Post by McGiever » Sun. Jul. 08, 2018 4:34 pm

Split returns are a nice touch. :yes:

If they are unbalanced a well positioned valve can tweak the side with less resistance to overcome the unbalance...but that's getting pretty fancy. ;)


 
lzaharis
Member
Posts: 2366
Joined: Sun. Mar. 25, 2007 8:41 pm
Location: Ithaca, New York
Stoker Coal Boiler: Keystoker KAA-4-1 dual fuel boiler
Hand Fed Coal Boiler: former switzer CWW100-sold
Coal Size/Type: rice
Other Heating: kerosene for dual fuel Keystoker/unused

Post by lzaharis » Sun. Jul. 08, 2018 11:50 pm

I closed the 2 ball valves half way on the return to sump lines before the common sump line header to slow the hot water down from the single B+G NRF25 last year and it worked pretty well moving 12 GPM using one speed one.
I still wish I had long low cast iron radiators in the house though.
But as my dear mother in law was so fond of saying "if wishes were horses you would have a stable full.

I cleaned up enough after horses and calves so...................

 
coalnewbie
Member
Posts: 8601
Joined: Sat. May. 24, 2008 4:26 pm
Location: Chester, NY
Hot Air Coal Stoker Stove: LL AnthraKing 180K, Pocono110K,KStokr 90K, DVC
Hand Fed Coal Stove: Invader 2
Baseburners & Antiques: Wings Best, Glenwood #8(x2) Herald 116x
Coal Size/Type: Rice,
Other Heating: Heating Oil CH, Toyotomi OM 22

Post by coalnewbie » Mon. Jul. 09, 2018 8:41 am

I cleaned up enough after horses and calves so...................
and there is nothing wrong with that ...

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Mon. Jul. 09, 2018 9:02 pm

COAL!!!!

5 ton worth!
IMG_2896.JPG
.JPG | 416.5KB | IMG_2896.JPG
IMG_2897.JPG
.JPG | 406.8KB | IMG_2897.JPG
The view through the coal port.
IMG_2901.JPG
.JPG | 445.4KB | IMG_2901.JPG
IMG_2902.JPG
.JPG | 344.6KB | IMG_2902.JPG
Still a bit of room in there. We should have got another half ton.

I built a brace between the wall and the doghouse to keep the inrush of coal from breaking the doghouse off the bin.
IMG_2889.JPG
.JPG | 323.2KB | IMG_2889.JPG
IMG_2893.JPG
.JPG | 308.8KB | IMG_2893.JPG
I turned it on for a minute just to see if the auger ran OK. No problems found.
IMG_2903.JPG
.JPG | 364.6KB | IMG_2903.JPG
IMG_2895.JPG
.JPG | 396KB | IMG_2895.JPG
-Don

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Tue. Jul. 24, 2018 8:52 pm

Well, the re-plumbing has been going very slow. I originally wanted to unhook the boiler, move it and reconnect everything over one weekend. It's been 3 weeks now. Since this has taken so long I have decided to pull the boiler, clean it up and paint it.

Then, I decided to remove the base to clean and paint that. This won't be a real re-furb but it will look much better than it does now.
First I removed the wiring and electrical components. The motor is still there.
IMG_2921.JPG
.JPG | 365.8KB | IMG_2921.JPG
IMG_2922.JPG
.JPG | 360.5KB | IMG_2922.JPG
I only had to disconnect the motor, Anthrastat and pump. Everything else is still wired in, just removed.
IMG_2923.JPG
.JPG | 404.3KB | IMG_2923.JPG
Here's what the Anthrastat looks like inside.
IMG_2924.JPG
.JPG | 366.6KB | IMG_2924.JPG
IMG_2925.JPG
.JPG | 359.1KB | IMG_2925.JPG
IMG_2926.JPG
.JPG | 373.1KB | IMG_2926.JPG
Looks like the Van Wert will be doing DHW duty for a while longer.

-Don

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sat. Jul. 28, 2018 8:30 am

Yesterday, I disconnected the auger and suspended it from the bin with some tie down straps.
IMG_2928.JPG
.JPG | 400.1KB | IMG_2928.JPG
Then removed the boiler from the base.
IMG_2929.JPG
.JPG | 363.6KB | IMG_2929.JPG
IMG_2932.JPG
.JPG | 348.1KB | IMG_2932.JPG
I need to do a little repair work on the base. The bolts that hold things onto the base are threaded into the base. This puts the threads in the ash pit area causing them to rust badly. The 4 bolts that hold the boiler to the base just broke off when I removed them. Time for some drilling and tapping!
IMG_2933.JPG
.JPG | 351.6KB | IMG_2933.JPG
IMG_2931.JPG
.JPG | 350.8KB | IMG_2931.JPG
We are going to pull the DHW coil again. On the last bolt snug down, one of the studs started moving. I was pretty sure it was broken so I didn't tighten it any more.
IMG_2936.JPG
.JPG | 334.6KB | IMG_2936.JPG
Today will be drilling, tapping and cleaning.
IMG_2930.JPG
.JPG | 312.4KB | IMG_2930.JPG
IMG_2934.JPG
.JPG | 355.4KB | IMG_2934.JPG
IMG_2935.JPG
.JPG | 355.7KB | IMG_2935.JPG
-Don

