Post by Lightning » Tue. Mar. 23, 2021 8:27 am

Thats very cool... but with our coal boilers it makes more sense to me to decrease the differential during low heat loads to help the health of the fire and possibly get more complete coal combustion. What's your thoughts?


 
User avatar
StokerDon
Site Moderator
Posts: 7496
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sun. Mar. 28, 2021 7:26 pm

Mostly warm this week, highs in the 50's and 60's, lows in the 40's.
IMG_7870.JPG
.JPG | 342.7KB | IMG_7870.JPG
Over the past 7 days;
Fan reading, 737.6 - 698.2 = 39.4 hours of fan run time, 5.63 hours per day.
Ash reading, 425.7 - 406.0 = 19.7 hours of ashing, 2.81 hours per day.
IMG_7871.JPG
.JPG | 391.4KB | IMG_7871.JPG
34 pounds of ash. Starting to look a bit rocky in this warmer weather.
IMG_7872.JPG
.JPG | 427.6KB | IMG_7872.JPG
Ash is probably closer to 15% this week.
12% = 283.33 pounds, 40.49 pounds per day. 7.19 pounds per fan hour.
15% = 226.66 pounds, 32.39 pounds per day. 5.75 pounds per fan hour.
18% = 188.88 pounds, 26.99 pounds per day. 4.79 pounds per fan hour.

The Gofer is still at work. Almost down to the auger.
IMG_7875.JPG
.JPG | 474.9KB | IMG_7875.JPG
I use coal as my "Winter weight" in the back of my truck. I pulled the 10 bags of Blashchak out of the truck and put it in the bin.
IMG_7876.JPG
.JPG | 431.4KB | IMG_7876.JPG
That coal is pretty wet. I hope the Gofer doesn't get indigestion from it! :lol:

Current settings,

Fan RPM = 1293.75 RPM (Stock is 2875 RPM)
Ashing = 2.0 Teeth
Auger speed = 4.31 RPM (Stock is 8.05 RPM)
Grate cycles per hour = 10.35
Pounds per hour = About 6 pounds per fan run time hour
Aquastat = 160*F (Inkbird), ON/OFF, Hysteresis = 5*
Anthrastat = 125*F (Inkbird), Hysteresis = 0.5*
Low flue temperature cut off = 160*F, Hysteresis = 0.1*

-Don

 
User avatar
StokerDon
Site Moderator
Posts: 7496
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sun. Apr. 04, 2021 7:20 pm

Happy Easter!

It's been mostly on the cold side this week. Today and the week to come it will be on the warm side, 60's every day in the forecast.
IMG_7877.JPG
.JPG | 348.1KB | IMG_7877.JPG
IMG_7878.JPG
.JPG | 404.2KB | IMG_7878.JPG
Over the past 7 days;
Fan reading, 792.4 - 737.6 = 54.8 hours of fan run time, 7.83 hours per day.
Ash reading, 448.2 - 425.7 = 22.5 hours of ashing, 3.21 hours per day.
IMG_7879.JPG
.JPG | 356.4KB | IMG_7879.JPG
37 pounds of ash, about 12%.
IMG_7881.JPG
.JPG | 421.8KB | IMG_7881.JPG
Ash is probably closer to 12% this week.
12% = 308.33 pounds, 44.05 pounds per day. 5.63 pounds per fan hour.
15% = 246.66 pounds, 35.24 pounds per day. 4.50 pounds per fan hour.
18% = 205.55 pounds, 29.36 pounds per day. 3.75 pounds per fan hour.

