Noisy Taco Flocheck

Stoker Coal Boilers automatically feed the coal and have controls and pumps just like any conventions boiler. They are intended to be used as a primary heat and often have domestic hot water coils as an added bonus. They can be set up independently or in dual sytem with your existing oil/gas boiler. They can accommodate both hot water base board or steam plumbing.
User avatar
stovepipemike
Member
Posts: 1198
Joined: Sun. Jun. 15, 2008 11:53 am
Stove/Furnace Make: Keystoker
Stove/Furnace Model: KAA-2
Location: Morgantown ,Penna

Post Fri. Mar. 22, 2013 7:47 am

I also tried the dead weight hammer approach but for me it did zip.Then I just had to have a look at the internals of the flowcheck. I field stripped it and found a seating disc with a very free moving clearance type fit. Nothing to be gained by looking at parts that were not rusted up,and free to move when motivated by pressure differences.Thats when it dawned on me that in my particular instance it had to be some type of a flow condition. Mike

waldo lemieux
Member
Posts: 2261
Joined: Sun. Sep. 30, 2012 8:20 pm
Stove/Furnace Make: efm
Stove/Furnace Model: s-20
Location: Ithaca,NY

Post Fri. Mar. 22, 2013 8:35 am

Mike,

I heard this said before and maybe it really works, Get a bigger hammer :rofl: sorry ,I couldn't help myself, its been a long winter....

Waldo
When faced with a seemingly impossible task, my grandfather always said "can't never can, untill try comes along"

Don
Member
Posts: 74
Joined: Tue. Apr. 15, 2008 8:20 am
Stove/Furnace Make: Keystoker k-2
Stove/Furnace Model: utica starfire
Location: Northwestern Ct

Post Fri. Mar. 22, 2013 9:06 pm

Mine is piped the way Dan Holohan shows in his book pumping away, and it rattles.

User avatar
jpete
Member
Posts: 10575
Joined: Thu. Nov. 22, 2007 9:52 am
Hand Fed Coal Stove: Harman Mk II
Coal Size/Type: Stove, Nut, Pea
Other Heating: Dino juice
Location: Warwick, RI

Post Fri. Mar. 22, 2013 9:18 pm

Rob R. wrote:Air in the system can also cause flow checks to rattle. This situation can occur with the circulator on either side of the boiler...but it is somewhat easier to rid the system of air with the circulators on the supply side.

:idea: Another "old rule" is to have at least 12" of straight pipe before and after the circulator to reduce turbulence.
Not sure about the circulator, but the rule is to have 18" of straight pipe before the air scoop to reduce turbulence. I was just at a class and took a tour of Taco last week.

EDIT: I just emailed the trainer at Taco and quoted the OP. If I get an answer, I'll pass it on here.
Jeff

“Many people want the government to protect the consumer. A much more urgent problem is to protect the consumer from the government.”

Milton Friedman

Visit Alternate Heating Sytems

Don
Member
Posts: 74
Joined: Tue. Apr. 15, 2008 8:20 am
Stove/Furnace Make: Keystoker k-2
Stove/Furnace Model: utica starfire
Location: Northwestern Ct

Post Sat. Mar. 23, 2013 7:44 am

jpete wrote:
Rob R. wrote:Air in the system can also cause flow checks to rattle. This situation can occur with the circulator on either side of the boiler...but it is somewhat easier to rid the system of air with the circulators on the supply side.

:idea: Another "old rule" is to have at least 12" of straight pipe before and after the circulator to reduce turbulence.
Not sure about the circulator, but the rule is to have 18" of straight pipe before the air scoop to reduce turbulence. I was just at a class and took a tour of Taco last week.

EDIT: I just emailed the trainer at Taco and quoted the OP. If I get an answer, I'll pass it on here.

I have 18 inches for the air scoop and 12 inches for flo check. I put in a 3 speed Cir and they now they rattle according to the speed of the cir.I hope the trainer gets back to you.

User avatar
Yanche
Member
Posts: 3032
Joined: Fri. Dec. 23, 2005 12:45 pm
Stoker Coal Boiler: Alternate Heating Systems S-130
Coal Size/Type: Anthracite Pea
Location: Sykesville, Maryland

Post Sat. Mar. 23, 2013 5:46 pm

I have the same noise issue with weighted flow checks. In my opinion weighted flow checks are not the preferred design. If a check is needed a spring loaded plastic one is the better choice. It's silent. There are two styles, in the circulator or in the circulator flange. I prefer the latter.

