Boiler Pressure Keeps Climbing to 20

Stoker Coal Boilers automatically feed the coal and have controls and pumps just like any conventions boiler. They are intended to be used as a primary heat and often have domestic hot water coils as an added bonus. They can be set up independently or in dual sytem with your existing oil/gas boiler. They can accommodate both hot water base board or steam plumbing.
User avatar
northernmainecoal
Member
Posts: 502
Joined: Wed. Jan. 22, 2014 8:33 am
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Hitzer 30-95
Baseburners & Antiques: Herald Baseheater #6
Coal Size/Type: Rice/Nut/Stove
Location: Aroostook County, Maine

Post Mon. Apr. 14, 2014 7:34 am

Good morning
Up until this weekend the boiler pressure had been staying at just about 15 psi. I noticed Sunday that it was up to 20 psi, quite a bit higher then I'd like it to be, so I drained off a bit of water, checked the pressure and it was 13 or 14. Went back and checked an hour or so later and it was back up to 20, drained a little more water, pressure was good. Now I'm back at 20 again...obviously something isn't right or I'm doing something wrong, I don't know which. I've been using the drain just above the circ on the return. I've attached pictures of all the piping, I'm using the DHW coil in the oil boiler. another thing I should mention is there is a quiet ticking type noise coming from (I believe) the expansion tank on the EFM supply. Aquastat: 180LL 15ldf. 4 teeth, 4.5 air.
Attachments
IMG_20140414_061331.jpg
IMG_20140414_061340.jpg
IMG_20140414_061349.jpg
IMG_20140414_061405.jpg
Rob

Visit Alternate Heating Sytems

User avatar
blrman07
Member
Posts: 2379
Joined: Mon. Sep. 27, 2010 3:39 pm
Hand Fed Coal Boiler: Bucket a Day
Hand Fed Coal Stove: Vigilant Casting 2310
Coal Size/Type: Pea/Nut/Wood in the VC and anything that will fit in the Bucket a Day. It's not fussy.
Location: Girardville Pa.

Post Mon. Apr. 14, 2014 7:49 am

Your automatic pressure regulator valve that lets water in the boiler to maintain pressure is probably going bad. It's either that or your DHW coil is leaking. Cheapest way to test this is shut off the makeup water valve, return the boiler to normal pressure. If it goes up again it's your DHW coil. To verify that shut the DHW coil valves, return the boiler to regular pressure and if it doesn't go up, it's the coil.

Rev. Larry
New Beginning Church
Ashland Pa.
Rev. Larry
Ashland Pa.

1 John 1:9... If we sin and we confess that sin He is faithful and just and will forgive us and cleanse us from all unrighteousness.

User avatar
northernmainecoal
Member
Posts: 502
Joined: Wed. Jan. 22, 2014 8:33 am
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Hitzer 30-95
Baseburners & Antiques: Herald Baseheater #6
Coal Size/Type: Rice/Nut/Stove
Location: Aroostook County, Maine

Post Mon. Apr. 14, 2014 8:00 am

The valve to let water in to maintain pressure was replaced 2 or 3 years ago, do they go bad often?
Rob

User avatar
blrman07
Member
Posts: 2379
Joined: Mon. Sep. 27, 2010 3:39 pm
Hand Fed Coal Boiler: Bucket a Day
Hand Fed Coal Stove: Vigilant Casting 2310
Coal Size/Type: Pea/Nut/Wood in the VC and anything that will fit in the Bucket a Day. It's not fussy.
Location: Girardville Pa.

Post Mon. Apr. 14, 2014 8:18 am

northernmainecoal wrote:The valve to let water in to maintain pressure was replaced 2 or 3 years ago, do they go bad often?
I've had em bad out of the box. Easy way to check it. Close the water inlet to the regulator, drop your boiler pressure, see if it stays there. If it does it's the regulator.

Rev. Larry
New Beginning Church
Ashland Pa.
Rev. Larry
Ashland Pa.

