AA 130 M Restoration and Installation

 
User avatar
coaledsweat
Site Moderator
Posts: 13763
Joined: Fri. Oct. 27, 2006 2:05 pm
Location: Guilford, Connecticut
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea

Post by coaledsweat » Fri. Mar. 16, 2018 3:40 pm

Usually 4-8 hours on a pressure test. Charge it and shut the valve, if the pressure doesn't drop in 8 hours you're good.

Axeman recommends aluminum paint, reduces heat radiation is the idea I believe.

Do not, under any circumstances, remove the blower wheel from the shaft. It is a balanced assembly. Note the position of any other items on the shaft and make sure they get replaced exactly as they were.


 
User avatar
Lightning
Site Moderator
Posts: 14659
Joined: Wed. Nov. 16, 2011 9:51 am
Location: Olean, NY
Stoker Coal Boiler: Modified AA 130
Coal Size/Type: Pea Size - Anthracite

Post by Lightning » Fri. Mar. 16, 2018 5:03 pm

coaledsweat wrote:
Fri. Mar. 16, 2018 3:40 pm
Do not, under any circumstances, remove the blower wheel from the shaft. It is a balanced assembly. Note the position of any other items on the shaft and make sure they get replaced exactly as they were.
Right, I saw something about that on another thread somewhere, thanks for the reinforcement. So the way it appears to me, the fan and shaft don't touch anything once thru the fan housing? There is no bearings past that wall, instead it's all suspended from the box out front that the shaft runs thru?
Last edited by Lightning on Fri. Mar. 16, 2018 5:08 pm, edited 1 time in total.

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Fri. Mar. 16, 2018 5:17 pm

Lightning wrote:
Fri. Mar. 16, 2018 5:03 pm
... So the way it appears to me, the fan and shaft don't touch anything once thru the fan housing? There is no bearings past that wall, instead it's all suspended from the box out front that the shaft runs thru?
Correct.

 
User avatar
coaledsweat
Site Moderator
Posts: 13763
Joined: Fri. Oct. 27, 2006 2:05 pm
Location: Guilford, Connecticut
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea

Post by coaledsweat » Fri. Mar. 16, 2018 5:59 pm

No bearing would last in that heat. The 260M actually has a finned disc on the shaft behind the big plate. It's sole function is to keep the heat from travelling down the shaft to the bushing box. Not sure if it is on the 130M.

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Fri. Mar. 16, 2018 9:18 pm

Lightning wrote:
Fri. Mar. 16, 2018 1:50 pm
Then candy cane stripe the auger.
Coaledsweat will absolutely love that! :lol:

-Don

 
User avatar
Lightning
Site Moderator
Posts: 14659
Joined: Wed. Nov. 16, 2011 9:51 am
Location: Olean, NY
Stoker Coal Boiler: Modified AA 130
Coal Size/Type: Pea Size - Anthracite

Post by Lightning » Sun. Mar. 18, 2018 6:46 pm

I spent a few hours on the AA today...

Pulled out the ash grate.
20180318_164802.jpg
.JPG | 393.7KB | 20180318_164802.jpg

Bottom of the burn chamber.
20180318_164904.jpg
.JPG | 394.9KB | 20180318_164904.jpg

Two of the four ash grate rollers are frozen. The fly ash cyclone was clogged with ash, I cleaned it out.
20180318_164911_001.jpg
.JPG | 339.6KB | 20180318_164911_001.jpg

Here's the cyclonic flue gas heat exchanger. Yeah she looks rough but nothin some spit and shine can't fix!
20180318_165102.jpg
.JPG | 547.6KB | 20180318_165102.jpg

I broke the two bolts hold this bracket to the fan housing. I'll need to grind off the nuts and weld on new ones. The bolts were pretty weak, it didn't take much to snap them off.
20180318_165016.jpg
.JPG | 321.7KB | 20180318_165016.jpg

Question. What is the best way to get this fan plate out from between that box and the fan blades?
20180318_171603.jpg
.JPG | 414.2KB | 20180318_171603.jpg

 
User avatar
windyhill4.2
Member
Posts: 6072
Joined: Fri. Nov. 22, 2013 2:17 pm
Location: Jonestown,Pa.17038
Stoker Coal Boiler: 1960 EFM520 installed in truck box
Hand Fed Coal Stove: Crane 404 with variable blower
Coal Size/Type: 404-nut, 520 rice ,anthracite for both

