Post by StokerDon » Mon. Jan. 15, 2018 6:48 pm

I spent a little time today cleaning up this side of the boiler and Anthrastat area.
IMG_2089.JPG
.JPG | 373.3KB | IMG_2089.JPG
Since this auger is bent, where is couples to the transfer head everything moves around. This is causing crushed coal to leak out at the coupling.
IMG_2087.JPG
.JPG | 363.7KB | IMG_2087.JPG
I installed this part of an old lamp as a catch can for the coal and oil. I might make something better later, but for right now, this will work.
IMG_2090.JPG
.JPG | 361.5KB | IMG_2090.JPG
IMG_2088.JPG
.JPG | 361.1KB | IMG_2088.JPG
We've got a pretty healthy gofer hole already!
IMG_2085.JPG
.JPG | 486.1KB | IMG_2085.JPG
I removed the top slat on the coal bin door. I currently have no way to measure the coal usage. Looks like we are still at 80 to 100 pounds per day. I have nothing to base that estimate on other than what the bin looked like before.
IMG_2086.JPG
.JPG | 401.6KB | IMG_2086.JPG
In other news, I treated the Axeman to a set of new green belts.
IMG_2083.JPG
.JPG | 376.4KB | IMG_2083.JPG
IMG_2084.JPG
.JPG | 326.7KB | IMG_2084.JPG
-Don


 
User avatar
coaledsweat
Site Moderator
Posts: 13766
Joined: Fri. Oct. 27, 2006 2:05 pm
Location: Guilford, Connecticut
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea

Post by coaledsweat » Mon. Jan. 15, 2018 7:19 pm

StokerDon wrote:
Mon. Jan. 15, 2018 6:48 pm
Since this auger is bent, where is couples to the transfer head everything moves around. This is causing crushed coal to leak out at the coupling.
I think they all toss a little pile of small chips where the auger transitions to the head. Mine spits bigger chips at the hanging port cover. The shelf in front is always littered with its dribbling. It's like having a retarded child. :D

 
User avatar
StokerDon
Site Moderator
Posts: 7496
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Mon. Jan. 15, 2018 7:48 pm

coaledsweat wrote:
Mon. Jan. 15, 2018 7:19 pm
I think they all toss a little pile of small chips where the auger transitions to the head. Mine spits bigger chips at the hanging port cover. The shelf in front is always littered with its dribbling. It's like having a retarded child. :D
It's good to know that this is normal then. All the more reason to make a catch pan for it.

Mine spits coal and ash out the view port to. After there is a good fire going and then it shuts down, the new crackling coal spits pieces at the fire door, "Ding,,,,, Ding,,, Ding!". Some of this ends up on the shelf.

-Don

 
User avatar
coaledsweat
Site Moderator
Posts: 13766
Joined: Fri. Oct. 27, 2006 2:05 pm
Location: Guilford, Connecticut
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea

Post by coaledsweat » Mon. Jan. 15, 2018 9:08 pm

Yup, add up all the sounds it makes and you'd swear you had a Fischer-Price toy! :D

 
Olllotj
Member
Posts: 558
Joined: Thu. Sep. 04, 2014 10:01 am
Location: Western NY 14141
Stoker Coal Boiler: Keystoker KB-8
Coal Size/Type: Buckwheat
Other Heating: Utica Propane Hot Water

Post by Olllotj » Mon. Jan. 15, 2018 9:12 pm

No wonder the cat is angry

 
User avatar
StokerDon
Site Moderator
Posts: 7496
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Tue. Jan. 16, 2018 6:51 pm

Olllotj wrote:
Mon. Jan. 15, 2018 9:12 pm
No wonder the cat is angry
Really! It constantly interrupts her nap time. :lol:


-Don

 
User avatar
swyman
Member
Posts: 2355
Joined: Mon. Apr. 13, 2015 9:50 pm
Location: Blissfield, MI
Stoker Coal Boiler: Axeman-Anderson 260M Leisure Line AA-220 Boiler (FOR SALE)
Coal Size/Type: Lehigh Pea

Post by swyman » Wed. Jan. 17, 2018 7:29 am

Hey SD, enjoyed the video! I noticed that you placed the draft control just before it leaves the building. I placed mine as close as I could to the boiler....what change would happen if I moved mine to that location instead. Just wondering if it would make a difference with fly ash? NOTE: I do run a power vent.


