terrykennedy
New Member
Posts: 1
Joined: Wed. Dec. 23, 2009 8:47 am
Stove/Furnace Make: efm520
Stove/Furnace Model: 520

Post Wed. Dec. 23, 2009 9:04 am

i recently added more baseboards to my home the plumber said my furnace is plenty big enough but I don't get much heat in them baseboards must I move the thermostat into the last room also [/

User avatar
Sting
Member
Posts: 2966
Joined: Mon. Feb. 25, 2008 4:24 pm
Other Heating: OBSO Lennox Pulse "Air Scorcher" burning NG
Location: Lower Fox Valley = Wisconsin

Post Wed. Dec. 23, 2009 9:27 am

Can you verify that there is or isn't energy charged liquid flowing in that zone?

User avatar
WNY
Member
Posts: 5865
Joined: Mon. Nov. 14, 2005 8:40 am
Hot Air Coal Stoker Stove: Keystoker 90K, Leisure Line Hyfire I
Coal Size/Type: Rice
Stove/Furnace Make: Keystoker, LL & CoalTrol
Stove/Furnace Model: 90K, Hyfire I, VF3000 Soon
Location: Cuba, NY
Contact:

Post Wed. Dec. 23, 2009 2:29 pm

Are you getting ANY heat? or none at all? Was it added to an existing run? You can only go so far with a single run, otherwise it will cool off too much. Did you bleed them to get the air out? Make sure there no valves turned off? make sure the pumps working....etc....there is a lot to check to verify everything is working properly first. What's your boiler Aquastat set at? what's your water temperature?

Visit Alternate Heating Sytems

User avatar
Pa Dealer
Member
Posts: 244
Joined: Fri. Aug. 15, 2008 10:12 am
Stoker Coal Boiler: EFM 520 DF
Coal Size/Type: Rice
Other Heating: Keystoker
Stove/Furnace Make: EFM DF 520
Stove/Furnace Model: Keystoker
Location: NEPA

Post Wed. Dec. 23, 2009 3:08 pm

Purge the system.

ry

jim d
Member
Posts: 1271
Joined: Mon. Dec. 08, 2008 7:16 pm
Stove/Furnace Make: alaska//coaljck
Stove/Furnace Model: liberty// cj3
Location: taunton ma
Contact:

Post Wed. Dec. 23, 2009 4:32 pm

why don't you call the plumber back that's what my customers would do ,call backs are free, unless there are extenuating circumstances

User avatar
stoker-man
Verified Business Rep.
Posts: 2063
Joined: Mon. Nov. 19, 2007 9:33 pm
Hand Fed Coal Boiler: 1981 efm wcb-24 in use 365 days a year
Coal Size/Type: Anthracite/Chestnut
Other Heating: Hearthstone wood stove
Location: Lehigh Valley, PA

Post Wed. Dec. 23, 2009 4:34 pm

Try adjusting the aquastat differential to 25 for the longer run. Moving the tstat to the coldest room will only overheat the rooms on the circuit before it. You probably should have a separate zone for that cold area.