Post by windyhill4.2 » Sun. Mar. 18, 2018 7:14 pm

coaledsweat wrote:
Thu. Mar. 15, 2018 9:05 pm
Use something that is non hardening.
I just read the info for Blue Monster dope... it is non-hardening. :yes:


 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sun. Mar. 18, 2018 7:16 pm

Lightning wrote:
Sun. Mar. 18, 2018 6:46 pm
I broke the two bolts hold this bracket to the fan housing. I'll need to grind off the nuts and weld on new ones. The bolts were pretty weak, it didn't take much to snap them off.
Remeber, that bracket is just for shipping. Don't leave it on there after you install the boiler.
Lightning wrote:
Sun. Mar. 18, 2018 6:46 pm
Question. What is the best way to get this fan plate out from between that box and the fan blades?
I would pull the fan off. Make sure you make alignment marks on the fan and the shaft before you remove it.

-Don

 
User avatar
Lightning
Site Moderator
Posts: 14659
Joined: Wed. Nov. 16, 2011 9:51 am
Location: Olean, NY
Stoker Coal Boiler: Modified AA 130
Coal Size/Type: Pea Size - Anthracite

Post by Lightning » Sun. Mar. 18, 2018 7:27 pm

StokerDon wrote:
Sun. Mar. 18, 2018 7:16 pm
would pull the fan off. Make sure you make alignment marks on the fan and the shaft before you remove it.
I tried that. Do these two bolts thread into the blocks that are clamped around the shaft? I was able to remove the nuts but couldn't get any further.
20180318_164556.jpg
.JPG | 327.4KB | 20180318_164556.jpg

 
User avatar
hotblast1357
Member
Posts: 5657
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Sun. Mar. 18, 2018 7:29 pm

The AA doesn’t have any of the tubes inside the cyclone?

Attachments


 
User avatar
Lightning
Site Moderator
Posts: 14659
Joined: Wed. Nov. 16, 2011 9:51 am
Location: Olean, NY
Stoker Coal Boiler: Modified AA 130
Coal Size/Type: Pea Size - Anthracite

Post by Lightning » Sun. Mar. 18, 2018 7:34 pm

That bracket goes here. It's not needed? I don't believe it lol.

Attachments

20180318_193047.jpg
.JPG | 77.1KB | 20180318_193047.jpg

 
User avatar
Lightning
Site Moderator
Posts: 14659
Joined: Wed. Nov. 16, 2011 9:51 am
Location: Olean, NY
Stoker Coal Boiler: Modified AA 130
Coal Size/Type: Pea Size - Anthracite

Post by Lightning » Sun. Mar. 18, 2018 7:35 pm

hotblast1357 wrote:
Sun. Mar. 18, 2018 7:29 pm
The AA doesn’t have any of the tubes inside the cyclone?
No, I didn't see anything like that in there.

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Sun. Mar. 18, 2018 7:41 pm

No to both...Bracket for transport only...fan needs to be free and only supported off rubber foot on floor and the horizontal flat iron brace half way up. Fan pretty much "floats" through the plate hole.

No, AA has ever had those AHS/Eshland "gizzys" in the center tube.
Last edited by McGiever on Sun. Mar. 18, 2018 8:40 pm, edited 1 time in total.

 
User avatar
Lightning
Site Moderator
Posts: 14659
Joined: Wed. Nov. 16, 2011 9:51 am
Location: Olean, NY
Stoker Coal Boiler: Modified AA 130
Coal Size/Type: Pea Size - Anthracite

Post by Lightning » Sun. Mar. 18, 2018 7:48 pm

Well I'll be dammed lol

Attachments

20180318_194538.jpg
.JPG | 204.3KB | 20180318_194538.jpg
20180318_194520.jpg
.JPG | 225.1KB | 20180318_194520.jpg

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sun. Mar. 18, 2018 7:59 pm

Lightning wrote:
Sun. Mar. 18, 2018 7:27 pm
I tried that. Do these two bolts thread into the blocks that are clamped around the shaft? I was able to remove the nuts but couldn't get any further.
20180318_164556.jpg
That sure looks like a clamp. Maybe the blocks are threaded too. I don't know you are ahead of me, I haven't even pulled the fan plate on mine.

I saw this fan removal topic discussed before, and I am pretty sure it was McGiever's fan that needed to be removed. I did a quick search for the thread and couldn't find it.

-Don