Is High Temp Normal in AA 130

Stoker Coal Boilers automatically feed the coal and have controls and pumps just like any conventions boiler. They are intended to be used as a primary heat and often have domestic hot water coils as an added bonus. They can be set up independently or in dual sytem with your existing oil/gas boiler. They can accommodate both hot water base board or steam plumbing.
User avatar
BigFoot
Member
Posts: 132
Joined: Tue. Dec. 22, 2009 3:41 pm
Stoker Coal Boiler: AA130
Coal Size/Type: PEA
Stove/Furnace Make: Axeman Anderson
Stove/Furnace Model: AA130
Location: 102 Marchak Lane Greenfield PA

Post Wed. Apr. 09, 2014 1:29 pm

so you guys say 145 low 165 high for the AA130 for summer ? I heat my water with it too

Visit Alternate Heating Sytems

User avatar
McGiever
Member
Posts: 5997
Joined: Sun. May. 02, 2010 11:26 pm
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Coal Size/Type: PEA / ANTHRACITE
Other Heating: Ground Source Heat Pump
Stove/Furnace Make: Hydro Heat /Mega Tek
Location: Junction of PA-OH-WV

Post Wed. Apr. 09, 2014 5:28 pm

You been running 190 degrees for radiant??? WOW!
SLOW AND STEADY WINS THE RACE

User avatar
franksnbeans
Member
Posts: 27
Joined: Tue. Mar. 11, 2014 11:56 am
Stoker Coal Boiler: AA 130
Coal Size/Type: Pea
Location: Eastern CT

Post Wed. Apr. 09, 2014 5:39 pm

No about 130 degrees

User avatar
coaledsweat
Site Moderator
Posts: 9825
Joined: Fri. Oct. 27, 2006 2:05 pm
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea
Location: Guilford, Connecticut

Post Thu. Apr. 10, 2014 8:31 am

BigFoot wrote:so you guys say 145 low 165 high for the AA130 for summer ? I heat my water with it too
As long as your DHW is at the temp you want, why run it higher? When I first started with my 260 I ran the temps high, 180-190° peak. It just eats more coal and you run a greater risk of overshooting. Remember those high temps mean higher chimney gas temps and radiat losses because it will try and maintain them. You need to maintain a low around 145° as oxygen disassociates from water at 152° and you don't want that present in your boiler to prevent rust.
Nothing is impossible for people who don't have to do it themselves.

User avatar
whistlenut
Member
Posts: 3549
Joined: Sat. Mar. 17, 2007 6:29 pm
Stoker Coal Boiler: AA130's,260's, AHS130&260's,EFM900,GJ & V-Wert
Hand Fed Coal Boiler: Franks,Itasca 415,Jensen, NYer 130,Van Wert
Hot Air Coal Stoker Furnace: Alaska, EFM, Keystoker, Yellow Flame
Hot Air Coal Stoker Stove: Alaska, Keystoker-2,Leisure Line
Hand Fed Coal Stove: Alaska, Gibraltar, Keystone,Vc Vigilant 2
Hand Fed Coal Furnace: Ford, Jensen, NYer, Van Wert,
Baseburners & Antiques: Glenwoods
Coal Size/Type: Barley, Buck, Rice ,Nut, Stove
Other Heating: Oil HWBB
Location: Central NH, Concord area

Post Thu. Apr. 10, 2014 9:59 am

I also agree and recommend what the other AA and AHS guys say, but with a couple notes. IF you are using a domestic hot water coil, you are NOT able to modulate the demand like early showers.....laundry......dishwasher and the typical early in the day demands for heating. As I always say, you HAVE to give serious thought to using an indirect water heater and or larger tankage.

With solid fuel; especially coal, you create that early morning demand so the boiler is running full tilt for a couple hours, then all of a sudden, you have NO demand and a runaway freight train snortin' and jumping wanting to take over the world. This is where I interject: Please add more expansion capacity immediately, AND check the damned tank or tanks daily because they can and do fail without visible signs. Those of you who don't respect the knowledge Sting offers for free: shame on you" :mad: I understand money is tight for everyone, but look on Craigslist or local papers and keep an eye out for indirects that have been removed in favor of some dinky instant hot water gas rig.

