Stoker Coal Boilers automatically feed the coal and have controls and pumps just like any conventions boiler. They are intended to be used as a primary heat and often have domestic hot water coils as an added bonus. They can be set up independently or in dual sytem with your existing oil/gas boiler. They can accommodate both hot water base board or steam plumbing.
User avatar
gaw
Member
Posts: 2606
Joined: Fri. Jan. 26, 2007 2:51 am
Stoker Coal Boiler: Keystoker KA-6
Coal Size/Type: Rice from Schuylkill County
Location: Parts Unknown

Post Thu. Feb. 06, 2014 5:06 pm

blrman07 wrote:If you close it all the way and seal it with duct tape where is it going to get air to blow through the holes in the grates?
See the hole where the shaft comes out to the gearbox. It will scavenge air from where ever it can. I have seen it happen.

Trust me I'm a doctor!
Some people make the world happen;
More watch the world happen;
Most wonder what happened.
Its your choice, Which group you want to belong to….

If a man is a fool, you don't train him out of being a fool by sending him to university. You merely turn him into a trained fool, ten times more dangerous.
Desmond Bagley

Visit Alternate Heating Sytems

User avatar
blrman07
Member
Posts: 2379
Joined: Mon. Sep. 27, 2010 3:39 pm
Hand Fed Coal Boiler: Bucket a Day
Hand Fed Coal Stove: Vigilant Casting 2310
Coal Size/Type: Pea/Nut/Wood in the VC and anything that will fit in the Bucket a Day. It's not fussy.
Location: Girardville Pa.

Post Thu. Feb. 06, 2014 5:25 pm

Ok you will get some air and probably enough air to keep the fire going. Gotta give ya that one.
Rev. Larry
Ashland Pa.

1 John 1:9... If we sin and we confess that sin He is faithful and just and will forgive us and cleanse us from all unrighteousness.

User avatar
gaw
Member
Posts: 2606
Joined: Fri. Jan. 26, 2007 2:51 am
Stoker Coal Boiler: Keystoker KA-6
Coal Size/Type: Rice from Schuylkill County
Location: Parts Unknown

Post Thu. Feb. 06, 2014 5:59 pm

blrman07 wrote:Ok you will get some air and probably enough air to keep the fire going. Gotta give ya that one.
That is the extreme but I have seen one that was done that way. I would suggest when the large motor is running play with the flap and as stated before, as you close the air off you should see a decrease in flame height, then you know you are getting somewhere. That will confirm that air flow has been reduced. The barometric damper should compensate accordingly for the draft. What you must be mindful of is blowing too much air in when you have poor draft.
Some people make the world happen;
More watch the world happen;
Most wonder what happened.
Its your choice, Which group you want to belong to….

If a man is a fool, you don't train him out of being a fool by sending him to university. You merely turn him into a trained fool, ten times more dangerous.
Desmond Bagley

BennyLumpkin
Member
Posts: 88
Joined: Mon. Dec. 10, 2012 1:15 pm
Stove/Furnace Make: Keystoker
Stove/Furnace Model: KA6

Post Thu. Feb. 06, 2014 6:31 pm

Thankfully poor draft isn't an issue. My flue starts in my basement and it's 4' above my widows walk on top of my 2 story Victorian. Here are a few pics to show and to give an idea of how big the place is. The main house has no wall insulation....just in the attic. Thats to be hopefully addressed soon.

Image

Image

BennyLumpkin
Member
Posts: 88
Joined: Mon. Dec. 10, 2012 1:15 pm
Stove/Furnace Make: Keystoker
Stove/Furnace Model: KA6

Post Thu. Feb. 06, 2014 10:35 pm

I've been adjusting that tonight and found the less air I have it the worse the coking got songs the more fines I had. So now I'm going the other way. I think it's a losing battle till I get different coal. Not sure where to go though. ....I don't want Blaschak again because that's what I have now

User avatar
blrman07
Member
Posts: 2379
Joined: Mon. Sep. 27, 2010 3:39 pm
Hand Fed Coal Boiler: Bucket a Day
Hand Fed Coal Stove: Vigilant Casting 2310
Coal Size/Type: Pea/Nut/Wood in the VC and anything that will fit in the Bucket a Day. It's not fussy.
Location: Girardville Pa.

Post Thu. Feb. 06, 2014 11:02 pm

Ok you got me. Your telling me you cut back on the combustion air which should have resulted in a lower flame, meaning a cooler fire, meaning a cooler ash bed, which drops the ash temp to a point below the ash fusion range, and after waiting at least an hour, it started getting worse, meaning the ash started fusing more, in a cooler flame, than when you had a hot flame, and the ash, which is now cooler, started making ash cakes more prevalent instead of not forming at all?
Do I have the situation correct?

Rev. Larry
New Beginning Church
Ashland Pa.
Rev. Larry
Ashland Pa.

1 John 1:9... If we sin and we confess that sin He is faithful and just and will forgive us and cleanse us from all unrighteousness.

User avatar
blrman07
Member
Posts: 2379
Joined: Mon. Sep. 27, 2010 3:39 pm
Hand Fed Coal Boiler: Bucket a Day
Hand Fed Coal Stove: Vigilant Casting 2310
Coal Size/Type: Pea/Nut/Wood in the VC and anything that will fit in the Bucket a Day. It's not fussy.
Location: Girardville Pa.

