Location: Halifax, Pa
Stoker Coal Boiler: axeman anderson 130
Coal Size/Type: Pea

Post by ziggy87 » Wed. Oct. 26, 2016 9:51 pm

It is time to start installing my Axeman Anderson 130 finally. I purchased four of them at an auction two summers ago for scrap price. To my surprise one of the boilers still had all the banding and plugs in it from factory. So this is the one that I will be installing. I am heating with wood pellets right now and go through 15 tons of them a year. So with this change I am hoping to save at least $1500 a year. I have put up an out building to keep the mess out of the house. I will be piping the coal boiler into the pellet boiler so that I still have use of it for the summer time to heat my hot water.
I do have one question on putting in a chimney and that is how tall do I need to go? I am figuring on going at least bare min of 15 feet. My out building sits caddy corner to the house. The chimney will be erected on the far side of the out building 20-25 feet away from the house and 15 feet behind the house. I am hoping that I don't need to go super high to get above the house roof. Any input is much appreciated.

Jason

Attachments

20161005_171605.jpg
.JPG | 190.5KB | 20161005_171605.jpg
20161005_155639.jpg
.JPG | 198.5KB | 20161005_155639.jpg
20161005_155619.jpg
.JPG | 135.5KB | 20161005_155619.jpg
20161005_155604.jpg
.JPG | 144.9KB | 20161005_155604.jpg


 
User avatar
coaledsweat
Site Moderator
Posts: 13763
Joined: Fri. Oct. 27, 2006 2:05 pm
Location: Guilford, Connecticut
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea

Post by coaledsweat » Wed. Oct. 26, 2016 10:15 pm

They don't need a lot of chimney. Axemans essentially die when the blower isn't running because no air will come through 6-8" of ash without the blower running. :)

 
ziggy87
Member
Posts: 311
Joined: Sat. Oct. 25, 2014 11:22 am
Location: Halifax, Pa
Stoker Coal Boiler: axeman anderson 130
Coal Size/Type: Pea

Post by ziggy87 » Wed. Oct. 26, 2016 10:46 pm

coaledsweat wrote:They don't need a lot of chimney. Axemans essentially die when the blower isn't running because no air will come through 6-8" of ash without the blower running. :)
Thank you that is good to know.
Also forgot to add, possibly looking to use a digital temp controller for ashing since there was no anthrastat with the unit. Anyone with any experience on this?

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Wed. Oct. 26, 2016 10:51 pm

Here's some reading at Link >>> How Should an AA130's Fire Look at Full Burn?

 
User avatar
Rob R.
Site Moderator
Posts: 17979
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Thu. Oct. 27, 2016 6:34 am

I will be piping the coal boiler into the pellet boiler so that I still have use of it for the summer time to heat my hot water.
??? You want to use the pellet boiler in the summer? That doesn't make any sense to me - either run the AA130 or put in an electric or gas water heater.

 
ziggy87
Member
Posts: 311
Joined: Sat. Oct. 25, 2014 11:22 am
Location: Halifax, Pa
Stoker Coal Boiler: axeman anderson 130
Coal Size/Type: Pea

Post by ziggy87 » Thu. Oct. 27, 2016 8:54 am

Thank you for the reading material McGiever. That is the route that I will be going. As for using the pellet boiler in the summer I only average 15 to 20 pounds of pellets a day to heat hot water via two 40 gallon indirects. One is for me and the other is for my parents. We have a duplex house. I only use about a ton of pellets in the summer.

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Thu. Oct. 27, 2016 9:03 am

ziggy87 wrote:Thank you for the reading material McGiever. That is the route that I will be going. As for using the pellet boiler in the summer I only average 15 to 20 pounds of pellets a day to heat hot water via two 40 gallon indirects. One is for me and the other is for my parents. We have a duplex house. I only use about a ton of pellets in the summer.
I go through only about 13 to 13.5 lbs. of coal per day during the non heating months to provide for our homes DHW. Thats less by weight, and also by cost, than for your pellet stoves DHW performance. My AHS S130 and your AA-130 are close cousins.


