- Stoker Coal Boiler: 1984 Eshland S260 coal gun
- Coal Size/Type: Lehigh anthracite pea
- Other Heating: air source heat pump, oil furnace
I was talkin about the pics from pintoplumber.
Idk how the dhw coil is setup as mine has the big plug in it. You will most likely have to shut down though to repair it, unless you attemp some boiler sealer.
Idk if they are washered, or pipe thread?
Idk how the dhw coil is setup as mine has the big plug in it. You will most likely have to shut down though to repair it, unless you attemp some boiler sealer.
Idk if they are washered, or pipe thread?
-
- Member
- Posts: 438
- Joined: Wed. Dec. 07, 2016 3:57 pm
- Location: north west of Pitts Pa.
- Stoker Coal Boiler: AHS S-130
- Coal Size/Type: pea/anthracite
They are pipe thread inside and outside looks like 1 inch outside and 1/2 inch inside, no washers or gaskets between the nuts and the face plate.
How long will it take the fire in the COAL GUN to cool down ? Do I just shut it off or must I do something special ?
How long will it take the fire in the COAL GUN to cool down ? Do I just shut it off or must I do something special ?
- lsayre
- Member
- Posts: 21781
- Joined: Wed. Nov. 23, 2005 9:17 pm
- Location: Ohio
- Stoker Coal Boiler: AHS S130 Coal Gun
- Coal Size/Type: Lehigh Anthracite Pea
- Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75
I've never tried simply shutting off the main power, but I gather that would completely shut it down within a few days. I either just let it run out of coal, or I scoop the coal out of the hopper so it runs out sooner. In the summer it can take about 21-22 days to run out of coal from a full hopper, and with the power left on. When I want to clean it out, I plan that far ahead.
- hotblast1357
- Member
- Posts: 5661
- Joined: Mon. Mar. 10, 2014 10:06 pm
- Location: Peasleeville NY
- Stoker Coal Boiler: 1984 Eshland S260 coal gun
- Coal Size/Type: Lehigh anthracite pea
- Other Heating: air source heat pump, oil furnace
Yes as Larry said it will take very long time!
Fastest thing to do, scoop or vacuum out the coal, and manually power on the ash motor till it dumps the fire, then let boiler coil down enough and drain it down only enough to repair leak.
Fastest thing to do, scoop or vacuum out the coal, and manually power on the ash motor till it dumps the fire, then let boiler coil down enough and drain it down only enough to repair leak.
-
- Member
- Posts: 438
- Joined: Wed. Dec. 07, 2016 3:57 pm
- Location: north west of Pitts Pa.
- Stoker Coal Boiler: AHS S-130
- Coal Size/Type: pea/anthracite
Thanks again guys,
I will try some boiler sealer first, if that don't work I will shut it down. I will return soon I hope. BE SAFE !!
I will try some boiler sealer first, if that don't work I will shut it down. I will return soon I hope. BE SAFE !!
- hotblast1357
- Member
- Posts: 5661
- Joined: Mon. Mar. 10, 2014 10:06 pm
- Location: Peasleeville NY
- Stoker Coal Boiler: 1984 Eshland S260 coal gun
- Coal Size/Type: Lehigh anthracite pea
- Other Heating: air source heat pump, oil furnace
How bad is it leaking?
- Rob R.
- Site Moderator
- Posts: 18004
- Joined: Fri. Dec. 28, 2007 4:26 pm
- Location: Chazy, NY
- Stoker Coal Boiler: EFM 520
- Hand Fed Coal Stove: Chubby Jr
If you are careful you should be able to depressurize the boiler, back off that nut, and snug it up with some pipe dope & tape on the threads. Please work safe - a jacket, gloves, and face shield would be a good idea.
Boiler seal is another option, if the leak is small that might be the way to go.
Boiler seal is another option, if the leak is small that might be the way to go.
- StokerDon
- Site Moderator
- Posts: 7496
- Joined: Mon. Nov. 11, 2013 11:17 am
- Location: PA, Southern York County!
- Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
- Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
- Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
- Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood
Does it leak like this one?
https://www.youtube.com/watch?v=sk6uCafU0sI&list= ... I&index=10
I used Hercules Boiler Liquid sealer on this one and it has not leaked since. The boiler needs to be at least 160 degrees for it to work so you don't need to worry about shutting down the boiler.
I've used Hercules Boiler Liquid sealer a few times now and it has always worked.
-Don
https://www.youtube.com/watch?v=sk6uCafU0sI&list= ... I&index=10
I used Hercules Boiler Liquid sealer on this one and it has not leaked since. The boiler needs to be at least 160 degrees for it to work so you don't need to worry about shutting down the boiler.
I've used Hercules Boiler Liquid sealer a few times now and it has always worked.
-Don
-
- Member
- Posts: 438
- Joined: Wed. Dec. 07, 2016 3:57 pm
- Location: north west of Pitts Pa.
