Eshland S 260 Rebuild

 
User avatar
hotblast1357
Member
Posts: 5661
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Tue. Jan. 22, 2019 6:05 pm

Since Friday auger ran .6 hours, so 36 minutes, 6lbs/minute so 216 lbs. 54 lbs per day, used around 300 gallons of hot water, so 23 lbs of coal for DHW. It was crazy cold, I was to busy plowing though to keep record, I know yesterday the high was -5..


 
User avatar
hotblast1357
Member
Posts: 5661
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Thu. Jan. 31, 2019 5:09 pm

This month is pretty much a wrap, went by fast, only had one day off work. Was brutally cold for most of it.

The results are in.

Auger ran 4.3 hours, 258 minutes, at 6 pounds per minute,

1548 pounds, or 49.9/day.

1386 gallons of hot water, so 107 pounds of coal for hot water.

Total of 5,580 lbs for the season, since October 1st.

I burned 1884 pounds last January.

 
User avatar
StokerDon
Site Moderator
Posts: 7496
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Thu. Jan. 31, 2019 7:00 pm

That's pretty good mileage there H.B. I would have thought most up in your area would burn closer to 3,000 pounds during a cold January.

These weird shaped coal burning contraptions are pretty dern interesting to say the least.

-Don

 
User avatar
hotblast1357
Member
Posts: 5661
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Wed. Feb. 27, 2019 5:30 am

I’m ready for spring.. boiler is still chugging along with no problems, My coal is getting down to where I’m gonna have to hop into the bin and rake it a little over the auger.

Attachments

BA7A5DEE-DC3C-4AA4-B05A-4B6BBB8E0EEE.png
.PNG | 235KB | BA7A5DEE-DC3C-4AA4-B05A-4B6BBB8E0EEE.png

 
User avatar
hotblast1357
Member
Posts: 5661
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Thu. May. 02, 2019 6:25 am

Story time for April.

It has still been rather cold here, we’ve had some nice sunny days but it was 23 over the weekend, today it won’t get over 40 and rain.

Burnt 720 pounds last month, 24 pounds per day.

We used 1240 gallons of hot water. It took 96 pounds of coal for the month, or 3.2 pounds per day.

This thing still seems to smoke a lot, after the fan has shut off.

Attachments


 
User avatar
coaledsweat
Site Moderator
Posts: 13766
Joined: Fri. Oct. 27, 2006 2:05 pm
Location: Guilford, Connecticut
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea

Post by coaledsweat » Thu. May. 02, 2019 6:53 am

Are you sure that isn't water vapour? Not smoke?

 
User avatar
hotblast1357
Member
Posts: 5661
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Thu. May. 02, 2019 7:14 am

I don’t know where it would be coming from. In the chimney maybe?


 
User avatar
coaledsweat
Site Moderator
Posts: 13766
Joined: Fri. Oct. 27, 2006 2:05 pm
Location: Guilford, Connecticut
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea

Post by coaledsweat » Thu. May. 02, 2019 7:32 am

On a damp morning wouldn't it be in the air feeding the aplliance?

 
User avatar
hotblast1357
Member
Posts: 5661
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Thu. May. 02, 2019 8:03 am

That’s very possible, it’s raining and very damp out.

 
User avatar
hotblast1357
Member
Posts: 5661
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Sun. May. 12, 2019 6:50 am

So far this heating season we’ve used 9648 lbs since October 1st.

We used 216 lbs last week, 30 lbs per day, still heating the house every day.

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Mon. May. 27, 2019 8:45 am

That would of been a lot of propain....

 
User avatar
StokerDon
Site Moderator
Posts: 7496
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Mon. May. 27, 2019 8:02 pm

How is the heating element in place of the DHW coil project going.??? I was actually thinking of doing something like that for shoulder season, but I was afraid it would make my electric bill go crazy.

-Don

 
User avatar
hotblast1357
Member
Posts: 5661
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Mon. May. 27, 2019 9:01 pm

It’s at a stand still right now, doing a lot of work outside, boiler is still going, gotta get some studs.

 
User avatar
hotblast1357
Member
Posts: 5661
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Fri. Jun. 21, 2019 10:36 am

Ok got some studs today, I’m drawing a blank on which aquastat I can use, I just need it to come on at around 80-90 and turn off around like 120. And can I get one that I can run my main 240v through straight to my heating element? So that I don’t have a bunch of relays.

Could I use this?

https://www.houseneeds.com/heating/hydronic-heat- ... 421abc-02c

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Fri. Jun. 21, 2019 11:09 am

hotblast1357 wrote:
Fri. Jun. 21, 2019 10:36 am
Ok got some studs today, I’m drawing a blank on which aquastat I can use, I just need it to come on at around 80-90 and turn off around like 120. And can I get one that I can run my main 240v through straight to my heating element? So that I don’t have a bunch of relays.

Could I use this?

https://www.houseneeds.com/heating/hydronic-heat- ... 421abc-02c
If it is rated for the voltage and can handle the amps draw of the htr. elements you can use it directly w/o contactor/relay...Ohms Law if you get stuck.
Last edited by McGiever on Fri. Jun. 21, 2019 11:10 am, edited 1 time in total.


Post Reply