Stoker Coal Boilers automatically feed the coal and have controls and pumps just like any conventions boiler. They are intended to be used as a primary heat and often have domestic hot water coils as an added bonus. They can be set up independently or in dual sytem with your existing oil/gas boiler. They can accommodate both hot water base board or steam plumbing.
crzynuz
New Member
Posts: 3
Joined: Thu. Jan. 06, 2011 9:41 am
Stove/Furnace Make: efm
Stove/Furnace Model: 520

Post Thu. Jan. 06, 2011 9:47 am

My water temp will not go above 150 and I just had the aqua stat and circulation pump replaced. changed my aqua stat settings 160-200 no heat in my house for 3 days HELP

Visit Alternate Heating Sytems

User avatar
AA130FIREMAN
Member
Posts: 1951
Joined: Sat. Feb. 28, 2009 4:13 pm
Stove/Furnace Make: axeman anderson
Stove/Furnace Model: 130 anthratube

Post Thu. Jan. 06, 2011 10:07 am

Are you shure it is wired correctly (triple aquastat)? L1 hot L2 neutral coming from the main switch, TT are low voltage from a thermostat, B1 B2 go to the stoker motor, C1 C2 are for the circulator pump, ZC ZR can go to a switching relay. Can you post a picture of how it is wired ?

User avatar
CoalHeat
Site Moderator
Posts: 8327
Joined: Sat. Feb. 10, 2007 9:48 pm
Stoker Coal Boiler: 1959 EFM 350
Hand Fed Coal Stove: Harman Magnafire Mark I
Baseburners & Antiques: Sears Signal Oak 15 & Andes Kitchen Range
Coal Size/Type: Rice and Chestnut
Other Heating: Fisher Fireplace Insert
Location: Stillwater, New Jersey

Post Thu. Jan. 06, 2011 10:11 am

Did you have this problem before the aquastat and pump were replaced? I'm assuming that you did, that's why the work was done.
With the current aquastat settings of 160/200 and a water temperature of 150° the stoker should not shut off. Is it running continuously?
Heating a circa 1832 farmhouse with a Harman Magnafire Mark I & a 1959 EFM 350 (heating DHW).
100% Oil Free!
"It's what we learn after we think we know it all that counts."

User avatar
Rob R.
Site Moderator
Posts: 11343
Joined: Fri. Dec. 28, 2007 4:26 pm
Stoker Coal Boiler: EFM DF520
Hand Fed Coal Stove: Hitzer 50-93
Coal Size/Type: Lehigh Rice
Other Heating: Dad's 1953 EFM Highboy
Location: Chazy, NY

Post Thu. Jan. 06, 2011 10:12 am

I hate to ask the obvious...but is the stoker running? Does the fire look orange and bright? What is the feed rate set at?

User avatar
CoalHeat
Site Moderator
Posts: 8327
Joined: Sat. Feb. 10, 2007 9:48 pm
Stoker Coal Boiler: 1959 EFM 350
Hand Fed Coal Stove: Harman Magnafire Mark I
Baseburners & Antiques: Sears Signal Oak 15 & Andes Kitchen Range
Coal Size/Type: Rice and Chestnut
Other Heating: Fisher Fireplace Insert
Location: Stillwater, New Jersey

Post Thu. Jan. 06, 2011 10:13 am

I hate to ask the obvious...but is the stoker running?
Why not? I did.
Heating a circa 1832 farmhouse with a Harman Magnafire Mark I & a 1959 EFM 350 (heating DHW).
100% Oil Free!
"It's what we learn after we think we know it all that counts."

crzynuz
New Member
Posts: 3
Joined: Thu. Jan. 06, 2011 9:41 am
Stove/Furnace Make: efm
Stove/Furnace Model: 520

Post Thu. Jan. 06, 2011 10:49 am

stoker is running I will have to upload pics

User avatar
Sting
Member
Posts: 2970
Joined: Mon. Feb. 25, 2008 4:24 pm
Other Heating: OBSO Lennox Pulse "Air Scorcher" burning NG
Location: Lower Fox Valley = Wisconsin

Post Thu. Jan. 06, 2011 11:22 am

EDIT---> Close the valve on the SUPPLY side of the circulator about half and see what happens then! 8-)

Get back to me or do a search for system balance.
Last edited by Sting on Thu. Jan. 06, 2011 2:10 pm, edited 1 time in total.
When you turn your boiler on -Does it return the favor?
I have finally lost my mind. Don't bother to return it. It wasn't working properly anyway!

User avatar
Rob R.
Site Moderator
Posts: 11343
Joined: Fri. Dec. 28, 2007 4:26 pm
Stoker Coal Boiler: EFM DF520
Hand Fed Coal Stove: Hitzer 50-93
Coal Size/Type: Lehigh Rice
Other Heating: Dad's 1953 EFM Highboy
Location: Chazy, NY

Post Thu. Jan. 06, 2011 1:09 pm

Did this boiler previously heat the house without any problems?

Visit Alternate Heating Sytems

crzynuz
New Member
Posts: 3
Joined: Thu. Jan. 06, 2011 9:41 am
Stove/Furnace Make: efm
Stove/Furnace Model: 520

Post Thu. Jan. 06, 2011 2:28 pm

I am new at all this! Never touched one before. I have to go and look these things up. Still having same problem I started out with. Trying the valve thing now.

