Water Jacket Compromised?
-
- New Member
- Posts: 10
- Joined: Sun. Apr. 08, 2018 6:40 pm
- Stoker Coal Boiler: van wert av400
- Coal Size/Type: buckwheat
Hello,
I just bought a Van Wert boiler. I thought I would tear the skin off of it and possibly replace the insulation. I also thought I would delete the domestic water heater coils seeing that I would not need them. When I took the coils out, I noticed "A lot" of black chalk like soot within the water jacket.......thick (1/16 of an inch) I am new at "coal" boilers, but this doesn't seem right. I expected to see rust......not coal soot. If anywhere, I would have expected to see coal soot in the burn box........in which their is rust. My question is, did I buy a $2,000 boat anchor? .....I am very worried about this and want to know if this is normal and or fixable......I have thought about tearing the whole thing apart and rebuilding it, but it will be difficult in that the whole thing was painted at one point in time......and, yes, painted over rust. (the nuts/bolts will not come out easily)
Also, do you guys know of a product I can dump into the water jacket to clean all the soot out?
Thank for the help,
Chris
I just bought a Van Wert boiler. I thought I would tear the skin off of it and possibly replace the insulation. I also thought I would delete the domestic water heater coils seeing that I would not need them. When I took the coils out, I noticed "A lot" of black chalk like soot within the water jacket.......thick (1/16 of an inch) I am new at "coal" boilers, but this doesn't seem right. I expected to see rust......not coal soot. If anywhere, I would have expected to see coal soot in the burn box........in which their is rust. My question is, did I buy a $2,000 boat anchor? .....I am very worried about this and want to know if this is normal and or fixable......I have thought about tearing the whole thing apart and rebuilding it, but it will be difficult in that the whole thing was painted at one point in time......and, yes, painted over rust. (the nuts/bolts will not come out easily)
Also, do you guys know of a product I can dump into the water jacket to clean all the soot out?
Thank for the help,
Chris
- freetown fred
- Member
- Posts: 30300
- Joined: Thu. Dec. 31, 2009 12:33 pm
- Location: Freetown,NY 13803
- Hand Fed Coal Stove: HITZER 50-93
- Coal Size/Type: BLASCHAK Nut
C, you gotta post some pix of all that situation. Make for better factual suggestions rather then shootin in the dark.
- windyhill4.2
- Member
- Posts: 6072
- Joined: Fri. Nov. 22, 2013 2:17 pm
- Location: Jonestown,Pa.17038
- Stoker Coal Boiler: 1960 EFM520 installed in truck box
- Hand Fed Coal Stove: Crane 404 with variable blower
- Coal Size/Type: 404-nut, 520 rice ,anthracite for both
Good suggestion.freetown fred wrote: ↑Sun. Apr. 15, 2018 10:32 amC, you gotta post some pix of all that situation. Make for better factual suggestions rather then shootin in the dark.
If i am reading correctly,this black "soot" is in the water chamber area.If that is correct,it is likely just the settlement from minerals in the water,possibly combined with "boiler" treatment chemicals like anti-corrosion & leak sealer. My boiler had some of that too,some of which fell out when moving the boiler ,the rest of it was sucked out by shop vac & air nozzle blasts.
- StokerDon
- Site Moderator
- Posts: 7496
- Joined: Mon. Nov. 11, 2013 11:17 am
- Location: PA, Southern York County!
- Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
- Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
- Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
- Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood
There is no such thing as "soot" in an anthracite coal boiler. Usually the first order of business when acquiring an old coal boiler is a pressure test. This will tell you right away if you have a boiler or a boat anchor.
As far as the stuff inside goes, all kinds of junk as been found inside old boilers. It depends on if it was left open, weather it was used in a steam system and what kind of water was put in it. This thread is by far the most junk I ever heard of inside an old coal boiler.
Difference between a Keystoker KA6 and KFA
You will need to remove both return plugs and bushings and give the boiler a good flushing with hot water. Since you have the DHW coil out, you can get right in there with the hose or pressure washer. If you are real ambitious, you should remove the third return plug in the front of the boiler, It's easy for gunk to get trapped in that front section.
-Don
As far as the stuff inside goes, all kinds of junk as been found inside old boilers. It depends on if it was left open, weather it was used in a steam system and what kind of water was put in it. This thread is by far the most junk I ever heard of inside an old coal boiler.
Difference between a Keystoker KA6 and KFA
You will need to remove both return plugs and bushings and give the boiler a good flushing with hot water. Since you have the DHW coil out, you can get right in there with the hose or pressure washer. If you are real ambitious, you should remove the third return plug in the front of the boiler, It's easy for gunk to get trapped in that front section.
-Don
- McGiever
- Member
- Posts: 10130
- Joined: Sun. May. 02, 2010 11:26 pm
- Location: Junction of PA-OH-WV
- Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
- Hand Fed Coal Boiler: BUCKET A DAY water heater
- Hand Fed Coal Stove: Warm Morning 414A
- Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
- Other Heating: Ground Source Heat Pump and some Solar
Like SD said, if it passes a pressure test you have no issue. It is amazing that there is no orange color, someone took good care of that boiler.