The Gofer is still hard at work.
IMG_7880.JPG
.JPG | 404.2KB | IMG_7880.JPG
Current settings,

Fan RPM = 1293.75 RPM (Stock is 2875 RPM)
Ashing = 2.0 Teeth
Auger speed = 4.31 RPM (Stock is 8.05 RPM)
Grate cycles per hour = 10.35
Pounds per hour = About 6 pounds per fan run time hour
Aquastat = 160*F (Inkbird), ON/OFF, Hysteresis = 5*
Anthrastat = 125*F (Inkbird), Hysteresis = 0.5*
Low flue temperature cut off = 160*F, Hysteresis = 0.1*

-Don

 
User avatar
StokerDon
Site Moderator
Posts: 7496
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sun. Apr. 11, 2021 5:35 pm

Mostly highs in the 70's with a couple 60's this week. These are the temps that are a little tricky for the Axeman. So far, no problems.
IMG_7883.JPG
.JPG | 368.5KB | IMG_7883.JPG
Over the past 7 days;
Fan reading, 828.6 - 792.4 = 36.2 hours of fan run time, 5.17 hours per day.
Ash reading, 467.1 - 448.2 = 18.9 hours of ashing, 2.70 hours per day.
IMG_7884.JPG
.JPG | 288.3KB | IMG_7884.JPG
33 pounds of ash. Ash still looks pretty good, between 12 and 15%.
IMG_7886.JPG
.JPG | 398.7KB | IMG_7886.JPG
Ash is probably closer to 12% this week.
12% = 275.00 pounds, 39.29 pounds per day. 7.60 pounds per fan hour.
15% = 220.00 pounds, 31.43 pounds per day. 6.01 pounds per fan hour.
18% = 183.33 pounds, 26.19 pounds per day. 5.06 pounds per fan hour.

The Gofer has eaten down to the auger. Time to move some coal over.
IMG_7885.JPG
.JPG | 400.8KB | IMG_7885.JPG
Current settings,

Fan RPM = 1293.75 RPM (Stock is 2875 RPM)
Ashing = 2.0 Teeth
Auger speed = 4.31 RPM (Stock is 8.05 RPM)
Grate cycles per hour = 10.35
Pounds per hour = About 6 pounds per fan run time hour
Aquastat = 160*F (Inkbird), ON/OFF, Hysteresis = 5*
Anthrastat = 125*F (Inkbird), Hysteresis = 0.5*
Low flue temperature cut off = 160*F, Hysteresis = 0.1*

-Don

 
User avatar
StokerDon
Site Moderator
Posts: 7496
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sun. Apr. 18, 2021 7:53 pm

Rainy, cool-ish week. Highs in the 50's and 60's.
IMG_7888.JPG
.JPG | 338.1KB | IMG_7888.JPG
Over the past 7 days;
Fan reading, 870.3 - 828.6 = 41.7 hours of fan run time, 5.96 hours per day.
Ash reading, 487.7 - 467.1 = 20.6 hours of ashing, 2.94 hours per day.
IMG_7889.JPG
.JPG | 380.8KB | IMG_7889.JPG
33 pounds of ash. Lots of clinkers this week.
IMG_7891.JPG
.JPG | 427.1KB | IMG_7891.JPG
Ash is between 12% and 15% this week.
12% = 275.00 pounds, 39.29 pounds per day. 6.59 pounds per fan hour.
15% = 220.00 pounds, 31.43 pounds per day. 5.28 pounds per fan hour.
18% = 183.33 pounds, 26.19 pounds per day. 4.40 pounds per fan hour.

The Gofer has eaten down to the auger, again. Sometime this week I will probably put the barrel in.
IMG_7890.JPG
.JPG | 464.4KB | IMG_7890.JPG
Current settings,

Fan RPM = 1293.75 RPM (Stock is 2875 RPM)
Ashing = 2.0 Teeth
Auger speed = 4.31 RPM (Stock is 8.05 RPM)
Grate cycles per hour = 10.35
Pounds per hour = About 6 pounds per fan run time hour
Aquastat = 160*F (Inkbird), ON/OFF, Hysteresis = 5*
Anthrastat = 125*F (Inkbird), Hysteresis = 0.5*
Low flue temperature cut off = 160*F, Hysteresis = 0.1*

