question for you guys out there, I have a 900sq foot pole building with 10 foot high celings, I just installed a modine heater in the ceiling that will heat with hot water. I ran 1 inch pex from the building to the house approx 150 ft total length from heater to stoker for return and supply. I have to circs on it one to push the water and one to return to the boiler. my house is 1400 sq feet will the 520 be able to heat all this and what should my setting be thanks
- Short Bus
- Member
- Posts: 510
- Joined: Sun. Jan. 10, 2010 12:22 am
- Location: Cantwell Alaska
- Stoker Coal Boiler: Kewanee boiler with Anchor stoker
- Coal Size/Type: Chestnut / Sub-bituminous C
- Other Heating: Propane wall furnace back up only
To answer that question correctly we need to know somthing about your heating load, typically quantified with a heat loss calculation, http://www.tombling.com/heaters/heatloss.htm , basically you determine the heat loss for each component of your structures and add them together. The more effort the more accuracy.
But since we all like to shoot form the hip.
How big is this Modine hydronic heater, how much heat loss can we expect form the piping, that information and the BTU rating of your coal can help you determine how much coal will be needed to run the Modine for one hour. Add some coal for inefficiency.
Good luck, it sounds like it is already built, so why worry about it, turn it on and see what happens.
You can probalby find a better heat loss calcuator, by searching this site in the upper right.
But since we all like to shoot form the hip.
How big is this Modine hydronic heater, how much heat loss can we expect form the piping, that information and the BTU rating of your coal can help you determine how much coal will be needed to run the Modine for one hour. Add some coal for inefficiency.
Good luck, it sounds like it is already built, so why worry about it, turn it on and see what happens.
You can probalby find a better heat loss calcuator, by searching this site in the upper right.
- Rob R.
- Site Moderator
- Posts: 17980
- Joined: Fri. Dec. 28, 2007 4:26 pm
- Location: Chazy, NY
- Stoker Coal Boiler: EFM 520
- Hand Fed Coal Stove: Chubby Jr
That is the big question. If it is well insulated and protected from ground water, the heat loss from the piping should be minimal.Short Bus wrote:how much heat loss can we expect form the piping
I agree, flip the switch and see what happens. If you discover that the boiler gets slammed with cold water from the piping, you may need to adjust the valves on your soon to be installed bypass.Short Bus wrote:Good luck, it sounds like it is already built, so why worry about it, turn it on and see what happens.
- whistlenut
- Member
- Posts: 3548
- Joined: Sat. Mar. 17, 2007 6:29 pm
- Location: Central NH, Concord area
- Stoker Coal Boiler: AA130's,260's, AHS130&260's,EFM900,GJ & V-Wert
- Hand Fed Coal Boiler: Franks,Itasca 415,Jensen, NYer 130,Van Wert
- Hot Air Coal Stoker Furnace: Alaska, EFM, Keystoker, Yellow Flame
- Hot Air Coal Stoker Stove: Alaska, Keystoker-2,Leisure Line
- Hand Fed Coal Stove: Alaska, Gibraltar, Keystone,Vc Vigilant 2
- Hand Fed Coal Furnace: Ford, Jensen, NYer, Van Wert,
- Baseburners & Antiques: Glenwoods
- Coal Size/Type: Barley, Buck, Rice ,Nut, Stove
- Other Heating: Oil HWBB
Without any further comment: Of course it will heat the house and shop. I'll bet that by January you will know all the answers to your questions. 'Learn as you burn' is the inverse of Murphy's Law, and is one great institution of higher learning!
(Part of the KISS Philosophy of Engineering)....... :surrender:
(Part of the KISS Philosophy of Engineering)....... :surrender:
- Scottscoaled
- Member
- Posts: 2812
- Joined: Tue. Jan. 08, 2008 9:51 pm
- Location: Malta N.Y.
- Stoker Coal Boiler: EFM 520, 700, Van Wert 800 GJ 61,53
- Baseburners & Antiques: Magic Stewart 16, times 2!
- Coal Size/Type: Lots of buck
- Other Heating: Slant Fin electric boiler backup
Might depend on if the 520 is in the pole barn or the house. The 1" will push in the neighborhood of 70k BTU'S. How big was your Modine?
-
- Member
- Posts: 145
- Joined: Tue. Jul. 03, 2012 10:00 pm
- Stoker Coal Boiler: efm coal boiler
- Coal Size/Type: rice
- Other Heating: Bryant evolution heat pump
my modine puts out 80,000 buts
- whistlenut
- Member
- Posts: 3548
- Joined: Sat. Mar. 17, 2007 6:29 pm
- Location: Central NH, Concord area
- Stoker Coal Boiler: AA130's,260's, AHS130&260's,EFM900,GJ & V-Wert
- Hand Fed Coal Boiler: Franks,Itasca 415,Jensen, NYer 130,Van Wert
- Hot Air Coal Stoker Furnace: Alaska, EFM, Keystoker, Yellow Flame
- Hot Air Coal Stoker Stove: Alaska, Keystoker-2,Leisure Line
- Hand Fed Coal Stove: Alaska, Gibraltar, Keystone,Vc Vigilant 2
- Hand Fed Coal Furnace: Ford, Jensen, NYer, Van Wert,
- Baseburners & Antiques: Glenwoods
- Coal Size/Type: Barley, Buck, Rice ,Nut, Stove
- Other Heating: Oil HWBB
80 K ON STEAM OR HOT WATER? The info tag usually displays the steam output first. Might be 67 K on hot water if it is like mine. Either way, the boiler will easily do the job for you. 1" copper is good for 80K ish at 8 gpm, so if you increase the circ size and up-tic the flow rate....it will be happy. If it is piped in pex, expect a somewhat lower BTU capability, simply due to a smaller inside diameter. Slow and steady wins the heating game, every single time.
-
- Member
- Posts: 145
- Joined: Tue. Jul. 03, 2012 10:00 pm
- Stoker Coal Boiler: efm coal boiler
- Coal Size/Type: rice
- Other Heating: Bryant evolution heat pump
hot water 80,000 its a heavy old think lol got it from an hospitol, they used in the boiler room