I have a AA130 heating my house, Old farm house ,1850 sq ft to 71 degrees down stairs and 67 degrees up (8 rooms) and my garage 2800 sq ft to 55 down stairs and 62 up ( 25 ft x 56 ft up and down )My house is heated true hot water to air , I have a air handler on top of my oil burner ( made to burn LP ) the blower pushes air true the air handler and true the ducks to the rooms , my garage has a air handler that is heated with hot water after 150 ft of PEX under ground, and the one air handler blows the hot air ,in the down stairs and true heat greats in the floor to the up stairs My AA130 will use about 130lb of Buckwheat in 24 hr at 33 degrees out side , when it under 25 degrees it will use a little more (50 to 60 more lb )
Last edited by BigFoot on Wed. Mar. 07, 2018 3:41 pm, edited 1 time in total.


 
User avatar
hotblast1357
Member
Posts: 5657
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Wed. Mar. 07, 2018 3:31 pm

I’m heating 2500 sqft of new construction, terrible insulation and not sealed, to 72 degrees, eshland 260 is out in building with 80’ of buried pex, I burn 55 pounds in 24 hours with 30 degree temps. Including dhw.

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Wed. Mar. 07, 2018 4:18 pm

I don't believe an old farm house can be compared to new construction with 6" stud walls and modern insulation. That said, 130 lbs. to 190 lbs. per day is a lot of coal. Heating a 2,800 ft. garage to 55 degrees is my guess as to where the biggest part of the coal consumption is going. It may actually not be excessive, given the garage demand.

 
User avatar
hotblast1357
Member
Posts: 5657
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Wed. Mar. 07, 2018 5:24 pm

It doesn’t heat that easy..

Attachments


 
User avatar
hotblast1357
Member
Posts: 5657
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Wed. Mar. 07, 2018 5:26 pm

I wasn’t necessarily saying he was usin a LOT of coal compared to me, just telling him what I’m hearing with a the same boiler just bigger.

 
User avatar
BigFoot
Member
Posts: 137
Joined: Tue. Dec. 22, 2009 3:41 pm
Location: 102 Marchak Lane Greenfield PA
Stoker Coal Boiler: AA130
Coal Size/Type: PEA

Post by BigFoot » Wed. Mar. 07, 2018 6:22 pm

Thanks for your talk backs ,when its 36 and up my coal use is drop off to 45 ot 65 lb in a day , still better then oil that I was using before coal ,with just the house I was close to 1500 to 2000 gal a year that hurt my fix was coal and I'm glad I did it with a AA130 ,it heats the two places great ,last year 9 1/2 ton this year I'm at 81/2 now ant I keep it going all year to heat my water ! been heating with coal almost 10 years

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Wed. Mar. 07, 2018 7:04 pm

BigFoot wrote:
Wed. Mar. 07, 2018 3:03 pm
My AA130 will use about 130lb of Buckwheat in 24 hr at 33 degrees out side , when it under 25 degrees it will use a little more (50 to 60 more lb )
I'm think'in that is very reasonable coal consumption. 4650 sq ft is a lot of area to heat even if 2800 of it is only 55 degrees.

You would get a little more power out of the 130M if you switched to pea coal in the winter. Although the heat exchanger/air handler systems work well, there are some inefficiencies with them. One of them is, no radiant heat. It might be a good idea to get a couple radiators in there, if you have the time, money and space to put them.

-Don


 
User avatar
BigFoot
Member
Posts: 137
Joined: Tue. Dec. 22, 2009 3:41 pm
Location: 102 Marchak Lane Greenfield PA
Stoker Coal Boiler: AA130
Coal Size/Type: PEA

Post by BigFoot » Wed. Mar. 07, 2018 9:11 pm

Thanks for your input

 
User avatar
Rob R.
Site Moderator
Posts: 17980
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Wed. Mar. 07, 2018 10:27 pm

The AA130 is doing a great job. 1800 gallons of fuel is about the same as 9-10 tons worth of coal. Now you are heating your garage as well, and using less btu's than you used to for just the house.

