Boiler Won't Make Temperature!

Stoker Coal Boilers automatically feed the coal and have controls and pumps just like any conventions boiler. They are intended to be used as a primary heat and often have domestic hot water coils as an added bonus. They can be set up independently or in dual sytem with your existing oil/gas boiler. They can accommodate both hot water base board or steam plumbing.
Buckslayer
Member
Posts: 25
Joined: Sun. Jan. 27, 2013 10:23 am
Stove/Furnace Make: Leisure Line
Stove/Furnace Model: 110k / lilheater

Post Sun. Jan. 27, 2013 4:42 pm

Dennis wrote:just a silly question,but does the boiler get to 180 degrees without a load on it.
Yup. Before my wife got in the shower it was at 200. I had the stove cranking today and the boiler hasn't had to run.

I guess the tankless is too much load. I had a cold shower after my wife.

Visit Alternate Heating Sytems

User avatar
Dennis
Member
Posts: 1066
Joined: Sun. Oct. 30, 2011 5:44 pm
Hand Fed Coal Boiler: AHS/WOC55-multi-fuel/wood,oil,coal
Coal Size/Type: Anthracite/stove size
Location: Pottstown,Pa

Post Sun. Jan. 27, 2013 5:03 pm

DHW takes a lot af BTU's,a DHW storage tank might help with that problem

plumber
Member
Posts: 375
Joined: Sun. Mar. 27, 2011 10:52 am
Stoker Coal Boiler: EFM 350
Location: Bridgeton, RI

Post Sun. Jan. 27, 2013 5:23 pm

I have my tankless circulating through a storage tank. I recommend that for all installations. It adds a lot of fudge factor, and you get steady water temperatures.
Ernie

Feet and knees together

Buckslayer
Member
Posts: 25
Joined: Sun. Jan. 27, 2013 10:23 am
Stove/Furnace Make: Leisure Line
Stove/Furnace Model: 110k / lilheater

Post Sun. Jan. 27, 2013 6:19 pm

Dennis wrote:DHW takes a lot af BTU's,a DHW storage tank might help with that problem
The boiler doesn't keep up with my hot water needs! I payed extra for a 5 gallon coil, the boiler should make 5 gallons.

franco b
Site Moderator
Posts: 8449
Joined: Wed. Nov. 05, 2008 5:11 pm
Hand Fed Coal Stove: V ermont Castings 2310, Franco Belge 262
Baseburners & Antiques: Glenwood Modern Oak 114
Coal Size/Type: nut and pea
Location: Kent CT

Post Sun. Jan. 27, 2013 7:52 pm

You would need about 120,000 BTU per hour to raise water temperature 50 degrees at a rate of 5 gallons per minute for one hour. Most use a restricter to limit out put to 3 gallons per minute which is usually adequate and usually demand is not for one hour steadily. Also the reverse aquastat should cut off the circulator at 140 degrees. At your firing rate you could produce a little over 2 gallons per minute for an hour with 50 degree rise.

User avatar
lsayre
Member
Posts: 12249
Joined: Wed. Nov. 23, 2005 9:17 pm
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Blaschak Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW)
Location: N/E Ohio, between Medina and Wadsworth

Post Sun. Jan. 27, 2013 7:57 pm

If I did the math correctly it takes 175,000 BTU's per hour (as output, not input) just to bring 5 GPM of initially 50 degree water up to 120 degrees.

At 80% efficiency that would require nearly 220,000 BTU's of input.
Last edited by lsayre on Sun. Jan. 27, 2013 8:02 pm, edited 1 time in total.
-Larry

Democracy rests upon the principle that collective wisdom arises from a pool of individual ignorance. A Republic rests squarely upon objective law, and fundamentally upon those laws which restrict the scope and actions of government.

Buckslayer
Member
Posts: 25
Joined: Sun. Jan. 27, 2013 10:23 am
Stove/Furnace Make: Leisure Line
Stove/Furnace Model: 110k / lilheater

Post Sun. Jan. 27, 2013 8:01 pm

franco b wrote:You would need about 120,000 BTU per hour to raise water temperature 50 degrees at a rate of 5 gallons per minute for one hour. Most use a restricter to limit out put to 3 gallons per minute which is usually adequate and usually demand is not for one hour steadily. Also the reverse aquastat should cut off the circulator at 140 degrees. At your firing rate you could produce a little over 2 gallons per minute for an hour with 50 degree rise.
So even at the 110000 btus they advertise I can't get 5 gallons per minute? Why do they sell a 5 gallon coil? I payed extra money to get 5 gallons per minute!