-Don

 
User avatar
StokerDon
Site Moderator
Posts: 7496
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sun. Apr. 25, 2021 6:34 pm

Highs in the 50's and 60's again this week.
IMG_7893.JPG
.JPG | 351.1KB | IMG_7893.JPG
I guess some people don't like my home made labels on the control box. :lol:
Member nepacoal sent me some nice new lables.
IMG_7895.JPG
.JPG | 332.2KB | IMG_7895.JPG
Thank you very much N! :yes:

Over the past 7 days;
Fan reading, 910.9 - 870.3 = 40.6 hours of fan run time, 5.80 hours per day.
Ash reading, 508.5 - 487.7 = 20.8 hours of ashing, 2.97 hours per day.
IMG_7896.JPG
.JPG | 340.4KB | IMG_7896.JPG
33 pounds of pretty good looking ash. Between 12% and 15% again.
IMG_7897.JPG
.JPG | 407.8KB | IMG_7897.JPG
Ash is between 12% and 15% this week.
12% = 275.00 pounds, 39.29 pounds per day. 6.77 pounds per fan hour.
15% = 220.00 pounds, 31.43 pounds per day. 5.42 pounds per fan hour.
18% = 183.33 pounds, 26.19 pounds per day. 4.52 pounds per fan hour.

Today it was time to through in the barrel!
IMG_7894.JPG
.JPG | 295.1KB | IMG_7894.JPG
Current settings,

Fan RPM = 1293.75 RPM (Stock is 2875 RPM)
Ashing = 2.0 Teeth
Auger speed = 4.31 RPM (Stock is 8.05 RPM)
Grate cycles per hour = 10.35
Pounds per hour = About 6 pounds per fan run time hour
Aquastat = 160*F (Inkbird), ON/OFF, Hysteresis = 5*
Anthrastat = 125*F (Inkbird), Hysteresis = 0.5*
Low flue temperature cut off = 160*F, Hysteresis = 0.1*

-Don

 
User avatar
StokerDon
Site Moderator
Posts: 7496
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sun. May. 02, 2021 7:55 pm

Well Spring has Sprung and this week Air Conditioning season has officially begun. :no1:

We are well into mowing season but the old John Deere F915 has a problem. The PTO bracket on the engine broke so that needs fixing before we can mow anything.
IMG_7904.JPG
.JPG | 535.7KB | IMG_7904.JPG
.
IMG_7906.JPG
.JPG | 476.4KB | IMG_7906.JPG
IMG_7907.JPG
.JPG | 358.4KB | IMG_7907.JPG
IMG_7909.JPG
.JPG | 409.8KB | IMG_7909.JPG
This is the piece that broke off. I will see if I can get a new one but I'm not holding my breath. The machine is over 25 years old so we will probably have to fix this one.
IMG_7913.JPG
.JPG | 319.7KB | IMG_7913.JPG
Fired up the snow blower and ran it out of gas. Then put it away until Winter.
IMG_7910.JPG
.JPG | 581.2KB | IMG_7910.JPG
On to the Axeman.

Last Sunday when I put the barrel in, I didn't get the hole in the bottom lined up correctly. When I came home from work on Monday, the fire was almost out! :o
IMG_7920.JPG
.JPG | 349.5KB | IMG_7920.JPG
The fan just kept running for hours and hours. The auger shut off on the "Low Stack Temp" limit. :yes:
I managed to recover the fire but our fan hour readings and consumption calculations would be very skewed, so we won't bother with them this week.