With that said, I'm sure there are some simple things you can do to keep some heat in that place. Heating the outside is a tall order.

 
mdprincipal
New Member
Posts: 14
Joined: Sat. Mar. 17, 2018 7:30 pm
Stoker Coal Boiler: Keystoker Lite

Post by mdprincipal » Sat. Mar. 17, 2018 7:43 pm

Hi all,
I am very new to this forum- I don't even know how to post a question, but my worry is the same as what was asked in this web. I am currently burning wood upstairs because my Keystoker Lite runs constantly if I don't. When it runs, it is loud and keeps me awake. The cold air return comes from a tiny vent in my room. It really sounds like a jet taking off. The person who installed it gave it maintenance in the fall and said that it was tip-top. I have my doubts since I am burning wood to keep it from blowing all day and night. I tried to dial it in, but I am frustrated and am considering getting rid of it. I have a 1600 sq. ft. ranch, and from reading here, it should adequately heat my home, but it doesn't. I used a manometer to see what draft it was pulling, but I don't think I am using it correctly. Please let me know if I am out of my league with this thing. I really just want to go back to wood. Oh, I bought the house this year with the Keystoker already installed. Ugh, I hate it.

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sat. Mar. 17, 2018 8:23 pm

Welcome to the forum M.D.

The way to approach this properly is to start for you to start a new thread with your question as the subject.

A very good freind of mine thet has been an avid wood burner for 30+ years recently installed a Keystoker Koker Lite in his 2400 sq ft home. This was a few years ago and the unit has done a grate job of heating his entire house. so there is hope and we can get you there.

-Don

 
mdprincipal
New Member
Posts: 14
Joined: Sat. Mar. 17, 2018 7:30 pm
Stoker Coal Boiler: Keystoker Lite

Post by mdprincipal » Sat. Mar. 17, 2018 9:11 pm

Hi all,
I am very new to this forum- I don't even know how to post a question, but my worry is the same as what was asked in this web. I am currently burning wood upstairs because my Keystoker Lite runs constantly if I don't. When it runs, it is loud and keeps me awake. The cold air return comes from a tiny vent in my room. It really sounds like a jet taking off. The person who installed it gave it maintenance in the fall and said that it was tip-top. I have my doubts since I am burning wood to keep it from blowing all day and night. I tried to dial it in, but I am frustrated and am considering getting rid of it. I have a 1600 sq. ft. ranch, and from reading here, it should adequately heat my home, but it doesn't. I used a manometer to see what draft it was pulling, but I don't think I am using it correctly. Please let me know if I am out of my league with this thing. I really just want to go back to wood. Oh, I bought the house this year with the Keystoker already installed. Ugh, I hate it.

I am already at 3 tons of coal while burning wood at the same time. I truly am lost with this thing. Any help is appreciated.

 
User avatar
freetown fred
Member
Posts: 30293
Joined: Thu. Dec. 31, 2009 12:33 pm
Location: Freetown,NY 13803
Hand Fed Coal Stove: HITZER 50-93
Coal Size/Type: BLASCHAK Nut

Post by freetown fred » Sat. Mar. 17, 2018 9:40 pm

Be patient M, the Keystoker guys will get ya where you need to be. :)

 
User avatar
oliver power
Member
Posts: 2970
Joined: Sun. Apr. 16, 2006 9:28 am
Location: Near Dansville, NY
Stoker Coal Boiler: KEYSTOKER Kaa-2
Hand Fed Coal Stove: Hitzer 50-93 & 30-95, Vigilant (pre-2310), D.S. 1600 Circulator, Hitzer 254

Post by oliver power » Sun. Apr. 01, 2018 2:11 am

Hi mdprincipal,

As StokerDon said, Start a new post of your own. This way all attention would be directed towards YOUR situation.

Some pictures of your set up would also be very helpful. Sounds like you may have restricted air flow problems.

 
User avatar
Rob R.
Site Moderator
Posts: 17980
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Sun. Apr. 01, 2018 8:21 am

oliver power wrote:
Sun. Apr. 01, 2018 2:11 am
Hi mdprincipal,

As StokerDon said, Start a new post of your own. This way all attention would be directed towards YOUR situation.

Some pictures of your set up would also be very helpful. Sounds like you may have restricted air flow problems.
They did start a new post. Pretty much ended up with giving up on the stove altogether.