Stoker Coal Boilers automatically feed the coal and have controls and pumps just like any conventions boiler. They are intended to be used as a primary heat and often have domestic hot water coils as an added bonus. They can be set up independently or in dual sytem with your existing oil/gas boiler. They can accommodate both hot water base board or steam plumbing.
User avatar
Scottscoaled
Member
Posts: 2597
Joined: Tue. Jan. 08, 2008 9:51 pm
Stoker Coal Boiler: EFM 520, 700, Van Wert 800 GJ 61,53
Baseburners & Antiques: Magic Stewart 16, times 2!
Coal Size/Type: Lots of buck
Other Heating: Slant Fin electric boiler backup
Location: Malta N.Y.

Post Sun. Jan. 26, 2014 11:46 am

I still have issue with the wet insulation around the pex. It is a major problem.
photo(11).JPG
Last edited by Scottscoaled on Sun. Jan. 26, 2014 11:51 am, edited 1 time in total.
I think a man does what he can, untill his destiny is revealed. Right now that is trying to sell my EFM plate boilers in 520 and 700 sizes.

Visit Alternate Heating Sytems

User avatar
Lightning
Member
Posts: 8304
Joined: Wed. Nov. 16, 2011 9:51 am
Hand Fed Coal Furnace: Overmodified/Bored out Clayton 1537
Coal Size/Type: Anthracite/Awesome Size
Location: Olean, NY

Post Sun. Jan. 26, 2014 11:47 am

Rob R. wrote:If the pex lines are uninsulated in a single piece of PVC, won't the heat try to transfer from the supply to return? Not sure how much...depends how tight the lines are to one another.
My send and return to my hot tub are in a single PVC pipe. It's a very tight too.

Seems to work out for what ever reason lol. No idea if they were separated if it would make a difference. The heat has to get there, otherwise the loop would boil, wouldn't it?

User avatar
Rob R.
Site Moderator
Posts: 11364
Joined: Fri. Dec. 28, 2007 4:26 pm
Stoker Coal Boiler: EFM DF520
Hand Fed Coal Stove: Hitzer 50-93
Coal Size/Type: Lehigh Rice
Other Heating: Dad's 1953 EFM Highboy
Location: Chazy, NY

Post Sun. Jan. 26, 2014 11:54 am

windyhill4.2 wrote:Sorry,i was not trying to beat on him,only trying to clarify a few things.My key board does not have the alphabet in order so typing goes slow for me,besides,repetition is often the only way to get thru my thick skull or slow functioning brain. :) Rob R. is it really critical if the pipe temps are similar IF you have hot enough water for needed heat ? at least the water going back to boiler is not cold in that scenario.
If it heats the house, then no, it doesn't matter. I don't know how much of an issue it is anyway, just mentioned it. It is generally preferred to insulate each pipe separately.

User avatar
windyhill4.2
Member
Posts: 5023
Joined: Fri. Nov. 22, 2013 2:17 pm
Stoker Coal Boiler: 1960 EFM520 installed in truck box
Hand Fed Coal Stove: Crane 404 with variable blower
Coal Size/Type: 404-nut, 520 rice ,anthracite for both
Location: Jonestown,Pa.17038

Post Sun. Jan. 26, 2014 12:11 pm

WOW, Scottscoaled, that is a very distinct melt line,i saw your pic.& looked outside where my pex line is ,i know where it is because I put it ther but if you were to look you would have no idea,snow cover is the same ! Rob R. some are very adamant about separation of the 2 pipes,we do have some insulation between ours.
David **** John14:6 Jesus saith unto him,"I am the way.the truth,and the life;no man cometh unto the father,but by me." Wise men sought for Jesus when he was born,wise men still seek Jesus today. Seek & you shall find.

dchartt
Member
Posts: 172
Joined: Fri. Sep. 02, 2011 5:22 pm
Stoker Coal Boiler: AHS 130
Hand Fed Coal Stove: Glacier Bay

Post Sun. Jan. 26, 2014 12:13 pm

never thought about the return getting warmer going back to the boiler good point, 3 inch pvc with two 1 inch pex lines inside...have never had any snow melt on top of where my line is WOW! and your set on it being wet insulation and not the fact its only 2 1/2 ft below the surface???

User avatar
windyhill4.2
Member
Posts: 5023
Joined: Fri. Nov. 22, 2013 2:17 pm
Stoker Coal Boiler: 1960 EFM520 installed in truck box
Hand Fed Coal Stove: Crane 404 with variable blower
Coal Size/Type: 404-nut, 520 rice ,anthracite for both
Location: Jonestown,Pa.17038

Post Sun. Jan. 26, 2014 12:22 pm

My lyme riddled brain works a bit slow at times & dchartt your reply does point out a downside to sending the water temp back at similar temp it left the boiler. If water temp is too little change that would prevent the boiler coming on until all the water temp is low ,causing more of the wide swings of up & down cycling.
David **** John14:6 Jesus saith unto him,"I am the way.the truth,and the life;no man cometh unto the father,but by me." Wise men sought for Jesus when he was born,wise men still seek Jesus today. Seek & you shall find.

dchartt
Member
Posts: 172
Joined: Fri. Sep. 02, 2011 5:22 pm
Stoker Coal Boiler: AHS 130
Hand Fed Coal Stove: Glacier Bay

