AHS S130 : Coal Consumption During Summer Months?

Stoker Coal Boilers automatically feed the coal and have controls and pumps just like any conventions boiler. They are intended to be used as a primary heat and often have domestic hot water coils as an added bonus. They can be set up independently or in dual sytem with your existing oil/gas boiler. They can accommodate both hot water base board or steam plumbing.
User avatar
CoalHeat
Site Moderator
Posts: 8327
Joined: Sat. Feb. 10, 2007 9:48 pm
Stoker Coal Boiler: 1959 EFM 350
Hand Fed Coal Stove: Harman Magnafire Mark I
Baseburners & Antiques: Sears Signal Oak 15 & Andes Kitchen Range
Coal Size/Type: Rice and Chestnut
Other Heating: Fisher Fireplace Insert
Location: Stillwater, New Jersey

Post Thu. Jan. 27, 2011 8:06 pm

If it will require that I burn 50-60 lbs. coal per day just to idle it and provide DHW,
Some of us burn that amount for heating on cold winter days. I can't see using that much during the summer.
My boiler will be running 365 days a year, I'll let you know in a few months.
Heating a circa 1832 farmhouse with a Harman Magnafire Mark I & a 1959 EFM 350 (heating DHW).
100% Oil Free!
"It's what we learn after we think we know it all that counts."

Visit Alternate Heating Sytems

User avatar
lsayre
Member
Posts: 12253
Joined: Wed. Nov. 23, 2005 9:17 pm
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Blaschak Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW)
Location: N/E Ohio, between Medina and Wadsworth

Post Thu. Jan. 27, 2011 8:12 pm

Many thanks Wood'nCoal. It will be very interesting to see how it turns out for you.
-Larry

Democracy rests upon the principle that collective wisdom arises from a pool of individual ignorance. A Republic rests squarely upon objective law, and fundamentally upon those laws which restrict the scope and actions of government.

User avatar
lsayre
Member
Posts: 12253
Joined: Wed. Nov. 23, 2005 9:17 pm
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Blaschak Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW)
Location: N/E Ohio, between Medina and Wadsworth

Post Thu. Jan. 27, 2011 8:17 pm

whistlenut wrote:I understand the situation, and it becomes a personal choice, however if the stove pipe and baro rust up, you will be out some cash anyway, and it the boiler is not cleaned and treated, the shorter life expectancy of the equipment has to weigh in. It is more than saving every cent.....you aren't an accountant are you??? :? :lol:

It could become a 'Penny wise and pound foolish' issue. I'm not saying it would, but it sure could. I'll bet Toyota wishes they had used a more rust resistant steel in the pickup frames.....

Either way it will work, I'm just trying to extend the life of the system; they are expensive enough the first time! :idea:
Not an accountant, but sometimes I think I might as well be one. I'm a buyer/planner (a purchasing agent who has to plan and manage plant inventory as well as seek out the best material prices).
-Larry

Democracy rests upon the principle that collective wisdom arises from a pool of individual ignorance. A Republic rests squarely upon objective law, and fundamentally upon those laws which restrict the scope and actions of government.

rangaller
Member
Posts: 39
Joined: Sat. Aug. 09, 2008 12:08 am
Stove/Furnace Make: Alternate Heating
Stove/Furnace Model: AHS S130
Location: NEPA

Post Thu. Jan. 27, 2011 8:48 pm

lsayre wrote:Many thanks Wood'nCoal. It will be very interesting to see how it turns out for you.
I really think that you would be using much less than the 40 lbs that I used. I never fine tuned for summer running as I really am still moving along the AHS/Coal burning learning curve. But recent findings indicate that my burn/dump temp was set at 140F. This can be set to 120F for low demand periods (summer) and this should maximize effieciency of burn for summer and probably cut coal consumption sharply.

For me, even at 4o pounds per day coal is still 1/2 the price of what oil would cost me.

