Re: EFM Pressure Is Too High

Posted: Mon. Feb. 11, 2008 11:19 pm
by Yanche
e.alleg wrote:If you put in a new one do yourself a favor and install ball or gate valves on both sides of it. I forgot to put one on the boiler side of mine, so even though it needs changing I really don't feel like draining the boiler. Live and learn.
Also install with pipe unions. Pipe it in such a way that you can pry the pipe so you can easily get it apart.

Re: EFM Pressure Is Too High

Posted: Mon. Feb. 11, 2008 11:31 pm
by e.alleg
This is actually one area where I screwed up when I installed my boiler. I wasn't sure if coal was going to work for me so I saved myself a bunch of money and used all leftover iron pipe and no unions or ball valves. Well, uh, now that the thing is working great I have to use a sawzall and take it all apart if there is a leak or something needs to be changed. In the summer I'm going to re plumb it with all copper and put ball valves on each side of every component that can break or need service. It sucks having to drain the boiler for a simple repair, a 10 minute job turns into an all day affair.

Re: EFM Pressure Is Too High

Posted: Tue. Feb. 12, 2008 5:55 am
by stoker-man
I have unions and shut-offs at my coil, shut-off flanges at the circulator and numerous ball valves at all other places. Besides being bad for fresh water to be added to a boiler, it's also a pain to re-purge the thing.

You might want to add some water conditioner while you're down. I drained a bit of water from my boiler recently and it was still milky white.

Re: EFM Pressure Is Too High

Posted: Tue. Feb. 12, 2008 7:49 am
by coaledsweat
If you have a few zone valves and isolation valves in the system, you won't lose much water anyway. Shut off the power so no zones open, close all isolation valves, bleed off the pressure and service it. You will lose a little water but not much, you can catch it in a pot or bucket. I change pumps like this all the time. If you only punch one hole in a juice can, how much juice do you get?

Re: EFM Pressure Is Too High

Posted: Thu. Feb. 14, 2008 5:46 am
by stoker-man
Dave, Have you figured out the problem yet?

Re: EFM Pressure Is Too High

Posted: Thu. Feb. 14, 2008 9:23 pm
by Scottscoaled
How come the pressure releif valve isn't blowing off. I thought they go at 30lbs. And you are reading 33#? Sure your pressure gauge is right? :?

Re: EFM Pressure Is Too High

Posted: Sat. Feb. 16, 2008 10:52 pm
by LsFarm
e.alleg wrote:If you put in a new one do yourself a favor and install ball or gate valves on both sides of it. I forgot to put one on the boiler side of mine, so even though it needs changing I really don't feel like draining the boiler. Live and learn.
a valve on both sides and dont' forget a union, then it is real simple to swap out the regulator... My first house had pretty poor water, and I had to replace the fill valve about every three years... it just started to over pressure the boiler.

Greg L

.

Re: EFM Pressure Is Too High

Posted: Sat. Feb. 16, 2008 11:35 pm
by gaw
I think the pressure reducing auto fill valves are a waste of money. Actually you are spending money now to give you problems down the road. I installed a gate valve in my fill line at a place where I could operate the valve while watching the pressure gauge on the boiler. Simple, works well, and cheap. What more could you want? This is the way many boiler were installed years ago so there is also a 50 year history of doing it this way without any issues. If you use an auto fill and shut the boiler down in the "off season" I would have a valve between the boiler and auto fill and shut this valve before allowing the fire to go out and the water to cool down. If you don't the auto fill valve will add water as the pressure drops and you will have higher pressure next season when the boiler heats up.
Just my thoughts, worth every penny you paid for them :lol: :)

Re: EFM Pressure Is Too High

Posted: Sun. Feb. 17, 2008 11:18 am
by Bob
gaw wrote:I think the pressure reducing auto fill valves are a waste of money. Actually you are spending money now to give you problems down the road. I installed a gate valve in my fill line at a place where I could operate the valve while watching the pressure gauge on the boiler. Simple, works well, and cheap. What more could you want? This is the way many boiler were installed years ago so there is also a 50 year history of doing it this way without any issues. If you use an auto fill and shut the boiler down in the "off season" I would have a valve between the boiler and auto fill and shut this valve before allowing the fire to go out and the water to cool down. If you don't the auto fill valve will add water as the pressure drops and you will have higher pressure next season when the boiler heats up.
Just my thoughts, worth every penny you paid for them :lol: :)
There is a potential safety issue ff there is no auto fill valve and no low water shut off--if a slow leak develops and the water level drops in the boiler it is possible for the boiler to fire continuously because there is inadequate heat transfer to the aqua stat that is no longer in water. I would add that auto fill valves are a lot cheaper than low water shut off controls--and more reliable.

