Problems With KAA-2 Temps.

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Wed. Jan. 29, 2014 4:45 am

farrell2k, Whats the boiler pressure gauge reading?


 
kstills
Member
Posts: 637
Joined: Tue. Jan. 18, 2011 6:41 am
Location: New Britain, PA
Stoker Coal Boiler: WL 110

Post by kstills » Wed. Jan. 29, 2014 7:19 am

farrell2k wrote:Both zones seem to return water at around the same temp, both pretty hot to the touch. The circulators don't seem to be running all the time. I can feel and hear them kick on and off.
What is the boiler temp when the circulators kick off?

 
User avatar
Sting
Member
Posts: 2983
Joined: Mon. Feb. 25, 2008 4:24 pm
Location: Lower Fox Valley = Wisconsin
Other Heating: OBSO Lennox Pulse "Air Scorcher" burning NG

Post by Sting » Wed. Jan. 29, 2014 7:21 am

blrman07 wrote:
Your circ pumps are not running constantly probably because they are wired to run from the low temp aquastat. Boiler water cools down to below the lower setting and the circ pumps shut off until the boiler gets back up to the low temp setting. Try setting the low temp aquastat higher or simply change the wiring so the pumps run off the thermostat not the aquastat. On another boiler I put in a manual switch so they would never shut off unless I wanted them to run in auto.

You can't get that water out to the system unless those circ pumps are running!!!

Rev. Larry
New Beginning Church
Ashland Pa.
Image

 
User avatar
Rob R.
Site Moderator
Posts: 18004
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Wed. Jan. 29, 2014 7:37 am

It doesn't look like anything is connected to the ZC terminal in the aquastat. Regardless, it doesn't sound like the controls are setup properly. Add that to poor quality coal, and you get cold. :cry:

Like Larry mentioned, get those circulators wired off a separate relay so they run on a heat call and connect the end switch to the aquastat...that way it will head for the high limit whenever there is a heat call.

 
waldo lemieux
Member
Posts: 2270
Joined: Sun. Sep. 30, 2012 8:20 pm
Location: Ithaca,NY

Post by waldo lemieux » Wed. Jan. 29, 2014 7:44 am

If your return lines feel hot coming back to the boiler, your not getting circulation. A) you have an air bubble in the system( do a zone purge with a hose). B) your circulator is not functioning correctly . I believe that I remember that you mentioned HEARING the water circulating in the pipes. That means one thing , you have air in the lines! Till your sure the air is out - forget about all the other drama.

 
kstills
Member
Posts: 637
Joined: Tue. Jan. 18, 2011 6:41 am
Location: New Britain, PA
Stoker Coal Boiler: WL 110

Post by kstills » Wed. Jan. 29, 2014 7:58 am

Rob R. wrote:It doesn't look like anything is connected to the ZC terminal in the aquastat. Regardless, it doesn't sound like the controls are setup properly. Add that to poor quality coal, and you get cold. :cry:

Like Larry mentioned, get those circulators wired off a separate relay so they run on a heat call and connect the end switch to the aquastat...that way it will head for the high limit whenever there is a heat call.
Let me ask a general question here.

Assuming the system is set up with proper controls, when it's running at design it should not shut off, ie the heat going out from the boiler should match the heat loss and you should be in a state of constant circulation, no?

With the temps we've gotten lately, my system never cools down, at least not like it does when it's 30 degree average temp. The radiators are always 'hot', so even when the tstat makes a call, getting the constant water temp back up to the low limit only takes a few cycles. Rads are much less prone to giving up all their heat compared to slant fin, I'll grant you, but slant fin also doesn't take as long to bring up to temp. And circulating 8 gallons with a 24 gallon reserve should be pretty easy to do, thermally speaking. Heck, the LL110 is a 12 gallon capacity and it does the job with a moderate amount of insulation.

If indeed his heat loss exceeds his boiler capacity, he should be running flat out,no: with his boiler temps maxed (either to the LL setting or the HL setting, depending on how he's wired in). He would have to be losing so much heat out of his radiation continuously to have a constant supply of water returning that was too cold to maintain circulation that it boggles the mind.

