Wiring the EFM 700

Post Reply
 
shy0302
Member
Posts: 32
Joined: Sat. Feb. 25, 2012 7:51 pm
Location: EAST WORCESTER NY

Post by shy0302 » Sat. Dec. 14, 2013 4:19 pm

I could use some information on wiring the high and low limit water switches, and also the wiring to the blower and auger.

 
User avatar
Rob R.
Site Moderator
Posts: 18004
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Sat. Dec. 14, 2013 4:30 pm

What are you using for controls?


 
shy0302
Member
Posts: 32
Joined: Sat. Feb. 25, 2012 7:51 pm
Location: EAST WORCESTER NY

Post by shy0302 » Fri. Dec. 20, 2013 7:00 pm

the control on the back is the first photo and is set at 200 degrees so I believe it is the high temp control. the second control , the second is set at 120 degrees so it looks like the low temp control, what do you think of this set up?

Attachments

100_2172.JPG
.JPG | 133.9KB | 100_2172.JPG
100_2176.JPG
.JPG | 80.2KB | 100_2176.JPG

 
User avatar
Rob R.
Site Moderator
Posts: 18004
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Sat. Dec. 21, 2013 7:27 am

Those should work fine. Use the first one for the high limit and use the other to maintain the boiler temperature. Bring the timer circuit in prior to the high limit control.