Stoker Coal Boilers automatically feed the coal and have controls and pumps just like any conventions boiler. They are intended to be used as a primary heat and often have domestic hot water coils as an added bonus. They can be set up independently or in dual sytem with your existing oil/gas boiler. They can accommodate both hot water base board or steam plumbing.
metrodave
New Member
Posts: 3
Joined: Sun. Feb. 10, 2008 12:34 pm
Stove/Furnace Make: EFM
Stove/Furnace Model: so old i cant tell

Post Sun. Feb. 10, 2008 2:42 pm

My efm has worked fine since I moved into this house 7 years ago. Lately the pressure has been going over 30# and will not come down unless I trip the releif valve. Looked over all the post in here and only conclusion I can come up with is maybe my coil is clogged. Looks like there is some rust spots on back of unit around coil plate. I drained all lines to copper heating units, thought I had air in lines. I am at a loss. Can anyone help.

Visit Alternate Heating Sytems

User avatar
Dallas
Member
Posts: 744
Joined: Mon. Nov. 12, 2007 12:14 pm
Hand Fed Coal Stove: Modified Russo C-35
Other Heating: Oil Hot Air
Stove/Furnace Make: Russo
Stove/Furnace Model: Modified C-35
Location: NE-PA

Post Sun. Feb. 10, 2008 4:56 pm

If you have a domestic hot water coil in the boiler, it could be leaking water into the water jacket. The domestic line will be of a higher pressure.

metrodave
New Member
Posts: 3
Joined: Sun. Feb. 10, 2008 12:34 pm
Stove/Furnace Make: EFM
Stove/Furnace Model: so old i cant tell

Post Sun. Feb. 10, 2008 5:13 pm

Dallas wrote:If you have a domestic hot water coil in the boiler, it could be leaking water into the water jacket. The domestic line will be of a higher pressure.
On another post someone said, if you release the pressure and turn off all the water into the unit that pressure should not rise. Unless of course there is a pinhole leak in the coil.

User avatar
Dallas
Member
Posts: 744
Joined: Mon. Nov. 12, 2007 12:14 pm
Hand Fed Coal Stove: Modified Russo C-35
Other Heating: Oil Hot Air
Stove/Furnace Make: Russo
Stove/Furnace Model: Modified C-35
Location: NE-PA

Post Sun. Feb. 10, 2008 5:18 pm

If you have the domestic coil, you have two water inputs into your boiler ... the "domestic hot water" and the "boiler feed". If it isn't the domestic coil, it would be in the "boiler feed". Eliminate one or the other. Of course, shutting off the boiler feed would disrupt your life less, while troubleshooting.

User avatar
stoker-man
Verified Business Rep.
Posts: 2063
Joined: Mon. Nov. 19, 2007 9:33 pm
Hand Fed Coal Boiler: 1981 efm wcb-24 in use 365 days a year
Coal Size/Type: Anthracite/Chestnut
Other Heating: Hearthstone wood stove
Location: Lehigh Valley, PA

Post Sun. Feb. 10, 2008 5:23 pm

You only have to turn off the water supply to the inlet and outlet of the coil. If the pressure remains within range, (boiler temperature will determine pressure), you have found your problem as a pinhole leak in the coil. Is your water acidic?

If the pressure still climbs, turn off the water make-up to the boiler and open up the coil again. The problem will then be in the pressure reducing valve.

Another potential problem is a broken bladder in the expansion tank, or a full ceiling-hung expansion tank. If the boiler is left to cool down, the pressure will drop.

Check these out and get back to us.
‹(•¿•)›

User avatar
stoker-man
Verified Business Rep.
Posts: 2063
Joined: Mon. Nov. 19, 2007 9:33 pm
Hand Fed Coal Boiler: 1981 efm wcb-24 in use 365 days a year
Coal Size/Type: Anthracite/Chestnut
Other Heating: Hearthstone wood stove
Location: Lehigh Valley, PA

Post Sun. Feb. 10, 2008 5:24 pm

Sorry Dallas, we're typing at the same time :)
‹(•¿•)›

User avatar
Dallas
Member
Posts: 744
Joined: Mon. Nov. 12, 2007 12:14 pm
Hand Fed Coal Stove: Modified Russo C-35
Other Heating: Oil Hot Air
Stove/Furnace Make: Russo
Stove/Furnace Model: Modified C-35
Location: NE-PA

Post Sun. Feb. 10, 2008 5:26 pm

stoker-man wrote:Sorry Dallas, we're typing at the same time :)
I thought you were out on a service call. :)

User avatar
e.alleg
Member
Posts: 1285
Joined: Fri. Feb. 16, 2007 10:31 am
Stove/Furnace Make: EFM
Stove/Furnace Model: 520
Location: western ny

Post Sun. Feb. 10, 2008 6:37 pm

what's the water temp? Mine will get up to 26-27 psi at 220 degrees, at 60 degrees it's 15psi. My tank is too small technically speaking, but the pressures stay within acceptable limits and never exceed the PRV 30psi rating so I live with it. put a bucket under the PRV pipe and see if it fills up, if it doesn't then don't worry about it.
Burning coal is definitely worth the extra work involved.
"Good enough" is not good enough.

