Problem with rice coal in my EFM

 
Highboy520
New Member
Posts: 11
Joined: Fri. Dec. 22, 2017 9:33 am
Stoker Coal Boiler: EFM 520 high boy
Hand Fed Coal Boiler: yes
Hand Fed Coal Furnace: yes
Coal Size/Type: rice
Other Heating: Gas firplace

Post by Highboy520 » Fri. Dec. 22, 2017 9:56 am

I have been burning my EFM for about 10 years now but never had this problem. The coal is clumping up in the pot area and not falling down to the ash bucket. also loosing a lot of coal as some is clumping and causing un-burnt coal to fall. About three extra buckets of ash compared to other years in a week. I believe i got some bad coal with a lot of iron in it! The problem being is i purchased almost 7 ton and going through it like water. I have attached some pics to see the ash. Can anyone help?

Attachments

bin.jpg
.JPG | 355.8KB | bin.jpg
fire pot area #2.jpg
.JPG | 214.5KB | fire pot area #2.jpg
fire pot area.jpg
.JPG | 495.6KB | fire pot area.jpg
un burnt coal.jpg
.JPG | 552.4KB | un burnt coal.jpg


 
User avatar
windyhill4.2
Member
Posts: 6072
Joined: Fri. Nov. 22, 2013 2:17 pm
Location: Jonestown,Pa.17038
Stoker Coal Boiler: 1960 EFM520 installed in truck box
Hand Fed Coal Stove: Crane 404 with variable blower
Coal Size/Type: 404-nut, 520 rice ,anthracite for both

Post by windyhill4.2 » Fri. Dec. 22, 2017 10:00 am

That stuff looks nasty !! Have you tried cutting the air back like 1/2 a setting to see if that helps ??

 
User avatar
Rob R.
Site Moderator
Posts: 17981
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Fri. Dec. 22, 2017 10:08 am

What are your feed and air settings?

 
Dave 1234
Member
Posts: 788
Joined: Tue. Nov. 13, 2012 9:05 am
Stoker Coal Boiler: 1948 International boiler, EFM S-20 stoker
Coal Size/Type: Buck,

Post by Dave 1234 » Fri. Dec. 22, 2017 1:04 pm

Best to get new coal asap . Next go see the ppl your bad coal came from and show them the mess that bad coal created.
I bet you are not the only one dealing with that trouble !

Dave

 
Pacowy
Member
Posts: 3555
Joined: Tue. Sep. 04, 2007 10:14 pm
Location: Dalton, MA
Stoker Coal Boiler: H.B. Smith 350 Mills boiler/EFM 85R stoker
Coal Size/Type: Buckwheat/anthracite

Post by Pacowy » Fri. Dec. 22, 2017 1:14 pm

Agree with WH that cutting the air a little might help to control the clinkers, but also agree with Dave that you should get some coal on hand that can better handle times when the unit needs to run hard.

Mike

 
User avatar
Rob R.
Site Moderator
Posts: 17981
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Fri. Dec. 22, 2017 1:23 pm

I just noticed you are a new member of the forum. Welcome.

I asked about your feed and air settings because it is possible you have been running a lot of extra air for the last 9 years, and have gotten some coal that can't tolerate it.

 
LehighanthraciteMatt
Verified Business Rep.
Posts: 742
Joined: Thu. Sep. 29, 2016 1:02 pm
Stoker Coal Boiler: Van Wert
Hot Air Coal Stoker Stove: Alaska
Hand Fed Coal Stove: Warm Morning
Coal Size/Type: Rice,Buck, and Nut

Post by LehighanthraciteMatt » Fri. Dec. 22, 2017 3:17 pm

Pacowy wrote:
Fri. Dec. 22, 2017 1:14 pm
Agree with WH that cutting the air a little might help to control the clinkers, but also agree with Dave that you should get some coal on hand that can better handle times when the unit needs to run hard.

Mike
Symptoms like that could be high higher carbon coal, Usually cutting back on the air and sometimes both the feed and air will solve this.


 
lincolnmania
Member
Posts: 2684
Joined: Fri. Jan. 26, 2007 9:55 pm
Location: Birdsboro PA.
Stoker Coal Boiler: EFM 350
Hot Air Coal Stoker Furnace: reading allegheny stoker
Hot Air Coal Stoker Stove: alaska kodiak stoker 1986. 1987 triburner, 1987 crane diamond
Coal Size/Type: rice

Post by lincolnmania » Fri. Dec. 22, 2017 4:07 pm

i would cut back the feed and the air. what are your current settings? is this stuff making decent heat?
do you pull the fines lever every day?