Post Sun. Jan. 26, 2014 12:28 pm

Do you actually think though that the return is rising in temp that much in the amount of time it travels 140 ft? I honestly don't see it I think thats a bit far fetched, how did your grandpop say it freetown fred?
What about my return cooling down my supply? Im not buying it

User avatar
Dennis
Member
Posts: 1066
Joined: Sun. Oct. 30, 2011 5:44 pm
Hand Fed Coal Boiler: AHS/WOC55-multi-fuel/wood,oil,coal
Coal Size/Type: Anthracite/stove size
Location: Pottstown,Pa

Post Sun. Jan. 26, 2014 12:40 pm

see if you can buy or even borrow a infered thermoter and check the return and supply lines(both) from the boiler to the house boiler and both lines from the house boiler to the outside boiler.What i'm infering is don't just read them at the outside boiler,you will get a better understanding of heat loss of the lines only.

Visit Alternate Heating Sytems

dchartt
Member
Posts: 172
Joined: Fri. Sep. 02, 2011 5:22 pm
Stoker Coal Boiler: AHS 130
Hand Fed Coal Stove: Glacier Bay

Post Sun. Jan. 26, 2014 12:51 pm

Ill bring one home from work and see what the temps are
Would the heat loss in taking the water to my house be evened out by the heat increase going back to the boiler? Its getting too technical!

dchartt
Member
Posts: 172
Joined: Fri. Sep. 02, 2011 5:22 pm
Stoker Coal Boiler: AHS 130
Hand Fed Coal Stove: Glacier Bay

Post Sun. Jan. 26, 2014 4:15 pm

how many of you guys running these coalguns remove the fan assembly during the season to clean out the air chamber that leads to on top of your fire? reason Im asking is because mine was half full of crap when I had mine tore apart yesterday and its definitely something I will be doing from now on during the winter

User avatar
McGiever
Member
Posts: 6009
Joined: Sun. May. 02, 2010 11:26 pm
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Coal Size/Type: PEA / ANTHRACITE
Other Heating: Ground Source Heat Pump
Stove/Furnace Make: Hydro Heat /Mega Tek
Location: Junction of PA-OH-WV

Post Sun. Jan. 26, 2014 4:27 pm

dchartt wrote:how many of you guys running these coalguns remove the fan assembly during the season to clean out the air chamber that leads to on top of your fire? reason Im asking is because mine was half full of crap when I had mine tore apart yesterday and its definitely something I will be doing from now on during the winter
Wish you had a picture of that...pictures is worth a 1000 words. ;)
SLOW AND STEADY WINS THE RACE

User avatar
McGiever
Member
Posts: 6009
Joined: Sun. May. 02, 2010 11:26 pm
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Coal Size/Type: PEA / ANTHRACITE
Other Heating: Ground Source Heat Pump
Stove/Furnace Make: Hydro Heat /Mega Tek
Location: Junction of PA-OH-WV

Post Sun. Jan. 26, 2014 4:32 pm

How did you insulate the outside of the sch 40 pipe?
How was that insulation then protected from the earth pressure/weight being at 4-1/2' buried depth?

Not so sure you would have a visible snow melt line showing due to pex being so deep buried.
SLOW AND STEADY WINS THE RACE

User avatar
Dennis
Member
Posts: 1066
Joined: Sun. Oct. 30, 2011 5:44 pm
Hand Fed Coal Boiler: AHS/WOC55-multi-fuel/wood,oil,coal
Coal Size/Type: Anthracite/stove size
Location: Pottstown,Pa

Post Sun. Jan. 26, 2014 5:36 pm

McGiever wrote:How did you insulate the outside of the sch 40 pipe?
How was that insulation then protected from the earth pressure/weight being at 4-1/2' buried depth?

Not so sure you would have a visible snow melt line showing due to pex being so deep buried.
what type of insulatoin did you use,fiberglass,open/closed cell.?

dchartt
Member
Posts: 172
Joined: Fri. Sep. 02, 2011 5:22 pm
Stoker Coal Boiler: AHS 130
Hand Fed Coal Stove: Glacier Bay

Post Sun. Jan. 26, 2014 5:56 pm

closed cell pipe insulation, my theory was the deeper I buried it the more insulation the earth itself would provide, didnt make sense to bury it within the frost line

waldo lemieux
Member
Posts: 2261
Joined: Sun. Sep. 30, 2012 8:20 pm
Stove/Furnace Make: efm
Stove/Furnace Model: s-20
Location: Ithaca,NY

Post Sun. Jan. 26, 2014 7:25 pm

Lightning wrote:Rob R. wrote:If the pex lines are uninsulated in a single piece of PVC, won't the heat try to transfer from the supply to return? Not sure how much...depends how tight the lines are to one another.
Two pex lines in a single pvc conduit would exibit little exchange , UNLESS said conduit wasnt glued together to above ground levels. If not you would have a water filled conduit and a great heat exchanger. Same goes for a gravel /sand filled trench in clay (non draining)soils :idea:
When faced with a seemingly impossible task, my grandfather always said "can't never can, untill try comes along"

Visit Alternate Heating Sytems