 
User avatar
hotblast1357
Member
Posts: 5661
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Wed. Jan. 17, 2018 7:35 am

It would do nothing, it just controls the draft.

 
User avatar
coaledsweat
Site Moderator
Posts: 13766
Joined: Fri. Oct. 27, 2006 2:05 pm
Location: Guilford, Connecticut
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea

Post by coaledsweat » Wed. Jan. 17, 2018 7:39 am

Ideally they should be in the middle of a straight run of pipe to obtain a laminar flow. That said, it probably won't make a discernable difference.

 
User avatar
swyman
Member
Posts: 2355
Joined: Mon. Apr. 13, 2015 9:50 pm
Location: Blissfield, MI
Stoker Coal Boiler: Axeman-Anderson 260M Leisure Line AA-220 Boiler (FOR SALE)
Coal Size/Type: Lehigh Pea

Post by swyman » Wed. Jan. 17, 2018 7:43 am

hotblast1357 wrote:
Wed. Jan. 17, 2018 7:35 am
It would do nothing, it just controls the draft.
There is a higher velocity down stream though correct? Assuming that you are pulling a harder draft than what it is set for.... I try to adjust my draft so the butterfly is just bouncing a bit.

 
User avatar
hotblast1357
Member
Posts: 5661
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Wed. Jan. 17, 2018 9:05 am

U should adjust ur draft so that the manometer reads whatever it’s supposed to! Not what the baro is doing.

 
User avatar
swyman
Member
Posts: 2355
Joined: Mon. Apr. 13, 2015 9:50 pm
Location: Blissfield, MI
Stoker Coal Boiler: Axeman-Anderson 260M Leisure Line AA-220 Boiler (FOR SALE)
Coal Size/Type: Lehigh Pea

Post by swyman » Wed. Jan. 17, 2018 9:53 am

hotblast1357 wrote:
Wed. Jan. 17, 2018 9:05 am
U should adjust ur draft so that the manometer reads whatever it’s supposed to! Not what the baro is doing.
Correct, but I can adjust the draft with the rheostat and then set the baro door to open if you exceed set draft? Unless I'm doing it wrong? I set it to open if you draw harder than -.04 at the boiler breech as in when the combustion fans shut down in idle fire. The crappy thing with the PV is it runs all the time so when the combustion fans stop there is a huge excess of draft. Does the same thing happen with a chimney?

 
User avatar
hotblast1357
Member
Posts: 5661
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Wed. Jan. 17, 2018 10:26 am

A chimney drafts what it drafts, we just set the weight on the baro so that it starts to open when we exceed the limited draft setting.

 
User avatar
swyman
Member
Posts: 2355
Joined: Mon. Apr. 13, 2015 9:50 pm
Location: Blissfield, MI
Stoker Coal Boiler: Axeman-Anderson 260M Leisure Line AA-220 Boiler (FOR SALE)
Coal Size/Type: Lehigh Pea

Post by swyman » Wed. Jan. 17, 2018 10:46 am

hotblast1357 wrote:
Wed. Jan. 17, 2018 10:26 am
A chimney drafts what it drafts, we just set the weight on the baro so that it starts to open when we exceed the limited draft setting.
Perfect, same thing I'm doing!

 
User avatar
StokerDon
Site Moderator
Posts: 7496
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Wed. Jan. 17, 2018 6:59 pm

swyman wrote:
Wed. Jan. 17, 2018 7:29 am
Hey SD, enjoyed the video! I noticed that you placed the draft control just before it leaves the building. I placed mine as close as I could to the boiler....what change would happen if I moved mine to that location instead. Just wondering if it would make a difference with fly ash? NOTE: I do run a power vent.
Thanks!

I sorry to say I don't know much about power vents, but I also don't understand your question about fly ash. Do you have fly ash coming out your baro?
My baro is at the base of the chimney on this one because I had to put it in the 8" part of the stove pipe. It's a 7" baro. The rest of the pipe is 5".

-Don