Post by Tryingitout » Thu. Feb. 09, 2017 1:01 pm

Don, I just realized that I posted back that I installed the pump in the bypass, not so. It is installed in the return line, but it is close to the bypass, not much options for the placement.

Q. I plan to run vertical pipe to the floor, but I have to get a piece. It is a KAA-2, Keystokers instructions require the bladder tank off the top of the boiler, not much I could do other than that. The tank I installed for the domestic coil is in line.

Coaledsweat, good idea on the dirt leg.


 
Ritcho
New Member
Posts: 1
Joined: Wed. Apr. 12, 2017 2:58 am

Post by Ritcho » Wed. Apr. 12, 2017 5:02 am

Great pics everybody.

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Mon. Apr. 17, 2017 7:55 pm

Here are some pics of my little Gentleman Janitor GJ-671. I converted this to run an EFM S-15 stoker unit.
IMG_1090.JPG
.JPG | 108.7KB | IMG_1090.JPG
IMG_1094.JPG
.JPG | 102.2KB | IMG_1094.JPG
IMG_1097.JPG
.JPG | 107.6KB | IMG_1097.JPG
This boiler was converted to oil a long time ago. They mounted the oil gun right in the fire door.
SmallGJ 002.JPG
.JPG | 139.7KB | SmallGJ 002.JPG
I cut the hole square and mounted a piece of 6"x6" wood stove glass in it. Now I have a fire view Gentleman Janitor!
IMG_1098.JPG
.JPG | 99KB | IMG_1098.JPG
IMG_1104.JPG
.JPG | 68.8KB | IMG_1104.JPG
IMG_1101.JPG
.JPG | 49.1KB | IMG_1101.JPG
This one was done quick & dirty. I cut an EFM sized hole in the GJ stoker mounting plate, drilled the 3 holes for the EFM feed pipe sealing collar and nailed it together.
IMG_1081.JPG
.JPG | 108.7KB | IMG_1081.JPG
I flushed the boiler out real good and that's all. The EFM was a running unit and I just stuck it in there. After I got it running, I had to re-face the drive pawl so it would stop skipping teeth.

-Don

 
User avatar
franpipeman
Member
Posts: 689
Joined: Fri. Jan. 11, 2008 4:27 pm
Location: Wernersville pa
Stoker Coal Boiler: efm 520 stoker fitzgibbons pressure vessel
Hand Fed Coal Stove: harman, russo
Coal Size/Type: rice
Other Heating: alpine propane condensing boiler radiant floor

Post by franpipeman » Sun. Nov. 19, 2017 8:46 am

pictures from the archives

Attachments

DSC00920.JPG

dhw coil repair

.JPG | 876.2KB | DSC00920.JPG
DSC01037.JPG

gravity circulating primary loop

.JPG | 813.1KB | DSC01037.JPG
DSC01038.JPG
.JPG | 759.7KB | DSC01038.JPG
DSC01039.JPG
.JPG | 960.7KB | DSC01039.JPG
DSC01040.JPG
.JPG | 962.9KB | DSC01040.JPG

 
User avatar
BunkerdCaddis
Member
Posts: 708
Joined: Sun. Jan. 18, 2015 10:26 am
Location: SW Lancaster County
Stoker Coal Boiler: Bairmatic-Van Wert
Hand Fed Coal Boiler: Van Wert VW85H
Hand Fed Coal Stove: Saey Hanover II working when I feel the desire, Waterford 105 out on vacation, Surdiac Gotha hiding somewhere
Coal Size/Type: pea/nut/rice/stove-anthracite, nut/stove bit when I feel the urge
Other Heating: oil fired hydronic

Post by BunkerdCaddis » Sun. Nov. 19, 2017 11:00 am

franpipeman wrote:
Sun. Nov. 19, 2017 8:46 am
pictures from the archives
Victaulic and welded... :o dang... (I'm assuming residential)

 
User avatar
franpipeman
Member
Posts: 689
Joined: Fri. Jan. 11, 2008 4:27 pm
Location: Wernersville pa
Stoker Coal Boiler: efm 520 stoker fitzgibbons pressure vessel
Hand Fed Coal Stove: harman, russo
Coal Size/Type: rice
Other Heating: alpine propane condensing boiler radiant floor

Post by franpipeman » Sun. Nov. 19, 2017 7:02 pm

yes two building residential , large diameter supports gravity circulation seems to work well.

 
bobok
Member
Posts: 105
Joined: Mon. Jan. 13, 2014 10:03 pm
Location: Richfiled Springs, ny
Stoker Coal Boiler: efm700 stoker, Pacific 350K boiler
Hand Fed Coal Boiler: D&S Machine hand fed
Coal Size/Type: stove / buck
Other Heating: Bethleham Dynatherm Oil boiler

Post by bobok » Sun. Dec. 31, 2017 4:21 pm

Our 1961 EFM 700 in 1951 Pacific boiler Hummin' along on New years eve at -7 in the am, in central NY. Running 9-10 hrs in 24. Two large shops and the house. Happy New year all. Bobok

Attachments

Resized_20171231_080054.jpeg

Nice n' Hot

.JPEG | 49KB | Resized_20171231_080054.jpeg


 
horses_rus
New Member
Posts: 9
Joined: Mon. Oct. 27, 2008 1:24 pm
Location: Beech Creek PA.
Stoker Coal Boiler: Stoker Coal Boiler 4 Circulator Systom
Coal Size/Type: Rice
Other Heating: Oil

Post by horses_rus » Sun. Dec. 31, 2017 9:17 pm

Very nice fire but seems to me not enough air because the ash ring has hot red coal over the ash ring. I would suggest giving it just a little bit more air so you have just ashes over the ash ring. And the center will become a darker spot. Just what I see from the picture. Happy New Year :)

 
User avatar
Scottscoaled
Member
Posts: 2812
Joined: Tue. Jan. 08, 2008 9:51 pm
Location: Malta N.Y.
Stoker Coal Boiler: EFM 520, 700, Van Wert 800 GJ 61,53
Baseburners & Antiques: Magic Stewart 16, times 2!
Coal Size/Type: Lots of buck
Other Heating: Slant Fin electric boiler backup

Post by Scottscoaled » Mon. Jan. 01, 2018 12:10 am

Looks good Bob! Happy New Year to you. Nice rotating pot stoker. Looking perfectly adjusted as usual. You should give us some more pictures.

 
Dave 1234
Member
Posts: 788
Joined: Tue. Nov. 13, 2012 9:05 am
Stoker Coal Boiler: 1948 International boiler, EFM S-20 stoker
Coal Size/Type: Buck,

Post by Dave 1234 » Mon. Jan. 01, 2018 9:10 am

Scottscoaled wrote:
Mon. Jan. 01, 2018 12:10 am
Looks good Bob! Happy New Year to you. Nice rotating pot stoker. Looking perfectly adjusted as usual. You should give us some more pictures.
I'm with Scott , Bob you built a nice heat plant there. We def need more pictures !!

( someone said you can get kicked off the site for lack of pics.) Lol idk if thats true.

Dave

 
User avatar
Rob R.
Site Moderator
Posts: 17979
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Mon. Jan. 01, 2018 9:19 am

Dave 1234 wrote:
Mon. Jan. 01, 2018 9:10 am
I'm with Scott , Bob you built a nice heat plant there. We def need more pictures !!

( someone said you can get kicked off the site for lack of pics.) Lol idk if thats true.

Dave
Dave, check out his install thread: EFM 700 Reconditioned by Me and Installed in 1955 Pacific

 
Dave 1234
Member
Posts: 788
Joined: Tue. Nov. 13, 2012 9:05 am
Stoker Coal Boiler: 1948 International boiler, EFM S-20 stoker
Coal Size/Type: Buck,

Post by Dave 1234 » Mon. Jan. 01, 2018 10:45 am

That is a nice hy-bred setup !
I'm very interested in the performance of Bob's 700 stoker during warm weather, if he has it fired ?
It's been a while sense I have seen Bob post. So hopefully he will have time to reply .

Dave

 
User avatar
Scottscoaled
Member
Posts: 2812
Joined: Tue. Jan. 08, 2008 9:51 pm
Location: Malta N.Y.
Stoker Coal Boiler: EFM 520, 700, Van Wert 800 GJ 61,53
Baseburners & Antiques: Magic Stewart 16, times 2!
Coal Size/Type: Lots of buck
Other Heating: Slant Fin electric boiler backup

Post by Scottscoaled » Mon. Jan. 01, 2018 11:10 am

His name is actually Bill.

 
bobok
Member
Posts: 105
Joined: Mon. Jan. 13, 2014 10:03 pm
Location: Richfiled Springs, ny
Stoker Coal Boiler: efm700 stoker, Pacific 350K boiler
Hand Fed Coal Boiler: D&S Machine hand fed
Coal Size/Type: stove / buck
Other Heating: Bethleham Dynatherm Oil boiler

Post by bobok » Wed. Jan. 03, 2018 7:34 pm

Thanks guys for the comps, Yes I did burn it through the summer for DHW. Timer came on 2 min every hour and only went on high limit a few times in the 90+ weather. never lost the fire, cleaned it twice in the early and mid summer. Burning Lehigh buck and very happy with it. It really hums along in in the sub zero weather and the auto ash removal new this past summer works great. Bill (bobok)

 
bobok
Member
Posts: 105
Joined: Mon. Jan. 13, 2014 10:03 pm
Location: Richfiled Springs, ny
Stoker Coal Boiler: efm700 stoker, Pacific 350K boiler
Hand Fed Coal Boiler: D&S Machine hand fed
Coal Size/Type: stove / buck
Other Heating: Bethleham Dynatherm Oil boiler

Post by bobok » Wed. Jan. 03, 2018 7:36 pm

Forgot to mention that scottscoaled helped a lot with settings last year. Thanks again Scott. Bobok.