Axeman Anderson 1959 130M

 
User avatar
Lightning
Member
Posts: 12620
Joined: Wed. Nov. 16, 2011 9:51 am
Location: Olean, NY
Stoker Coal Boiler: AA 130
Coal Size/Type: Pea Size - Anthracite

Post by Lightning » Tue. Mar. 23, 2021 8:27 am

Thats very cool... but with our coal boilers it makes more sense to me to decrease the differential during low heat loads to help the health of the fire and possibly get more complete coal combustion. What's your thoughts?

 
User avatar
StokerDon
Site Moderator
Posts: 6288
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: 1959Axeman Anderson130M, 1991Axeman Anderson130M, BairMatic BMC-500/Van Wert VA400 Stoker, Wert VA-600
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Pea, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sun. Mar. 28, 2021 7:26 pm

Mostly warm this week, highs in the 50's and 60's, lows in the 40's.
IMG_7870.JPG
.JPG | 342.7KB | IMG_7870.JPG
Over the past 7 days;
Fan reading, 737.6 - 698.2 = 39.4 hours of fan run time, 5.63 hours per day.
Ash reading, 425.7 - 406.0 = 19.7 hours of ashing, 2.81 hours per day.
IMG_7871.JPG
.JPG | 391.4KB | IMG_7871.JPG
34 pounds of ash. Starting to look a bit rocky in this warmer weather.
IMG_7872.JPG
.JPG | 427.6KB | IMG_7872.JPG
Ash is probably closer to 15% this week.
12% = 283.33 pounds, 40.49 pounds per day. 7.19 pounds per fan hour.
15% = 226.66 pounds, 32.39 pounds per day. 5.75 pounds per fan hour.
18% = 188.88 pounds, 26.99 pounds per day. 4.79 pounds per fan hour.

The Gofer is still at work. Almost down to the auger.
IMG_7875.JPG
.JPG | 474.9KB | IMG_7875.JPG
I use coal as my "Winter weight" in the back of my truck. I pulled the 10 bags of Blashchak out of the truck and put it in the bin.
IMG_7876.JPG
.JPG | 431.4KB | IMG_7876.JPG
That coal is pretty wet. I hope the Gofer doesn't get indigestion from it! :lol:

Current settings,

Fan RPM = 1293.75 RPM (Stock is 2875 RPM)
Ashing = 2.0 Teeth
Auger speed = 4.31 RPM (Stock is 8.05 RPM)
Grate cycles per hour = 10.35
Pounds per hour = About 6 pounds per fan run time hour
Aquastat = 160*F (Inkbird), ON/OFF, Hysteresis = 5*
Anthrastat = 125*F (Inkbird), Hysteresis = 0.5*
Low flue temperature cut off = 160*F, Hysteresis = 0.1*

-Don

 
User avatar
StokerDon
Site Moderator
Posts: 6288
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: 1959Axeman Anderson130M, 1991Axeman Anderson130M, BairMatic BMC-500/Van Wert VA400 Stoker, Wert VA-600
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Pea, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sun. Apr. 04, 2021 7:20 pm

Happy Easter!

It's been mostly on the cold side this week. Today and the week to come it will be on the warm side, 60's every day in the forecast.
IMG_7877.JPG
.JPG | 348.1KB | IMG_7877.JPG
IMG_7878.JPG
.JPG | 404.2KB | IMG_7878.JPG
Over the past 7 days;
Fan reading, 792.4 - 737.6 = 54.8 hours of fan run time, 7.83 hours per day.
Ash reading, 448.2 - 425.7 = 22.5 hours of ashing, 3.21 hours per day.
IMG_7879.JPG
.JPG | 356.4KB | IMG_7879.JPG
37 pounds of ash, about 12%.
IMG_7881.JPG
.JPG | 421.8KB | IMG_7881.JPG
Ash is probably closer to 12% this week.
12% = 308.33 pounds, 44.05 pounds per day. 5.63 pounds per fan hour.
15% = 246.66 pounds, 35.24 pounds per day. 4.50 pounds per fan hour.
18% = 205.55 pounds, 29.36 pounds per day. 3.75 pounds per fan hour.