New, corrected labels. Thanks again N! :D
IMG_7921.JPG
.JPG | 404.7KB | IMG_7921.JPG
Over the past 7 days;
Fan reading, 956.5 - 910.9 = 45.6 hours of fan run time, 6.51 hours per day.
Ash reading, 530.9 - 508.5 = 22.4 hours of ashing, 3.20 hours per day.
IMG_7922.JPG
.JPG | 358.3KB | IMG_7922.JPG
37 pounds of rocky with some coal in it ash.
IMG_7924.JPG
.JPG | 411.1KB | IMG_7924.JPG
Ash is completely off track this week.
12% = XXX.00 pounds, XX.XX pounds per day. X.XX pounds per fan hour.
15% = XXX.00 pounds, XX.XX pounds per day. X.XX pounds per fan hour.
18% = XXX.00 pounds, XX.XX pounds per day. X.XX pounds per fan hour.
We used a little more that half a barrel this week.
IMG_7923.JPG
.JPG | 370.6KB | IMG_7923.JPG
Filled it up again. Ready for another week!
IMG_7926.JPG
.JPG | 400.1KB | IMG_7926.JPG
IMG_7927.JPG
.JPG | 368.6KB | IMG_7927.JPG
Current settings,

Fan RPM = 1293.75 RPM (Stock is 2875 RPM)
Ashing = 2.0 Teeth
Auger speed = 4.31 RPM (Stock is 8.05 RPM)
Grate cycles per hour = 10.35
Pounds per hour = About X pounds per fan run time hour
Aquastat = 160*F (Inkbird), ON/OFF, Hysteresis = 5*
Anthrastat = 125*F (Inkbird), Hysteresis = 0.5*
Low flue temperature cut off = 160*F, Hysteresis = 0.1*

-Don


 
lzaharis
Member
Posts: 2379
Joined: Sun. Mar. 25, 2007 8:41 pm
Location: Ithaca, New York
Stoker Coal Boiler: Keystoker KAA-4-1 dual fuel boiler
Hand Fed Coal Boiler: former switzer CWW100-sold
Coal Size/Type: rice
Other Heating: kerosene for dual fuel Keystoker/unused

Post by lzaharis » Thu. May. 06, 2021 11:28 am

Hey Don,

If you have not done this on that beautiful Toro snowblower already
you should drain the carburator fuel bowl too.

 
User avatar
StokerDon
Site Moderator
Posts: 7496
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sat. May. 08, 2021 8:46 am

lzaharis wrote:
Thu. May. 06, 2021 11:28 am
you should drain the carburator fuel bowl too.
That's why we run it out of gas. When it stops running the tank and the float bowel are empty.

In other news, it's a little chillier and wetter down here this week. I had the radiators shut off and the AC on last week. Last night I had to open a couple radiators back up. :o
IMG_7928.JPG
.JPG | 197.3KB | IMG_7928.JPG
IMG_7929.JPG
.JPG | 274KB | IMG_7929.JPG
IMG_7930.JPG
.JPG | 325.3KB | IMG_7930.JPG
-Don

 
User avatar
StokerDon
Site Moderator
Posts: 7496
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sun. May. 09, 2021 6:57 pm

We managed to get the Old John Deere F915 Running just enough to do some mowing. The PTO bracket on the engine is broke. I have it clamped together. It also needs a PTO driveshaft, the splines on this one are worn to the point that it vibrates pretty bad. New parts are on order.
IMG_7931.JPG
.JPG | 308.9KB | IMG_7931.JPG
IMG_7932.JPG
.JPG | 380.8KB | IMG_7932.JPG
Down to business.
IMG_7933.JPG
.JPG | 350.4KB | IMG_7933.JPG
IMG_7934.JPG
.JPG | 353.8KB | IMG_7934.JPG
Over the past 7 days;
Fan reading, 991.8 - 956.5 = 35.3 hours of fan run time, 5.04 hours per day.
Ash reading, 551.6 - 530.9 = 20.7 hours of ashing, 2.96 hours per day.
IMG_7935.JPG
.JPG | 411.9KB | IMG_7935.JPG
34 pounds of rocky look'in ash.
IMG_7939.JPG
.JPG | 469.2KB | IMG_7939.JPG
Ash is About 15% this week.
12% = 283.33 pounds, 40.47 pounds per day. 8.03 pounds per fan hour.
15% = 226.66 pounds, 32.38 pounds per day. 6.42 pounds per fan hour.
18% = 188.88 pounds, 26.98 pounds per day. 5.35 pounds per fan hour.