Re: EFM Pressure Is Too High

Posted: Sun. Feb. 17, 2008 2:41 pm
by Yanche
Bob wrote:
gaw wrote:I think the pressure reducing auto fill valves are a waste of money. Actually you are spending money now to give you problems down the road. I installed a gate valve in my fill line at a place where I could operate the valve while watching the pressure gauge on the boiler. Simple, works well, and cheap. What more could you want? This is the way many boiler were installed years ago so there is also a 50 year history of doing it this way without any issues. If you use an auto fill and shut the boiler down in the "off season" I would have a valve between the boiler and auto fill and shut this valve before allowing the fire to go out and the water to cool down. If you don't the auto fill valve will add water as the pressure drops and you will have higher pressure next season when the boiler heats up.
Just my thoughts, worth every penny you paid for them :lol: :)
There is a potential safety issue ff there is no auto fill valve and no low water shut off--if a slow leak develops and the water level drops in the boiler it is possible for the boiler to fire continuously because there is inadequate heat transfer to the aqua stat that is no longer in water. I would add that auto fill valves are a lot cheaper than low water shut off controls--and more reliable.
I use automatic fill valves because they do give some protection against the loss of boiler water and potential overheating. I guess with sufficient overheating without water the overtemp safety aquast would eventually trip. I always pipe a water by-pass around the auto fill valve. This allows me to get full water pressure and flow into the boiler when power purging the heating system. I find the automatic fill valves to be very unreliable. They are constantly getting stuck. The tiny needle valve corrodes in place and no water will flow. It's easily cleaned upon dis-assembly.

My goal is to have a system free of leaks so no make up water is needed. Like a refrigerant loop. It's a illusive goal because in spite of my best efforts there are leaks at valve stems. Not so much water leaking out but air leaking in. When a system cools it's pressure drops allowing air in. This air is eventually purged taking with it some water. I also find leaks at the automatic air vents, both water out and air in depending on the level of the float in it. So I normally have the metal tire valve cap screwed down tight. Like gaw says, my pennys worth.

Re: EFM Pressure Is Too High

Posted: Sun. Feb. 17, 2008 2:45 pm
by stoker-man
In PA, there was a rumor going around by our dealers that a low water cutoff was required/or going to be required on all residential hot water and steams boilers. I contacted the local state rep and found this to be untrue.

Last week we started supplying low water cutoffs to any steam boiler sale because our dealers were saying they were required, possibly by local codes.

As far a ANY commercial use for a hot water or steam unit, two low water cutoffs are required by L&I. Also, ANY commercial application in PA requires a coded boiler. It was rumored that Key Stoker was going to get out of the commercial end of the boiler business because of this requirement. Coding adds about $2000 to the cost of a boiler. At efm, we have been making ALL boilers coded for many years.

I asked our local L&I inspector, Nate Smith, how he determines what is a commercial business. He says, anything with a sign outside qualifies. He created a big stir in Harrisburg when he forced a state legislator in NE PA to remove an almost-new boiler in his home office (commercial) because it wasn't coded. There was alot of pressure put upon him in Harrisburg to back down, which he did not do. You do not want to see Nate knocking at your door if your boiler is not registered with the state.

For the above reason, whether required or not, an auto-fill valve is a good idea if you don't have a low water cutoff. A boiler can develop a small leak and go unnoticed, and because the water evaporates before hitting the floor, you won't notice it. Without the auto-fill valve, your water level will drop. The first sign will be that your hot water coil will stop producing hot water and if the water turns to steam you will have a vessel pressurized at least at 30# psi with steam; an invitation to an explosion. An efm steam boiler normally runs at 1 1/2# pounds of steam with a 10# pressure relief valve.

I would have either an auto-fill valve, or a low-water cutoff on any boiler and for this reason many municipalities are requiring one or both.

Re: EFM Pressure Is Too High

Posted: Sun. Feb. 17, 2008 3:25 pm
by Yanche
stoker-man wrote:I asked our local L&I inspector, Nate Smith, how he determines what is a commercial business. He says, anything with a sign outside qualifies. He created a big stir in Harrisburg when he forced a state legislator in NE PA to remove an almost-new boiler to be removed because it wasn't coded. There was alot of pressure put upon him in Harrisburg to back down, which he did not do. You do not want to see Nate knocking at your door if your boiler is not registered with the state.
Well, I guess the state legislator won. PA passed an amendment to their Mechanical Code that had required coded boiler in residences. See the PA Senate version of what got passed in the attached pdf. Any chance one of the bill's sponsor is the person?

Re: EFM Pressure Is Too High

Posted: Sun. Feb. 17, 2008 3:54 pm
by e.alleg
in reading that link, it seems the only difference between a boiler with the stamp and one that doesn't have the stamp is simply the physical stamp?

Re: EFM Pressure Is Too High

Posted: Sun. Feb. 17, 2008 6:07 pm
by coaledsweat

Re: EFM Pressure Is Too High

Posted: Sun. Feb. 17, 2008 6:30 pm
by stoker-man
I don't think the state legislator won. His office was considered commercial because there were employees on site and I know that the boiler was removed. This was about two years ago.

As far as I know, residences are not required to have coded boilers, but commercial places have been.

I edited my original post to read "residential" in the first sentence. I was carrying over a thought from another's post and residential was implied and I didn't differentiate.

I also edited to show that the state legislator's office was considered commercial because it employed at least one person.