Visit Alternate Heating Sytems

metrodave
New Member
Posts: 3
Joined: Sun. Feb. 10, 2008 12:34 pm
Stove/Furnace Make: EFM
Stove/Furnace Model: so old i cant tell

Post Sun. Feb. 10, 2008 7:02 pm

stoker-man wrote:You only have to turn off the water supply to the inlet and outlet of the coil. If the pressure remains within range, (boiler temperature will determine pressure), you have found your problem as a pinhole leak in the coil. Is your water acidic?

If the pressure still climbs, turn off the water make-up to the boiler and open up the coil again. The problem will then be in the pressure reducing valve.

Another potential problem is a broken bladder in the expansion tank, or a full ceiling-hung expansion tank. If the boiler is left to cool down, the pressure will drop.

Check these out and get back to us.
OK, dropped the pressure in the unit. Then I closed off the inlet and outlet of the coil. Water pressure went to about 33#. Dropped the pressure again, opened both valves and closed the make-up valve. water pressure stayed the same. The entire time I was maintaining a temp of about 190 degrees. The expansion tank is new because the bladder got a hole in it, I"m thinking maybe water is acidic. Would also like to know what kind of pressure should be in the expansion tank. When I checked it after doing your test it showed 22# . Just another note, maybe this is a combination coil and reducer problem. When my wife turned on the hot water after the tests it was all dirty looking. Thank you for all the help so far.
P.S. It is too darn cold to turn off this baby.

User avatar
stoker-man
Verified Business Rep.
Posts: 2063
Joined: Mon. Nov. 19, 2007 9:33 pm
Hand Fed Coal Boiler: 1981 efm wcb-24 in use 365 days a year
Coal Size/Type: Anthracite/Chestnut
Other Heating: Hearthstone wood stove
Location: Lehigh Valley, PA

Post Sun. Feb. 10, 2008 9:54 pm

opened both valves and closed the make-up valve. water pressure stayed the same.
What was the pressure? zero or 33?

Drain the boiler just enough to reduce the pressure to zero. Measure the pressure at the tank. The expansion tank should be pre-set to around 12#. If not, let some air out (or add).

Probably the rush of water into the coil when you opened the valves stirred up some sediment inside the coil. Nothing to worry about.

Your test kind of rules out the coil. Where else could unauthorized water be entering the boiler system?

By the way, if you have rust around the coil gasket, it's because it leaked in the past. Tighten up the coil nuts a little each year. In the worst case scenario, a patch plate is available to repair that area. See the pictorials of the boiler.
‹(•¿•)›

User avatar
stoker-man
Verified Business Rep.
Posts: 2063
Joined: Mon. Nov. 19, 2007 9:33 pm
Hand Fed Coal Boiler: 1981 efm wcb-24 in use 365 days a year
Coal Size/Type: Anthracite/Chestnut
Other Heating: Hearthstone wood stove
Location: Lehigh Valley, PA

Post Sun. Feb. 10, 2008 9:55 pm

You say your boiler is "so old". What is the serial number?
‹(•¿•)›

User avatar
e.alleg
Member
Posts: 1285
Joined: Fri. Feb. 16, 2007 10:31 am
Stove/Furnace Make: EFM
Stove/Furnace Model: 520
Location: western ny

Post Sun. Feb. 10, 2008 11:31 pm

the fill valve, or pressure reducing valve might have a strainer in it. Take it out and clean it, mine was full of junk and the thing wouldn't shut off over pressurizing the system.
Burning coal is definitely worth the extra work involved.
"Good enough" is not good enough.

Bob
Member
Posts: 304
Joined: Sun. Mar. 18, 2007 11:28 am
Stoker Coal Boiler: AHS 130
Coal Size/Type: Pea/Anthracite
Location: Schuylkill County

Post Mon. Feb. 11, 2008 8:24 am

Automatic fill valves can fail. Sounds like your may have. The solution is to replace the automatic fill valve.

User avatar
coaledsweat
Site Moderator
Posts: 9825
Joined: Fri. Oct. 27, 2006 2:05 pm
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea
Location: Guilford, Connecticut

Post Mon. Feb. 11, 2008 5:36 pm

If your house has 40 or more pounds of pressure and the boiler never goes over 33# its the boiler feed pressure valve. It could need adjusting, cleaning or replacement. I would start by backing off the pressure setting and blowing off the actual water pressure in the boiler. If it comes back up to a lower pressure, adjust it back to about 12-13#. If it stays there, your all set. If it climbs, then you have work to do.

It could also be your gauge is bad.
Nothing is impossible for people who don't have to do it themselves.

User avatar
e.alleg
Member
Posts: 1285
Joined: Fri. Feb. 16, 2007 10:31 am
Stove/Furnace Make: EFM
Stove/Furnace Model: 520
Location: western ny

Post Mon. Feb. 11, 2008 8:20 pm

If you put in a new one do yourself a favor and install ball or gate valves on both sides of it. I forgot to put one on the boiler side of mine, so even though it needs changing I really don't feel like draining the boiler. Live and learn.
Burning coal is definitely worth the extra work involved.