 
User avatar
North Candlewood
Member
Posts: 240
Joined: Sun. Dec. 09, 2007 9:00 pm
Location: Ct
Stoker Coal Boiler: Eshland S-130
Hot Air Coal Stoker Furnace: Keystoker A 120
Hand Fed Coal Stove: Chubby
Hand Fed Coal Furnace: Clayton 1602
Baseburners & Antiques: Princess Atlantic Cookstove
Coal Size/Type: Nut Rice

Post by North Candlewood » Wed. Jan. 29, 2014 8:19 am

I'm with Waldo,
I just read thru this whole thread and my thoughts exactly.
Purge & this goes back to someone saying "Flow"
Then I'd search out air leaks in home that maybe robbing heat. Sill plates, splits in siding allowing air into wall cavity.
Attic access sealed up to reduce the chimney effect.


 
User avatar
Sting
Member
Posts: 2983
Joined: Mon. Feb. 25, 2008 4:24 pm
Location: Lower Fox Valley = Wisconsin
Other Heating: OBSO Lennox Pulse "Air Scorcher" burning NG

Post by Sting » Wed. Jan. 29, 2014 8:25 am

Is there a hunk of cheese at the end of this Maze?

 
waldo lemieux
Member
Posts: 2270
Joined: Sun. Sep. 30, 2012 8:20 pm
Location: Ithaca,NY

Post by waldo lemieux » Wed. Jan. 29, 2014 8:32 am

Sting

just remember, its the second mouse that gets the cheese!

 
User avatar
Rob R.
Site Moderator
Posts: 18004
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Wed. Jan. 29, 2014 8:37 am

Maybe we have a forum member in the area that can take a look? A stoker boiler guy with basic electrical skills should have this diagnosed in short order.

 
kstills
Member
Posts: 637
Joined: Tue. Jan. 18, 2011 6:41 am
Location: New Britain, PA
Stoker Coal Boiler: WL 110

Post by kstills » Wed. Jan. 29, 2014 8:41 am

Rob R. wrote:Maybe we have a forum member in the area that can take a look? A stoker boiler guy with basic electrical skills should have this diagnosed in short order.
Farrell isn't going to be able to handle control changes, unless I misunderstand his posts. And it doesn't seem he's in a position fiscally to put much money into having someone fix it for him.

 
User avatar
oliver power
Member
Posts: 2970
Joined: Sun. Apr. 16, 2006 9:28 am
Location: Near Dansville, NY
Stoker Coal Boiler: KEYSTOKER Kaa-2
Hand Fed Coal Stove: Hitzer 50-93 & 30-95, Vigilant (pre-2310), D.S. 1600 Circulator, Hitzer 254

Post by oliver power » Wed. Jan. 29, 2014 8:42 am

YES, YES, YES!!! ABSOLUTLY CORRECT!!!!!!! Boiler and circulators should be running flat out, non stop. But, that's ONLY ONCE THE STOKER CATCHES UP! The problem here is, the stoker never CAUTCHES UP before the triple aquastat shuts it down. Long before the stoker has a chance to ramp up, the boiler water drops below thriple aquastat low setting, and SHUTS DOWN THE STOKER. Three groups of 4, or 5 pins takes care of that lag time, due to small idle fire. With the HOTTER IDLE FIRE, the stoker is able to catch up before the triple aquastat's low setting shuts it down. Once it's caught up, she'll run flat out, as you say. This is how it's wired from the factory. He should start with the settings I gave him earlier on. At least he'll have a positive starting point. If nothing else, JUST ADD THE PINS. Then check back with us in an hour or so to give results. One step at a time. My Kaa-2 performs excellent in ALL weather conditions. I would think he'd start out with positive proven settings. NO WAY is that Kaa-2 too small to heat his house. If the problem is that the boiler is not capable of putting out the BTU's he needs, it's not a boiler problem at all. It's an insulation problem.

 
titleist1
Member
Posts: 5226
Joined: Wed. Nov. 14, 2007 4:06 pm

Post by titleist1 » Wed. Jan. 29, 2014 8:44 am

waldo lemieux wrote:Sting

just remember, its the second mouse that gets the cheese!
not always....... 8-)