CAN THIS BOILER DO ANYTHING LEISURE LINE CLAIMS IT CAN!????

For the kind of money I spent, I expect to get what I payed for. I'm not even getting a fraction of that. From what I've gathered today I'm not the only one with the same problems. What's going on here?

franco b
Site Moderator
Posts: 8449
Joined: Wed. Nov. 05, 2008 5:11 pm
Hand Fed Coal Stove: V ermont Castings 2310, Franco Belge 262
Baseburners & Antiques: Glenwood Modern Oak 114
Coal Size/Type: nut and pea
Location: Kent CT

Post Sun. Jan. 27, 2013 8:12 pm

Buckslayer wrote:So even at the 110000 btus they advertise I can't get 5 gallons per minute? Why do they sell a 5 gallon coil? I payed extra money to get 5 gallons per minute!
The 5 gallon coil gives faster recovery time and provides a little extra as the coil loses efficiency over time.

The bigger concern is why 100 pound a day is not giving you enough heat, especially in a modern house. Even radiant losses from the boiler and piping are in the heated area.

Visit Alternate Heating Sytems

User avatar
lsayre
Member
Posts: 12249
Joined: Wed. Nov. 23, 2005 9:17 pm
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Blaschak Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW)
Location: N/E Ohio, between Medina and Wadsworth

Post Sun. Jan. 27, 2013 8:15 pm

Buckslayer wrote:
franco b wrote:You would need about 120,000 BTU per hour to raise water temperature 50 degrees at a rate of 5 gallons per minute for one hour. Most use a restricter to limit out put to 3 gallons per minute which is usually adequate and usually demand is not for one hour steadily. Also the reverse aquastat should cut off the circulator at 140 degrees. At your firing rate you could produce a little over 2 gallons per minute for an hour with 50 degree rise.
So even at the 110000 btus they advertise I can't get 5 gallons per minute? Why do they sell a 5 gallon coil? I payed extra money to get 5 gallons per minute!
To be fair, most calls for hot water are measured in minutes, not hours, and for a few minutes it should handle the task. Also, to be fair, 5 GPM is a lot of flow, and so is 3 GPM. Most shower heads are probably delivering in the 2 to 2.5 GPM range.
-Larry

Democracy rests upon the principle that collective wisdom arises from a pool of individual ignorance. A Republic rests squarely upon objective law, and fundamentally upon those laws which restrict the scope and actions of government.

User avatar
johnniecuse
Member
Posts: 40
Joined: Fri. Jul. 29, 2011 10:04 pm
Stoker Coal Boiler: Leisure Line 110K Boiler
Coal Size/Type: Rice
Location: Lafayette NY

Post Sun. Jan. 27, 2013 8:17 pm

Yes, I have had the same issues. The boiler is running constantly and I can only get the house up to 62 on real cold days. It was 22F today and I got the house to 66F.

I spoke to Matthaus a couple of times this week and he said many owners are experiencing the same thing. The combustion air fan is simply undersized for the extreme low temperatures. Hopefully they will have new fans available this week.

User avatar
Rick 386
Member
Posts: 2474
Joined: Mon. Jan. 28, 2008 4:26 pm
Stoker Coal Boiler: AA 260 heating both sides of twin farmhouse
Hot Air Coal Stoker Stove: LL Hyfire II w/ coaltrol in garage
Coal Size/Type: Pea in AA 260, Rice in LL Hyfire II
Other Heating: Gas fired infared at work
Location: Royersford, Pa
Contact:

Post Sun. Jan. 27, 2013 8:23 pm

Buckslayer,

I have an AA 260 with I believe a 7 gpm coil in it. If the boiler drops to 140*, we get cold showers. And that temp is also where it shuts off the circulators. And my AA 260 certainly hold more water than your LL110. I try to keep an eye on the boiler temp before me and the wife get our back to back showers. Otherwise 1 of us is getting cool water. This past week has been brutal for a lot of us. Temps that we haven't seen in 2 years and with wind.

Call LL tomorrow and I'm sure they will get you straightened out. It appears that a larger fan will help you and the others out.

Rick
Master of "Trial and Error."

