The Van Wert VA600 Project

 
Dave 1234
Member
Posts: 788
Joined: Tue. Nov. 13, 2012 9:05 am
Stoker Coal Boiler: 1948 International boiler, EFM S-20 stoker
Coal Size/Type: Buck,

Post by Dave 1234 » Mon. Dec. 25, 2017 12:18 pm

Love the new fire door Don !

Merry Christmas !!

Dave


 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sun. Dec. 31, 2017 6:46 pm

Meter reading today was, 3819.3 - 3758.1 = 61.2 hours over the passed 7 days, 8.74 hours per day, times 12.25 pound per hour = 107.1 pounds per day. WOW!
IMG_1933.JPG
.JPG | 338.7KB | IMG_1933.JPG
IMG_1934.JPG
.JPG | 294.4KB | IMG_1934.JPG
So, we're back in the 100+ pound per day club. It has been very cold though, down in the ice box, below 30 degrees for the passed week and the temps aren't going up at all in the forecast. I don't feel to bad though, I'm in good company. Many other members are reporting over 100 pounds per day in this cold stretch.

Gofer.
IMG_1937.JPG
.JPG | 445.9KB | IMG_1937.JPG
In other news, earlier in the week I put together the doghouse stoker cover from the other VA-600 and installed it on this one. It fits real good and keeps the stoker a little bit quieter.
IMG_1935.JPG
.JPG | 304.6KB | IMG_1935.JPG
IMG_1936.JPG
.JPG | 257.4KB | IMG_1936.JPG
The Van Wert is doing a great job of keeping up with this cold weather. It's running pretty hard, 8.74 hours per day. I have thought about bumping the feed rate up from 12.25 to 15 pounds per hour. I'm not 100% sure that would help.

-Don

 
User avatar
Rob R.
Site Moderator
Posts: 17980
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Sun. Dec. 31, 2017 9:30 pm

Don, 8 hrs out of 24 is just a trot.

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sun. Jan. 07, 2018 6:57 pm

Rob R. wrote:
Sun. Dec. 31, 2017 9:30 pm
Don, 8 hrs out of 24 is just a trot.
I guess you're right Rob. This is the first real Winter we have had since I put the boiler in the basement. I've gotten used to 4 hour a day run times.

Meter reading Friday was, 3863.0 - 3819.3 = 43.7 hours over the passed 5 days, 8.74 hours per day, times 12.25 pound per hour = 107.1 pounds per day. The Axeman Anderson has been pushing heat into the house since Friday so we won't count those days.
Wow, that's interesting, those 5 days average run time was exactly the same as last week 8.74 hours!
IMG_2035.JPG
.JPG | 313.7KB | IMG_2035.JPG
IMG_2036.JPG
.JPG | 316.8KB | IMG_2036.JPG
Gofer action.
IMG_2038.JPG
.JPG | 446KB | IMG_2038.JPG
The Axeman Anderson in the garage is constantly pushing 170 degree water into the return of the Van Wert.
IMG_2037.JPG
.JPG | 316.9KB | IMG_2037.JPG
For the receord, the Van Wert ran for 4.5 hours over the passed 2 days, 27.6 pounds per day.

-Don

 
User avatar
Rob R.
Site Moderator
Posts: 17980
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Sun. Jan. 07, 2018 7:20 pm

Don, what are the milk crates for next to the boiler?

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sun. Jan. 07, 2018 7:32 pm

Rob R. wrote:
Sun. Jan. 07, 2018 7:20 pm
Don, what are the milk crates for next to the boiler?
They are for standing on. The plumbing and wiring are up in the floor joists. The coal bin is 6 feet high to. You need something to stand on to see what the gofer is doing.

Your not going to turn me in to the milk police, are you?

-Don

 
LehighanthraciteMatt
Verified Business Rep.
Posts: 742
Joined: Thu. Sep. 29, 2016 1:02 pm
Stoker Coal Boiler: Van Wert
Hot Air Coal Stoker Stove: Alaska
Hand Fed Coal Stove: Warm Morning
Coal Size/Type: Rice,Buck, and Nut

Post by LehighanthraciteMatt » Mon. Jan. 08, 2018 4:20 pm

StokerDon wrote:
Sun. Jan. 07, 2018 7:32 pm
They are for standing on. The plumbing and wiring are up in the floor joists. The coal bin is 6 feet high to. You need something to stand on to see what the gofer is doing.

Your not going to turn me in to the milk police, are you?

-Don
:lol:


 
User avatar
Rob R.
Site Moderator
Posts: 17980
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Mon. Jan. 08, 2018 4:41 pm

The black Suburbans are already on their way.

 
titleist1
Member
Posts: 5226
Joined: Wed. Nov. 14, 2007 4:06 pm

Post by titleist1 » Mon. Jan. 08, 2018 5:09 pm

8-) Don't tell Lightning but the black suburbans have to stop at his place first because of his unauthorized use of the bread trays as coal sifters! :stfu:

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sat. Jan. 13, 2018 2:44 pm

For the passed week or so, I have been running an Axeman Anderson 130M out in the garage pumping it through the Van Wert to heat the house. I was trying to keep the Van Wert lit by having the HI limit slightly lower than the Axeman. That didn't work out to well, so the Van Wert went out on Wednesday.

