AHS S130 Coalgun- Puffbacks & Explosions

Stoker Coal Boilers automatically feed the coal and have controls and pumps just like any conventions boiler. They are intended to be used as a primary heat and often have domestic hot water coils as an added bonus. They can be set up independently or in dual sytem with your existing oil/gas boiler. They can accommodate both hot water base board or steam plumbing.
Bob
Member
Posts: 304
Joined: Sun. Mar. 18, 2007 11:28 am
Stoker Coal Boiler: AHS 130
Coal Size/Type: Pea/Anthracite
Location: Schuylkill County

Post Tue. Nov. 15, 2011 9:47 pm

lsayre wrote:
Bob wrote:Thanks for posting the response.

I think it is a bit puzzling that AHS makes no mention of the information that has been in the Axeman manual for 50 years--that improper "thickness of the fire" can cause puff-backs and that with an AHS boiler with the thermograte option the way to adjust the thickness of the fire is by changing SV.
Am I understanding this correctly that at SV=140 the fire column should be thicker (less ash bed below the hot coals), and at SV=120 it should be thiner (more ash bed below the hot coals)?
Yes.

Visit Alternate Heating Sytems

dchartt
Member
Posts: 172
Joined: Fri. Sep. 02, 2011 5:22 pm
Stoker Coal Boiler: AHS 130
Hand Fed Coal Stove: Glacier Bay

Post Tue. Nov. 15, 2011 9:49 pm

.o4 while idling and .06 or .07 while running?

Bob
Member
Posts: 304
Joined: Sun. Mar. 18, 2007 11:28 am
Stoker Coal Boiler: AHS 130
Coal Size/Type: Pea/Anthracite
Location: Schuylkill County

Post Tue. Nov. 15, 2011 9:52 pm

dchartt wrote:.o4 while idling and .06 or .07 while running?
The draft spec for the AHS is at idle and the barometric damper should be adjusted to maintain .04 at idle. Depending on your chimney, wind, etc the draft it idle may drop below .04 but should not go above .04 at idle.

User avatar
lsayre
Member
Posts: 12205
Joined: Wed. Nov. 23, 2005 9:17 pm
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Blaschak Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW)
Location: N/E Ohio, between Medina and Wadsworth

Post Wed. Nov. 16, 2011 5:52 am

My baro damper is just beginning to open at 0.04", and is well opened at 0.05". Is that correct, or should I adjust for a bit more draft?
-Larry

Democracy rests upon the principle that collective wisdom arises from a pool of individual ignorance. A Republic rests squarely upon objective law, and fundamentally upon those laws which restrict the scope and actions of government.

User avatar
Rob R.
Site Moderator
Posts: 11348
Joined: Fri. Dec. 28, 2007 4:26 pm
Stoker Coal Boiler: EFM DF520
Hand Fed Coal Stove: Hitzer 50-93
Coal Size/Type: Lehigh Rice
Other Heating: Dad's 1953 EFM Highboy
Location: Chazy, NY

Post Wed. Nov. 16, 2011 5:57 am

lsayre wrote:My baro damper is just beginning to open at 0.04", and is well opened at 0.05". Is that correct, or should I adjust for a bit more draft?
Since you seem to be one of the few with no puff-backs, I would leave it alone.

User avatar
lsayre
Member
Posts: 12205
Joined: Wed. Nov. 23, 2005 9:17 pm
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Blaschak Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW)
Location: N/E Ohio, between Medina and Wadsworth

Post Wed. Nov. 16, 2011 6:05 am

markviii wrote:
lsayre wrote:My baro damper is just beginning to open at 0.04", and is well opened at 0.05". Is that correct, or should I adjust for a bit more draft?
Since you seem to be one of the few with no puff-backs, I would leave it alone.
Still no puff-backs so far. This morning I just checked and I'm only at 0.025" of draft right now at idle. It is quite calm here right now and a balmy 52 degrees as of 6:00 AM. Should that be a major concern?
-Larry

Democracy rests upon the principle that collective wisdom arises from a pool of individual ignorance. A Republic rests squarely upon objective law, and fundamentally upon those laws which restrict the scope and actions of government.

dchartt
Member
Posts: 172
Joined: Fri. Sep. 02, 2011 5:22 pm
Stoker Coal Boiler: AHS 130
Hand Fed Coal Stove: Glacier Bay

Post Wed. Nov. 16, 2011 8:20 am

is anyone running 6 inch flue pipe on their s130? im pretty sure my plumber has my whole freaking setup messed up, I toldem it took 5 and he ordered 6 and he even had the manual in his possession, my coalgun is up in my barn, well my circulator pump he put in my basement, he has my thermostat hooked up to my pump through a acquastat also in the basement, so when my thermostat calls for heat my pump kicks on, now if that drops my boiler temp way down to say 100 my pump doesnt shut off it keeps pumpin cold water, and with the 6inch flue pipe im gettin all kinds of flyash gathering in my barometric damper, and I also just noticed when my boiler just started to fire I have smoke coming out of the top of my flue pipe outside, I couldnt believe it, I really need help, im burning like a 100lb a day and its not really cold at all here

