Post by StokerDon » Thu. May. 24, 2018 8:55 pm

coaledsweat wrote:
Thu. May. 24, 2018 8:42 pm
The risk of puffback will increase with the feedrate increase.
Humm,,,,

Your probably right.

-Don


 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Thu. May. 24, 2018 9:39 pm

*SD*, What are your fan pulley sizes?

 
User avatar
StokerDon
Site Moderator
Posts: 7496
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sat. May. 26, 2018 7:51 pm

McGiever wrote:
Thu. May. 24, 2018 9:39 pm
*SD*, What are your fan pulley sizes?
StokerDon wrote:
Thu. May. 24, 2018 8:53 pm
For the record, this 130M had a 3.5" pulley on the motor and a 3" on the gearbox before I changed the motor and the pulleys. This was very likely the original factory set because this unit is relatively new, 1991. I guess at some point during the production life they felt the need to speed the auger up a little.

This unit is currently running the opposite pulley set up, 3" on the motor and 3.5" on the gearbox. This makes the auger and ashing a bit slower than normal.
-Don

 
User avatar
StokerDon
Site Moderator
Posts: 7496
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sat. May. 26, 2018 8:07 pm

Well, I figured out where all the fly ash is coming from and it ain't from puff-backs!
IMG_2643.JPG
.JPG | 326.5KB | IMG_2643.JPG
IMG_2644.JPG
.JPG | 322.9KB | IMG_2644.JPG
IMG_2645.JPG
.JPG | 318.3KB | IMG_2645.JPG
IMG_2651.JPG
.JPG | 338.9KB | IMG_2651.JPG
It turns out that the gasket between the fan plate and the boiler has failed. This allows fly ash and some combustion gas to push out while the fan is running.
IMG_2648.JPG
.JPG | 323.4KB | IMG_2648.JPG
IMG_2649.JPG
.JPG | 424.9KB | IMG_2649.JPG
IMG_2650.JPG
.JPG | 375.3KB | IMG_2650.JPG
We're gonna run whats left in the barrel and doghouse, then shut it down.
IMG_2653.JPG
.JPG | 398.4KB | IMG_2653.JPG
I guess if ya get 27 years out of a fan plate gasket it's a pretty good gasket!

I have not decided if we are going to fix it and re-fire it, or just take it completely apart and start the re-furb now. I can always just re-lite the Van Wert, or I could be really lazy and fire up the electric water heater.

-Don

 
User avatar
coaledsweat
Site Moderator
Posts: 13767
Joined: Fri. Oct. 27, 2006 2:05 pm
Location: Guilford, Connecticut
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea

Post by coaledsweat » Sat. May. 26, 2018 8:54 pm

Oh yeah! When that gasket goes, instant dust storm.

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Sat. May. 26, 2018 11:27 pm

*SD*, What are your fan pulley sizes?

No, NOT the gearbox...THE FAN. ;)


BTW: That Puff Back that launched your baro flapper door musta been a good one...it blew out that gasket too. :P

 
User avatar
StokerDon
Site Moderator
Posts: 7496
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sun. May. 27, 2018 9:18 am

McGiever wrote:
Sat. May. 26, 2018 11:27 pm
*SD*, What are your fan pulley sizes?
5" on the motor and 3" on the fan. That comes out to 2875 RPM for the fan.
McGiever wrote:
Sat. May. 26, 2018 11:27 pm
BTW: That Puff Back that launched your baro flapper door musta been a good one...it blew out that gasket too. :P
Good catch! The dust storm started right after the baro blew off. I guess this means puff-backs can blow gaskets out as well as stove pipe parts.

-Don


 
User avatar
StokerDon
Site Moderator
Posts: 7496
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sun. May. 27, 2018 7:38 pm

Well so much for being lazy or fire'in up the Van Wert!