User avatar
Flyer5
Verified Business Rep.
Posts: 10382
Joined: Sun. Oct. 21, 2007 4:23 pm
Stoker Coal Boiler: Leisure Line WL110
Hot Air Coal Stoker Stove: Leisure Line Pioneer
Location: Montrose PA
Contact:

Post Sun. Jan. 27, 2013 8:25 pm

The blower will correct the issue. I have one installed on my boiler since Thursday for testing. I was able to get my 2900sq ft leak box up to 80* with 0* or single digits outside. Recovery times are very much improved . It seems the blower for some reason is effected by the static pressure much more than realised, I believe the supplier for the blower wheels has changed in the last 2 yrs. This may have something to do with it. I am finding just over .3 static pressure on the blower at the feeder during operation. This cuts the standard fan down to about 40cfm and is not enough. The new blower gives 60 CFM at .3 and does a much better job.

To make a long story short we will correct the issue, and we apologize for the inconvenience. So give Matt or me a call or PM us and as soon as we get the fans in we will get them out too those who need them.

Thanks, Dave
http://www.leisurelinestove.com


You know when people say it was "better back in my day"?

They were right.

User avatar
lsayre
Member
Posts: 12249
Joined: Wed. Nov. 23, 2005 9:17 pm
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Blaschak Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW)
Location: N/E Ohio, between Medina and Wadsworth

Post Sun. Jan. 27, 2013 8:31 pm

You absolutely can't beat the level of concern, assistance, attentiveness, fairness, and honesty in bringing full satisfaction to the owners of their products that Leisure Line offers to its customers. Just being willing to openly participate on this forum is a great testimony to this.
-Larry

Democracy rests upon the principle that collective wisdom arises from a pool of individual ignorance. A Republic rests squarely upon objective law, and fundamentally upon those laws which restrict the scope and actions of government.

User avatar
stoker_RI
Member
Posts: 274
Joined: Tue. Dec. 28, 2010 2:01 pm
Stove/Furnace Make: Leisure Line
Stove/Furnace Model: WL 110 Boiler
Location: Northern RI

Post Sun. Jan. 27, 2013 9:09 pm

Flyer5 wrote:The blower will correct the issue. I have one installed on my boiler since Thursday for testing. I was able to get my 2900sq ft leak box up to 80* with 0* or single digits outside. Recovery times are very much improved . It seems the blower for some reason is effected by the static pressure much more than realised, I believe the supplier for the blower wheels has changed in the last 2 yrs. This may have something to do with it. I am finding just over .3 static pressure on the blower at the feeder during operation. This cuts the standard fan down to about 40cfm and is not enough. The new blower gives 60 CFM at .3 and does a much better job.

To make a long story short we will correct the issue, and we apologize for the inconvenience. So give Matt or me a call or PM us and as soon as we get the fans in we will get them out too those who need them.

Thanks, Dave
Dave..can you elaborate on the relationship between static air in the base and the current fan?

-isn't the stock fan rated at 60 cfm also? Is the new fan the same brand?
-with the old fan, what would u expect your home temps to be?
-are you seeing an increase in coal usage? And/or are u able to burn more coal?
-Are you burning rice or buck?...fyi...no buck anywhere in New England that I know of.
THANKS

Rigar
Member
Posts: 857
Joined: Tue. Dec. 04, 2012 6:30 am
Hot Air Coal Stoker Furnace: Keystoker A 150
Coal Size/Type: anthracite rice
Stove/Furnace Make: Keystoker
Stove/Furnace Model: A 150 warm air furnace
Location: central new york (syracuse area)

Post Sun. Jan. 27, 2013 9:29 pm

Lol...while we're asking questions...i got some too ( I've been following this post... And I have stayed out of it until now)
...matthaus stated.
LL ran boilers for 2 days... flat out... while doingUL testing
flat out they were able to burn 65 pounds of coal per operation shift....
how many hours is an operation shift ??
testing resulted in BTU output of 85000 to 101000 ...
.... how or why is this boiler rated at 110 000 BTU ?
... I know leisure line will stand behind their product... I just was curious as to some numbers...

.... bottom line... the boiler does seem to be lacking combustion air.
.. there is a correlation between supply air... draft...and stack velocity
... regardless... I would suggest 10-15 cfm (comb air)/ lb coal...minimum

thanks...and stay warm
....'Rigar