Post Thu. Feb. 06, 2014 11:04 pm

I gotta ask. When you closed the silver flap which closed the opening for the main combustion blower, what happened to the height of the fire.
Rev. Larry
Ashland Pa.

1 John 1:9... If we sin and we confess that sin He is faithful and just and will forgive us and cleanse us from all unrighteousness.

BennyLumpkin
Member
Posts: 88
Joined: Mon. Dec. 10, 2012 1:15 pm
Stove/Furnace Make: Keystoker
Stove/Furnace Model: KA6

Post Thu. Feb. 06, 2014 11:07 pm

It dropped the flame. Not sure why it got worse but it did.

Visit Alternate Heating Sytems

User avatar
blrman07
Member
Posts: 2379
Joined: Mon. Sep. 27, 2010 3:39 pm
Hand Fed Coal Boiler: Bucket a Day
Hand Fed Coal Stove: Vigilant Casting 2310
Coal Size/Type: Pea/Nut/Wood in the VC and anything that will fit in the Bucket a Day. It's not fussy.
Location: Girardville Pa.

Post Fri. Feb. 07, 2014 8:42 am

How long did you let it run at a lower flame height before changing it back and/or increasing the air flow?
Rev. Larry
Ashland Pa.

1 John 1:9... If we sin and we confess that sin He is faithful and just and will forgive us and cleanse us from all unrighteousness.

BennyLumpkin
Member
Posts: 88
Joined: Mon. Dec. 10, 2012 1:15 pm
Stove/Furnace Make: Keystoker
Stove/Furnace Model: KA6

Post Fri. Feb. 07, 2014 9:07 am

Probably 3 hours

User avatar
McGiever
Member
Posts: 5997
Joined: Sun. May. 02, 2010 11:26 pm
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Coal Size/Type: PEA / ANTHRACITE
Other Heating: Ground Source Heat Pump
Stove/Furnace Make: Hydro Heat /Mega Tek
Location: Junction of PA-OH-WV

Post Fri. Feb. 07, 2014 11:11 am

BennyLumpkin wrote:The grey flapper is for the main combustion air correct? The one in the first pic right?
Benny, You're driving us Nucking Futs!!!

We do NOT care what you do with the GD black blower fan hanging out the back.

The GD silver pivot flap underneath in your SECOND picture is the only one we care about.

Do you get it???
SLOW AND STEADY WINS THE RACE

BennyLumpkin
Member
Posts: 88
Joined: Mon. Dec. 10, 2012 1:15 pm
Stove/Furnace Make: Keystoker
Stove/Furnace Model: KA6

Post Fri. Feb. 07, 2014 11:25 am

If you read my comments which are very clear I NEVER TOUCHED THE BLACK FAN. Apparently reading isn't a strong point? I've said several times about the silver flapper. A few people said closing the black fan more would help keeping it cooler when not running so I tried that but I know it doesn't affect my actual burn. Just keeping the unit burning when not calling for heat. The grey flapper is all I've worked with.....I've ran it from clear open to clear shut and its still coking leading me to the conclusion its the coal. Its worked without an issue for over a year and all of the sudden its been nothing but trouble and I'm to the coal in the bottom of my bin. I got the coal im into now last spring then dumped Harmony on top of it. See what I'm saying now? Im trying to be as clear as possible though I thought I was.

BennyLumpkin
Member
Posts: 88
Joined: Mon. Dec. 10, 2012 1:15 pm
Stove/Furnace Make: Keystoker
Stove/Furnace Model: KA6

Post Fri. Feb. 07, 2014 11:30 am

I don't mean to sound rude but that black fan keeps getting brought up and I'm not using it to try to adjust my burn air. I appreciate the advise I've been getting. ...I really do.

User avatar
gaw
Member
Posts: 2606
Joined: Fri. Jan. 26, 2007 2:51 am
Stoker Coal Boiler: Keystoker KA-6
Coal Size/Type: Rice from Schuylkill County
Location: Parts Unknown

Post Fri. Feb. 07, 2014 12:09 pm

At this point if I were BennyLumpkin I would be trying to find new coal. I get mine from Superior and as I stated before have never had clinkers larger than about 2 to 3 inches in diameter. A few more with this last delivery than in the past but they are a non-issue as far as the operation of the stoker goes. Superior only sells bulk. Superior, R & R, Kimmel, Sherman’s, Lenig’s; these should all be different than Blaschak. Try a few hundred pounds and if it works fill the bin.
Some people make the world happen;
More watch the world happen;
Most wonder what happened.
Its your choice, Which group you want to belong to….

If a man is a fool, you don't train him out of being a fool by sending him to university. You merely turn him into a trained fool, ten times more dangerous.
Desmond Bagley

BennyLumpkin
Member
Posts: 88
Joined: Mon. Dec. 10, 2012 1:15 pm
Stove/Furnace Make: Keystoker
Stove/Furnace Model: KA6

Post Fri. Feb. 07, 2014 12:42 pm

Where is Superior? Problem for me it's a two hour drive to get any to try