Fire Burnes Out

Post Reply
chuckraes
New Member
Posts: 5
Joined: Sun. Dec. 16, 2012 7:58 pm
Stove/Furnace Make: efm
Stove/Furnace Model: af 150

Post Sun. Dec. 16, 2012 8:11 pm

I have an efm af150,rice burner.i got a fresh load of coal,started the burner,had a good fire and it went out.no biggie. I started over, watched it, lookin good and started the feed. it seems to burn around the outside and fresh unburned coal pushes up, but doesnt burn.I cleaned the pot, unplugged a few holes started fresh and that keeps happening.whats wrong? I had the feed at 2 clicks, air on 3 tried pushing the air up to 4, nothing I do is working and i'm getting frustrated.pleeeease help.

User avatar
Rob R.
Site Moderator
Posts: 11501
Joined: Fri. Dec. 28, 2007 4:26 pm
Stoker Coal Boiler: EFM DF520
Hand Fed Coal Stove: Hitzer 50-93
Coal Size/Type: Lehigh Rice
Other Heating: Dad's 1953 EFM Highboy
Location: Chazy, NY

Post Sun. Dec. 16, 2012 8:43 pm

Welcome to the forum. Was your EFM running fine before this load of coal?

User avatar
Scottscoaled
Member
Posts: 2599
Joined: Tue. Jan. 08, 2008 9:51 pm
Stoker Coal Boiler: EFM 520, 700, Van Wert 800 GJ 61,53
Baseburners & Antiques: Magic Stewart 16, times 2!
Coal Size/Type: Lots of buck
Other Heating: Slant Fin electric boiler backup
Location: Malta N.Y.

Post Sun. Dec. 16, 2012 8:51 pm

Look up from underneath your burn pot and see if the fines cleanout is closed.

User avatar
Rick 386
Member
Posts: 2474
Joined: Mon. Jan. 28, 2008 4:26 pm
Stoker Coal Boiler: AA 260 heating both sides of twin farmhouse
Hot Air Coal Stoker Stove: LL Hyfire II w/ coaltrol in garage
Coal Size/Type: Pea in AA 260, Rice in LL Hyfire II
Other Heating: Gas fired infared at work
Location: Royersford, Pa
Contact:

Post Sun. Dec. 16, 2012 11:50 pm

Chuck

Where are you located ???

Perhaps someone is local to you and come by and brainstorm to resolve this issue................

Rick

Visit Alternate Heating Sytems

User avatar
stoker-man
Verified Business Rep.
Posts: 2063
Joined: Mon. Nov. 19, 2007 9:33 pm
Hand Fed Coal Boiler: 1981 efm wcb-24 in use 365 days a year
Coal Size/Type: Anthracite/Chestnut
Other Heating: Hearthstone wood stove
Location: Lehigh Valley, PA

Post Mon. Dec. 17, 2012 5:43 am

Just worked on one with a similar problem. Turned out it was the fan housing. The area around the inside surface of the fan housing was filled with fine house dust. Cleaned out the dust and it runs like new. The owner had been having problems, but it reached a point suddenly where it wouldn't even keep kindling wood mixed with coal burning.

chuckraes
New Member
Posts: 5
Joined: Sun. Dec. 16, 2012 7:58 pm
Stove/Furnace Make: efm
Stove/Furnace Model: af 150

Post Mon. Dec. 17, 2012 9:23 am

ya it worked great last year.i'm going to take the fan assy. apart today and see what I come up with.there seems to be a lot of fines when it gets to the pot,could that be a problem?

chuckraes
New Member
Posts: 5
Joined: Sun. Dec. 16, 2012 7:58 pm
Stove/Furnace Make: efm
Stove/Furnace Model: af 150

Post Mon. Dec. 17, 2012 9:26 am

i'm in lyons,ny(near rochester) the fines cleanout is closed.

User avatar
Rob R.
Site Moderator
Posts: 11501
Joined: Fri. Dec. 28, 2007 4:26 pm
Stoker Coal Boiler: EFM DF520
Hand Fed Coal Stove: Hitzer 50-93
Coal Size/Type: Lehigh Rice
Other Heating: Dad's 1953 EFM Highboy
Location: Chazy, NY

Post Mon. Dec. 17, 2012 10:00 am

If your coal has a lot of fines, it will require additional air to get a proper burn pattern. It could be as simple as your new load of coal requires more air. But as long as you are troubleshooting....make sure that your auger & pipes are in good shape, and not grinding the coal. You should have 2-4 flights of auger sticking out of the pipe, and the pipes must fit tightly together in the coupler (no gaps). See if the auger flights in the pot are sharp...if so, the auger & pot bushing may need to be replaced.

Visit Alternate Heating Sytems

User avatar
k9 Bara
Member
Posts: 498
Joined: Mon. Mar. 31, 2008 11:27 am
Stoker Coal Boiler: 1996 EFM 520 DF
Coal Size/Type: Buck / Reading
Location: Red Creek, Fair Haven area NY

Post Mon. Dec. 17, 2012 10:31 am

Chuck,

I'll be headed to Lyons later today. Probably around 2 or 3. Headed to the range, would be glad to try and help.

chuckraes
New Member
Posts: 5
Joined: Sun. Dec. 16, 2012 7:58 pm
Stove/Furnace Make: efm
Stove/Furnace Model: af 150

Post Mon. Dec. 17, 2012 11:35 am

that would be great,give me a call-3158797779

User avatar
k9 Bara
Member
Posts: 498
Joined: Mon. Mar. 31, 2008 11:27 am
Stoker Coal Boiler: 1996 EFM 520 DF
Coal Size/Type: Buck / Reading
Location: Red Creek, Fair Haven area NY

Post Tue. Dec. 18, 2012 3:57 am

How did you make out? Sorry, work was busy. How did the burn go after I left? Losing air somewhere, I think a grate.

chuckraes
New Member
Posts: 5
Joined: Sun. Dec. 16, 2012 7:58 pm
Stove/Furnace Make: efm
Stove/Furnace Model: af 150

Post Tue. Dec. 18, 2012 9:02 am

it worked great.the fire was good,flames up where they should be.i'm going to try to figure out where the air is leaking.thanks for helping.

User avatar
k9 Bara
Member
Posts: 498
Joined: Mon. Mar. 31, 2008 11:27 am
Stoker Coal Boiler: 1996 EFM 520 DF
Coal Size/Type: Buck / Reading
Location: Red Creek, Fair Haven area NY

Post Tue. Dec. 18, 2012 10:44 am

Glad to hear it.

Post Reply