 
LehighanthraciteMatt
Verified Business Rep.
Posts: 742
Joined: Thu. Sep. 29, 2016 1:02 pm
Stoker Coal Boiler: Van Wert
Hot Air Coal Stoker Stove: Alaska
Hand Fed Coal Stove: Warm Morning
Coal Size/Type: Rice,Buck, and Nut

Post by LehighanthraciteMatt » Fri. Dec. 22, 2017 4:17 pm

Pacowy wrote:
Fri. Dec. 22, 2017 1:14 pm
Agree with WH that cutting the air a little might help to control the clinkers, but also agree with Dave that you should get some coal on hand that can better handle times when the unit needs to run hard.

Mike
What you are seeing there is not a clinker, it is ash caking. A clinker will not break up easily by hand. a true clinker is caused by the low fusion coal, caking is generally cause by over firing the stoker or stove.

 
Pacowy
Member
Posts: 3555
Joined: Tue. Sep. 04, 2007 10:14 pm
Location: Dalton, MA
Stoker Coal Boiler: H.B. Smith 350 Mills boiler/EFM 85R stoker
Coal Size/Type: Buckwheat/anthracite

Post by Pacowy » Fri. Dec. 22, 2017 5:36 pm

The OP cited getting a batch of coal with a lot of iron in it. Doesn't the iron reduce the AFT, making this a clinker even as you have defined it?

Mike

 
Dave 1234
Member
Posts: 788
Joined: Tue. Nov. 13, 2012 9:05 am
Stoker Coal Boiler: 1948 International boiler, EFM S-20 stoker
Coal Size/Type: Buck,

Post by Dave 1234 » Fri. Dec. 22, 2017 5:47 pm

The third pic looks like the ash is swelling , and clinkering too. Not fun if you want heat !
Dump the fire, empty the bin, run the auger clean and start over with new coal.

IMHO Dave

 
User avatar
Scottscoaled
Member
Posts: 2812
Joined: Tue. Jan. 08, 2008 9:51 pm
Location: Malta N.Y.
Stoker Coal Boiler: EFM 520, 700, Van Wert 800 GJ 61,53
Baseburners & Antiques: Magic Stewart 16, times 2!
Coal Size/Type: Lots of buck
Other Heating: Slant Fin electric boiler backup

Post by Scottscoaled » Fri. Dec. 22, 2017 6:08 pm

That coal looks real familiar. Would you be in the Scranton/Wilkesbarre area by chance?

 
User avatar
Pauliewog
Member
Posts: 1824
Joined: Mon. Dec. 02, 2013 12:15 am
Location: Pittston, Pennsylvania
Hot Air Coal Stoker Furnace: Alaska 140 Dual Paddle Feed
Baseburners & Antiques: Fame Rosemont #20, Home Stove Works #25, Glenwood #6, Happy Thought Oak, Merry Bride #214, Sunnyside, Worlds Argand #114, New Golden Sun , & About 30 others.
Coal Size/Type: Stove, Chesnut, Pea, Rice / Anthracite

Post by Pauliewog » Fri. Dec. 22, 2017 6:48 pm

Scottscoaled wrote:
Fri. Dec. 22, 2017 6:08 pm
That coal looks real familiar. Would you be in the Scranton/Wilkesbarre area by chance?
What breaker are you thinking Scott ?

Paulie

 
Highboy520
New Member
Posts: 11
Joined: Fri. Dec. 22, 2017 9:33 am
Stoker Coal Boiler: EFM 520 high boy
Hand Fed Coal Boiler: yes
Hand Fed Coal Furnace: yes
Coal Size/Type: rice
Other Heating: Gas firplace

Post by Highboy520 » Sat. Dec. 23, 2017 10:27 am

Rob R. wrote:
Fri. Dec. 22, 2017 1:23 pm
I just noticed you are a new member of the forum. Welcome.

I asked about your feed and air settings because it is possible you have been running a lot of extra air for the last 9 years, and have gotten some coal that can't tolerate it.
coal is at 3 and air is at 4

 
Highboy520
New Member
Posts: 11
Joined: Fri. Dec. 22, 2017 9:33 am
Stoker Coal Boiler: EFM 520 high boy
Hand Fed Coal Boiler: yes
Hand Fed Coal Furnace: yes
Coal Size/Type: rice
Other Heating: Gas firplace

Post by Highboy520 » Sat. Dec. 23, 2017 10:29 am

lincolnmania wrote:
Fri. Dec. 22, 2017 4:07 pm
i would cut back the feed and the air. what are your current settings? is this stuff making decent heat?
do you pull the fines lever every day?
coal is at 3 and air 4
not getting good heat I go trough 10 ton a year on a average just got this in Nov. and over half of the 7 ton is gone