Stephen

User avatar
brckwlt
Member
Posts: 2743
Joined: Tue. Jan. 27, 2009 8:32 pm
Stove/Furnace Make: Axeman-Anderson
Stove/Furnace Model: Rebuilt 1953 AA-130
Location: Sunbury, PA

Post Fri. Jan. 28, 2011 12:04 am

i have an aa-13o which is similar to your ahs 130 and I burned on average about 20lbs a day over the summer
burning pea coal from harmony mine, picked up in my 2002 Pontiac "Coalfire"

User avatar
lsayre
Member
Posts: 12253
Joined: Wed. Nov. 23, 2005 9:17 pm
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Blaschak Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW)
Location: N/E Ohio, between Medina and Wadsworth

Post Fri. Jan. 28, 2011 5:59 am

Thanks brckwlt! Based on all of the testimony here, I'm resolved to running year round, sans for a brief outage for tube cleaning and maintenance.
-Larry

Democracy rests upon the principle that collective wisdom arises from a pool of individual ignorance. A Republic rests squarely upon objective law, and fundamentally upon those laws which restrict the scope and actions of government.

lew
New Member
Posts: 16
Joined: Sat. Jan. 22, 2011 4:28 pm
Stove/Furnace Make: AHS
Stove/Furnace Model: ahs-30

Post Fri. Jan. 28, 2011 7:14 am

I just installed an AHS S130 this December. On average I would say that we are going through 60 lbs. a day heating 2,000 squaare ft. and DHW. I have my thermo ash control set at 120 and have had 0 problems. I have been slowly dropping the temp. setting from 140. Would like to set it lower and see where it takes me. I too, am thinking of running it all summer, but am concernend about the cost versus benefits. I will be trying it for some time just to see where that takes me.

Tull
Member
Posts: 50
Joined: Thu. Oct. 30, 2008 12:31 pm
Stoker Coal Boiler: AHS-S130
Coal Size/Type: Pea/Anthracite
Other Heating: Oil for standby
Location: South Central PA

Post Tue. Feb. 01, 2011 2:46 pm

Isayre:

Do a search under "low load capabilities of the coal gun". You will find that Yanche says he was consuming 17-18 lb per day; you probably won't get much lower than that. I have been using my S130 year-round since mid 2009 and am quite satisfied. I did not measure summer coal consumption, though. Perhaps next summer. Good luck, anyway!
Wayne L

Visit Alternate Heating Sytems

User avatar
lsayre
Member
Posts: 12253
Joined: Wed. Nov. 23, 2005 9:17 pm
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Blaschak Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW)
Location: N/E Ohio, between Medina and Wadsworth

Post Tue. Feb. 01, 2011 2:48 pm

Thanks! Others have suggested that about 20 lbs./day is the low limit, so Yanche's 17-18 is probably the absolute minimum for daily summer consumption. Some of the heating cost that I gain during the winter will be lost during the summer, but apparently such is the price to be paid to keep the system from corroding or rusting and giving up the ghost prematurely.
-Larry

Democracy rests upon the principle that collective wisdom arises from a pool of individual ignorance. A Republic rests squarely upon objective law, and fundamentally upon those laws which restrict the scope and actions of government.

Tull
Member
Posts: 50
Joined: Thu. Oct. 30, 2008 12:31 pm
Stoker Coal Boiler: AHS-S130
Coal Size/Type: Pea/Anthracite
Other Heating: Oil for standby
Location: South Central PA

Post Tue. Feb. 01, 2011 3:06 pm

Isayre:

I generally agree with your statement, but perhaps rather than saying "Some of the heating cost that I gain during the winter will be lost during the summer" it may be that you will be basically breaking even during the summer, while saving big in the winter. Depends on oil prices, coal prices, amount of DHW use, etc. I will try to measure my consumption his summer and see what it really is. Hope things go as well for you as they have for me.
Wayne L

homecomfort
Member
Posts: 485
Joined: Sat. Feb. 05, 2011 1:10 pm
Stove/Furnace Make: Franco-Belge,+ Penn Stove
Stove/Furnace Model: Normandie, + Chubby
Location: Bucks county, Pa.

