Coal Boiler Pressure Question
- lsayre
- Member
- Posts: 21781
- Joined: Wed. Nov. 23, 2005 9:17 pm
- Location: Ohio
- Stoker Coal Boiler: AHS S130 Coal Gun
- Coal Size/Type: Lehigh Anthracite Pea
- Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75
I bumped up my pressure recently, and today I'm seeing 16 lbs. at 205 degrees. Is that OK, or should I drop it down a bit?
Edited to correct my poor spelling.
Edited to correct my poor spelling.
Last edited by lsayre on Sat. Sep. 14, 2013 10:29 am, edited 1 time in total.
- lsayre
- Member
- Posts: 21781
- Joined: Wed. Nov. 23, 2005 9:17 pm
- Location: Ohio
- Stoker Coal Boiler: AHS S130 Coal Gun
- Coal Size/Type: Lehigh Anthracite Pea
- Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75
No way at this juncture (that I know of) to tell what the cold fill pressure is. Will be shutting down and cleaning out sometime in early October, so I can check it then.Rob R. wrote:15-16 psi is fine, so is 20...but your expansion tank should match the cold-fill pressure.
-
- Site Moderator
- Posts: 11417
- Joined: Wed. Nov. 05, 2008 5:11 pm
- Location: Kent CT
- Hand Fed Coal Stove: V ermont Castings 2310, Franco Belge 262
- Baseburners & Antiques: Glenwood Modern Oak 114
- Coal Size/Type: nut and pea
Pressure as I understand it is only to raise the water to the highest radiator or heat exchanger. Three story house needs more than two story house.
- Freddy
- Member
- Posts: 7301
- Joined: Fri. Apr. 11, 2008 2:54 pm
- Location: Orrington, Maine
- Stoker Coal Boiler: Axeman Anderson 130 (pea)
- Coal Size/Type: Pea size, Superior, deep mined
As long as it stays below the blow off point of the pressure relief valve it's fine. Most are 30PSI. But, yes, the ideal would be as low as possible and still do the job.... 12 for a one or two story house, around 17 I think for a three story house. Generally.... 5 pounds for every 10 feet up.
- gaw
- Member
- Posts: 4461
- Joined: Fri. Jan. 26, 2007 2:51 am
- Location: Parts Unknown
- Stoker Coal Boiler: Keystoker KA-6
- Coal Size/Type: Rice from Schuylkill County
If you are worried over 16 psi you don’t have enough to worry about. Like the others said, it is a couple pounds higher than “normal” but it ain’t broke so I would not fix it.
- whistlenut
- Member
- Posts: 3548
- Joined: Sat. Mar. 17, 2007 6:29 pm
- Location: Central NH, Concord area
- Stoker Coal Boiler: AA130's,260's, AHS130&260's,EFM900,GJ & V-Wert
- Hand Fed Coal Boiler: Franks,Itasca 415,Jensen, NYer 130,Van Wert
- Hot Air Coal Stoker Furnace: Alaska, EFM, Keystoker, Yellow Flame
- Hot Air Coal Stoker Stove: Alaska, Keystoker-2,Leisure Line
- Hand Fed Coal Stove: Alaska, Gibraltar, Keystone,Vc Vigilant 2
- Hand Fed Coal Furnace: Ford, Jensen, NYer, Van Wert,
- Baseburners & Antiques: Glenwoods
- Coal Size/Type: Barley, Buck, Rice ,Nut, Stove
- Other Heating: Oil HWBB
Larry, what size pressure tank do you have on that system? Your 16 lb question is not anything I would worry about......above 20, start looking for a reason.......or if it creeps up.
- lsayre
- Member
- Posts: 21781
- Joined: Wed. Nov. 23, 2005 9:17 pm
- Location: Ohio
- Stoker Coal Boiler: AHS S130 Coal Gun
- Coal Size/Type: Lehigh Anthracite Pea
- Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75
I have a #90 on it.whistlenut wrote:Larry, what size pressure tank do you have on that system? Your 16 lb question is not anything I would worry about......above 20, start looking for a reason.......or if it creeps up.
- Rob R.
- Site Moderator
- Posts: 18004
- Joined: Fri. Dec. 28, 2007 4:26 pm
- Location: Chazy, NY
- Stoker Coal Boiler: EFM 520
- Hand Fed Coal Stove: Chubby Jr
You did your homework, that is a great tank to have on a coal-fired system. Every single expansion tank I have purchased has come through with about 8 psi. As you know, this is too low for a typical system that uses a static fill pressure of 12 psi. If the tank pressure isn't adjusted to match, you will have used part of the tank's expansion capacity before the water even gets heated.