Post by Northern Maine » Tue. Dec. 04, 2012 8:17 am

Rob R. wrote:Your load is very light considering the size of your house and your location. I used to burn about 1200 gallons MORE per year. :fear:

The 110k figure for the LL boiler is the gross input?? It is less than I am used to dealing with when it comes to boilers, but it might be fine for your needs.
May be a light load...but not light on the pocket ;)


 
User avatar
Rob R.
Site Moderator
Posts: 18003
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Tue. Dec. 04, 2012 8:24 am

Northern Maine wrote:
Rob R. wrote:Your load is very light considering the size of your house and your location. I used to burn about 1200 gallons MORE per year. :fear:

The 110k figure for the LL boiler is the gross input?? It is less than I am used to dealing with when it comes to boilers, but it might be fine for your needs.
May be a light load...but not light on the pocket ;)
I guess that depends on your point of reference.

Fuel was $3 per gallon when I "quit". It is $3.80 here right now, and I am sure glad the fuel truck doesn't stop at our place any longer.

Back to the heat load - didn't you recently measure the radiators in your house? What was the total length?

 
Northern Maine
Member
Posts: 680
Joined: Sat. Nov. 10, 2012 6:12 pm
Location: Aroostok County, Easton, Maine

Post by Northern Maine » Tue. Dec. 04, 2012 8:44 am

Rob R. wrote:
Northern Maine wrote: May be a light load...but not light on the pocket ;)
I guess that depends on your point of reference.

Fuel was $3 per gallon when I "quit". It is $3.80 here right now, and I am sure glad the fuel truck doesn't stop at our place any longer.

Back to the heat load - didn't you recently measure the radiators in your house? What was the total length?
In my home 120 feet.

 
xandrew245x
Member
Posts: 504
Joined: Sat. Nov. 24, 2012 2:26 pm
Location: Gardners, PA
Hot Air Coal Stoker Stove: keystoker 90
Hand Fed Coal Stove: aarrow stratford 75
Coal Size/Type: anthracite nut/rice
Other Heating: Oil boiler, fireplace

Post by xandrew245x » Tue. Dec. 04, 2012 8:57 am

What I am paying for heating oil right now is $3.49. It is much higher than that, but we switched oil companies, and they locked us in at 3.49, I think it is in the high 3.60s normally.

 
User avatar
dh1200s
Member
Posts: 67
Joined: Sat. Jul. 18, 2009 1:12 pm
Location: Honey Brook, Pa.
Stoker Coal Boiler: Leisure Line WL-110
Hand Fed Coal Boiler: HS-Tarm 202
Hand Fed Coal Stove: Harman TLC 2000

Post by dh1200s » Tue. Dec. 04, 2012 9:46 am

jpd989 wrote:I have mine in since January 2012. Best move I made in my opinion. I am heating 1000sqft. And I have the standard hot water coil, 3gallons a minute. No trouble keeping up with water demands. Keeps the house very comfortable.

I agree the other WL110K users I haven't gone thru cold weather yet (on line 10/23) but I feel it will do the job well based on my experience to date with my old HS Tarm 202 hand fed boiler. I'm heating 1900 Sq's in South East PA.

My DHW heater is just a well insulated storage tank that gets recharged from time to time via the WL110K 5GPM coil.

 
xandrew245x
Member
Posts: 504
Joined: Sat. Nov. 24, 2012 2:26 pm
Location: Gardners, PA
Hot Air Coal Stoker Stove: keystoker 90
Hand Fed Coal Stove: aarrow stratford 75
Coal Size/Type: anthracite nut/rice
Other Heating: Oil boiler, fireplace

Post by xandrew245x » Tue. Dec. 04, 2012 9:49 am

I am going to do a heat loss calculation on my house today, that will determine if the 110 will be sufficient, I have no doubts it don't be sufficient.

 
xandrew245x
Member
Posts: 504
Joined: Sat. Nov. 24, 2012 2:26 pm
Location: Gardners, PA
Hot Air Coal Stoker Stove: keystoker 90
Hand Fed Coal Stove: aarrow stratford 75
Coal Size/Type: anthracite nut/rice
Other Heating: Oil boiler, fireplace

Post by xandrew245x » Tue. Dec. 04, 2012 11:34 am

So for the heat loss calculation I came up with about 30k btu/hr heat loss. Based on the measurements, I actually only have 1576 sq ft of heated space. I was going off the numbers they gave me when I bought the house 1200 sq ft up stairs, 900 down. I have no doubts now that the 110 will provide more than enough heat for my house.


