Post by vtec350 » Mon. May. 12, 2008 5:21 pm

Finally got some great news today from the building inspector regarding the ASME stamp needed here in Ma. I met with him this morning, asked him if there's anyway to instal the boiler legally, gave him all the info and asked him to call Jim at Keystoker. This guys usually known for being a hard ass to deal with and doing everything by the book. Two hours later he called me and said he spoke with Jim and said that the presure relief valve is AMSE listed and he would approve it. Going down tomorrow and ordering my KA-6 :D I know the AA and the EFM boilers are great boilers, but I don't have an extra $4K rite now. Thanks to you guys on here, I've learned a lot about coal and boilers in the last 2 weeks. Hopefully I don't have any problems with the install, but if I do, I now know where to go......


 
User avatar
coaledsweat
Site Moderator
Posts: 13767
Joined: Fri. Oct. 27, 2006 2:05 pm
Location: Guilford, Connecticut
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea

Post by coaledsweat » Mon. May. 12, 2008 5:24 pm

vtec350 wrote:This guys usually known for being a hard ass to deal with and doing everything by the book. Two hours later he called me and said he spoke with Jim and said that the presure relief valve is AMSE listed and he would approve it.
Lucky for you he is also an idiot. :roll:

 
dipep41
New Member
Posts: 16
Joined: Thu. May. 08, 2008 4:00 pm

Post by dipep41 » Mon. May. 12, 2008 5:30 pm

What about the rest of the boiler?

 
User avatar
Flyer5
Member
Posts: 10376
Joined: Sun. Oct. 21, 2007 4:23 pm
Location: Montrose PA
Stoker Coal Boiler: Leisure Line WL110
Hot Air Coal Stoker Stove: Leisure Line Pioneer
Contact:

Post by Flyer5 » Mon. May. 12, 2008 5:36 pm

coaledsweat wrote:
vtec350 wrote:This guys usually known for being a hard ass to deal with and doing everything by the book. Two hours later he called me and said he spoke with Jim and said that the presure relief valve is AMSE listed and he would approve it.
Lucky for you he is also an idiot. :roll:
I don't understand the reasoning for that statement ? Seems a little harsh considering he went out of the way and helped find a solution . Dave

 
User avatar
coaledsweat
Site Moderator
Posts: 13767
Joined: Fri. Oct. 27, 2006 2:05 pm
Location: Guilford, Connecticut
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea

Post by coaledsweat » Mon. May. 12, 2008 6:47 pm

Yes, I realize it is a little harsh. But he is accepting an ancillary parts approval when the code speaks to the device itself. I realize also that in this case he was one heck of a guy too. :) Don't take it so hard, every now and then, I'm an idiot too.

 
User avatar
vtec350
Member
Posts: 303
Joined: Thu. May. 08, 2008 4:47 pm
Location: Western Mass.

Post by vtec350 » Mon. May. 12, 2008 6:52 pm

Flyer5 wrote:
coaledsweat wrote: Lucky for you he is also an idiot. :roll:
I don't understand the reasoning for that statement ? Seems a little harsh considering he went out of the way and helped find a solution . Dave
The building Inspectors have the final say in any areas of the code book. I've even seen him make builders do More than the code requires, so it's up to his discreation to approve it or not, he spent the time to look into it. Insurance Co. already said as long as I have a signed inspection I'm good with them too.

 
CapeCoaler
Member
Posts: 6515
Joined: Sun. Feb. 10, 2008 3:48 pm
Location: Cape Cod, MA
Stoker Coal Boiler: want AA130
Hand Fed Coal Stove: DS Machine BS#4, Harman MKII, Hitzer 503,...
Coal Size/Type: Pea/Nut/Stove

Post by CapeCoaler » Mon. May. 12, 2008 9:28 pm

Glad to hear it worked out ok with the building inspector. I have found it is far easier to be upfront with them and end up with a mutually acceptable outcome then try to sneak it by and deal with it after the fact. They make the rules, for the most part; it is easier to work with them than against them.


 
User avatar
Freddy
Member
Posts: 7301
Joined: Fri. Apr. 11, 2008 2:54 pm
Location: Orrington, Maine
Stoker Coal Boiler: Axeman Anderson 130 (pea)
Coal Size/Type: Pea size, Superior, deep mined

Post by Freddy » Mon. May. 12, 2008 11:28 pm

I woulsn't say the inspector was an idiot. I'd say he knows how to use common sense. The relief valve blows off at 20 PSI. No matter how the boiler was constructed, how much of an explosion can happen at 20 PSI?

What get's me, last I knew MA does not require a low water cut off. Maine does. Even if Maine didn't, I would have one. Especially if you have PEX tubing or any chance whatsoever of a freeze and pipe break. Without the low water cut off, if the system goes dry, it heats until meltdown, quite literally. Houses burn down because of a leaky pipe. The low water cutoff shuts the unit down if it runs dry..... actually, before it runs dry.