The Gofer is still hard at work.
IMG_7880.JPG
.JPG | 404.2KB | IMG_7880.JPG
Current settings,

Fan RPM = 1293.75 RPM (Stock is 2875 RPM)
Ashing = 2.0 Teeth
Auger speed = 4.31 RPM (Stock is 8.05 RPM)
Grate cycles per hour = 10.35
Pounds per hour = About 6 pounds per fan run time hour
Aquastat = 160*F (Inkbird), ON/OFF, Hysteresis = 5*
Anthrastat = 125*F (Inkbird), Hysteresis = 0.5*
Low flue temperature cut off = 160*F, Hysteresis = 0.1*

-Don

 
User avatar
StokerDon
Site Moderator
Posts: 6288
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: 1959Axeman Anderson130M, 1991Axeman Anderson130M, BairMatic BMC-500/Van Wert VA400 Stoker, Wert VA-600
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Pea, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sun. Apr. 11, 2021 5:35 pm

Mostly highs in the 70's with a couple 60's this week. These are the temps that are a little tricky for the Axeman. So far, no problems.
IMG_7883.JPG
.JPG | 368.5KB | IMG_7883.JPG
Over the past 7 days;
Fan reading, 828.6 - 792.4 = 36.2 hours of fan run time, 5.17 hours per day.
Ash reading, 467.1 - 448.2 = 18.9 hours of ashing, 2.70 hours per day.
IMG_7884.JPG
.JPG | 288.3KB | IMG_7884.JPG
33 pounds of ash. Ash still looks pretty good, between 12 and 15%.
IMG_7886.JPG
.JPG | 398.7KB | IMG_7886.JPG
Ash is probably closer to 12% this week.
12% = 275.00 pounds, 39.29 pounds per day. 7.60 pounds per fan hour.
15% = 220.00 pounds, 31.43 pounds per day. 6.01 pounds per fan hour.
18% = 183.33 pounds, 26.19 pounds per day. 5.06 pounds per fan hour.

The Gofer has eaten down to the auger. Time to move some coal over.
IMG_7885.JPG
.JPG | 400.8KB | IMG_7885.JPG
Current settings,

Fan RPM = 1293.75 RPM (Stock is 2875 RPM)
Ashing = 2.0 Teeth
Auger speed = 4.31 RPM (Stock is 8.05 RPM)
Grate cycles per hour = 10.35
Pounds per hour = About 6 pounds per fan run time hour
Aquastat = 160*F (Inkbird), ON/OFF, Hysteresis = 5*
Anthrastat = 125*F (Inkbird), Hysteresis = 0.5*
Low flue temperature cut off = 160*F, Hysteresis = 0.1*

-Don


 
User avatar
StokerDon
Site Moderator
Posts: 6288
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: 1959Axeman Anderson130M, 1991Axeman Anderson130M, BairMatic BMC-500/Van Wert VA400 Stoker, Wert VA-600
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Pea, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sun. Apr. 18, 2021 7:53 pm

Rainy, cool-ish week. Highs in the 50's and 60's.
IMG_7888.JPG
.JPG | 338.1KB | IMG_7888.JPG
Over the past 7 days;
Fan reading, 870.3 - 828.6 = 41.7 hours of fan run time, 5.96 hours per day.
Ash reading, 487.7 - 467.1 = 20.6 hours of ashing, 2.94 hours per day.
IMG_7889.JPG
.JPG | 380.8KB | IMG_7889.JPG
33 pounds of ash. Lots of clinkers this week.
IMG_7891.JPG
.JPG | 427.1KB | IMG_7891.JPG
Ash is between 12% and 15% this week.
12% = 275.00 pounds, 39.29 pounds per day. 6.59 pounds per fan hour.
15% = 220.00 pounds, 31.43 pounds per day. 5.28 pounds per fan hour.
18% = 183.33 pounds, 26.19 pounds per day. 4.40 pounds per fan hour.

The Gofer has eaten down to the auger, again. Sometime this week I will probably put the barrel in.
IMG_7890.JPG
.JPG | 464.4KB | IMG_7890.JPG
Current settings,

Fan RPM = 1293.75 RPM (Stock is 2875 RPM)
Ashing = 2.0 Teeth
Auger speed = 4.31 RPM (Stock is 8.05 RPM)
Grate cycles per hour = 10.35
Pounds per hour = About 6 pounds per fan run time hour
Aquastat = 160*F (Inkbird), ON/OFF, Hysteresis = 5*
Anthrastat = 125*F (Inkbird), Hysteresis = 0.5*
Low flue temperature cut off = 160*F, Hysteresis = 0.1*

-Don

 
User avatar
StokerDon
Site Moderator
Posts: 6288
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: 1959Axeman Anderson130M, 1991Axeman Anderson130M, BairMatic BMC-500/Van Wert VA400 Stoker, Wert VA-600
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Pea, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sun. Apr. 25, 2021 6:34 pm

Highs in the 50's and 60's again this week.
IMG_7893.JPG
.JPG | 351.1KB | IMG_7893.JPG
I guess some people don't like my home made labels on the control box. :lol:
Member nepacoal sent me some nice new lables.
IMG_7895.JPG
.JPG | 332.2KB | IMG_7895.JPG
Thank you very much N! :yes:

Over the past 7 days;
Fan reading, 910.9 - 870.3 = 40.6 hours of fan run time, 5.80 hours per day.
Ash reading, 508.5 - 487.7 = 20.8 hours of ashing, 2.97 hours per day.
IMG_7896.JPG
.JPG | 340.4KB | IMG_7896.JPG
33 pounds of pretty good looking ash. Between 12% and 15% again.
IMG_7897.JPG
.JPG | 407.8KB | IMG_7897.JPG
Ash is between 12% and 15% this week.
12% = 275.00 pounds, 39.29 pounds per day. 6.77 pounds per fan hour.
15% = 220.00 pounds, 31.43 pounds per day. 5.42 pounds per fan hour.
18% = 183.33 pounds, 26.19 pounds per day. 4.52 pounds per fan hour.