User avatar
Rob R.
Site Moderator
Posts: 11348
Joined: Fri. Dec. 28, 2007 4:26 pm
Stoker Coal Boiler: EFM DF520
Hand Fed Coal Stove: Hitzer 50-93
Coal Size/Type: Lehigh Rice
Other Heating: Dad's 1953 EFM Highboy
Location: Chazy, NY

Post Wed. Nov. 16, 2011 8:27 am

dchartt wrote:now if that drops my boiler temp way down to say 100 my pump doesnt shut off it keeps pumpin cold water, and with the 6inch flue pipe im gettin all kinds of flyash gathering in my barometric damper, and I also just noticed when my boiler just started to fire I have smoke coming out of the top of my flue pipe outside, I couldnt believe it, I really need help, im burning like a 100lb a day and its not really cold at all here
It sounds like you have some control issues, and possibly flue gas condensation...which could create "smoke" (probably water vapor) you are seeing. I would either move the circulator to the boiler room and control it with an aquastat, or install a mixing valve on your boiler piping to keep the return temperature above 140 degrees.

How about taking some pictures of your setup in the boiler room and in the basement, then creating a new thread to discuss.

Visit Alternate Heating Sytems

dchartt
Member
Posts: 172
Joined: Fri. Sep. 02, 2011 5:22 pm
Stoker Coal Boiler: AHS 130
Hand Fed Coal Stove: Glacier Bay

Post Wed. Nov. 16, 2011 8:31 am

ok, I do have a mixing valve but its setup to keep my pex below 180, im going to take pictures right now

User avatar
Rob R.
Site Moderator
Posts: 11348
Joined: Fri. Dec. 28, 2007 4:26 pm
Stoker Coal Boiler: EFM DF520
Hand Fed Coal Stove: Hitzer 50-93
Coal Size/Type: Lehigh Rice
Other Heating: Dad's 1953 EFM Highboy
Location: Chazy, NY

Post Wed. Nov. 16, 2011 9:17 am

dchartt wrote:ok, I do have a mixing valve but its setup to keep my pex below 180, im going to take pictures right now
Sounds good. Just create a new thread and we will go from there.

rychw
Member
Posts: 92
Joined: Wed. Jan. 30, 2008 2:23 pm
Stoker Coal Boiler: AHS 130
Coal Size/Type: Pea
Stove/Furnace Make: AHS
Stove/Furnace Model: 130
Location: Sykesville, MD

Post Wed. Nov. 16, 2011 6:05 pm

dchartt wrote:if the temp doesnt go down its locked, theres 2 buttons on the left of the up n down arrows,
dchartt,

My Fuji controller only has one button to the left of the up and down buttons and I can't unlock it. Anyone else out there with any ideas how to unlock the controller to lower my as temps?

Bob
Member
Posts: 304
Joined: Sun. Mar. 18, 2007 11:28 am
Stoker Coal Boiler: AHS 130
Coal Size/Type: Pea/Anthracite
Location: Schuylkill County

Post Wed. Nov. 16, 2011 6:19 pm

rychw wrote:
dchartt wrote:if the temp doesnt go down its locked, theres 2 buttons on the left of the up n down arrows,
dchartt,

My Fuji controller only has one button to the left of the up and down buttons and I can't unlock it. Anyone else out there with any ideas how to unlock the controller to lower my as temps?
Follow the directions in the attachment.
Attachments
AHS Thermo grate programmingl.pdf
(67.1 KiB) Downloaded 14 times

rychw
Member
Posts: 92
Joined: Wed. Jan. 30, 2008 2:23 pm
Stoker Coal Boiler: AHS 130
Coal Size/Type: Pea
Stove/Furnace Make: AHS
Stove/Furnace Model: 130
Location: Sykesville, MD

Post Wed. Nov. 16, 2011 6:30 pm

Thanks Bob. Will follow and reprogram. I have had no booms this week but I have been monitoring the boiler when it runs and shutting off the grate switch manually when the grate runs without the fan running, or there is no fire in the tube and the grate is dumping and adding fresh coal. The silence from AHS on this thread is un-nerving. :o I hoped that they would jump in and try to help us figure this explosion problem out, but it appears we have do so by trial and error. :mad:

dchartt
Member
Posts: 172
Joined: Fri. Sep. 02, 2011 5:22 pm
Stoker Coal Boiler: AHS 130
Hand Fed Coal Stove: Glacier Bay

Post Thu. Nov. 17, 2011 8:18 am

sorry I don't have the fugi controls, my are the love controls

dchartt
Member
Posts: 172
Joined: Fri. Sep. 02, 2011 5:22 pm
Stoker Coal Boiler: AHS 130
Hand Fed Coal Stove: Glacier Bay

Post Thu. Nov. 17, 2011 8:22 am

i also manually operated my boiler the same way, seemed like everything got a little worse as far as ashing, it never ashed when it shouldve thus not bringing the fire closer to the grate and heating the grate temp up which caused it to want to ash more often because the temps were low which cause more unburnt coal in my ashpan