Immersion Well Top of Boiler Supply

Post Reply
 
User avatar
skobydog
Member
Posts: 275
Joined: Mon. Jun. 10, 2013 9:53 am
Location: Greenfield MA
Hand Fed Coal Stove: Hitzer 50-93
Coal Size/Type: Nut Anthracite

Post by skobydog » Fri. Feb. 16, 2018 3:46 pm

Is it acceptable to add an immersion well into supply line on boiler?

I don't have anywhere to put one. I have the tee that comes out of the top of the boiler that could work, I just haven't seen it done like this anywhere. I just want to a well for a hi limit cut off.

20180216_153919.jpg
.JPG | 110.8KB | 20180216_153919.jpg
20180216_153952.jpg
.JPG | 132.4KB | 20180216_153952.jpg

 
User avatar
nepacoal
Member
Posts: 1696
Joined: Wed. Nov. 21, 2012 7:49 am
Location: Coal Country
Stoker Coal Boiler: Keystoker KAA-4 / "Kelly" and an EFM 520 at my in-laws
Hand Fed Coal Boiler: Harman SF-260 - retired
Coal Size/Type: Buck

Post by nepacoal » Fri. Feb. 16, 2018 3:57 pm

The Keystoker boiler manual shows the 4006b being installed in a tee off of the supply pipe...

 
User avatar
skobydog
Member
Posts: 275
Joined: Mon. Jun. 10, 2013 9:53 am
Location: Greenfield MA
Hand Fed Coal Stove: Hitzer 50-93
Coal Size/Type: Nut Anthracite

Post by skobydog » Fri. Feb. 16, 2018 4:10 pm

nepacoal wrote:
Fri. Feb. 16, 2018 3:57 pm
The Keystoker boiler manual shows the 4006b being installed in a tee off of the supply pipe...
There it is :) thanks
tee.jpg
.JPG | 18.4KB | tee.jpg


 
waldo lemieux
Member
Posts: 2270
Joined: Sun. Sep. 30, 2012 8:20 pm
Location: Ithaca,NY

Post by waldo lemieux » Fri. Feb. 16, 2018 5:27 pm

That should work just fine. I dont think it will obstruct flow .... or trap air.... hmmmm

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Fri. Feb. 16, 2018 7:21 pm

The supply pipe right on top of the boiler is actually a good place to put a high limit aquastat. There it will see the hottest water temperature. That Tee you are referring to is actually in the bypass loop. It should still work fine as long as you keep the bypass valve open.

It's important to remember that different parts of the boiler are at different temperatures. On this one, the triple aquastat well is on the side that the return water comes into. This is where it will see some of the cold water returning into the boiler giving the stoker a head start on a heat call.

-Don

 
franco b
Site Moderator
Posts: 11416
Joined: Wed. Nov. 05, 2008 5:11 pm
Location: Kent CT
Hand Fed Coal Stove: V ermont Castings 2310, Franco Belge 262
Baseburners & Antiques: Glenwood Modern Oak 114
Coal Size/Type: nut and pea

Post by franco b » Fri. Feb. 16, 2018 9:58 pm

The aquastat in the manual is a B, which is a reverse aquastat.


 
User avatar
skobydog
Member
Posts: 275
Joined: Mon. Jun. 10, 2013 9:53 am
Location: Greenfield MA
Hand Fed Coal Stove: Hitzer 50-93
Coal Size/Type: Nut Anthracite

Post by skobydog » Fri. Feb. 16, 2018 11:06 pm

Thanks everyone.

I actually came across some surface mount temp controllers that were inexpensive so I'm going to use those. I bought two because they can be wired for either make or break on rise. I'll use one for high limit and the other to shut the boiler down if I ever have an outfire/timer issue. :)

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Sat. Feb. 17, 2018 5:46 am

I didn't have any unused tappings, so that is where I placed my LWCO unit.

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Sat. Feb. 17, 2018 7:58 pm

skobydog wrote:
Fri. Feb. 16, 2018 11:06 pm
Thanks everyone.

I actually came across some surface mount temp controllers that were inexpensive so I'm going to use those. I bought two because they can be wired for either make or break on rise. I'll use one for high limit and the other to shut the boiler down if I ever have an outfire/timer issue. :)
What will be the differential? fixed or adjustable?

Don't know where you will place these at...

Timers can fail a couple different ways...steady off or steady on.

Are you okay w/ cooling back down after after a HH/L shut down and back to running again? Or will you series both together to prevent this?

For a timer issue and both switchs not wired in series, it is best to have a "manual reset" with the controller or it will resume pushing coal on it's own again after cooling down. I guess if you were sensing flue pipe temps for out-fire no manual reset is needed on a cold flue.

Out-fire controller will need to be temporarily bypassed in order to start from a cold boiler too.