Still about half a barrel left. Maybe we'll let it ride until next week. The coming week should be a bit warmer, Hopefully we will start getting closer to 20 pounds per day soon.
IMG_7936.JPG
.JPG | 405KB | IMG_7936.JPG
Current settings,

Fan RPM = 1293.75 RPM (Stock is 2875 RPM)
Ashing = 2.0 Teeth
Auger speed = 4.31 RPM (Stock is 8.05 RPM)
Grate cycles per hour = 10.35
Pounds per hour = About X pounds per fan run time hour
Aquastat = 160*F (Inkbird), ON/OFF, Hysteresis = 5*
Anthrastat = 125*F (Inkbird), Hysteresis = 0.5*
Low flue temperature cut off = 160*F, Hysteresis = 0.1*

-Don

 
User avatar
StokerDon
Site Moderator
Posts: 7496
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sun. May. 16, 2021 8:46 pm

Today we shut off the heating loop for the house. Now the only thing the Axeman will be heating is the indirect water heater. We'll see if this reduces our per day coal usage.
IMG_7950.JPG
.JPG | 310.9KB | IMG_7950.JPG
IMG_7951.JPG
.JPG | 331KB | IMG_7951.JPG
Over the past 7 days;
Fan reading, 1026.2 - 991.8 = 34.4 hours of fan run time, 4.91 hours per day.
Ash reading, 573.5 - 551.6 = 21.9 hours of ashing, 3.13 hours per day.
IMG_7952.JPG
.JPG | 293.9KB | IMG_7952.JPG
35 pounds of rocky look'in ash.
IMG_7954.JPG
.JPG | 298.9KB | IMG_7954.JPG
Ash is About 15% this week.
12% = 283.33 pounds, 40.47 pounds per day. 8.03 pounds per fan hour.
15% = 226.66 pounds, 32.38 pounds per day. 6.42 pounds per fan hour.
18% = 188.88 pounds, 26.98 pounds per day. 5.35 pounds per fan hour.
Hummm,,, That's exactly the same as last week.

The barrel full lasted 13 days. I through a few shovels full in yesterday morning to keep it going till today.
IMG_7953.JPG
.JPG | 366.9KB | IMG_7953.JPG
That's almost it for Pea coal! Probably less than a barrel full left in the bin. :o
IMG_7955.JPG
.JPG | 337.8KB | IMG_7955.JPG
This should get us into early to mid June. The Summer coal prices should be in effect by then.

Current settings,

Fan RPM = 1293.75 RPM (Stock is 2875 RPM)
Ashing = 2.0 Teeth
Auger speed = 4.31 RPM (Stock is 8.05 RPM)
Grate cycles per hour = 10.35
Pounds per hour = About 6.5 pounds per fan run time hour
Aquastat = 160*F (Inkbird), ON/OFF, Hysteresis = 5*
Anthrastat = 125*F (Inkbird), Hysteresis = 0.5*
Low flue temperature cut off = 160*F, Hysteresis = 0.1*