 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Thu. Oct. 27, 2016 9:10 am

lsayre wrote:
ziggy87 wrote:Thank you for the reading material McGiever. That is the route that I will be going. As for using the pellet boiler in the summer I only average 15 to 20 pounds of pellets a day to heat hot water via two 40 gallon indirects. One is for me and the other is for my parents. We have a duplex house. I only use about a ton of pellets in the summer.
I go through only about 13 to 13.5 lbs. of coal per day during the non heating months to provide for our homes DHW. Thats less by weight, and also by cost, than for your pellet stoves DHW performance. My AHS S130 and your AA-130 are close cousins.
Larry,
Not apples to apples if he is doing 2 households to your 1. :)

Bet you got him beat on ash output though. :P

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Thu. Oct. 27, 2016 9:17 am

McGiever wrote:
lsayre wrote: I go through only about 13 to 13.5 lbs. of coal per day during the non heating months to provide for our homes DHW. Thats less by weight, and also by cost, than for your pellet stoves DHW performance. My AHS S130 and your AA-130 are close cousins.
Larry,
Not apples to apples if he is doing 2 households to your 1. :)

Bet you got him beat on ash output though. :P
I should read more closely. As to the ash of coal vs. wood, that's one fight that coal will never win, not only with regard to DHW, but with regard to any use.

Pellets generally have about 0.8% ash by weight on paper (under strict lab conditions), and perhaps 1.25% by weight in the real world. Coal generally has about 9.5% ash by weight on paper (under strict lab conditions), and about 15% to 17% by weight in the real world.
Last edited by lsayre on Thu. Oct. 27, 2016 9:24 am, edited 1 time in total.

 
User avatar
coaledsweat
Site Moderator
Posts: 13763
Joined: Fri. Oct. 27, 2006 2:05 pm
Location: Guilford, Connecticut
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea

Post by coaledsweat » Thu. Oct. 27, 2016 9:23 am

ziggy87 wrote:Thank you that is good to know.
Also forgot to add, possibly looking to use a digital temp controller for ashing since there was no anthrastat with the unit. Anyone with any experience on this?
Best to just buy an anthrastat from Axeman, a beginner doesn't need a science project to add to their adventure. :)

 
cabinover
Member
Posts: 2344
Joined: Wed. Feb. 04, 2009 7:13 am
Location: Fair Haven, VT
Stoker Coal Boiler: Hybrid Axeman Anderson 130
Baseburners & Antiques: Sparkle #12
Coal Size/Type: Pea, Buckwheat, Nut
Other Heating: LP Hot air. WA TX for coal use.

Post by cabinover » Thu. Oct. 27, 2016 4:56 pm

And the anthrastat is so easy once dialed in. Set it and forget it...until it warms up outside...then adjust slightly.

 
User avatar
coaledsweat
Site Moderator
Posts: 13763
Joined: Fri. Oct. 27, 2006 2:05 pm
Location: Guilford, Connecticut
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea

Post by coaledsweat » Thu. Oct. 27, 2016 5:54 pm

cabinover wrote:And the anthrastat is so easy once dialed in. Set it and forget it...until it warms up outside...then adjust slightly.
Yup, just don't touch the dial, you can only adjust it with an allen wrench. Touching the dial itself will screw up the calibration. That is how it is calibrated, with the knob. Once everything is set right, you do nothing forever. :)

 
User avatar
Rob R.
Site Moderator
Posts: 17979
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Thu. Oct. 27, 2016 6:46 pm

Heating domestic hot water for two homes is actually better - because there is a better chance of the BTU's produced by the idling boiler going into the domestic hot water rather than the atmosphere. If it were me I would probably try running the AA and see how it does, but to each their own.

 
User avatar
coaledsweat
Site Moderator
Posts: 13763
Joined: Fri. Oct. 27, 2006 2:05 pm
Location: Guilford, Connecticut
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea

Post by coaledsweat » Thu. Oct. 27, 2016 6:59 pm

Another weird trait of the Axeman design, they don't give up a lot of heat. When I had my handfired, the cellar was warm as toast. WIth the Axeman, it's a bit chilly even standing next to it.

 
User avatar
mozz
Member
Posts: 1351
Joined: Mon. Sep. 17, 2007 5:27 pm
Location: Wayne county PA.
Stoker Coal Boiler: Axeman Anderson 1982 AA-130 Steam

Post by mozz » Fri. Oct. 28, 2016 7:26 pm

I get plenty of heat from the axeman, keeps my entire basement warm year round. The aa130 actually wastes coal in the summer(incomplete burn) and it would be cheaper to use electric for water heating, I run 24/7/365 though, it prolongs the life of the boiler and dries out the basement every time is rains.