I do run the temps on my AA's at 180/165 in the winter and now 165/145. 40 gallon Indirect in place, 12 years now. Dump zone in place........and It is a waste to have to run a boiler at 180/165 all summer if all you are doing is heating water. However if the demand is huge for the domestic hot water cycle, give some thought to dedicating or creating a dump zone for this very issue. Also, set the overtemp aquastat up to 210, because when the timer is overridden, an out-fire is the possibility. As Sting tries to educate folks about 'running' your system is about balance, of the entire system. The 'Jackrabbit starts and demands' need to be slowed down and managed smoothly. Functioning from 'Panic Mode' creates more panic and more situations beyond our control. :idea: :idea: :idea:
"Political correctness is a doctrine, fostered by a delusional, illogical minority, and rabidly promoted by an unscrupulous mainstream media, which holds forth the proposition that it is entirely possible to pick up a 'piece of human solid waste' by the clean end." More true today....

User avatar
mikeandgerry
Member
Posts: 1882
Joined: Sat. Jul. 29, 2006 8:19 pm
Stoker Coal Boiler: Axeman-Anderson Anthratube 130-M
Location: North Norwich, NY

Post Thu. Apr. 10, 2014 2:47 pm

Axeman suggests setting the Hi limit aquastat to 220! That is so you don't have an outfire from the time not cycling due to a slight overtemp (which is normal). Don't worry. (The AA is rated for 250 degrees.) So long as you keep 5-10psi of pressure in the system the water won't boil.

Try your boiler at a triple aquastat low setting of 150 and a high of 170 with a differential of 10. I would set the hi limit aquastat at 220. You may still have the occasional overtemp but the timer will still cycle the stoker to hold the fire. Be sure the grate solenoid is working properly and the anthrastat is properly calibrated and set at 130 to 140 degrees (procedure for that is withing these pages and searchable). Don't have your "shake", as Axeman calls it, set too low or it won't feed enough coal. You will experience more unburned coal in fall/spring.

Since you are running radiant and have TMVs to modulate temperature, your boiler temp should be lower in the fall/spring as opposed to winter because your load requirements are far less. If you had outdoor reset it would shift to setback temps due to higher outdoor temps. This should be sufficient as most radiant systems don't need the heat to go over 100degF in my research. Low and slow is what I have heard, but I don't know that area of heating.
The essence of freedom is the proper limitation of government.

User avatar
franksnbeans
Member
Posts: 27
Joined: Tue. Mar. 11, 2014 11:56 am
Stoker Coal Boiler: AA 130
Coal Size/Type: Pea
Location: Eastern CT

Post Thu. Apr. 10, 2014 3:54 pm

Thanks for all the great advice. I have been running at 165-145 and all seems good. And I do have a dhw indirect tank 40 gallons. So life is good. My anthrastat is been set at 135 for a couple days and I have good ash. I had a lot of unburnt coal at 140.

Thanks again for the great advice!!

User avatar
mikeandgerry
Member
Posts: 1882
Joined: Sat. Jul. 29, 2006 8:19 pm
Stoker Coal Boiler: Axeman-Anderson Anthratube 130-M
Location: North Norwich, NY

Post Thu. Apr. 10, 2014 4:09 pm

for the future if the anthrastat gets out of calibration:

Anthrastat
The essence of freedom is the proper limitation of government.

Visit Alternate Heating Sytems

User avatar
LsFarm
Member
Posts: 7385
Joined: Sun. Nov. 20, 2005 8:02 pm
Stoker Coal Boiler: Axeman Anderson 260
Hand Fed Coal Boiler: Self-built 'Big Bertha' SS Boiler
Baseburners & Antiques: Keystone 11, Art Garland
Location: Michigan

Post Fri. Apr. 11, 2014 11:14 pm

Was your fire actually 'OUT' ?? after only part of a day's time ? That doesn't sound right.. you have an 11" diameter firepot with 3-5" of burning coal. It does not need a fluff-up, or more coal every hour.. I have my timer set at 2 min every hour when I use the timer, and I usually only use the timer for the first month and last month of heating season. All winter I don't use or need a timer.

Greg L
Burning Pea/Buckwheat through an antique stoker [semi retired SSboiler],
Running an Axeman-Anderson 260M boiler burning Pea, About 150-250#per day
Farming, Fixing, Fabricating and Flying: 'spare time' what's that?

