I've calculated that each of my 4 roughly equal length zones when looked at independently has about 7.2 ft. of head. And also that to deliver the full 100,000 output BTU's of my Coal Gun requires a flow of 10 GPM (at 20 degrees of temperature drop).
What I can't seem to fully get my head around is the requirement of the pump when all 4 zones are open at once. Is the entire systems head still only 7.2 ft. at that juncture, or is it something else? I believe the head of the system remains at 7.2 ft., but I'll need an expert to confirm (or correct) this.
What I can't seem to fully get my head around is the requirement of the pump when all 4 zones are open at once. Is the entire systems head still only 7.2 ft. at that juncture, or is it something else? I believe the head of the system remains at 7.2 ft., but I'll need an expert to confirm (or correct) this.
- lsayre
- Member
- Posts: 21781
- Joined: Wed. Nov. 23, 2005 9:17 pm
- Location: Ohio
- Stoker Coal Boiler: AHS S130 Coal Gun
- Coal Size/Type: Lehigh Anthracite Pea
- Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75
I've answered my own question. Each zone opening up effectively expands the diameter of the pipe that the water is circulating through, thus dropping the resistance to flow, and causing the flow rate (GPM's) to increase. This moves the intersection of the combined zones head loss downward on the pumps curve.
Conclusion: The overall systems head does not remain constant or go up as more zones open, but rather it decreases as more zone valves open.
By the time my 4 x 3/4" diameter pipe zones are open the water is flowing through an effective 1.5" diameter pipe.
I've also re-calculated the head loss for my single longest zone loop at 8.4 ft.
Conclusion: The overall systems head does not remain constant or go up as more zones open, but rather it decreases as more zone valves open.
By the time my 4 x 3/4" diameter pipe zones are open the water is flowing through an effective 1.5" diameter pipe.
I've also re-calculated the head loss for my single longest zone loop at 8.4 ft.
- Lightning
- Site Moderator
- Posts: 14669
- Joined: Wed. Nov. 16, 2011 9:51 am
- Location: Olean, NY
- Stoker Coal Boiler: Modified AA 130
- Coal Size/Type: Pea Size - Anthracite
I agree that more zones open would decrease flow resistance which would allow faster turnover of the water thru the boiler.lsayre wrote:Conclusion: The overall systems head does not remain constant or go up as more zones open, but rather it decreases as more zone valves open.
- Yanche
- Member
- Posts: 3026
- Joined: Fri. Dec. 23, 2005 12:45 pm
- Location: Sykesville, Maryland
- Stoker Coal Boiler: Alternate Heating Systems S-130
- Coal Size/Type: Anthracite Pea
I agree also. But what will also happen is the flow rate in each zone will be reduced and less heat delivered to that zone as more and more zones are active. One can calculate the resistance in each zone individually. Then when multiple zones are operating it's like parallel resistors (electric circuit analogy). Determining the flow in each zone is possible but is it's more involved.
My preferred design is to use multiple zone pumps not zone valves.
My preferred design is to use multiple zone pumps not zone valves.
-
- Member
- Posts: 2270
- Joined: Sun. Sep. 30, 2012 8:20 pm
- Location: Ithaca,NY
Are you a plumber or a heating guy?
- Carbon12
- Member
- Posts: 2226
- Joined: Tue. Oct. 11, 2011 6:53 pm
- Location: Harrisburg, PA
- Stoker Coal Boiler: Keystoker KA-6
- Coal Size/Type: Rice/Anthracite
- Other Heating: Heat Pump/Forced Hot Air Oil Furnace
A general rule is, the more zones/feet of radiation, the more likely individual circulator pumps will work best, so,....it depends.
- lsayre
- Member
- Posts: 21781
- Joined: Wed. Nov. 23, 2005 9:17 pm
- Location: Ohio
- Stoker Coal Boiler: AHS S130 Coal Gun
- Coal Size/Type: Lehigh Anthracite Pea
- Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75
My house has been set up for a single circulator and 4 zone valves since it was first made in 1964. it has gone through an oil boiler phase, a resistance boiler phase, and now a coal boiler phase, and all have worked well with a single circulator and zone valves.
- whistlenut
- Member
- Posts: 3548
- Joined: Sat. Mar. 17, 2007 6:29 pm
- Location: Central NH, Concord area
- Stoker Coal Boiler: AA130's,260's, AHS130&260's,EFM900,GJ & V-Wert
- Hand Fed Coal Boiler: Franks,Itasca 415,Jensen, NYer 130,Van Wert
- Hot Air Coal Stoker Furnace: Alaska, EFM, Keystoker, Yellow Flame
- Hot Air Coal Stoker Stove: Alaska, Keystoker-2,Leisure Line
- Hand Fed Coal Stove: Alaska, Gibraltar, Keystone,Vc Vigilant 2
- Hand Fed Coal Furnace: Ford, Jensen, NYer, Van Wert,
- Baseburners & Antiques: Glenwoods
- Coal Size/Type: Barley, Buck, Rice ,Nut, Stove
- Other Heating: Oil HWBB
Keep a spare circ on hand(gaskets also), a 5/8" and 11/16" open end/ box end. Penetrating oil the bolts NOW unless they were anti-seized when installed. Shut off flanges or valves in place? Keep a spare zone valve head on hand, also.
As to circs or zone valves; depends........many system are hybrids with both. They are both very effective, but if the 'one circ' fails......with no replacement handy......on a twenty below evening.......
Gonna be a costly error on your part.
As to circs or zone valves; depends........many system are hybrids with both. They are both very effective, but if the 'one circ' fails......with no replacement handy......on a twenty below evening.......
Gonna be a costly error on your part.
- Carbon12
- Member
- Posts: 2226
- Joined: Tue. Oct. 11, 2011 6:53 pm
- Location: Harrisburg, PA
- Stoker Coal Boiler: Keystoker KA-6
- Coal Size/Type: Rice/Anthracite
- Other Heating: Heat Pump/Forced Hot Air Oil Furnace
@ Sting:
I seriously thought about not adding that,.....I didn't want to steal your thunder! I guess I did, however.
I seriously thought about not adding that,.....I didn't want to steal your thunder! I guess I did, however.
- lsayre
- Member
- Posts: 21781
- Joined: Wed. Nov. 23, 2005 9:17 pm
- Location: Ohio
- Stoker Coal Boiler: AHS S130 Coal Gun
- Coal Size/Type: Lehigh Anthracite Pea
- Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75
I have a new in box circulator, a complete new zone valve, and a new zone valve control head on stand-by.whistlenut wrote:Keep a spare circ on hand(gaskets also), a 5/8" and 11/16" open end/ box end. Penetrating oil the bolts NOW unless they were anti-seized when installed. Shut off flanges or valves in place? Keep a spare zone valve head on hand, also.
As to circs or zone valves; depends........many system are hybrids with both. They are both very effective, but if the 'one circ' fails......with no replacement handy......on a twenty below evening.......
Gonna be a costly error on your part.
My previous circulator (B&G NRF-22) was 11 years old when I replaced it as part of the entire system makeover I did when installing the coal boiler. It had no issues, but I replaced it anyway.
- Sting
- Member
- Posts: 2983
- Joined: Mon. Feb. 25, 2008 4:24 pm
- Location: Lower Fox Valley = Wisconsin
- Other Heating: OBSO Lennox Pulse "Air Scorcher" burning NG
Imitation is the sincerest form of flatteryCarbon12 wrote:@ Sting:
I seriously thought about not adding that,.....I didn't want to steal your thunder! I guess I did, however.