 
User avatar
Richard S.
Mayor
Posts: 15243
Joined: Fri. Oct. 01, 2004 8:35 pm
Location: NEPA
Stoker Coal Boiler: Van Wert VA1200
Coal Size/Type: Buckwheat/Anthracite

Post by Richard S. » Mon. May. 12, 2008 11:35 pm

Freddy wrote: how much of an explosion can happen at 20 PSI?
I'd imagine it's not much but wouldn't want to be around to test that theory. :P

 
User avatar
Yanche
Member
Posts: 3026
Joined: Fri. Dec. 23, 2005 12:45 pm
Location: Sykesville, Maryland
Stoker Coal Boiler: Alternate Heating Systems S-130
Coal Size/Type: Anthracite Pea

Post by Yanche » Mon. May. 12, 2008 11:59 pm

Freddy wrote:I woulsn't say the inspector was an idiot. I'd say he knows how to use common sense. The relief valve blows off at 20 PSI. No matter how the boiler was constructed, how much of an explosion can happen at 20 PSI?

What get's me, last I knew MA does not require a low water cut off. Maine does. Even if Maine didn't, I would have one. Especially if you have PEX tubing or any chance whatsoever of a freeze and pipe break. Without the low water cut off, if the system goes dry, it heats until meltdown, quite literally. Houses burn down because of a leaky pipe. The low water cutoff shuts the unit down if it runs dry..... actually, before it runs dry.
Mass. requires a low water cut off on all steam boilers and on water boilers of 200K BTU/hr or more.

 
User avatar
Freddy
Member
Posts: 7301
Joined: Fri. Apr. 11, 2008 2:54 pm
Location: Orrington, Maine
Stoker Coal Boiler: Axeman Anderson 130 (pea)
Coal Size/Type: Pea size, Superior, deep mined

Post by Freddy » Tue. May. 13, 2008 6:21 am

Richard S. wrote:
Freddy wrote: how much of an explosion can happen at 20 PSI?
I'd imagine it's not much but wouldn't want to be around to test that theory. :P
*giGgLe* You got that right.... After I posted I thought about it & ya know.... I wouldn't want to be around either.

Low water cut off's on 200K & larger? OK, a step in the right direction,, I wonder when they'll realize that leaves almost every home off the list. For anyone reading, they cost about $100 and are a fun electrical challange to install, but with one you get a higher level peace of mind.

 
User avatar
coalkirk
Member
Posts: 5185
Joined: Wed. May. 17, 2006 8:12 pm
Location: Forest Hill MD
Stoker Coal Boiler: 1981 EFM DF520 retired
Hand Fed Coal Stove: Jotul 507 on standby
Coal Size/Type: Lehigh anthracite/rice coal

Post by coalkirk » Tue. May. 13, 2008 6:54 am

Freddy wrote:I woulsn't say the inspector was an idiot. I'd say he knows how to use common sense. The relief valve blows off at 20 PSI. No matter how the boiler was constructed, how much of an explosion can happen at 20 PSI?

What get's me, last I knew MA does not require a low water cut off. Maine does. Even if Maine didn't, I would have one. Especially if you have PEX tubing or any chance whatsoever of a freeze and pipe break. Without the low water cut off, if the system goes dry, it heats until meltdown, quite literally. Houses burn down because of a leaky pipe. The low water cutoff shuts the unit down if it runs dry..... actually, before it runs dry.
Pressure relief valves blow off at 30 psi unless MA requires something different tha the rest of the country.

 
User avatar
Freddy
Member
Posts: 7301
Joined: Fri. Apr. 11, 2008 2:54 pm
Location: Orrington, Maine
Stoker Coal Boiler: Axeman Anderson 130 (pea)
Coal Size/Type: Pea size, Superior, deep mined

Post by Freddy » Tue. May. 13, 2008 7:41 am

coalkirk wrote:
Pressure relief valves blow off at 30 psi unless MA requires something different tha the rest of the country.
Slap me! :doh: Of course, Yes, 30 PSI for hot water boilers, 150 PSI for hot water tanks.

(Now instead of standing 20 feet away when I test blow a boiler, I have to stand 30! )

 
User avatar
coalkirk
Member
Posts: 5185
Joined: Wed. May. 17, 2006 8:12 pm
Location: Forest Hill MD
Stoker Coal Boiler: 1981 EFM DF520 retired
Hand Fed Coal Stove: Jotul 507 on standby
Coal Size/Type: Lehigh anthracite/rice coal

Post by coalkirk » Tue. May. 13, 2008 7:48 am

Freddy wrote:
coalkirk wrote:
Slap me! :doh: Of course, Yes, 30 PSI for hot water boilers, 150 PSI for hot water tanks.

(Now instead of standing 20 feet away when I test blow a boiler, I have to stand 30! )
If by hot water tanks you mean water heaters, they're 30 psi also. Nothing in a home should have 150 psi. :blowup: :blowup:

 
CapeCoaler
Member
Posts: 6515
Joined: Sun. Feb. 10, 2008 3:48 pm
Location: Cape Cod, MA
Stoker Coal Boiler: want AA130
Hand Fed Coal Stove: DS Machine BS#4, Harman MKII, Hitzer 503,...
Coal Size/Type: Pea/Nut/Stove

Post by CapeCoaler » Tue. May. 13, 2008 7:57 am

Ask anyone who worked/works with steam if they want to be near anything that blows.
The problem begins when the relief valve fails to open.
The pressure will then rise till the next “relief valve” opens, usually with very destructive force.
Myth Busters did a show where they removed the relief valve and cooked the water heater till it blew, at 300 psi, turned it into a missile that took a very long time to return to earth.
It makes sense to allow the boiler to be installed with the stamped relief valve because water heaters use 40 -80 psi working pressure and, I believe, do not require the stamp on the vessel.
The part that everyone is relying on to work is the pressure relief valve. If it does its job the boiler is usually under 20 psi