Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Wed. Jan. 05, 2022 9:15 am

Jerrybro wrote:
Wed. Jan. 05, 2022 7:45 am
Thats not much more than I use on my Mark3 in the basement. Well done!
Thanks! I think it does pretty well.


 
User avatar
hotblast1357
Member
Posts: 5657
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Wed. May. 11, 2022 6:18 am

Another heating season done, only burnt 8,200 pounds this year, this summer I will rip out the oil forced hot air system and instal l baseboard throughout the house, also need to fix my hopper, there are some holes in the bottom from wear, and need to purchase another fan motor assembly from AHS as the boiler will be the only supply of heat from here on it so I want a spare on hand, and maybe a spare aquastat. Only really need to get the backup electric heating element setup squared away.

 
User avatar
Rob R.
Site Moderator
Posts: 17977
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Wed. May. 11, 2022 7:26 am

What model aquastat do you need?

 
User avatar
hotblast1357
Member
Posts: 5657
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Wed. May. 11, 2022 9:25 am

Rob R. wrote:
Wed. May. 11, 2022 7:26 am
What model aquastat do you need?
I would have to look and see what’s on it, it’s the original one, but I also know it does more than I need, I just need one that controls the fan, just a spare.

 
User avatar
freetown fred
Member
Posts: 30293
Joined: Thu. Dec. 31, 2009 12:33 pm
Location: Freetown,NY 13803
Hand Fed Coal Stove: HITZER 50-93
Coal Size/Type: BLASCHAK Nut

Post by freetown fred » Wed. May. 11, 2022 9:31 am

You'd think after 76 pages--you'd have all that stuff memorized!!!! LOL Mornin my friend :)

 
User avatar
Lightning
Site Moderator
Posts: 14658
Joined: Wed. Nov. 16, 2011 9:51 am
Location: Olean, NY
Stoker Coal Boiler: Modified AA 130
Coal Size/Type: Pea Size - Anthracite

Post by Lightning » Wed. May. 11, 2022 11:29 am

hotblast1357 wrote:
Wed. May. 11, 2022 9:25 am
I would have to look and see what’s on it, it’s the original one, but I also know it does more than I need, I just need one that controls the fan, just a spare.
A PID with relay?
That's what I'm using...

 
User avatar
nepacoal
Member
Posts: 1696
Joined: Wed. Nov. 21, 2012 7:49 am
Location: Coal Country
Stoker Coal Boiler: Keystoker KAA-4 / "Kelly" and an EFM 520 at my in-laws
Hand Fed Coal Boiler: Harman SF-260 - retired
Coal Size/Type: Buck

Post by nepacoal » Wed. May. 11, 2022 11:56 am

hotblast1357 wrote:
Wed. May. 11, 2022 9:25 am
I would have to look and see what’s on it, it’s the original one, but I also know it does more than I need, I just need one that controls the fan, just a spare.
An L6006a has both high and low limit functions, plus an adjustable differential. It could be a spare for the fan control and a dump zone...


 
User avatar
Rob R.
Site Moderator
Posts: 17977
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Wed. May. 11, 2022 1:01 pm

Lightning wrote:
Wed. May. 11, 2022 11:29 am
A PID with relay?
That's what I'm using...
I am in the "analog" camp when it comes to controls, but I think moving the motor load to a relay is a good idea.
nepacoal wrote:
Wed. May. 11, 2022 11:56 am
An L6006a has both high and low limit functions, plus an adjustable differential. It could be a spare for the fan control and a dump zone...
Yes sir, that is a good all-around aquastat to have in stock.

 
User avatar
Lightning
Site Moderator
Posts: 14658
Joined: Wed. Nov. 16, 2011 9:51 am
Location: Olean, NY
Stoker Coal Boiler: Modified AA 130
Coal Size/Type: Pea Size - Anthracite

Post by Lightning » Wed. May. 11, 2022 2:53 pm

Rob R. wrote:
Wed. May. 11, 2022 1:01 pm
I am in the "analog" camp when it comes to controls
I totally understand.. It'll take me a while to build trust with these cheap foreign controls. Fortunately, so far so good :)

 
User avatar
hotblast1357
Member
Posts: 5657
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Wed. May. 11, 2022 5:09 pm

I use a PID with relay for the ash motor, and I’ve wanted to switch the aquastat over, but am to worried about the cheap Chinese lol but I haven’t had a problem with the ashing one since install back in 2017, guess that should be good enough lol plus then I could have spares for both fan and ash motors… I should be able to use the relay (SSR?) that I have with my ash motor that way there both the same.

 
User avatar
Rob R.
Site Moderator
Posts: 17977
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Thu. May. 12, 2022 8:25 am

I would research the SSR a bit more and make sure it is rated for the load of your fan motor.

 
User avatar
hotblast1357
Member
Posts: 5657
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Thu. May. 12, 2022 9:11 am

Rob R. wrote:
Thu. May. 12, 2022 8:25 am
I would research the SSR a bit more and make sure it is rated for the load of your fan motor.
Good idea.

 
User avatar
freetown fred
Member
Posts: 30293
Joined: Thu. Dec. 31, 2009 12:33 pm
Location: Freetown,NY 13803
Hand Fed Coal Stove: HITZER 50-93
Coal Size/Type: BLASCHAK Nut

Post by freetown fred » Thu. May. 12, 2022 2:31 pm

You'd think after 76 pages--you'd have all that stuff memorized!!!! LOL Mornin my friend :)------ :? :cry:

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Fri. May. 13, 2022 10:24 am

hotblast1357 wrote:
Wed. May. 11, 2022 5:09 pm
I use a PID with relay for the ash motor, and I’ve wanted to switch the aquastat over, but am to worried about the cheap Chinese lol but I haven’t had a problem with the ashing one since install back in 2017, guess that should be good enough lol plus then I could have spares for both fan and ash motors… I should be able to use the relay (SSR?) that I have with my ash motor that way there both the same.
On the Axemans there is a separate HI Limit Honeywell aquastat that we leave in place just in case the digital boiler control does something stupid. I suspect your Eshland has the same feature. Make sure you keep it wired in.

With the Inkbird digital controllers that some of us are using, they come with an SSR. These SSR's are either 25 amp or 40 amp and will easily handle your fan motor. Personally, I haven't built up enough trust in the SSR's to use them. I use a standard industrial, electro-mechanical relay.

-Don

 
User avatar
hotblast1357
Member
Posts: 5657
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Fri. May. 13, 2022 12:36 pm

StokerDon wrote:
Fri. May. 13, 2022 10:24 am
On the Axemans there is a separate HI Limit Honeywell aquastat that we leave in place just in case the digital boiler control does something stupid. I suspect your Eshland has the same feature. Make sure you keep it wired in.

With the Inkbird digital controllers that some of us are using, they come with an SSR. These SSR's are either 25 amp or 40 amp and will easily handle your fan motor. Personally, I haven't built up enough trust in the SSR's to use them. I use a standard industrial, electro-mechanical relay.

-Don
I don’t have the hi hi hi hi limit safety wired in lol my ashing inkbird came with a 40 amp, I didn’t think I could trust it either, but My ash one has worked perfect since 2017, and the current aquastat I assume is original from 1984 so lol I’m a fan of don’t broke don’t fix but I want a spare for just in case, so just didn’t know which spare to get, a new aquastat or another inkbird.. after this summer the eshland will be my only source of heat so I want a spare of everything.