Since it is taking it's heat from the Axeman in the garage, I was worried that the chimney draft would steal some of the heat.
IMG_2061.JPG
.JPG | 257.2KB | IMG_2061.JPG
IMG_2062.JPG
.JPG | 302.4KB | IMG_2062.JPG
I took an old piece of 8" pipe and used it as a block off for the pipe coming up out of the Van Wert.
IMG_2063.JPG
.JPG | 323.9KB | IMG_2063.JPG
IMG_2065.JPG
.JPG | 297.7KB | IMG_2065.JPG
There we go, no more heat sucking draft.
IMG_2066.JPG
.JPG | 291.1KB | IMG_2066.JPG
The Axeman is sending about 160 - 170.
IMG_2069.JPG
.JPG | 378.4KB | IMG_2069.JPG
The Van Wert is pushing out about the same.
IMG_2068.JPG
.JPG | 269.8KB | IMG_2068.JPG
The aquastat Hi and LO limits are turned all the way down to prevent the stoker from running.
IMG_2067.JPG
.JPG | 331.8KB | IMG_2067.JPG
This allows us to run all the controls as if the Van Wert were fired up.

-Don

 
User avatar
Lightning
Site Moderator
Posts: 14659
Joined: Wed. Nov. 16, 2011 9:51 am
Location: Olean, NY
Stoker Coal Boiler: Modified AA 130
Coal Size/Type: Pea Size - Anthracite

Post by Lightning » Sun. Jan. 14, 2018 12:25 pm

titleist1 wrote:
Mon. Jan. 08, 2018 5:09 pm
8-) Don't tell Lightning but the black suburbans have to stop at his place first because of his unauthorized use of the bread trays as coal sifters! :stfu:
Oh no! Time to hide the contraband!

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Fri. Mar. 09, 2018 7:09 pm

It's been about two months now that the Van Wert has been without a fire. Today I figured out that if I run the pump on the Van Wert 24/7 rather than the pump on the Axeman Anderson in the garage, I should be able to keep both fires going.
IMG_2292.JPG
.JPG | 313.5KB | IMG_2292.JPG
3873.5 hours.
IMG_2299.JPG
.JPG | 535.8KB | IMG_2299.JPG
Draft -.02
IMG_2295.JPG
.JPG | 341.3KB | IMG_2295.JPG
Supply 176 degrees.
IMG_2296.JPG
.JPG | 294.3KB | IMG_2296.JPG
Return 160 ish degrees.
IMG_2297.JPG
.JPG | 324.7KB | IMG_2297.JPG
Stack 350 degrees.
IMG_2298.JPG
.JPG | 317.9KB | IMG_2298.JPG
I raked the bin level. It looks like there is a little lees than 3 ton left. That will last quite a while because we are less than 2 weeks from Spring.
IMG_2294.JPG
.JPG | 385.4KB | IMG_2294.JPG
So, this is now set up to run constant circulation and the PEX loop to the garage is just another zone, but it is open all the time. This will make the garage boiler constantly warm, but if the garage radiator calls the garage boiler for heat it will start stoking. This way we should be able to keep both boilers from going out.

-Don

 
User avatar
BunkerdCaddis
Member
Posts: 708
Joined: Sun. Jan. 18, 2015 10:26 am
Location: SW Lancaster County
Stoker Coal Boiler: Bairmatic-Van Wert
Hand Fed Coal Boiler: Van Wert VW85H
Hand Fed Coal Stove: Saey Hanover II working when I feel the desire, Waterford 105 out on vacation, Surdiac Gotha hiding somewhere
Coal Size/Type: pea/nut/rice/stove-anthracite, nut/stove bit when I feel the urge
Other Heating: oil fired hydronic

Post by BunkerdCaddis » Fri. Mar. 09, 2018 10:57 pm

Oh Great, now that you've figured out how little coal you can burn with the boilers, you realize it's not enough coal being burned to keep the addiction happy... :what: I'm telling you... A primary/secondary loop with a logic controller that switches between boilers for heat calls is what you need... :lol: :yes: :out:

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sun. Mar. 11, 2018 6:33 pm

Getting these two boilers to balance is a little tricky. This is all manual so it's cracking valves and adjusting aquastats trying to keep one boiler from overheating the other and keeping them both from going out.

Meter reading Friday was, 3884.2 - 3873.5 = 10.7 hours over the passed 2 days, 5.35 hours per day, times 12.25 pound per hour = 65.5 pounds per day.
IMG_2321.JPG
.JPG | 214.5KB | IMG_2321.JPG
IMG_2322.JPG
.JPG | 109KB | IMG_2322.JPG
IMG_2323.JPG
.JPG | 399.4KB | IMG_2323.JPG
Got a pretty good gofer hole already!
IMG_2324.JPG
.JPG | 499.2KB | IMG_2324.JPG
IMG_2325.JPG
.JPG | 538.5KB | IMG_2325.JPG
-Don

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sun. Mar. 18, 2018 7:10 pm

Meter reading Friday was, 3898.8 - 3884.2 = 14.6 hours over the passed 5 days, 2.9 hours per day, times 12.25 pound per hour = 35.8 pounds per day.
We shut down the Van Wert again on Friday. The Axeman Anderson in the garage is carrying the full load right now.
IMG_2373.JPG
.JPG | 330.7KB | IMG_2373.JPG
IMG_2374.JPG
.JPG | 490.6KB | IMG_2374.JPG
IMG_2375.JPG
.JPG | 295.6KB | IMG_2375.JPG
IMG_2376.JPG
.JPG | 365.8KB | IMG_2376.JPG
IMG_2377.JPG
.JPG | 424.2KB | IMG_2377.JPG
-Don