Today it was time to through in the barrel!
IMG_7894.JPG
.JPG | 295.1KB | IMG_7894.JPG
Current settings,

Fan RPM = 1293.75 RPM (Stock is 2875 RPM)
Ashing = 2.0 Teeth
Auger speed = 4.31 RPM (Stock is 8.05 RPM)
Grate cycles per hour = 10.35
Pounds per hour = About 6 pounds per fan run time hour
Aquastat = 160*F (Inkbird), ON/OFF, Hysteresis = 5*
Anthrastat = 125*F (Inkbird), Hysteresis = 0.5*
Low flue temperature cut off = 160*F, Hysteresis = 0.1*

-Don

 
User avatar
StokerDon
Site Moderator
Posts: 6288
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: 1959Axeman Anderson130M, 1991Axeman Anderson130M, BairMatic BMC-500/Van Wert VA400 Stoker, Wert VA-600
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Pea, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sun. May. 02, 2021 7:55 pm

Well Spring has Sprung and this week Air Conditioning season has officially begun. :no1:

We are well into mowing season but the old John Deere F915 has a problem. The PTO bracket on the engine broke so that needs fixing before we can mow anything.
IMG_7904.JPG
.JPG | 535.7KB | IMG_7904.JPG
.
IMG_7906.JPG
.JPG | 476.4KB | IMG_7906.JPG
IMG_7907.JPG
.JPG | 358.4KB | IMG_7907.JPG
IMG_7909.JPG
.JPG | 409.8KB | IMG_7909.JPG
This is the piece that broke off. I will see if I can get a new one but I'm not holding my breath. The machine is over 25 years old so we will probably have to fix this one.
IMG_7913.JPG
.JPG | 319.7KB | IMG_7913.JPG
Fired up the snow blower and ran it out of gas. Then put it away until Winter.
IMG_7910.JPG
.JPG | 581.2KB | IMG_7910.JPG
On to the Axeman.

Last Sunday when I put the barrel in, I didn't get the hole in the bottom lined up correctly. When I came home from work on Monday, the fire was almost out! :o
IMG_7920.JPG
.JPG | 349.5KB | IMG_7920.JPG
The fan just kept running for hours and hours. The auger shut off on the "Low Stack Temp" limit. :yes:
I managed to recover the fire but our fan hour readings and consumption calculations would be very skewed, so we won't bother with them this week.

New, corrected labels. Thanks again N! :D
IMG_7921.JPG
.JPG | 404.7KB | IMG_7921.JPG
Over the past 7 days;
Fan reading, 956.5 - 910.9 = 45.6 hours of fan run time, 6.51 hours per day.
Ash reading, 530.9 - 508.5 = 22.4 hours of ashing, 3.20 hours per day.
IMG_7922.JPG
.JPG | 358.3KB | IMG_7922.JPG
37 pounds of rocky with some coal in it ash.
IMG_7924.JPG
.JPG | 411.1KB | IMG_7924.JPG
Ash is completely off track this week.
12% = XXX.00 pounds, XX.XX pounds per day. X.XX pounds per fan hour.
15% = XXX.00 pounds, XX.XX pounds per day. X.XX pounds per fan hour.
18% = XXX.00 pounds, XX.XX pounds per day. X.XX pounds per fan hour.
We used a little more that half a barrel this week.
IMG_7923.JPG
.JPG | 370.6KB | IMG_7923.JPG
Filled it up again. Ready for another week!
IMG_7926.JPG
.JPG | 400.1KB | IMG_7926.JPG
IMG_7927.JPG
.JPG | 368.6KB | IMG_7927.JPG
Current settings,

Fan RPM = 1293.75 RPM (Stock is 2875 RPM)
Ashing = 2.0 Teeth
Auger speed = 4.31 RPM (Stock is 8.05 RPM)
Grate cycles per hour = 10.35
Pounds per hour = About X pounds per fan run time hour
Aquastat = 160*F (Inkbird), ON/OFF, Hysteresis = 5*
Anthrastat = 125*F (Inkbird), Hysteresis = 0.5*
Low flue temperature cut off = 160*F, Hysteresis = 0.1*

-Don

Post Reply