1 John 1:9... If we sin and we confess that sin He is faithful and just and will forgive us and cleanse us from all unrighteousness.

User avatar
northernmainecoal
Member
Posts: 502
Joined: Wed. Jan. 22, 2014 8:33 am
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Hitzer 30-95
Baseburners & Antiques: Herald Baseheater #6
Coal Size/Type: Rice/Nut/Stove
Location: Aroostook County, Maine

Post Mon. Apr. 14, 2014 12:17 pm

Ok I shut a valve on the boiler side of the regulator there wasn't any good valve to close to stop supply to the regulator itself....Dropped the pressure and now we'll wait and see what happens.
While I was home I took a recording of the ticking/knocking noise that the expansion tank is making...any ideas on the cause?
Thanks
Attachments
data-2014-4-14-10-43-40.mp3
(276.04 KiB) Downloaded 17 times
Rob

User avatar
Carbon12
Member
Posts: 2230
Joined: Tue. Oct. 11, 2011 6:53 pm
Stoker Coal Boiler: Keystoker KA-6
Coal Size/Type: Rice/Anthracite
Other Heating: Heat Pump/Forced Hot Air Oil Furnace
Location: Harrisburg, PA

Post Mon. Apr. 14, 2014 12:22 pm

Has the boiler water temperature fluctuated significantly lately?
No matter where you go,......there you are.

User avatar
whistlenut
Member
Posts: 3549
Joined: Sat. Mar. 17, 2007 6:29 pm
Stoker Coal Boiler: AA130's,260's, AHS130&260's,EFM900,GJ & V-Wert
Hand Fed Coal Boiler: Franks,Itasca 415,Jensen, NYer 130,Van Wert
Hot Air Coal Stoker Furnace: Alaska, EFM, Keystoker, Yellow Flame
Hot Air Coal Stoker Stove: Alaska, Keystoker-2,Leisure Line
Hand Fed Coal Stove: Alaska, Gibraltar, Keystone,Vc Vigilant 2
Hand Fed Coal Furnace: Ford, Jensen, NYer, Van Wert,
Baseburners & Antiques: Glenwoods
Coal Size/Type: Barley, Buck, Rice ,Nut, Stove
Other Heating: Oil HWBB
Location: Central NH, Concord area

Post Mon. Apr. 14, 2014 12:33 pm

Don't forget that the pressure will rise as the boiler temp does. If 20 psi is all you see, relax. The PRV blows at 30, so you have a looooong way to get to that point. It could be lots of things, so shutting down the boiler feed is a good 'first look'. Hard water can corrode the inside of the valve. However if that is not the issue, look toward the domestic coil...could have a pinhole starting.

Don't overlook the expansion tank either. Tap if with your knuckles and evaluate the sound. If you are short on valves to isolate, I'd give some serious thought to resolving that issue.
"Political correctness is a doctrine, fostered by a delusional, illogical minority, and rabidly promoted by an unscrupulous mainstream media, which holds forth the proposition that it is entirely possible to pick up a 'piece of human solid waste' by the clean end." More true today....

User avatar
northernmainecoal
Member
Posts: 502
Joined: Wed. Jan. 22, 2014 8:33 am
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Hitzer 30-95
Baseburners & Antiques: Herald Baseheater #6
Coal Size/Type: Rice/Nut/Stove
Location: Aroostook County, Maine

Post Mon. Apr. 14, 2014 1:03 pm

The biggest drop in temp was about a month ago (I think) I had a shear pin break and the water got down to 135-140. Other than that the water temp stays within the 15 degree diff.

I was under the impression the expansion tanks would absorb any rise in pressure when the water heats? I do need to work on adding more valves, the newly installed section is in good shape, but the rest could stand to be cleaned up and have more valves added...it's on the never ending to do list
Rob

Visit Alternate Heating Sytems

User avatar
Sting
Member
Posts: 2970
Joined: Mon. Feb. 25, 2008 4:24 pm
Other Heating: OBSO Lennox Pulse "Air Scorcher" burning NG
Location: Lower Fox Valley = Wisconsin

Post Mon. Apr. 14, 2014 2:49 pm

long read - but the link I posted in this thread appeared to have helped the OP and his pressure drama

maybe you too??
When you turn your boiler on -Does it return the favor?
I have finally lost my mind. Don't bother to return it. It wasn't working properly anyway!

