Yellow Flame Boiler 100K(Unsure of Model #)

Post Reply
User avatar
affperf
New Member
Posts: 1
Joined: Fri. Jan. 24, 2014 9:22 pm
Stoker Coal Boiler: yellow flame

Post Sat. Jan. 25, 2014 8:50 am

Having issues keeping from going out????

It seems to go out within hour after aquastat shuts down. I have a 5 degree diff. trying to keep going. I have tried lowest feed setting to highest.

setup:
8" pipe 8' across with rise to 6" reducer and chimney(14')
chestnut coal

Do I need timer to fire every 1/2 hour?????

Also smoke and steam come through coal in hopper when running?????

Any help greatly appreciated.

Thank you

User avatar
titleist1
Member
Posts: 4405
Joined: Wed. Nov. 14, 2007 4:06 pm
Hot Air Coal Stoker Stove: Harman Mag Stoker (old style) one in basement, one in workshop
Hand Fed Coal Stove: Harman Mark III on standby for long power outages
Coal Size/Type: Rice/Anthracite; Nut/Anthracite
Location: Cecil County, MD

Post Sat. Jan. 25, 2014 8:55 am

check your pipe run for fly ash....
exhaust coming out hopper is an indicator of poor draft and the fly ash could be the cause of that....

CO monitor in place??!!??!!
A manometer would be useful to have permanently installed to watch your draft numbers.
You will need to run via timer periodically to keep the fire going. how often is a little installation dependent.

I'm not used to seeing a stoker using nut coal. :)

User avatar
McGiever
Member
Posts: 6074
Joined: Sun. May. 02, 2010 11:26 pm
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Coal Size/Type: PEA / ANTHRACITE
Other Heating: Ground Source Heat Pump
Stove/Furnace Make: Hydro Heat /Mega Tek
Location: Junction of PA-OH-WV

Post Sat. Jan. 25, 2014 8:58 am

Also smoke and steam come through coal in hopper when running?????
Got Carbon Monoxide Detectors?Alarms?????
These are the signs of poor or blocked chimney draft. Urgent solution needed immediately.
Do I need timer to fire every 1/2 hour?????
I believe you want a 15min. timer.

titleist1 beat me :)

Visit Alternate Heating Sytems

User avatar
blrman07
Member
Posts: 2380
Joined: Mon. Sep. 27, 2010 3:39 pm
Hand Fed Coal Boiler: Bucket a Day
Hand Fed Coal Stove: Vigilant Casting 2310
Coal Size/Type: Pea/Nut/Wood in the VC and anything that will fit in the Bucket a Day. It's not fussy.
Location: Girardville Pa.

Post Sat. Jan. 25, 2014 9:02 am

You need to do two things right away.

1. Shut down!!! Remove and clean the pipe from the boiler to the chimney and make sure your chimney is clear.

2. Get a repeat cycle timer and install it where it starts the stoker mechanism every 15 minutes or at least 1 to 1 and 1/2 minutes.

Cleaning out the piping will stop the fan from pushing the products of combustion up into the hopper. The repeat cycle timer will get air going through the grates to keep the coal lit.

Rev. Larry
New Beginning Church
Ashland Pa.
Last edited by blrman07 on Sat. Jan. 25, 2014 9:04 am, edited 1 time in total.

User avatar
blrman07
Member
Posts: 2380
Joined: Mon. Sep. 27, 2010 3:39 pm
Hand Fed Coal Boiler: Bucket a Day
Hand Fed Coal Stove: Vigilant Casting 2310
Coal Size/Type: Pea/Nut/Wood in the VC and anything that will fit in the Bucket a Day. It's not fussy.
Location: Girardville Pa.

Post Sat. Jan. 25, 2014 9:03 am

oops double post

Rev. Larry
New Beginning Church
Ashland Pa.[/quote]

User avatar
StokerDon
Site Moderator
Posts: 3290
Joined: Mon. Nov. 11, 2013 11:17 am
Stoker Coal Boiler: BairMatic BMC-500 with Van Wert VA400 Stoker, Gentleman Janitor GJ-671/EFM S-15 stoker, Van Wert VA-600
Hand Fed Coal Furnace: Harman SF3500
Coal Size/Type: Rice and Chestnut
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood
Location: PA, Southern York County!

Post Sat. Jan. 25, 2014 9:33 am

affperf wrote:Having issues keeping from going out????

setup:
8" pipe 8' across with rise to 6" reducer and chimney(14')
chestnut coal

8 foot of 8" pipe horizontal run is going to give you a problem. That problem is compouned by the reduction to 6" pipe. This long horizontal run will become blocked with flyash in a short time.

I have never heard of using chestnut coal in one of these, only buck rice and barley.

Do I need timer to fire every 1/2 hour?????

As stated above, you need to run a 15 min or less timer cycle.

Also smoke and steam come through coal in hopper when running?????
Your chiminey is not ideal, you can try limiting the combustion air. If you do not have a choke on your combustion blower you can make it out of sheetmetal, it's easy. I have my Yellow Flame running into a 6" chimney and have the same problem, choking down the combustion air helped a lot. Looks like this.
FeedrateFlame2 001.JPG
Choke
FeedrateFlame2 002.JPG
Choke
Please post some photos of your boiler and setup. We all would like to see another Yellow Flame, They are a little rare these days.

Also post your location, One of us may live close by and be able to help you get straitned out.

-Don