The claimed advantage of some weighted flow check was the ability to manually turn a knob and have gravity flow. This advantage is of no value today, because we don't have massive coal fired boilers with lots of thermal energy to supply flow when there's no electricity. Today it's pumps and electric operated stokers.
Yanche
Alternate Heating Systems S-130
Stoker Boiler burning Anthracite Pea Coal

Don
Member
Posts: 74
Joined: Tue. Apr. 15, 2008 8:20 am
Stove/Furnace Make: Keystoker k-2
Stove/Furnace Model: utica starfire
Location: Northwestern Ct

Post Sun. Mar. 24, 2013 8:33 am

Yanche wrote:I have the same noise issue with weighted flow checks. In my opinion weighted flow checks are not the preferred design. If a check is needed a spring loaded plastic one is the better choice. It's silent. There are two styles, in the circulator or in the circulator flange. I prefer the latter.

The claimed advantage of some weighted flow check was the ability to manually turn a knob and have gravity flow. This advantage is of no value today, because we don't have massive coal fired boilers with lots of thermal energy to supply flow when there's no electricity. Today it's pumps and electric operated stokers.
That sounds like a good fix I would like to get the flange flow check so if it fails I won't have to buy a new circulator. Do you have any info on the flange type, I can't seem to find them.

User avatar
Yanche
Member
Posts: 3032
Joined: Fri. Dec. 23, 2005 12:45 pm
Stoker Coal Boiler: Alternate Heating Systems S-130
Coal Size/Type: Anthracite Pea
Location: Sykesville, Maryland

Post Sun. Mar. 24, 2013 10:32 am

Pex Supply

Here's the one for 3/4":

http://www.pexsupply.com/Wilo-2705085-3-4-Check-Flange-Set

They have other sizes. It's the most economical solution for a flow control problem. Allows you to use the less expensive circulator without flow checks. The check valve can be removed from the flange if you don't need it.
Yanche
Alternate Heating Systems S-130
Stoker Boiler burning Anthracite Pea Coal

Visit Alternate Heating Sytems

User avatar
jpete
Member
Posts: 10575
Joined: Thu. Nov. 22, 2007 9:52 am
Hand Fed Coal Stove: Harman Mk II
Coal Size/Type: Stove, Nut, Pea
Other Heating: Dino juice
Location: Warwick, RI

Post Mon. Mar. 25, 2013 8:51 am

Got a couple emails back this morning. Here they are FWIW.
You are right, there isn’t a lot to go on here, but that’s the fun part of this job it think. Put on the detective hat and jump in.

My initial thought was “ OK, they may have only changed the boiler, but was an air elimination device installed, where is it compared to before and where is the expansion tank and what size is it?”

The original questions was is it low flow or air? It may be neither, it may be low pressure in the system. You could get low pressure in the system from air.

Lots of things to look at here
Another thing to think about with a floChek or any thing for that matter in a system, when you try to re-use components in a system, there could be an incredible amount of crud that settled in the old system, now it is all dislodged and floating around
This doesn't help at all but at least he got back to me....
Jeff

“Many people want the government to protect the consumer. A much more urgent problem is to protect the consumer from the government.”

Milton Friedman

User avatar
JRDepew
Member
Posts: 110
Joined: Fri. Feb. 24, 2012 8:35 am
Stoker Coal Boiler: EFM 350
Location: Port Crane, NY

Post Mon. Mar. 25, 2013 9:04 am

I'm guessing it is air...When I was having my air in the plumbing problems the flo-check would rattle loudly when the air slug was moving through that part of the system. Pumping away and installing the expansion tank solved my problems and my system is now very quiet.

Joe

User avatar
dh1200s
Member
Posts: 67
Joined: Sat. Jul. 18, 2009 1:12 pm
Stoker Coal Boiler: Leisure Line WL-110
Hand Fed Coal Boiler: HS-Tarm 202
Hand Fed Coal Stove: Harman TLC 2000
Location: Honey Brook, Pa.

Post Tue. Mar. 26, 2013 7:28 am

AKHEARTH

I redid my entire system when I installed my WL110K boiler. I’m primary/secondary loop setup and use Webstone isolation flanges with Spring Check Valves on Taco 007 pumps secondary loops and the primary loop 007 pump.

They are more expensive but the combo makes it easy to isolate the pump and check valve if you need to work on either down the road…….no rattles or ghost flow in my system. http://www.pexsupply.com/Webstone-52403-3-4-Full- ... ring-Check

I also use Webstone Isolation Valves with drain port for system purge.

My original system installed (1979) by the builder was bare bones nothing was easy to break into for maintenance/replacement.

Pics of the Isolation flange with spring check valve removed……. a real easy job to replace it or the pump if needed.
My pump board early part of install;
Good luck on quieting down your system.........Dick