User avatar
Rob R.
Site Moderator
Posts: 11346
Joined: Fri. Dec. 28, 2007 4:26 pm
Stoker Coal Boiler: EFM DF520
Hand Fed Coal Stove: Hitzer 50-93
Coal Size/Type: Lehigh Rice
Other Heating: Dad's 1953 EFM Highboy
Location: Chazy, NY

Post Sat. Apr. 12, 2014 1:17 pm

Must have poor draft if the fire goes out that quickly.

User avatar
lsayre
Member
Posts: 12200
Joined: Wed. Nov. 23, 2005 9:17 pm
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Blaschak Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW)
Location: N/E Ohio, between Medina and Wadsworth

Post Sat. Apr. 12, 2014 1:57 pm

My similar AHS Coal Gun has no timer (I tried one once, but it failed in relatively short order so I abandoned it) and except for when I shut it down intentionally for clean outs, it runs 24/7 year round with no timer, and I've never lost the fire.
-Larry

Democracy rests upon the principle that collective wisdom arises from a pool of individual ignorance. A Republic rests squarely upon objective law, and fundamentally upon those laws which restrict the scope and actions of government.

User avatar
whistlenut
Member
Posts: 3549
Joined: Sat. Mar. 17, 2007 6:29 pm
Stoker Coal Boiler: AA130's,260's, AHS130&260's,EFM900,GJ & V-Wert
Hand Fed Coal Boiler: Franks,Itasca 415,Jensen, NYer 130,Van Wert
Hot Air Coal Stoker Furnace: Alaska, EFM, Keystoker, Yellow Flame
Hot Air Coal Stoker Stove: Alaska, Keystoker-2,Leisure Line
Hand Fed Coal Stove: Alaska, Gibraltar, Keystone,Vc Vigilant 2
Hand Fed Coal Furnace: Ford, Jensen, NYer, Van Wert,
Baseburners & Antiques: Glenwoods
Coal Size/Type: Barley, Buck, Rice ,Nut, Stove
Other Heating: Oil HWBB
Location: Central NH, Concord area

Post Sat. Apr. 12, 2014 1:59 pm

Like Greg mentions, you don't see any orange coals, just a gray layer with black coal over it. Not to be a PITA, but if you SLOWLY introduce your hand into the viewing port, you will feel some warmth from below. If you are completely retarded, you will show your buddies that it is out and stick your hand into the gray layer. If you aren't into visiting the Shriners Burn Center, perhaps that is not a good idea. A 130 will last 36 hrs +/- and a 260 will be even longer, perhaps in excess of 48 hrs. A Keystoker guy should NOT play this game, or any inclined grate system. 10 minutes and your fun is over.
"Political correctness is a doctrine, fostered by a delusional, illogical minority, and rabidly promoted by an unscrupulous mainstream media, which holds forth the proposition that it is entirely possible to pick up a 'piece of human solid waste' by the clean end." More true today....

User avatar
franksnbeans
Member
Posts: 27
Joined: Tue. Mar. 11, 2014 11:56 am
Stoker Coal Boiler: AA 130
Coal Size/Type: Pea
Location: Eastern CT

Post Sat. Apr. 12, 2014 3:44 pm

I hear what you guys are saying and would love the fire to last all day. I do assure you it was out because I pulled every bit of coal out to restart it. I am currently working on the draft issue. I borrowed a draft meter and it measured .015 to .02. Added 6' stack and had no change. Single wall. So then went to insulated stack 3'. Still no change. I am in process of going to 6' of insulated stack. If no change then what? I also got another draft meter and also read same. Fun Fun!

User avatar
McGiever
Member
Posts: 5997
Joined: Sun. May. 02, 2010 11:26 pm
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Coal Size/Type: PEA / ANTHRACITE
Other Heating: Ground Source Heat Pump
Stove/Furnace Make: Hydro Heat /Mega Tek
Location: Junction of PA-OH-WV

Post Sat. Apr. 12, 2014 9:17 pm

I haven't seen any mention of number of clicks you're running at.
SLOW AND STEADY WINS THE RACE

User avatar
franksnbeans
Member
Posts: 27
Joined: Tue. Mar. 11, 2014 11:56 am
Stoker Coal Boiler: AA 130
Coal Size/Type: Pea
Location: Eastern CT

Post Sat. Apr. 12, 2014 9:22 pm

2 clicks. And 135 on athrastat

Visit Alternate Heating Sytems