Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Sun. May. 13, 2018 8:09 pm

Due to it idling so much, I’m sure it’s actually that my idle consumption has gone up, and not just the fan consumption going up.

I’m sure Larry can figure it all out lol


 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Sun. May. 13, 2018 8:18 pm

hotblast1357 wrote:
Sun. May. 13, 2018 8:09 pm
Due to it idling so much, I’m sure it’s actually that my idle consumption has gone up, and not just the fan consumption going up.

I’m sure Larry can figure it all out lol
I've given you the means, The rest is now up to you grasshopper.

 
User avatar
hotblast1357
Member
Posts: 5657
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Sun. May. 13, 2018 8:49 pm

Lol ya I’m good!

Just happy with 28 lbs a day with heat calls still.

 
User avatar
hotblast1357
Member
Posts: 5657
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Thu. May. 31, 2018 6:52 pm

18 days on a hopper, there was prob 40lbs in there still.

462 pounds, 25.6 lbs per day.

Throughout the 18 days there was many heat calls. Next weeks highs are in the 60s so I’m sure we’ll have some more heat calls.

Pretty happy with the eshland.

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sun. Jun. 03, 2018 7:28 pm

Your set up is doing pretty well. I can barely get my 130M under 30 pounds per day. That is just for heating DHW with no heat calls at all.

-Don

 
User avatar
hotblast1357
Member
Posts: 5657
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Sun. Jun. 03, 2018 8:23 pm

How’s that even make any sense since I’m constant circulation and still heating?

I will say, my boiler is insulated pretty well.

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Sun. Jun. 03, 2018 8:25 pm

Insulation vs. no insulation.


 
User avatar
hotblast1357
Member
Posts: 5657
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Sun. Jun. 24, 2018 8:03 pm

Burnt 12,600 pounds this last heating season, October 17-june18.

Shut the power off 4 days ago to the boiler, yesterday I sucked the rest of the coal out of the hopper, about 50 pounds. Coal was still burning inside after 4 days of no fan or ashing.

Took everything apart, only had a build up of fly ash in my stove pipe, due to it being 8’ horizontal.

Have to cut out and weld in patches in the bottom of my hopper.

Then install the auger system.

Then have to finish installing the rest of my block and tile chimney.

Hoping to get this done over the long weekend coming up.

Also cleaned the boiler room and sealed the concrete floor.

Attachments

1E01512B-A09D-40C6-91C9-DFF06FE82807.jpeg
.JPEG | 1.3MB | 1E01512B-A09D-40C6-91C9-DFF06FE82807.jpeg

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sun. Jun. 24, 2018 8:11 pm

Look'in good there H.B.!

Hard to believe, 4 days since the power was cut and it still has a fire in it's belly!

Tell us more about this auger set up. How big is it and what RPM will it be running?

-Don

 
User avatar
hotblast1357
Member
Posts: 5657
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Sun. Jun. 24, 2018 9:01 pm

It’s a 6”, Idk what RPM yet, I’ll have to setup the motor that came with it and see what it turns when I get it set up, I’m guessing very slow. Lol

This was off a eshland 500.

 
User avatar
hotblast1357
Member
Posts: 5657
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Fri. Jun. 29, 2018 5:07 am

Alright with this big 6” auger, do I still just want 2” or exposed flights sticking out the pipe?

 
lzaharis
Member
Posts: 2366
Joined: Sun. Mar. 25, 2007 8:41 pm
Location: Ithaca, New York
Stoker Coal Boiler: Keystoker KAA-4-1 dual fuel boiler
Hand Fed Coal Boiler: former switzer CWW100-sold
Coal Size/Type: rice
Other Heating: kerosene for dual fuel Keystoker/unused

Post by lzaharis » Fri. Jun. 29, 2018 9:41 am

hotblast1357 wrote:
Fri. Jun. 29, 2018 5:07 am
Alright with this big 6” auger, do I still just want 2” or exposed flights sticking out the pipe?
============================================================================================================

Hello hotblast,

With your auger or for that matter any auger used to transfer commodities you need to have the auger flighting exposed to carry away the material up through the tube and to the discharge point being the dump boot under the motor and pulleys.

You will only have an issue when the coal pile begins to shrink significantly as gravity will not let the remaining coal fall towards and down to the auger inlet under the dog house as you will need to shovel or wheel barrow coal to the area of the dog house to keep the auger supplied with Anthracite Pea Coal.

If you have the time would you be so kind as to upload picture images of the auger tube and the auger discharge boot, motor and pulleys so in that way it would help me to help you more with this.

I hope explanation this helps you with your decisions.

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Fri. Jun. 29, 2018 11:03 am

Likewise curious to see balance of auger assembly.

HB, Was this auger from a AHS-500 a factory design?...or a prior owner's adaptation?
Even a 1725 rpm motor would move a lot of coal in a hurry w/o gear reduction or large pulley reduction.

As far as the feed bin doghouse goes...gravity or "critical angle of repose" can be either freind or foe, good design by you will determine that outcome.
I do know us older guys would rather not need any hoe or shovel to make this all to work. ;)

 
User avatar
hotblast1357
Member
Posts: 5657
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Fri. Jun. 29, 2018 4:56 pm

Lol I just want to know how much of the flights should be sticking out of the tube because I have to shorten it.

This is a factory setup from eshland/AHS.

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Fri. Jun. 29, 2018 6:18 pm

hotblast1357 wrote:
Fri. Jun. 29, 2018 4:56 pm
Lol I just want to know how much of the flights should be sticking out of the tube because I have to shorten it.

This is a factory setup from eshland/AHS.
It should feed just fine with 2 flights sticking out the end, I wouldn't go less than that. Before you cut it, make sure you have it mocked up and marked properly so you don't cut it to short.

How many flights are sticking out of it now?

-Don