In other news,
On Friday I met forum member MacCoon1 to pick up a pile of AHS parts. I got 2 fan plates, one is for the direct drive fan, the other is for the belt drive fan. Also, 3 fans, ashing motor, ashing crank, 2 new fan plate insulators and a couple aquastats.
IMG_7940.JPG
.JPG | 322KB | IMG_7940.JPG
IMG_7941.JPG
.JPG | 287.5KB | IMG_7941.JPG
IMG_7942.JPG
.JPG | 238.3KB | IMG_7942.JPG
IMG_7943.JPG
.JPG | 246.5KB | IMG_7943.JPG
IMG_7944.JPG
.JPG | 409.7KB | IMG_7944.JPG
IMG_7945.JPG
.JPG | 283.1KB | IMG_7945.JPG
IMG_7946.JPG
.JPG | 287.5KB | IMG_7946.JPG
IMG_7947.JPG
.JPG | 297.3KB | IMG_7947.JPG
IMG_7948.JPG
.JPG | 293KB | IMG_7948.JPG
I did a quick test fit of the direct drive fan plate on the 1956 Axeman.
IMG_7949.JPG
.JPG | 338.2KB | IMG_7949.JPG
It fits pretty good! More later.

-Don

 
User avatar
StokerDon
Site Moderator
Posts: 7496
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sun. May. 23, 2021 5:52 pm

Well, down here it's pretty much Summer. 80's and 90's this week, YUK!
IMG_7981.JPG
.JPG | 327.3KB | IMG_7981.JPG
Over the past 7 days;
Fan reading, 1054.7 - 1026.2 = 28.5 hours of fan run time, 4.07 hours per day.
Ash reading, 597.6 - 573.5 = 24.1 hours of ashing, 3.44 hours per day.
IMG_7982.JPG
.JPG | 418.5KB | IMG_7982.JPG
I don't know what happened this week, but the ash is Horrible!!! :what:
IMG_7983.JPG
.JPG | 370.7KB | IMG_7983.JPG
60 pounds of rocks and a little bit of powder. :x
IMG_7984.JPG
.JPG | 453.5KB | IMG_7984.JPG
That's twice as heavy as normal. And I have no idea what ash percentage it is. It's got to be close to 50%.

The strange thing is that we used less coal than normal. It used, maybe a third of a barrel?
IMG_7986.JPG
.JPG | 360.7KB | IMG_7986.JPG
Current settings,

Fan RPM = 1293.75 RPM (Stock is 2875 RPM)
Ashing = 2.0 Teeth
Auger speed = 4.31 RPM (Stock is 8.05 RPM)
Grate cycles per hour = 10.35
Pounds per hour = About 6.5? pounds per fan run time hour
Aquastat = 160*F (Inkbird), ON/OFF, Hysteresis = 5*
Anthrastat = 125*F (Inkbird), Hysteresis = 0.5*
Low flue temperature cut off = 160*F, Hysteresis = 0.1*

 
User avatar
StokerDon
Site Moderator
Posts: 7496
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sun. May. 30, 2021 9:40 pm

Hot weather early in the week. Cool weather later in the week. Due to the horrible looking ash from last week I dropped the ashing temp from 125 to 110 degrees. Tuesday we had an outfire due to the warm weather. It was so warm that the fire door would not suck closed so we increased the fan speed to 1725 RPM.
IMG_8011.JPG
.JPG | 332.1KB | IMG_8011.JPG
IMG_8008.JPG
.JPG | 327.3KB | IMG_8008.JPG
Over the past 7 days;
Fan reading, 1089.5 - 1054.7 = 34.8 hours of fan run time, 4.97 hours per day.
Ash reading, 620.3 - 597.6 = 22.7 hours of ashing, 3.24 hours per day.
IMG_8009.JPG
.JPG | 359.3KB | IMG_8009.JPG
54 pounds of what looks like rocks and some powder on the bottom with clinkers on top.
IMG_8010.JPG
.JPG | 416.6KB | IMG_8010.JPG
The Gofer finished off this barrel this afternoon.
IMG_8013.JPG
.JPG | 353.1KB | IMG_8013.JPG
I scrapped the bottom of the bin and came up with one more full barrel.
IMG_8014.JPG
.JPG | 348.6KB | IMG_8014.JPG
That's it for the Pea coal. There are a bunch of fines in there so we will probably have some puff-backs and outfires in the near future! :what:

Current settings,

Fan RPM = 1725 RPM (Stock is 2875 RPM)
Ashing = 2.0 Teeth
Auger speed = 4.31 RPM (Stock is 8.05 RPM)
Grate cycles per hour = 10.35
Pounds per hour = ??.? pounds per fan run time hour
Aquastat = 160*F (Inkbird), ON/OFF, Hysteresis = 5*
Anthrastat = 110*F (Inkbird), Hysteresis = 0.5*
Low flue temperature cut off = 160*F, Hysteresis = 0.1*

-Don

 
User avatar
Idlorah
Member
Posts: 520
Joined: Wed. Nov. 18, 2020 6:31 pm
Location: New Ringgold, PA
Stoker Coal Boiler: Allen 700 stoker
Hand Fed Coal Stove: Gibralter MCC
Coal Size/Type: Buck in the Allen and anything goes in the MCC, Anthracite
Other Heating: None, maybe some wood in the MCC in the shoulder season

Post by Idlorah » Tue. Jun. 01, 2021 8:39 pm

I see i am not the only one who pulls out a barrel towards the end of the season, I just shut my allen stoker off 2 weeks ago but had to turn it back on this weekend we had low temps in the 50s during the day and 40s at night. Coal mice are a life saver for starting the fire but damp coal mice are pretty useless, learned the the hard way. My Allen is now shut off for the season and deserves a good cleaning and a gear box reseal.

 
User avatar
StokerDon
Site Moderator
Posts: 7496
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Sun. Jun. 06, 2021 5:42 pm

Idlorah wrote:
Tue. Jun. 01, 2021 8:39 pm
I see i am not the only one who pulls out a barrel towards the end of the season,
Yup, the barrel is the way to go when the bin gets low.

Well, it's been a very challenging week for the old Axeman. This bottom of the bin coal doesn't want to hold a fire. Also it's been Hot! Hot! Hot! Temps in the 80's and 90's.
IMG_8058.JPG
.JPG | 354.9KB | IMG_8058.JPG
We've had 5 outfires this week. We had to make some drastic setting changes to make it work. First we changed the ashing temp back to 125. Then we increased the fan speed to 1725 RPM. The fire still went out. Then we increased the fan speed to 2300 RPM, increased the ashing to 3 teeth and set the timer for 1 minute every half hour.
IMG_8061.JPG
.JPG | 284.6KB | IMG_8061.JPG
Hopefully it stays lit this week!

Fire depth was 7" this morning, 2.5" up to 9.5".

Over the past 7 days;
Fan reading, 1136.9 - 1089.5 = 47.4 hours of fan run time, 6.77 hours per day.
Ash reading, 639.9 - 620.3 = 19.6 hours of ashing, 2.80 hours per day.
IMG_8060.JPG
.JPG | 385.4KB | IMG_8060.JPG
Ash is mostly part burnt coal and raw coal with a little ash. Pretty Friggin Bad! :x
IMG_8063.JPG
.JPG | 396.1KB | IMG_8063.JPG
It's got to be 100 pounds or more. It totally pegged my scale!
IMG_8064.JPG
.JPG | 342KB | IMG_8064.JPG
Only used about 1/3rd barrel of coal though?
IMG_8062.JPG
.JPG | 383.8KB | IMG_8062.JPG
Current settings,

Timer = 1 minute every half hour
Fan RPM = 2300 RPM (Stock is 2875 RPM)
Ashing = 3.0 Teeth
Auger speed = 4.31 RPM (Stock is 8.05 RPM)
Grate cycles per hour = 10.35
Pounds per hour = ??.? pounds per fan run time hour
Aquastat = 160*F (Inkbird), ON/OFF, Hysteresis = 5*
Anthrastat = 125*F (Inkbird), Hysteresis = 0.5*
Low flue temperature cut off = 160*F, Hysteresis = 0.1*

Here is an update video with the deafening Cicada population explosion!


-Don