User avatar
AA130FIREMAN
Member
Posts: 1951
Joined: Sat. Feb. 28, 2009 4:13 pm
Stove/Furnace Make: axeman anderson
Stove/Furnace Model: 130 anthratube

Post Thu. Jan. 06, 2011 2:56 pm

crzynuz wrote:I am new at all this! Never touched one before. I have to go and look these things up. Still having same problem I started out with. Trying the valve thing now.
If you are not that familiar with the controls, who replaced the aquastat ? And if you had to pay the person or company, why not call them ? Could it be they didn't replace what was wrong and you pay for their guess work until they get it right ? I would not pay until they fix the problem and give an explination on why they replaced what they did.
Last edited by AA130FIREMAN on Thu. Jan. 06, 2011 3:03 pm, edited 1 time in total.

User avatar
Rob R.
Site Moderator
Posts: 11343
Joined: Fri. Dec. 28, 2007 4:26 pm
Stoker Coal Boiler: EFM DF520
Hand Fed Coal Stove: Hitzer 50-93
Coal Size/Type: Lehigh Rice
Other Heating: Dad's 1953 EFM Highboy
Location: Chazy, NY

Post Thu. Jan. 06, 2011 3:00 pm

crzynuz wrote:I am new at all this! Never touched one before. I have to go and look these things up. Still having same problem I started out with. Trying the valve thing now.
Where do you live? If you are lucky there will be an EFM guru nearby that can educate you on this unit.

User avatar
Sting
Member
Posts: 2970
Joined: Mon. Feb. 25, 2008 4:24 pm
Other Heating: OBSO Lennox Pulse "Air Scorcher" burning NG
Location: Lower Fox Valley = Wisconsin

Post Thu. Jan. 06, 2011 3:03 pm

Not saying the replaced control is the issue

Unsure why this is a problem today and not last year

but

It wouldn't be the first time a mechanic changed a burner control and opened the valves that used to keep the system in balance - because he didn't understand circulation.

so there is the root of my suggestion - and that's all it is -- just a suggestion from a figment of the public internet - anything you do on your system is of your doing alone - always understand what you doing and why - then take full custody and control of the result.
When you turn your boiler on -Does it return the favor?
I have finally lost my mind. Don't bother to return it. It wasn't working properly anyway!

User avatar
AA130FIREMAN
Member
Posts: 1951
Joined: Sat. Feb. 28, 2009 4:13 pm
Stove/Furnace Make: axeman anderson
Stove/Furnace Model: 130 anthratube

Post Thu. Jan. 06, 2011 3:06 pm

Sting wrote:always understand what you doing and why - then take full custody and control of the result.
In other words, YOU BREAK IT, YOU BOUGHT IT. :mad:

User avatar
stoker-man
Verified Business Rep.
Posts: 2063
Joined: Mon. Nov. 19, 2007 9:33 pm
Hand Fed Coal Boiler: 1981 efm wcb-24 in use 365 days a year
Coal Size/Type: Anthracite/Chestnut
Other Heating: Hearthstone wood stove
Location: Lehigh Valley, PA

Post Thu. Jan. 06, 2011 4:45 pm

This comes from the Honeywell site and the aquastat is probably an L7224A since it was recently replaced.

Adjusting Settings
To discourage unauthorized changing of Aquastat® settings, a
procedure to enter the adjustment mode is required. To enter the
adjustment mode, press the UP, DOWN, and I buttons
simultaneously for three seconds. Press the I button until the
feature requiring adjustment is displayed:
• HL—High Limit.
• LL—Low Limit.
• Ldf—Low Limit differential.
• F - C—°F or °C.
Then press the UP and/or DOWN buttons to move the set point to
the desired value. After 60 seconds without any button inputs, the
control will automatically return to the READ mode.
To use the L7224U in a cold start boiler application, disable the
Low Limit function by pressing the UP arrow button, DOWN arrow
button and I buttons simultaneously for three seconds. Then push
the I button until LL is displayed. Then press the down arrow
button until OFF is displayed.

With the thermostat turned up and the water temperature above the low limit, the circulator should start. If it's a Taco 007, you may have to put your ear directly against it to hear it running, or use a piece of wood against the body of the circulator and to your ear. If the circulator isn't running, that's the problem. If it is running, then the boiler pressure may be too low. It should be at least 12#. If you have 12 pounds and the zones are open, then I would suspect air in the lines.

What exactly happened just before the problem began.
‹(•¿•)›

User avatar
CoalHeat
Site Moderator
Posts: 8327
Joined: Sat. Feb. 10, 2007 9:48 pm
Stoker Coal Boiler: 1959 EFM 350
Hand Fed Coal Stove: Harman Magnafire Mark I
Baseburners & Antiques: Sears Signal Oak 15 & Andes Kitchen Range
Coal Size/Type: Rice and Chestnut
Other Heating: Fisher Fireplace Insert
Location: Stillwater, New Jersey

Post Thu. Jan. 06, 2011 6:11 pm

Before we jump to conclusions we need crzynuz to answer all our questions. :idea: :idea:
Heating a circa 1832 farmhouse with a Harman Magnafire Mark I & a 1959 EFM 350 (heating DHW).
100% Oil Free!
"It's what we learn after we think we know it all that counts."