Emf 520 Boiler Coal Not Burning up All the Way

Post Reply
 
Union123
New Member
Posts: 4
Joined: Fri. Dec. 10, 2010 5:52 am

Post by Union123 » Sat. Dec. 11, 2010 8:57 am

We have a efm 520 boiler and are using to much coal it looks to me like it isn't all burning, we have the feed set at 4 the air set about 4 1/2 water temp 180 not sure where to go with this, time is 1 1/2 min. every 15 min.

 
User avatar
stoker-man
Verified Business Rep.
Posts: 2071
Joined: Mon. Nov. 19, 2007 9:33 pm
Location: Lehigh Valley, PA
Hand Fed Coal Boiler: 1981 efm wcb-24 in use 365 days a year
Coal Size/Type: Anthracite/Chestnut
Other Heating: Hearthstone wood stove

Post by stoker-man » Sat. Dec. 11, 2010 12:48 pm

How wide is the ash ring after it's been burning for 45 minutes straight?

What is the diameter of the dark spot in the center after it's been burning for 45 minutes straight?

Did this problem start with a delivery of new coal?

Does the pot glow completely orange when it's stoking and then turn to salt and pepper in the ash ring?

 
Union123
New Member
Posts: 4
Joined: Fri. Dec. 10, 2010 5:52 am

Post by Union123 » Sat. Dec. 11, 2010 1:01 pm

1 1/2 ash ring not realy any dark ring in center ash does look salt and pepper this has been going on since we installed it

 
User avatar
Pa Dealer
Member
Posts: 242
Joined: Fri. Aug. 15, 2008 10:12 am
Location: NEPA
Stoker Coal Boiler: EFM 520 DF
Coal Size/Type: Rice
Other Heating: Keystoker

Post by Pa Dealer » Sat. Dec. 11, 2010 5:14 pm

When it's running are the flames licking the top of the boiler,is there unburnt coal in the ashes ,maybe bad coal.

ry

 
User avatar
stoker-man
Verified Business Rep.
Posts: 2071
Joined: Mon. Nov. 19, 2007 9:33 pm
Location: Lehigh Valley, PA
Hand Fed Coal Boiler: 1981 efm wcb-24 in use 365 days a year
Coal Size/Type: Anthracite/Chestnut
Other Heating: Hearthstone wood stove

Post by stoker-man » Sat. Dec. 11, 2010 7:26 pm

Does the burning coal in the pot glow completely orange?


 
Union123
New Member
Posts: 4
Joined: Fri. Dec. 10, 2010 5:52 am

Post by Union123 » Wed. Dec. 22, 2010 10:26 am

we checke the draft and the best we could get was about 3 coming out of boiler with the air at about 3 1/2 but with it like that we had alot of unburnt coal in ash, we bumped the air back to about 4 1/2 could this be some of our problem

 
User avatar
Rob R.
Site Moderator
Posts: 17980
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Wed. Dec. 22, 2010 10:46 am

I have a list of questions to try and help narrow this down. Here goes:

What size coal are you burning? Rice? Buck?

Do you know the source of the coal?

Does it have a lot of small pieces or fines?

Are you sure the "unburned" coal you are seeing isn't shale/bone?

How did you end up with the timer set to run the stoker every 15 minutes?

How much coal are you burning per day and what kind of load are you putting on the boiler?

-Rob

 
Union123
New Member
Posts: 4
Joined: Fri. Dec. 10, 2010 5:52 am

Post by Union123 » Thu. Dec. 23, 2010 11:00 am

Rice coal
Not sure of source
not alot of fines
burning at feed on 4 and air on 4 1/2 ash looks pretty good kinda klinky
Not sure my brother got that info
When it is in the teens we burn at least 4 five gallon buckets a day/the house is about 3000 sq ft well insulated good windows, but the boiler is in the garage about 40ft from house and lines anr undergound in pvc not sure how deep

 
User avatar
Rob R.
Site Moderator
Posts: 17980
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Thu. Dec. 23, 2010 11:33 am

If 4.5 air gives you a good burn, leave it there. As for the draft, as long as you have negative draft at the firedoor -0.03 at the flue will work. I also would change the timer to run the stoker for 2 minutes every 30 minutes, that is EFM's recommended starting point.

