Coal Boiler Pressure Question

Post Reply
 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Sat. Sep. 14, 2013 10:16 am

I bumped up my pressure recently, and today I'm seeing 16 lbs. at 205 degrees. Is that OK, or should I drop it down a bit?

Edited to correct my poor spelling.
Last edited by lsayre on Sat. Sep. 14, 2013 10:29 am, edited 1 time in total.

 
User avatar
blrman07
Member
Posts: 2383
Joined: Mon. Sep. 27, 2010 3:39 pm
Location: Tupelo Mississippi

Post by blrman07 » Sat. Sep. 14, 2013 10:23 am

It's supposed to be at or around 12 but your OK. If it was me, I would drop it to 12-13 but that's just me.

Rev. Larry

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Sat. Sep. 14, 2013 10:30 am

To drop it, will I need to bleed it a bit?

 
User avatar
Rob R.
Site Moderator
Posts: 18004
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Sat. Sep. 14, 2013 10:47 am

15-16 psi is fine, so is 20...but your expansion tank should match the cold-fill pressure.


 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Sat. Sep. 14, 2013 12:29 pm

Rob R. wrote:15-16 psi is fine, so is 20...but your expansion tank should match the cold-fill pressure.
No way at this juncture (that I know of) to tell what the cold fill pressure is. Will be shutting down and cleaning out sometime in early October, so I can check it then.

 
franco b
Site Moderator
Posts: 11417
Joined: Wed. Nov. 05, 2008 5:11 pm
Location: Kent CT
Hand Fed Coal Stove: V ermont Castings 2310, Franco Belge 262
Baseburners & Antiques: Glenwood Modern Oak 114
Coal Size/Type: nut and pea

Post by franco b » Sat. Sep. 14, 2013 2:11 pm

Pressure as I understand it is only to raise the water to the highest radiator or heat exchanger. Three story house needs more than two story house.

 
User avatar
Freddy
Member
Posts: 7301
Joined: Fri. Apr. 11, 2008 2:54 pm
Location: Orrington, Maine
Stoker Coal Boiler: Axeman Anderson 130 (pea)
Coal Size/Type: Pea size, Superior, deep mined

Post by Freddy » Sun. Sep. 15, 2013 6:57 am

As long as it stays below the blow off point of the pressure relief valve it's fine. Most are 30PSI. But, yes, the ideal would be as low as possible and still do the job.... 12 for a one or two story house, around 17 I think for a three story house. Generally.... 5 pounds for every 10 feet up.

 
User avatar
gaw
Member
Posts: 4461
Joined: Fri. Jan. 26, 2007 2:51 am
Location: Parts Unknown
Stoker Coal Boiler: Keystoker KA-6
Coal Size/Type: Rice from Schuylkill County

Post by gaw » Sun. Sep. 15, 2013 7:30 am

If you are worried over 16 psi you don’t have enough to worry about. :shock: Like the others said, it is a couple pounds higher than “normal” but it ain’t broke so I would not fix it.


 
User avatar
whistlenut
Member
Posts: 3548
Joined: Sat. Mar. 17, 2007 6:29 pm
Location: Central NH, Concord area
Stoker Coal Boiler: AA130's,260's, AHS130&260's,EFM900,GJ & V-Wert
Hand Fed Coal Boiler: Franks,Itasca 415,Jensen, NYer 130,Van Wert
Hot Air Coal Stoker Furnace: Alaska, EFM, Keystoker, Yellow Flame
Hot Air Coal Stoker Stove: Alaska, Keystoker-2,Leisure Line
Hand Fed Coal Stove: Alaska, Gibraltar, Keystone,Vc Vigilant 2
Hand Fed Coal Furnace: Ford, Jensen, NYer, Van Wert,
Baseburners & Antiques: Glenwoods
Coal Size/Type: Barley, Buck, Rice ,Nut, Stove
Other Heating: Oil HWBB

Post by whistlenut » Sun. Sep. 15, 2013 12:05 pm

Larry, what size pressure tank do you have on that system? Your 16 lb question is not anything I would worry about......above 20, start looking for a reason.......or if it creeps up.

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Sun. Sep. 15, 2013 12:10 pm

whistlenut wrote:Larry, what size pressure tank do you have on that system? Your 16 lb question is not anything I would worry about......above 20, start looking for a reason.......or if it creeps up.
I have a #90 on it.

 
User avatar
Rob R.
Site Moderator
Posts: 18004
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Sun. Sep. 15, 2013 12:32 pm

You did your homework, that is a great tank to have on a coal-fired system. Every single expansion tank I have purchased has come through with about 8 psi. As you know, this is too low for a typical system that uses a static fill pressure of 12 psi. If the tank pressure isn't adjusted to match, you will have used part of the tank's expansion capacity before the water even gets heated.

Post Reply