- Stoker Coal Boiler: AHS S-130
- Coal Size/Type: pea/anthracite
Thanks guys for the advice,
The leak is just a drip every 2 seconds or so, I am going out for the Hercules Boiler sealer and if that does not stop it, I will use a washer and a gasket behind the nut. THANKS AGAIN Just me Ron
The leak is just a drip every 2 seconds or so, I am going out for the Hercules Boiler sealer and if that does not stop it, I will use a washer and a gasket behind the nut. THANKS AGAIN Just me Ron
- hotblast1357
- Member
- Posts: 5661
- Joined: Mon. Mar. 10, 2014 10:06 pm
- Location: Peasleeville NY
- Stoker Coal Boiler: 1984 Eshland S260 coal gun
- Coal Size/Type: Lehigh anthracite pea
- Other Heating: air source heat pump, oil furnace
You need to seal the pipe thread, no washers or gaskets.
-
- Member
- Posts: 438
- Joined: Wed. Dec. 07, 2016 3:57 pm
- Location: north west of Pitts Pa.
- Stoker Coal Boiler: AHS S-130
- Coal Size/Type: pea/anthracite
I've used Hercules Boiler Liquid sealer a few times now and it has always worked.
-Don
The day I started the first fire I but in 2 bottles of the boiler treatment sealer that AhS gave me when I bought the boiler. Left to look for Hercules Boiler sealer, but the stores I went to did not have it and when I got back the leak had stopped. I still am gong to get the things I need so ill have them incase of future leaks.
Going back to the DHW coil, mixing valve and expansion tank install.
BTW its still gravity feeding and its 74 in the house, i guess ill deal with that after the DHW is hooked up. THANKS AGAIN Ron
-Don
The day I started the first fire I but in 2 bottles of the boiler treatment sealer that AhS gave me when I bought the boiler. Left to look for Hercules Boiler sealer, but the stores I went to did not have it and when I got back the leak had stopped. I still am gong to get the things I need so ill have them incase of future leaks.
Going back to the DHW coil, mixing valve and expansion tank install.
BTW its still gravity feeding and its 74 in the house, i guess ill deal with that after the DHW is hooked up. THANKS AGAIN Ron
- hotblast1357
- Member
- Posts: 5661
- Joined: Mon. Mar. 10, 2014 10:06 pm
- Location: Peasleeville NY
- Stoker Coal Boiler: 1984 Eshland S260 coal gun
- Coal Size/Type: Lehigh anthracite pea
- Other Heating: air source heat pump, oil furnace
Did you buy this unit brand new? Have you even posted pics of the install yet? I can’t remember!
-
- Member
- Posts: 438
- Joined: Wed. Dec. 07, 2016 3:57 pm
- Location: north west of Pitts Pa.
- Stoker Coal Boiler: AHS S-130
- Coal Size/Type: pea/anthracite
<r><QUOTE author="hotblast1357" post_id="643168" time="1511003457" user_id="20482"><s>
Yes I bought it new about a year ago, just slow getting a fire in it.
NO I have not posted any pictures, maybe when it is finished if I can figure out how to do it
Got the DHW hooked up tonight all but the expansion tank, need more fittings will go after them tomorrow.
Took out first showers with coal heated water tonight, loved it.
Sandy and I want you all to know we could not have done it without all the help we got from all of you!! Thanks again!! Ron & Sandy
</e></QUOTE>hotblast1357 wrote: ↑Sat. Nov. 18, 2017 6:10 am</s>
Did you buy this unit brand new? Have you even posted pics of the install yet? I can’t remember!
<e>
Yes I bought it new about a year ago, just slow getting a fire in it.
NO I have not posted any pictures, maybe when it is finished if I can figure out how to do it
Got the DHW hooked up tonight all but the expansion tank, need more fittings will go after them tomorrow.
Took out first showers with coal heated water tonight, loved it.
Sandy and I want you all to know we could not have done it without all the help we got from all of you!! Thanks again!! Ron & Sandy
- hotblast1357
- Member
- Posts: 5661
- Joined: Mon. Mar. 10, 2014 10:06 pm
- Location: Peasleeville NY
- Stoker Coal Boiler: 1984 Eshland S260 coal gun
- Coal Size/Type: Lehigh anthracite pea
- Other Heating: air source heat pump, oil furnace
Feeding that electric water tank, it’s going to take several showers to actually get coal fired water out of it, as you are mixing 40 gallons, it take a little while to bring it up to boiler temp.
- lsayre
- Member
- Posts: 21781
- Joined: Wed. Nov. 23, 2005 9:17 pm
- Location: Ohio
- Stoker Coal Boiler: AHS S130 Coal Gun
- Coal Size/Type: Lehigh Anthracite Pea
- Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75
Better have a mixing valve on the outlet of the HWT to protect you from the potential of scalding hot (boiler temperature) showers.