More questions.

Where do you live?
Does your EFM have an insulated jacket around the boiler?
Is the garage heated?
How well insulated are the lines?
Do you constantly circulate between the EFM and the house?

My thoughts are that if you have an uninsulated boiler running in an unheated garage, and you are losing some heat underground, 160 lbs per day is not impossible for heating a 3,000 sq. ft home in cold weather. As a means for comparison, do you know how much fuel/propane/wood/whatever it took the heat the house previously?

-Rob

 
User avatar
Scottscoaled
Member
Posts: 2812
Joined: Tue. Jan. 08, 2008 9:51 pm
Location: Malta N.Y.
Stoker Coal Boiler: EFM 520, 700, Van Wert 800 GJ 61,53
Baseburners & Antiques: Magic Stewart 16, times 2!
Coal Size/Type: Lots of buck
Other Heating: Slant Fin electric boiler backup

Post by Scottscoaled » Thu. Dec. 23, 2010 11:36 am

When did you last clean the inside of flyash? Flyash is one of the best insulators. If you don't clean the ash off once or twice a year your effeciency suffers. Mine was using way too much coal also. After I cleaned it , it cut my usage considerably. :)


 
Pacowy
Member
Posts: 3555
Joined: Tue. Sep. 04, 2007 10:14 pm
Location: Dalton, MA
Stoker Coal Boiler: H.B. Smith 350 Mills boiler/EFM 85R stoker
Coal Size/Type: Buckwheat/anthracite

Post by Pacowy » Thu. Dec. 23, 2010 2:57 pm

I think Rob has asked a lot of good questions, and I agree the usage rate doesn't look that bad under the circumstances. I also agree with Rob that the timer settings may have been contributing to the incomplete burn.

Mike
markviii wrote:If 4.5 air gives you a good burn, leave it there. As for the draft, as long as you have negative draft at the firedoor -0.03 at the flue will work. I also would change the timer to run the stoker for 2 minutes every 30 minutes, that is EFM's recommended starting point.

More questions.

Where do you live?
Does your EFM have an insulated jacket around the boiler?
Is the garage heated?
How well insulated are the lines?
Do you constantly circulate between the EFM and the house?

My thoughts are that if you have an uninsulated boiler running in an unheated garage, and you are losing some heat underground, 160 lbs per day is not impossible for heating a 3,000 sq. ft home in cold weather. As a means for comparison, do you know how much fuel/propane/wood/whatever it took the heat the house previously?

-Rob

 
Budsnblues
New Member
Posts: 2
Joined: Thu. Nov. 21, 2019 12:31 pm
Stoker Coal Boiler: EFM 520
Coal Size/Type: Rice

Post by Budsnblues » Thu. Nov. 21, 2019 12:38 pm

I have no idea about drafts or meters or gauges but have the same problem. Rice coal auger fed and had it professionally cleaned out two years ago. February of last year it started to not burn a lot of the coal. It finally just went out, so I switched over to oil. I just switched over to another vendor and go 3 tons of blaschak coal but the same problem. ?? Live just a couple streets outside of Schuylkill Haven

 
User avatar
nepacoal
Member
Posts: 1696
Joined: Wed. Nov. 21, 2012 7:49 am
Location: Coal Country
Stoker Coal Boiler: Keystoker KAA-4 / "Kelly" and an EFM 520 at my in-laws
Hand Fed Coal Boiler: Harman SF-260 - retired
Coal Size/Type: Buck

Post by nepacoal » Thu. Nov. 21, 2019 12:42 pm

What are your settings? How many teeth, how much air? Are you cleaning the inside of the boiler and stove pipe every year?

 
User avatar
StokerDon
Site Moderator
Posts: 7486
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Thu. Nov. 21, 2019 7:06 pm

Budsnblues wrote:
Thu. Nov. 21, 2019 12:38 pm
I have no idea about drafts or meters or gauges but have the same problem. Rice coal auger fed and had it professionally cleaned out two years ago.
Professional or not, it needs to be cleaned more that once every 2 years.

What feed setting is it at? What air setting is it at? Do you pull the fines clean out lever once a day, or at least once a week?

-Don