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sat. Jul. 28, 2018 1:28 pm

After pulling the coil and wire brushing the crud off of the studs, it's pretty obvious whats wrong with this stud!
IMG_2938.JPG
.JPG | 207.8KB | IMG_2938.JPG
IMG_2939.JPG
.JPG | 255KB | IMG_2939.JPG
Then I took a look at all the other studs...

Hummm,,, A couple of those are very questionable too!
IMG_2942.JPG
.JPG | 371KB | IMG_2942.JPG
IMG_2943.JPG
.JPG | 290.8KB | IMG_2943.JPG
Well, now what???

Here we are again in the same old coal boiler dilemma, repair the studs? Or, just cut them off and weld a plate over the whole thing?

This time I'm leaning toward welding a plate over it. I was thinking of using the DHW coil for garage hot water, but we can do the same thing with a plate heat exchanger. Plating it over will also ensure that the boiler can't be damaged by a leaking gasket.

-Don


 
User avatar
Rob R.
Site Moderator
Posts: 17980
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Sat. Jul. 28, 2018 1:38 pm

Personal preference, but I would weld a plate over it and be done with it.

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sat. Jul. 28, 2018 1:54 pm

Rob R. wrote:
Sat. Jul. 28, 2018 1:38 pm
Personal preference, but I would weld a plate over it and be done with it.
I'll have to give my favorite welder a call, see if he is still alive and willing to weld an old coal boiler. I still have the second Van Wert VA-600 that needs a plate welded on too.

-Don

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Sat. Jul. 28, 2018 10:25 pm

Seven years and counting, zero drama for me...
DSCF2027.JPG

Good piece of plate steel

.JPG | 376KB | DSCF2027.JPG
BoilerMate.JPG

Amtrol BoilerMate
Used, but near mint off Craig'sList for cheap

.JPG | 279.4KB | BoilerMate.JPG

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sat. Jul. 28, 2018 10:37 pm

Well, Scrapper is still alive! It's been a long time since I talked to him.

Here's look at one of the ware areas of an Axeman Anderson. The outer edge of the swirl chamber is constantly pelted with ash flung at it by the fan. On this one there is only a slight bit of ware.
IMG_2944.JPG
.JPG | 265.4KB | IMG_2944.JPG
IMG_2945.JPG
.JPG | 312.6KB | IMG_2945.JPG
This boiler is go'in for a ride tomorrow so I loaded it into the truck.
IMG_2946.JPG
.JPG | 349.8KB | IMG_2946.JPG
I screwed a couple 2x4's together and attached them to the bottom of the boiler. This will protect the cone at the bottom of the cyclone separator.
IMG_2947.JPG
.JPG | 361.4KB | IMG_2947.JPG
IMG_2949.JPG
.JPG | 300.4KB | IMG_2949.JPG
All ready to go!
IMG_2953.JPG
.JPG | 373.6KB | IMG_2953.JPG
-Don

 
User avatar
Rob R.
Site Moderator
Posts: 17980
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Sat. Jul. 28, 2018 10:43 pm

Nice job on the rigging. Scrapper will patch that thing up and you will never have to worry about it again.

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sat. Jul. 28, 2018 11:28 pm

McGiever wrote:
Sat. Jul. 28, 2018 10:25 pm
Seven years and counting, zero drama for me...
DSCF2027.JPGBoilerMate.JPG
Same deal for me, I've been running a BoilerMate for 4 years now. I bought it off of CL real cheap too! Works great.

-Don

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sat. Aug. 18, 2018 8:03 pm

Got the boiler back today!!!
IMG_2992.JPG
.JPG | 330.2KB | IMG_2992.JPG
That is a pretty sight!
IMG_2993.JPG
.JPG | 321KB | IMG_2993.JPG
And it will never leak again.
IMG_2994.JPG
.JPG | 358.8KB | IMG_2994.JPG
Scrapper even pressure tested it to 50 PSI.

Now it's all ready to be cleaned up and painted.

-Don

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Sat. Aug. 18, 2018 8:51 pm

Nice! It won't leak now. Did you find a BoilerMate or similar HWT?