User avatar
northernmainecoal
Member
Posts: 502
Joined: Wed. Jan. 22, 2014 8:33 am
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Hitzer 30-95
Baseburners & Antiques: Herald Baseheater #6
Coal Size/Type: Rice/Nut/Stove
Location: Aroostook County, Maine

Post Mon. Apr. 14, 2014 2:54 pm

Which thread is the link in?
Rob

User avatar
stoker-man
Verified Business Rep.
Posts: 2063
Joined: Mon. Nov. 19, 2007 9:33 pm
Hand Fed Coal Boiler: 1981 efm wcb-24 in use 365 days a year
Coal Size/Type: Anthracite/Chestnut
Other Heating: Hearthstone wood stove
Location: Lehigh Valley, PA

Post Mon. Apr. 14, 2014 3:24 pm

The expansion tank sounds hollow when you rap it with your knuckles. If you have an increase in pressure along with an increase in temperature, check the circulator. If the temperature doesn't increase, check the coil, as stated.
‹(•¿•)›

User avatar
Sting
Member
Posts: 2970
Joined: Mon. Feb. 25, 2008 4:24 pm
Other Heating: OBSO Lennox Pulse "Air Scorcher" burning NG
Location: Lower Fox Valley = Wisconsin

Post Mon. Apr. 14, 2014 3:25 pm

When you turn your boiler on -Does it return the favor?
I have finally lost my mind. Don't bother to return it. It wasn't working properly anyway!

User avatar
Lightning
Member
Posts: 8289
Joined: Wed. Nov. 16, 2011 9:51 am
Hand Fed Coal Furnace: Overmodified/Bored out Clayton 1537
Coal Size/Type: Anthracite/Awesome Size
Location: Olean, NY

Post Mon. Apr. 14, 2014 4:28 pm

Its possible the expansion tank is water logged and can't take any expansion...

But likely the other possibilities already mentioned...

User avatar
McGiever
Member
Posts: 5997
Joined: Sun. May. 02, 2010 11:26 pm
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Coal Size/Type: PEA / ANTHRACITE
Other Heating: Ground Source Heat Pump
Stove/Furnace Make: Hydro Heat /Mega Tek
Location: Junction of PA-OH-WV

Post Mon. Apr. 14, 2014 4:59 pm

northernmainecoal wrote:The biggest drop in temp was about a month ago (I think) I had a shear pin break and the water got down to 135-140. Other than that the water temp stays within the 15 degree diff.

I was under the impression the expansion tanks would absorb any rise in pressure when the water heats? I do need to work on adding more valves, the newly installed section is in good shape, but the rest could stand to be cleaned up and have more valves added...it's on the never ending to do list
You say Tanks...are there more than one?

Do they read the same pressure?

Does one sound more so hollow when you rap your knuckles on it?
SLOW AND STEADY WINS THE RACE

User avatar
jpete
Member
Posts: 10575
Joined: Thu. Nov. 22, 2007 9:52 am
Hand Fed Coal Stove: Harman Mk II
Coal Size/Type: Stove, Nut, Pea
Other Heating: Dino juice
Location: Warwick, RI

Post Mon. Apr. 14, 2014 10:18 pm

stoker-man wrote:The expansion tank sounds hollow when you rap it with your knuckles. If you have an increase in pressure along with an increase in temperature, check the circulator. If the temperature doesn't increase, check the coil, as stated.
It should sound solid above the seam and hollow below it. If it sound solid top to bottom, then it for sure needs to be replaced.

Another test is to QUICKLY depress the Schrader valve. You don't want to bleed off the factory charge. If ANY water comes out, the tank is dead.
Jeff