Post by lincolnmania » Wed. Jan. 17, 2018 9:52 pm

no flyash out of my baro don. i have a power vent on my reading stoker.


 
User avatar
swyman
Member
Posts: 2355
Joined: Mon. Apr. 13, 2015 9:50 pm
Location: Blissfield, MI
Stoker Coal Boiler: Axeman-Anderson 260M Leisure Line AA-220 Boiler (FOR SALE)
Coal Size/Type: Lehigh Pea

Post by swyman » Thu. Jan. 18, 2018 6:38 am

StokerDon wrote:
Wed. Jan. 17, 2018 6:59 pm
Thanks!

I sorry to say I don't know much about power vents, but I also don't understand your question about fly ash. Do you have fly ash coming out your baro?
My baro is at the base of the chimney on this one because I had to put it in the 8" part of the stove pipe. It's a 7" baro. The rest of the pipe is 5".

-Don
No fly ash coming out the baro but I do get some coming out the PV. Just thinking if moving baro locations would have an effect (reduce) my flay ash. My theory is this, I have my baro located right off the Tee on the boiler breech. The baro is set at -.04" but usually I set the rheostat on the power vent so it is pulling a little more than that so the baro gate is bouncing a bit.....it can fluctuate a little bit so I would rather have a little extra draft than not enough for safety reasons. So I would think that if I'm pulling in extra air through the baro gate, the velocity has to be greater down stream of the baro? Which if that was the case could accelerate the fly ash through the stove pipe? Am I over thinking this stuff?

 
Olllotj
Member
Posts: 558
Joined: Thu. Sep. 04, 2014 10:01 am
Location: Western NY 14141
Stoker Coal Boiler: Keystoker KB-8
Coal Size/Type: Buckwheat
Other Heating: Utica Propane Hot Water

Post by Olllotj » Thu. Jan. 18, 2018 7:31 am

Yes you are overthinking it.

The Baro will steady everything downstream either way, and the flyash is just a coal burning by product.

 
User avatar
hotblast1357
Member
Posts: 5657
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Thu. Jan. 18, 2018 8:21 am

Always going to have flyash, hook a leaf blower to the stove pipe to blow out fly ash if it’s to much of a pain lol

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Thu. Jan. 18, 2018 6:33 pm

swyman wrote:
Thu. Jan. 18, 2018 6:38 am
No fly ash coming out the baro but I do get some coming out the PV. Just thinking if moving baro locations would have an effect (reduce) my flay ash.
Not a chance. Fly ash is produced by burning coal, the location of the baro has nothing to do with it.
swyman wrote:
Thu. Jan. 18, 2018 6:38 am
So I would think that if I'm pulling in extra air through the baro gate, the velocity has to be greater down stream of the baro? Which if that was the case could accelerate the fly ash through the stove pipe? Am I over thinking this stuff?
Your not over thinking at all, your just thinking about the wrong thing. Like I said earlier, I don't know much about power vents but in my opinion, you should be thinking about putting up a masonry chimney. That way you wouldn't have to deal with the pain and suffering of this power vent thing.

With a masonry chimney, stoker at idle, the draft is very small. At full fire, the draft increases and the baro keeps it from pulling to much heat out of the boiler. It sounds like a power vent pulls heat out of the boiler constantly at idle.

-Don

 
User avatar
swyman
Member
Posts: 2355
Joined: Mon. Apr. 13, 2015 9:50 pm
Location: Blissfield, MI
Stoker Coal Boiler: Axeman-Anderson 260M Leisure Line AA-220 Boiler (FOR SALE)
Coal Size/Type: Lehigh Pea

Post by swyman » Fri. Jan. 19, 2018 7:40 am

StokerDon wrote:
Thu. Jan. 18, 2018 6:33 pm
. It sounds like a power vent pulls heat out of the boiler constantly at idle.

-Don
You know I didn't really think of this but I think you are absolutely correct as the draft never changes. When my boiler goes into low fire mode my firebox pressure goes from -.01 to -.04. That is pulling all that heat out of the boiler when idling isn't it?

 
User avatar
coaledsweat
Site Moderator
Posts: 13763
Joined: Fri. Oct. 27, 2006 2:05 pm
Location: Guilford, Connecticut
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea

Post by coaledsweat » Fri. Jan. 19, 2018 7:51 am

This is why they invented chimneys.


 
User avatar
hotblast1357
Member
Posts: 5657
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Fri. Jan. 19, 2018 7:57 am

Wire it up to slow down at idle, and kick up when the combustion fans come on.

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Fri. Jan. 19, 2018 8:24 am

hotblast1357 wrote:
Fri. Jan. 19, 2018 7:57 am
Wire it up to slow down at idle, and kick up when the combustion fans come on.
That may not be safe.

 
User avatar
hotblast1357
Member
Posts: 5657
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Fri. Jan. 19, 2018 9:33 am

Well it would have to be done safely of coarse!

 
User avatar
windyhill4.2
Member
Posts: 6072
Joined: Fri. Nov. 22, 2013 2:17 pm
Location: Jonestown,Pa.17038
Stoker Coal Boiler: 1960 EFM520 installed in truck box
Hand Fed Coal Stove: Crane 404 with variable blower
Coal Size/Type: 404-nut, 520 rice ,anthracite for both

Post by windyhill4.2 » Fri. Jan. 19, 2018 10:43 am

coaledsweat wrote:
Fri. Jan. 19, 2018 7:51 am
This is why they invented chimneys.
^^^ :yes:

Make it your top priority goal to build a chimney as soon as you financially can do it.

Meanwhile,let the stupid power vent do it's wasteful job.... safely,don't try to re-engineer what it does.

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Fri. Jan. 19, 2018 10:46 am

Hrmm....deja vu...PV a heat waster...think we expressed all this out in the barn some time ago too...

 
User avatar
windyhill4.2
Member
Posts: 6072
Joined: Fri. Nov. 22, 2013 2:17 pm
Location: Jonestown,Pa.17038
Stoker Coal Boiler: 1960 EFM520 installed in truck box
Hand Fed Coal Stove: Crane 404 with variable blower
Coal Size/Type: 404-nut, 520 rice ,anthracite for both

Post by windyhill4.2 » Fri. Jan. 19, 2018 10:49 am

McGiever wrote:
Fri. Jan. 19, 2018 10:46 am
Hrmm....deja vu...PV a heat waster...think we expressed all this out in the barn some time ago too...
I just woke up (mentally) & realized we are talking about stupid power vents on SD's AA130 thread..... :o :what: oops

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Fri. Jan. 19, 2018 10:57 am

windyhill4.2 wrote:
Fri. Jan. 19, 2018 10:49 am
I just woke up (mentally) & realized we are talking about stupid power vents on SD's AA130 thread..... :o :what: oops
And since the AA130 functions much like a hand fired stove when at idle, it is not possible to install a power vent on it at all. I shouldn't have propagated this within this thread either.

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Fri. Jan. 19, 2018 11:05 am

lsayre wrote:
Fri. Jan. 19, 2018 10:57 am
And since the AA130 functions much like a hand fired stove when at idle, it is not possible to install a power vent on it at all. I shouldn't have propagated this within this thread either.

And that plus not running any hold-fire-timer w/ a AA_130 plays largely into not burning extra coal just to stay alive.
Most, if not all, other stokers must idle...AA's 'hibernate' :mrgreen: