AHS S130 : Barometric Damper and Flue Diameter Question

Stoker Coal Boilers automatically feed the coal and have controls and pumps just like any conventions boiler. They are intended to be used as a primary heat and often have domestic hot water coils as an added bonus. They can be set up independently or in dual sytem with your existing oil/gas boiler. They can accommodate both hot water base board or steam plumbing.
User avatar
lsayre
Member
Posts: 12243
Joined: Wed. Nov. 23, 2005 9:17 pm
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Blaschak Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW)
Location: N/E Ohio, between Medina and Wadsworth

Post Sun. Feb. 20, 2011 7:27 pm

Since the AHS S130 has a 5" flue collar, would a 5" dia. Field Controls RC barometric damper and a 5" flue pipe be my best choice(s) for it, or would it be best to step things up to 6"?
-Larry

Democracy rests upon the principle that collective wisdom arises from a pool of individual ignorance. A Republic rests squarely upon objective law, and fundamentally upon those laws which restrict the scope and actions of government.

Visit Alternate Heating Sytems

User avatar
lsayre
Member
Posts: 12243
Joined: Wed. Nov. 23, 2005 9:17 pm
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Blaschak Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW)
Location: N/E Ohio, between Medina and Wadsworth

Post Sun. Feb. 20, 2011 7:37 pm

If 5" is adequate, does this seem like a fair deal for a baro damper?

**Broken Link(s) Removed**
-Larry

Democracy rests upon the principle that collective wisdom arises from a pool of individual ignorance. A Republic rests squarely upon objective law, and fundamentally upon those laws which restrict the scope and actions of government.

User avatar
AA130FIREMAN
Member
Posts: 1951
Joined: Sat. Feb. 28, 2009 4:13 pm
Stove/Furnace Make: axeman anderson
Stove/Furnace Model: 130 anthratube

Post Sun. Feb. 20, 2011 8:16 pm

I would set it up like axeman recomends, 5" half way threw a 6" T with a 6" barometric damper.

User avatar
lsayre
Member
Posts: 12243
Joined: Wed. Nov. 23, 2005 9:17 pm
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Blaschak Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW)
Location: N/E Ohio, between Medina and Wadsworth

Post Sun. Feb. 20, 2011 8:27 pm

Do you know why they would recommend that configuration? A 5" pipe has roughly 69% of the cross-sectional area of a 6" pipe, but if you extend a 5" pipe half way through a 6" pipe and thereby restrict it by somewhat less than 50% (less than 50% because a 5" pipe inside a 6" will not block the entire width), then in doing so doesn't this in some way restrict the the function of a 6" baro damper enough that a 5" wouldn't perform much differently?
Last edited by lsayre on Sun. Feb. 20, 2011 8:30 pm, edited 1 time in total.
-Larry

Democracy rests upon the principle that collective wisdom arises from a pool of individual ignorance. A Republic rests squarely upon objective law, and fundamentally upon those laws which restrict the scope and actions of government.

User avatar
coaledsweat
Site Moderator
Posts: 9826
Joined: Fri. Oct. 27, 2006 2:05 pm
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea
Location: Guilford, Connecticut

Post Sun. Feb. 20, 2011 8:30 pm

lsayre wrote:Do you know why they would recommend that configuration? A 5" pipe has roughly 69% of the cross-sectional area of a 6" pipe, but if you extend a 5" pipe half way through a 6" pipe and thereby restrict it by nearly 50%, then in doing so doesn't this in some way restrict the the function of a 6" baro damper enough that a 5" wouldn't perform much differently?
It doesn't have any effect on the baro, it just keeps the soot in the pipe instead of your cellar.
Nothing is impossible for people who don't have to do it themselves.

User avatar
lsayre
Member
Posts: 12243
Joined: Wed. Nov. 23, 2005 9:17 pm
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Blaschak Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW)
Location: N/E Ohio, between Medina and Wadsworth

Post Sun. Feb. 20, 2011 8:33 pm

I'm assuming that the main pipe is 5" over its entire length, and only the tee and Barometric damper are 6". Am I picturing this correctly in my mind?
-Larry

Democracy rests upon the principle that collective wisdom arises from a pool of individual ignorance. A Republic rests squarely upon objective law, and fundamentally upon those laws which restrict the scope and actions of government.

User avatar
Freddy
Member
Posts: 6606
Joined: Fri. Apr. 11, 2008 2:54 pm
Stoker Coal Boiler: Axeman Anderson 130 (pea)
Hot Air Coal Stoker Stove: Reading piece o' junk in the barn (rice)
Coal Size/Type: Pea size, Superior, deep mined
Location: Orrington, Maine

Post Sun. Feb. 20, 2011 8:38 pm

There is a reason to make a baro setup exactly as Axeman Anderson directs. You see, the AA exhaust is fan driven and therefore under pressure. If you use a 5" baro or even a 6" baro with a "normal" increaser, then exhaust gasses will tend to come out of the barometric damper. By having the 5" pipe go almost, but not quite, half way into a 6" T, then the gasses are pushed past the baro where the natural draft of the chimney will pick up and exhaust gasses out the chimney. When the fan first starts you might get a small puff out the baro, but within a second all gasses go up the chimney. If you do not do as AA directs, then gasses will constantly come into the boiler room.

Here's a pic looking into a AA baro. You can see how the 5" goes into the 6". It's a home made rig....they all are!
Attachments
Baro.JPG
Orrington, Maine
Fred

"If you can't say something nice, don't say anything at all".

User avatar
Yanche
Member
Posts: 3032
Joined: Fri. Dec. 23, 2005 12:45 pm
Stoker Coal Boiler: Alternate Heating Systems S-130
Coal Size/Type: Anthracite Pea
Location: Sykesville, Maryland

Post Sun. Feb. 20, 2011 8:40 pm

You should use 5" black stove pipe and a 6" Fields RC damper. See my installation photos in this post:

5" up to 6" Flu Pipe

This concentric pipe install is what A-A recommends in their installation manual. It's especially suitable for high natural draft flues. The baro should go at the chimney thimble. You want the 5" pipe to have the minimum of bends. Eliminate true 90 degree turns and clean out tees. What you are trying to achieve is high stove pipe velocity, ideally laminar flow. When the combustion blower is running this will convey the fly ash to the chimney. There a large change in pressure will occur because the velocity flow goes from 5" to the large chimney area. The fly ash will fall out and drop to the bottom of the chimney. You clean this annually.

There is no need for the more expensive Fields type M in this application. The Type M is for applications requiring more sensitivity in automatic adjustment to flue gas velocity changes. This is not one of those applications, especially with the concentric flue pipe arrangement. You will need a baro to get it set. Depending on your particular chimney you may need to add more weight to the baro flapper. Most certainly ignore the factory engraved settings, they are completely wrong for this use. It's possible you may need to change the position of the two pipes, i.e. how far they fit into each other. They other thing you can do to adjust things is to trim away some of the inter pipe at the damper. This will allow more chimney draft through the damper door rather than going through the 5" pipe. My install has worked well for me.
Yanche
Alternate Heating Systems S-130
Stoker Boiler burning Anthracite Pea Coal

Visit Alternate Heating Sytems

User avatar
Freddy
Member
Posts: 6606
Joined: Fri. Apr. 11, 2008 2:54 pm
Stoker Coal Boiler: Axeman Anderson 130 (pea)
Hot Air Coal Stoker Stove: Reading piece o' junk in the barn (rice)
Coal Size/Type: Pea size, Superior, deep mined
Location: Orrington, Maine

Post Sun. Feb. 20, 2011 8:42 pm

PS

I found that on very windy days my draft would go higher than it should and I would overheat a little bit. After the first season I added a second baro damper directly across from the one picured. Now if I took that same photo you would see the other damper on the other side. Now on windy days jusssst as the original damper is totally open, the second one opens & the draft stays correct. I keep mine at .02 to .03.

<edit> *smile* We got this one covered times two! LOL
Orrington, Maine
Fred

"If you can't say something nice, don't say anything at all".

User avatar
AA130FIREMAN
Member
Posts: 1951
Joined: Sat. Feb. 28, 2009 4:13 pm
Stove/Furnace Make: axeman anderson
Stove/Furnace Model: 130 anthratube

Post Sun. Feb. 20, 2011 8:58 pm

I did mine with all 6", but if I do it again, it will be 5" into 6", with mine I used a small piece of pipe cut down the middle to collapse it, inserted into the T , left it expand and screwed it fast. 5 inch stove pipe is harder to come by. This helps the flyash scoot by the baro (and stay inside) but not 100%
Attachments
axeman boiler 002.jpg

User avatar
lsayre
Member
Posts: 12243
Joined: Wed. Nov. 23, 2005 9:17 pm
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Blaschak Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW)
Location: N/E Ohio, between Medina and Wadsworth

Post Sun. Feb. 20, 2011 9:01 pm

Thanks Freddy and Yanche! The reasoning here is sound, and pictures sure help.

Yanche, what is the pipe sealant that I see in your photos, and what did you use for the 3 x 1/2" spacers?
-Larry

Democracy rests upon the principle that collective wisdom arises from a pool of individual ignorance. A Republic rests squarely upon objective law, and fundamentally upon those laws which restrict the scope and actions of government.

User avatar
lsayre
Member
Posts: 12243
Joined: Wed. Nov. 23, 2005 9:17 pm
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Blaschak Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW)
Location: N/E Ohio, between Medina and Wadsworth

Post Sun. Feb. 20, 2011 9:06 pm

I've been searching the net, and I'm not finding any single wall 5" stove pipe other than galvanized (which I assume is a big no-no). Do any of you have links that you can provide? Is stainless steel available?
-Larry

Democracy rests upon the principle that collective wisdom arises from a pool of individual ignorance. A Republic rests squarely upon objective law, and fundamentally upon those laws which restrict the scope and actions of government.

User avatar
coaledsweat
Site Moderator
Posts: 9826
Joined: Fri. Oct. 27, 2006 2:05 pm
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea
Location: Guilford, Connecticut

Post Sun. Feb. 20, 2011 9:14 pm

Find a local HVAC supply house. They should have commercial grade pipe in any size and adapters to make it work. You may have to play with the adapter to get the 5" a slip fit.
Nothing is impossible for people who don't have to do it themselves.

User avatar
lsayre
Member
Posts: 12243
Joined: Wed. Nov. 23, 2005 9:17 pm
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Blaschak Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW)
Location: N/E Ohio, between Medina and Wadsworth

Post Sun. Feb. 20, 2011 9:14 pm

Freddy wrote:PS

I found that on very windy days my draft would go higher than it should and I would overheat a little bit. After the first season I added a second baro damper directly across from the one picured. Now if I took that same photo you would see the other damper on the other side. Now on windy days jusssst as the original damper is totally open, the second one opens & the draft stays correct. I keep mine at .02 to .03.

<edit> *smile* We got this one covered times two! LOL
Are you using a 6" cross instead of a tee?
-Larry

Democracy rests upon the principle that collective wisdom arises from a pool of individual ignorance. A Republic rests squarely upon objective law, and fundamentally upon those laws which restrict the scope and actions of government.

User avatar
McGiever
Member
Posts: 6002
Joined: Sun. May. 02, 2010 11:26 pm
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Coal Size/Type: PEA / ANTHRACITE
Other Heating: Ground Source Heat Pump
Stove/Furnace Make: Hydro Heat /Mega Tek
Location: Junction of PA-OH-WV

Post Sun. Feb. 20, 2011 9:16 pm

SLOW AND STEADY WINS THE RACE