 
Northern Maine
Member
Posts: 680
Joined: Sat. Nov. 10, 2012 6:12 pm
Location: Aroostok County, Easton, Maine

Post by Northern Maine » Tue. Dec. 04, 2012 11:47 am

xandrew245x wrote:So for the heat loss calculation I came up with about 30k btu/hr heat loss. Based on the measurements, I actually only have 1576 sq ft of heated space. I was going off the numbers they gave me when I bought the house 1200 sq ft up stairs, 900 down. I have no doubts now that the 110 will provide more than enough heat for my house.
My heat loss came in at 28k

 
xandrew245x
Member
Posts: 504
Joined: Sat. Nov. 24, 2012 2:26 pm
Location: Gardners, PA
Hot Air Coal Stoker Stove: keystoker 90
Hand Fed Coal Stove: aarrow stratford 75
Coal Size/Type: anthracite nut/rice
Other Heating: Oil boiler, fireplace

Post by xandrew245x » Tue. Dec. 04, 2012 11:52 am

What did you set the inside temp and outside temp as, I did one for inside temp 72 and outside 30 and the other outside temp 15 at 15 degrees outside the heat loss is still only half of what the 110k should be able to put out, even at 80% efficiency.

The 110k should have no problem keeping up with my house heat and dhw.

 
Northern Maine
Member
Posts: 680
Joined: Sat. Nov. 10, 2012 6:12 pm
Location: Aroostok County, Easton, Maine

Post by Northern Maine » Tue. Dec. 04, 2012 12:00 pm

xandrew245x wrote:So for the heat loss calculation I came up with about 30k btu/hr heat loss. Based on the measurements, I actually only have 1576 sq ft of heated space. I was going off the numbers they gave me when I bought the house 1200 sq ft up stairs, 900 down. I have no doubts now that the 110 will provide more than enough heat for my house.
My heat loss came in at 32k after re-working some numbers

 
xandrew245x
Member
Posts: 504
Joined: Sat. Nov. 24, 2012 2:26 pm
Location: Gardners, PA
Hot Air Coal Stoker Stove: keystoker 90
Hand Fed Coal Stove: aarrow stratford 75
Coal Size/Type: anthracite nut/rice
Other Heating: Oil boiler, fireplace

Post by xandrew245x » Tue. Dec. 04, 2012 12:07 pm

Even at 0 Degrees outside, which doesn't happen to often around here, I could keep it at 76 degrees and its still be plenty okay.

 
Northern Maine
Member
Posts: 680
Joined: Sat. Nov. 10, 2012 6:12 pm
Location: Aroostok County, Easton, Maine

Post by Northern Maine » Tue. Dec. 04, 2012 12:09 pm

xandrew245x wrote:Even at 0 Degrees outside, which doesn't happen to often around here, I could keep it at 76 degrees and its still be plenty okay.
We see lot of 0 degree days and many -10 days as well....but I think the LL110 would keep up with my needs just fine!

 
xandrew245x
Member
Posts: 504
Joined: Sat. Nov. 24, 2012 2:26 pm
Location: Gardners, PA
Hot Air Coal Stoker Stove: keystoker 90
Hand Fed Coal Stove: aarrow stratford 75
Coal Size/Type: anthracite nut/rice
Other Heating: Oil boiler, fireplace

Post by xandrew245x » Tue. Dec. 04, 2012 12:13 pm

I live in south central pa and the coldest days I remember are like 10-15 degrees in the mornings.

 
User avatar
jpen1
Member
Posts: 614
Joined: Sat. Nov. 04, 2006 4:46 pm
Location: Bloomsburg, PA
Stoker Coal Boiler: LL110
Coal Size/Type: Rice/ Buck

Post by jpen1 » Tue. Dec. 04, 2012 10:10 pm

My heat loss came up to 42k when I did the calc. and when the hvac people did it, it came to 37k. I have 130' equivalent of standard baseboard and I have no issues with the boiler keeping up. Based on the oil boiler size I would say it will work just fine.

 
xandrew245x
Member
Posts: 504
Joined: Sat. Nov. 24, 2012 2:26 pm
Location: Gardners, PA
Hot Air Coal Stoker Stove: keystoker 90
Hand Fed Coal Stove: aarrow stratford 75
Coal Size/Type: anthracite nut/rice
Other Heating: Oil boiler, fireplace

Post by xandrew245x » Tue. Dec. 11, 2012 8:02 am

What kind of coal usage am I looking at with the boiler, I heard that boilers will use more coal than a normal stove.