I shut it off this morning, then I cut the fan plate bolts off with the grinder.
IMG_2654.JPG
.JPG | 347.7KB | IMG_2654.JPG
IMG_2655.JPG
.JPG | 368KB | IMG_2655.JPG
I removed the belts, then I removed the four bolts that hold the bearing housing on. This allowed me to take the bearing housing, fan plate and fan off in one piece.
IMG_2667.JPG
.JPG | 246.5KB | IMG_2667.JPG
The gasket came off in a lot of pieces. You can now see where the oil got fried onto it during the first fire up.
IMG_2666.JPG
.JPG | 455.2KB | IMG_2666.JPG
I spent some time with the wire wheel to clean up the fan plate. Then I mounted the whole thing to some wood. Then painted the fan plate.
IMG_2668.JPG
.JPG | 386.9KB | IMG_2668.JPG
IMG_2669.JPG
.JPG | 409.9KB | IMG_2669.JPG
IMG_2670.JPG
.JPG | 515.9KB | IMG_2670.JPG
IMG_2672.JPG
.JPG | 414.8KB | IMG_2672.JPG
I put some flat stove gasket on with HI Temp silicone.
IMG_2673.JPG
.JPG | 355.3KB | IMG_2673.JPG
IMG_2674.JPG
.JPG | 317.6KB | IMG_2674.JPG
Time to put it back together and fire it up!
IMG_2675.JPG
.JPG | 376.4KB | IMG_2675.JPG
IMG_2676.JPG
.JPG | 362.7KB | IMG_2676.JPG
I didn't hold the fire during this process so I torched up some charcoal.
IMG_2677.JPG
.JPG | 381.3KB | IMG_2677.JPG
I cleaned up the mess and put the fire view door back on.
IMG_2678.JPG
.JPG | 219.4KB | IMG_2678.JPG
IMG_2679.JPG
.JPG | 177.4KB | IMG_2679.JPG
IMG_2680.JPG
.JPG | 227.2KB | IMG_2680.JPG
I jumped in the bin and filled the barrel with leftover Pea coal. I also filled 8 buckets. There is a barrel or two still left in the bin so we will probably make it till July with what is left!.
IMG_2681.JPG
.JPG | 325KB | IMG_2681.JPG
IMG_2682.JPG
.JPG | 342.5KB | IMG_2682.JPG
We should be good to go for 1.5 to 2 weeks on this fill up.

-Don

 
User avatar
StokerDon
Site Moderator
Posts: 7496
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sun. Jun. 10, 2018 9:22 am

Yesterday it was time to fill the barrel again. It's been 13 days since the last fill with 20.6 hours of run time.

For the passed week the Van Wert in the basement has been heating the DHW. The Axeman has just been sitting here keeping itself and the loop to the basement warm.

Pretty amazing, it just sits here keeping itself warm for a week with no timer in Summer temperatures.
IMG_2692.JPG
.JPG | 366.6KB | IMG_2692.JPG
IMG_2693.JPG
.JPG | 398.7KB | IMG_2693.JPG
It took most of what was left in the bin to fill the barrel.
IMG_2695.JPG
.JPG | 405KB | IMG_2695.JPG
We still have this little bit and 8 buckets left.
IMG_2697.JPG
.JPG | 342.5KB | IMG_2697.JPG
IMG_2698.JPG
.JPG | 371.5KB | IMG_2698.JPG
I reset the clock and we're ready to run for another week or two.
IMG_2694.JPG
.JPG | 347.6KB | IMG_2694.JPG
We will shut down the Van Wert today and valve in the Axeman for DHW duty. Also, since we are back on Pea coal we will try letting the aquastat control the pump.

We have been running constant circulation to get more consistent stoker run times to avoid puff-backs. We have not had a puff-back since switching back to Pea coal.

-Don

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Sun. Jun. 10, 2018 9:24 am

Don, do you have sufficient data yet by which to declare which of these boilers is running more efficiently?

 
User avatar
StokerDon
Site Moderator
Posts: 7496
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sun. Jun. 10, 2018 9:34 am

Not yet. We can do a comparison of coal consumption between the Axeman and the Van Wert on DHW only next week.

It might not be a fair comparison though. The remote garage set-up here has always used more coal than the boiler in the basement. Summer or Winter the basement boiler has historically used less coal. I'm not 100% sure why.

-Don

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Sun. Jun. 10, 2018 10:21 am

My guess: Heat radiated to the basement contributes to home heat, and heat radiated to the garage does not. That plus a first guess that your home is insulated better overall than your garage.

 
User avatar
StokerDon
Site Moderator
Posts: 7496
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sun. Jun. 10, 2018 10:42 am

That is all true, but insulation (house and boiler) doesn't explain why this continues in Summer.

-Don

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Sun. Jun. 10, 2018 11:17 am

Good point! But even in the summer, if the garage is colder than the basement then the garages radiant heat loss will cause the boiler to fire more often and burn more coal.

 
User avatar
StokerDon
Site Moderator
Posts: 7496
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sun. Jun. 10, 2018 12:39 pm

lsayre wrote:
Sun. Jun. 10, 2018 11:17 am
Good point! But even in the summer, if the garage is colder than the basement then the garages radiant heat loss will cause the boiler to fire more often and burn more coal.
In Summer, with no boiler fired, the basement is typically between 64 and 68 degrees.

In Summer, with no boiler fired, the garage is typically between 80 and 95 degrees.
The sun beating on the roof of the garage all day drives the temperature up because there is no insulation in the ceiling.

We have had insulated boilers in the garage and the basement. The basement boilers have always gotten better fuel mileage than the garage boilers regardless of weather or not they were insulated. All this is leading me to consider the piping resistance between the garage and basement as a possibility. Piping is 1" insulated PEX but there are a lot of crimp connections at both ends. The crimp connections are 3/4" ID.

-Don