Post Thu. Mar. 10, 2011 9:31 pm

I installed an electric heat pump water heater in my cellar. It uses the free, renewable heat energy from the basement floor area. also the humidity contains energy which it removes and uses for heating water, along with dehumidifying the air, so mold is reduced. Unit gives 4 times the hot water as electric it consumes. %350 to 400 efficient. domestic hot water only requires 1/10 of the BTU capacity of heating the house. coal stove heat in basement is also recycled with it.

User avatar
Yanche
Member
Posts: 3032
Joined: Fri. Dec. 23, 2005 12:45 pm
Stoker Coal Boiler: Alternate Heating Systems S-130
Coal Size/Type: Anthracite Pea
Location: Sykesville, Maryland

Post Thu. Mar. 10, 2011 9:39 pm

homecomfort wrote:I installed an electric heat pump water heater in my cellar. It uses the free, renewable heat energy from the basement floor area. also the humidity contains energy which it removes and uses for heating water, along with dehumidifying the air, so mold is reduced. Unit gives 4 times the hot water as electric it consumes. %350 to 400 efficient. domestic hot water only requires 1/10 of the BTU capacity of heating the house. coal stove heat in basement is also recycled with it.
What brand and model number? Does the domestic hot water production capability vary winter vs. summer when the coal stove is not being used?
Yanche
Alternate Heating Systems S-130
Stoker Boiler burning Anthracite Pea Coal

Tull
Member
Posts: 50
Joined: Thu. Oct. 30, 2008 12:31 pm
Stoker Coal Boiler: AHS-S130
Coal Size/Type: Pea/Anthracite
Other Heating: Oil for standby
Location: South Central PA

Post Tue. Jun. 07, 2011 6:36 pm

I just measured my coal consumption for the week ending last Sunday (6/5/2011). My AHS S130 consumed 100 lb of pea coal in 7 days and produced 19 lb of ashes. This is for DHW for a family of 6. Comes out to 14.3 lb/day. I measured both the coal and ash by weight, not volume, and I would say my numbers are accurate to within +/- 5%. My unit has the thermocouple-controlled grate. Your mileage may vary.
Wayne L

coalnewbie
Member
Posts: 6207
Joined: Sat. May. 24, 2008 4:26 pm
Hot Air Coal Stoker Stove: LL AnthraKing 180K, Pocono110K,KStokr 90K, DVC
Hand Fed Coal Stove: Invader 2
Baseburners & Antiques: Wings Best, Glenwood #8(x2) Herald 116x
Coal Size/Type: Rice,
Other Heating: Heating Oil CH, Toyotomi OM 22
Location: Chester, NY

Post Tue. Jun. 07, 2011 8:40 pm

.. and if you put a Kilowatt ($30 Lowes) on the AHS how many KWH does it consume per month to give you that DHW?
Posted by an unreasonable adult.

cabinover
Member
Posts: 1589
Joined: Wed. Feb. 04, 2009 7:13 am
Stoker Coal Boiler: Hybrid Axeman Anderson 130
Baseburners & Antiques: Sparkle #12
Coal Size/Type: Pea, Buckwheat, Nut
Other Heating: LP Hot air. WA TX for coal use.
Location: Fair Haven, VT

Post Wed. Jun. 08, 2011 3:22 pm

Here's what I found with my AA130. I was having no problem keeping a fire with the coal StokerScot brought me last winter. When I ran out of that I bought some from a local guy with Cornwall as the source. It was out last night after running fine on the other coal. I have had to bump up the time to a minute and a half every half hour.

The UAE coal would do about 10-11 days on 300#, this other stuff fills the ash pan and barely does 7 days on the same charge.

At this rate I might as well go back to propane with a more efficient water heater, keeping my garage cooler in the process.
Always learning, still stupid though :D