Clearance on All Sides of EFM Stoker

Posted: Sat. Nov. 02, 2013 12:42 pm
by shy0302
I would like to know all the clearance needed from cellar celling, stone cellar walls, oil boiler which is now heating the house. how long is the max distance you run the auger? any help would be great.

Re: Clearance on All Sides of EFM Stoker

Posted: Sat. Nov. 02, 2013 5:28 pm
by fifthg
go to the board index page and scroll to the manufacturers corner,and you will see efm section.everything you need to know is there.

Re: Clearance on All Sides of EFM Stoker

Posted: Sat. Nov. 02, 2013 10:22 pm
by Rob R.
If possible you should really try to have at least three feet behind the boiler. It makes it much easier to service the unit, and is required to easily pull the tankless coil out of the boiler. 36" clearance to combustibles is pretty standard, and

Please print out a copy of the EFM manual for reference: http://efmheating.com/index.php/efm-online-manuals

The minimum clearances are on page 3.