low & Slow fan speed of 1293.75 RPM. The fire door closes better now. :D
IMG_7412.JPG
.JPG | 314.7KB | IMG_7412.JPG
Current settings,

Fan RPM = 1293.75 RPM (Stock is 2875 RPM)
Ashing = 3.0 Teeth
Auger speed = 3.45 RPM (Stock is 8.05 RPM)
Grate cycles per hour = 10.35
Pounds per hour = Between 4.60 and 6.90 pounds per fan run time hour
Aquastat = 160*F (Inkbird), PID
Anthrastat = 125*F (Inkbird), Hysteresis = 0.5*
Low flue temperature cut off = 160*F, Hysteresis = 0.1*

-Don


 
User avatar
swyman
Member
Posts: 2355
Joined: Mon. Apr. 13, 2015 9:50 pm
Location: Blissfield, MI
Stoker Coal Boiler: Axeman-Anderson 260M Leisure Line AA-220 Boiler (FOR SALE)
Coal Size/Type: Lehigh Pea

Post by swyman » Sat. Jan. 16, 2021 6:47 am

StokerDon wrote:
Fri. Jan. 15, 2021 6:31 pm

Back to the original Low & Slow fan speed of 1293.75 RPM. The fire door closes better now. :D
When my fan comes on it sounds like the glass is going to break!

 
User avatar
StokerDon
Site Moderator
Posts: 7502
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sat. Jan. 16, 2021 8:54 am

swyman wrote:
Sat. Jan. 16, 2021 6:47 am
When my fan comes on it sounds like the glass is going to break!
Currently the door is the loudest noise it makes. Boiler is in the garage but I can hear the door CLANK! shut in the living room. The CLUNK! from the solenoid used to be the loudest thing. :D

-Don

 
User avatar
swyman
Member
Posts: 2355
Joined: Mon. Apr. 13, 2015 9:50 pm
Location: Blissfield, MI
Stoker Coal Boiler: Axeman-Anderson 260M Leisure Line AA-220 Boiler (FOR SALE)
Coal Size/Type: Lehigh Pea

Post by swyman » Sat. Jan. 16, 2021 9:38 am

I think in the offseason I will get rid of the solenoid with the addition of a auger motor and possibly slow it down some. It is running so well and the temps here are ridiculously warm so this thing has had an easy life so far but it has proved it can run in these warm conditions without a hitch. Hopefully we get those -10* ambient temps with a 30mph West wind, then I will know if I should play with the speeds. From what I've seen the boiler will still short cycle. So giddy over this thing but there is just nothing to do but take out ash, which lately I'm going 4 days to a 2/3rds full pan!

 
User avatar
StokerDon
Site Moderator
Posts: 7502
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sat. Jan. 16, 2021 10:35 am

swyman wrote:
Sat. Jan. 16, 2021 9:38 am
then I will know if I should play with the speeds.
If you want to see it run longer you could do what Coaldsweat did. Swap the fan and motor pulleys. You don't need to buy anything and the only tool you need is an Allen key. :D

If it doesn't work out, just swap it back.

-Don

 
User avatar
swyman
Member
Posts: 2355
Joined: Mon. Apr. 13, 2015 9:50 pm
Location: Blissfield, MI
Stoker Coal Boiler: Axeman-Anderson 260M Leisure Line AA-220 Boiler (FOR SALE)
Coal Size/Type: Lehigh Pea

Post by swyman » Sat. Jan. 16, 2021 11:23 am

StokerDon wrote:
Sat. Jan. 16, 2021 10:35 am
If you want to see it run longer you could do what Coaldsweat did. Swap the fan and motor pulleys. You don't need to buy anything and the only tool you need is an Allen key. :D

If it doesn't work out, just swap it back.

-Don
That is as simple as it gets, might try that Monday while I'm off. Does the counterweight come off the fan shaft easy?

 
User avatar
StokerDon
Site Moderator
Posts: 7502
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sat. Jan. 16, 2021 11:50 am

swyman wrote:
Sat. Jan. 16, 2021 11:23 am
Does the counterweight come off the fan shaft easy?
How would I know? You're the 260M guy! :lol:

130M's don't have the fancy heat sink or the counterweight so, I have never seen one in person.

-Don

 
User avatar
swyman
Member
Posts: 2355
Joined: Mon. Apr. 13, 2015 9:50 pm
Location: Blissfield, MI
Stoker Coal Boiler: Axeman-Anderson 260M Leisure Line AA-220 Boiler (FOR SALE)
Coal Size/Type: Lehigh Pea

Post by swyman » Sat. Jan. 16, 2021 12:18 pm

StokerDon wrote:
Sat. Jan. 16, 2021 11:50 am


130M's don't have the fancy heat sink or the counterweight

-Don
Didn't know that, my bad

 
User avatar
coaledsweat
Site Moderator
Posts: 13768
Joined: Fri. Oct. 27, 2006 2:05 pm
Location: Guilford, Connecticut
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea

Post by coaledsweat » Sat. Jan. 16, 2021 1:14 pm

Yes, but mark everything before you take it off so it goes back exactly as it was.