 
User avatar
Sting
Member
Posts: 2983
Joined: Mon. Feb. 25, 2008 4:24 pm
Location: Lower Fox Valley = Wisconsin
Other Heating: OBSO Lennox Pulse "Air Scorcher" burning NG

Post by Sting » Wed. Jan. 29, 2014 8:58 am

oliver power wrote:YES, YES, YES!!! ABSOLUTLY CORRECT!!!!!!! Boiler and circulators should be running flat out, non stop. But, that's ONLY ONCE THE STOKER CATCHES UP! The problem here is, the stoker never CAUTCHES UP before the triple aquastat shuts it down. Long before the stoker has a chance to ramp up, the boiler water drops below thriple aquastat low setting, and SHUTS DOWN THE STOKER. Three groups of 4, or 5 pins takes care of that lag time, due to small idle fire. With the HOTTER IDLE FIRE, the stoker is able to catch up before the triple aquastat's low setting shuts it down. Once it's caught up, she'll run flat out, as you say. This is how it's wired from the factory. He should start with the settings I gave him earlier on. At least he'll have a positive starting point. If nothing else, JUST ADD THE PINS. Then check back with us in an hour or so to give results. One step at a time. My Kaa-2 performs excellent in ALL weather conditions. I would think he'd start out with positive proven settings. NO WAY is that Kaa-2 too small to heat his house. If the problem is that the boiler is not capable of putting out the BTU's he needs, it's not a boiler problem at all. It's an insulation problem.
I would like to visit this for a moment please
The little coal boiler will not be able to "catch up" as long as that Triple Aquastat -- "wired correctly" -->NOT<-- continues to only circulate energy bearing water when the boiler is OFF

the TT terminals of the blasted Trple A should be jumper-ed and the boiler should be running anytime it needs to keep itself HOT. The circulators should be running anytime the boiler is above condensing temperature and the load is calling for heat.

A triple Aquastat for total system control on a solid fuel heating appliance is just Sick and Wrong if the solid fuel appliance is allowed to continue to run full out as long as the load is calling and it has protection from circulation so it will not drop into condensing temperatures - then.... an undersized appliance will have a chance to be the little engine that could

 
kstills
Member
Posts: 637
Joined: Tue. Jan. 18, 2011 6:41 am
Location: New Britain, PA
Stoker Coal Boiler: WL 110

Post by kstills » Wed. Jan. 29, 2014 9:05 am

oliver power wrote:YES, YES, YES!!! ABSOLUTLY CORRECT!!!!!!! Boiler and circulators should be running flat out, non stop. But, that's ONLY ONCE THE STOKER CATCHES UP! The problem here is, the stoker never CAUTCHES UP before the triple aquastat shuts it down. Long before the stoker has a chance to ramp up, the boiler water drops below thriple aquastat low setting, and SHUTS DOWN THE STOKER. Three groups of 4, or 5 pins takes care of that lag time, due to small idle fire. With the HOTTER IDLE FIRE, the stoker is able to catch up before the triple aquastat's low setting shuts it down. Once it's caught up, she'll run flat out, as you say. This is how it's wired from the factory. He should start with the settings I gave him earlier on. At least he'll have a positive starting point. If nothing else, JUST ADD THE PINS. Then check back with us in an hour or so to give results. One step at a time. My Kaa-2 performs excellent in ALL weather conditions. I would think he'd start out with positive proven settings. NO WAY is that Kaa-2 too small to heat his house. If the problem is that the boiler is not capable of putting out the BTU's he needs, it's not a boiler problem at all. It's an insulation problem.
This is the part of the KA2 operation that is foreign to me.

On my boiler, when there is a heat call, the boiler is running at max output (determined by the initial adjustments made during setup). The Idle fire is set using a seperate rheostat control that is adjusted as needed for weather/temperature conditions.

So in my case, at some point when I'm running at design, the system will be running flat out, with the circulating water equaling the (in my case) low limit setting on the aquastat. If the heatloss of the dwelling exceeds the output at that point, I'll lose temperature in the dwelling, however the system should be running as stated.

I'm gathering from what your saying that the KA2 has more than one 'max setting' and that Farrel can increae that, thereby increasing the recovery time of the boiler?

I should add that, in my case, my stoker always catches up. It might take a while, but running at full burn eventually the system temp is circulating ~160f water.