- StokerDon
- Site Moderator
- Posts: 7496
- Joined: Mon. Nov. 11, 2013 11:17 am
- Location: PA, Southern York County!
- Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
- Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
- Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
- Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood
That boiler actually looks pretty good inside! Remove the return plugs and bushings and flush it out.
-Don
-Don
- McGiever
- Member
- Posts: 10130
- Joined: Sun. May. 02, 2010 11:26 pm
- Location: Junction of PA-OH-WV
- Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
- Hand Fed Coal Boiler: BUCKET A DAY water heater
- Hand Fed Coal Stove: Warm Morning 414A
- Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
- Other Heating: Ground Source Heat Pump and some Solar
Yes, I should of also mentioned, like SD did, now is your chance to give it a good wash and rinse.
How old is that boiler? I poked around and see it was stated prior that it was made in 1985.
How old is that boiler? I poked around and see it was stated prior that it was made in 1985.
Last edited by McGiever on Sun. Apr. 15, 2018 12:24 pm, edited 1 time in total.
- Rob R.
- Site Moderator
- Posts: 18004
- Joined: Fri. Dec. 28, 2007 4:26 pm
- Location: Chazy, NY
- Stoker Coal Boiler: EFM 520
- Hand Fed Coal Stove: Chubby Jr
A black coating is normal, and the boiler looks good to me. Rinse it out well and add a boiler treatment product when you put it in service.
http://hydronichappenings.blogspot.com/2011/10/wh ... k.html?m=1
http://hydronichappenings.blogspot.com/2011/10/wh ... k.html?m=1
-
- New Member
- Posts: 10
- Joined: Sun. Apr. 08, 2018 6:40 pm
- Stoker Coal Boiler: van wert av400
- Coal Size/Type: buckwheat
........phewwwwww!...........
Thanks guys! I will give it a good flush and pressure test it. I also thought of tearing it apart and clean all rings and "horn" of the stoker. I just thought it weird that I seen that in the water cap. This is an ongoing project that I hope to have done this summer for good reliable heat next winter and beyond.
Thanks Again, Very Much,
Chris
Thanks guys! I will give it a good flush and pressure test it. I also thought of tearing it apart and clean all rings and "horn" of the stoker. I just thought it weird that I seen that in the water cap. This is an ongoing project that I hope to have done this summer for good reliable heat next winter and beyond.
Thanks Again, Very Much,
Chris
- coaledsweat
- Site Moderator
- Posts: 13767
- Joined: Fri. Oct. 27, 2006 2:05 pm
- Location: Guilford, Connecticut
- Stoker Coal Boiler: Axeman Anderson 260M
- Coal Size/Type: Pea
When I bought my Axeman, it had been sitting for 27 years. The water drained from the pressure vessel was crystal clear. From the water coil, it was nasty and black. Nothing leaked but that was an ugly event watching it drain.
- Rob R.
- Site Moderator
- Posts: 18004
- Joined: Fri. Dec. 28, 2007 4:26 pm
- Location: Chazy, NY
- Stoker Coal Boiler: EFM 520
- Hand Fed Coal Stove: Chubby Jr
I think a lot of it depends on the system connected to the boiler. e.g. a large cast iron radiation system might produce more deposits than a copper baseboard, or the other way around.
My EFM had that black slimy layer as well.
My EFM had that black slimy layer as well.
- franpipeman
- Member
- Posts: 692
- Joined: Fri. Jan. 11, 2008 4:27 pm
- Location: Wernersville pa
- Stoker Coal Boiler: efm 520 stoker fitzgibbons pressure vessel
- Hand Fed Coal Stove: harman, russo
- Coal Size/Type: rice
- Other Heating: alpine propane condensing boiler radiant floor
Water in boiler is a science in itself . I wish I knew more about it . I asked a well known old timer water treatment guy i knew why does the water alway get black in boiler and chiller application or basically hydronics, and Was told Iron oxide particles. ? My current system is a efm 520 & stainless modulating condensing propane boiler , some black pipe and a lot of pex (radiant) and it is a clear liquid with a black hue to it . Likely due to the steel pipe and pressure vessels
I would flush a system made of 8 and 10 inch pipe till it was crystal clear and in two days it was Black again.
I would flush a system made of 8 and 10 inch pipe till it was crystal clear and in two days it was Black again.
- BunkerdCaddis
- Member
- Posts: 708
- Joined: Sun. Jan. 18, 2015 10:26 am
- Location: SW Lancaster County
- Stoker Coal Boiler: Bairmatic-Van Wert
- Hand Fed Coal Boiler: Van Wert VW85H
- Hand Fed Coal Stove: Saey Hanover II working when I feel the desire, Waterford 105 out on vacation, Surdiac Gotha hiding somewhere
- Coal Size/Type: pea/nut/rice/stove-anthracite, nut/stove bit when I feel the urge
- Other Heating: oil fired hydronic
Some one correct me if I am wrong but if I understand correctly the black deposit is what you get instead of rust, in a low oxygen steel/hydronic environment. In other words, the presence of a light dusting of black powder on the inside is a sign of a properly maintained boiler that did not have to have fresh water added very often.