Post by lsayre » Tue. Oct. 16, 2018 7:14 pm

My advice is to give it more time.


 
User avatar
StokerDon
Site Moderator
Posts: 7496
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Tue. Oct. 16, 2018 7:20 pm

That's the current plan Larry!

Thanks.
IMG_3363.JPG
.JPG | 345.9KB | IMG_3363.JPG
IMG_3362.JPG
.JPG | 358.3KB | IMG_3362.JPG
-Don

 
User avatar
Rob R.
Site Moderator
Posts: 18004
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Wed. Oct. 17, 2018 6:24 am

Don, did you check the calibration of the anthrastat?

 
ziggy87
Member
Posts: 312
Joined: Sat. Oct. 25, 2014 11:22 am
Location: Halifax, Pa
Stoker Coal Boiler: axeman anderson 130
Coal Size/Type: Pea

Post by ziggy87 » Wed. Oct. 17, 2018 7:33 am

Hi Don Axeman does sell a rebuild kit for that ashing solenoid.

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Wed. Oct. 17, 2018 9:24 am

SD, once you go digital controls you'll wonder why you didn't do it sooner.
Beside a set-point display you'll have a 'real time' temp display and also gain an adjustable hysterisis.

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Wed. Oct. 17, 2018 9:27 am

McGiever wrote:
Wed. Oct. 17, 2018 9:24 am
SD, once you go digital controls you'll wonder why you didn't do it sooner.
Beside a set-point display you'll have a 'real time' temp display and also gain an adjustable hysterisis.
And you can likely accomplish this for far less than the cost of a new Anthrastat.

 
User avatar
hotblast1357
Member
Posts: 5661
Joined: Mon. Mar. 10, 2014 10:06 pm
Location: Peasleeville NY
Stoker Coal Boiler: 1984 Eshland S260 coal gun
Coal Size/Type: Lehigh anthracite pea
Other Heating: air source heat pump, oil furnace

Post by hotblast1357 » Wed. Oct. 17, 2018 9:42 am

I couldn’t imagine running mine without it..

Attachments



 
User avatar
StokerDon
Site Moderator
Posts: 7496
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Wed. Oct. 17, 2018 7:08 pm

ziggy87 wrote:
Wed. Oct. 17, 2018 7:33 am
Hi Don Axeman does sell a rebuild kit for that ashing solenoid.
I took a quick look through the parts list but didn't see it. Here it is so you can look for yourself.
parts list-1.pdf
.PDF | 433.8KB | parts list-1.pdf
The solenoid is pretty simple, slug, spring and sleeve. The slug and sleeve could ware causing binding. The spring could get weak or brake.

And there is the 115 volt / 60Hz coil. If that doesn't work. it's smoked.

-Don

 
User avatar
StokerDon
Site Moderator
Posts: 7496
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Wed. Oct. 17, 2018 7:17 pm

Rob R. wrote:
Wed. Oct. 17, 2018 6:24 am
Don, did you check the calibration of the anthrastat?
I am not in the camp that think calibrating the Anthrastat is completely necessary. In reality, it doesn't really matter what number the knob is pointing at as long as the fire is at the right height.

In this case I probable should calibrate it since I am posting the results here. I will probably wait until we get it dialed in first.

-Don

 
User avatar
StokerDon
Site Moderator
Posts: 7496
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Wed. Oct. 17, 2018 7:31 pm

McGiever wrote:
Wed. Oct. 17, 2018 9:24 am
SD, once you go digital controls you'll wonder why you didn't do it sooner.
Beside a set-point display you'll have a 'real time' temp display and also gain an adjustable hysterisis.
I will get them, I'm just not going to let them "control" anything just yet. I have decades of experience with all kinds of electronics and the Chinese controls just don't give me the "warm & fuzzy feeling" of the old tried and true Honeywell controls.

They will have to earn my respect as standby controls first.

As long as we are talking about it, this is the PID I will probably order.
https://www.amazon.com/Universal-Temperature-Cont ... ller&psc=1

110 volt LED's
https://www.amazon.com/Baomain-AD16-22D-Energy-Sa ... 0+volt+LED

And a new hour meter.
https://www.amazon.com/SEARON-Generator-Chainsaw- ... eter&psc=1

-Don

 
User avatar
lsayre
Member
Posts: 21781
Joined: Wed. Nov. 23, 2005 9:17 pm
Location: Ohio
Stoker Coal Boiler: AHS S130 Coal Gun
Coal Size/Type: Lehigh Anthracite Pea
Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75

Post by lsayre » Wed. Oct. 17, 2018 7:53 pm

StokerDon wrote:
Wed. Oct. 17, 2018 7:17 pm
I am not in the camp that think calibrating the Anthrastat is completely necessary. In reality, it doesn't really matter what number the knob is pointing at as long as the fire is at the right height.

-Don
I fully agree with this.

 
User avatar
Rob R.
Site Moderator
Posts: 18004
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Wed. Oct. 17, 2018 8:24 pm

StokerDon wrote:
Wed. Oct. 17, 2018 7:17 pm
I am not in the camp that think calibrating the Anthrastat is completely necessary. In reality, it doesn't really matter what number the knob is pointing at as long as the fire is at the right height.

In this case I probable should calibrate it since I am posting the results here. I will probably wait until we get it dialed in first.

-Don
Bingo. The whole idea is that the settings should be repeatable. Most people would probably prefer to set the ash control to known setting, and have the fire height be close to correct on the first try.

Kind of like using a bore sight when putting a new scope on a rifle. It won't be perfect, but it will get you on the target on the first shot.

 
User avatar
McGiever
Member
Posts: 10130
Joined: Sun. May. 02, 2010 11:26 pm
Location: Junction of PA-OH-WV
Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
Hand Fed Coal Boiler: BUCKET A DAY water heater
Hand Fed Coal Stove: Warm Morning 414A
Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
Other Heating: Ground Source Heat Pump and some Solar

Post by McGiever » Wed. Oct. 17, 2018 11:11 pm

StokerDon wrote:
Wed. Oct. 17, 2018 7:31 pm
I will get them, I'm just not going to let them "control" anything just yet. I have decades of experience with all kinds of electronics and the Chinese controls just don't give me the "warm & fuzzy feeling" of the old tried and true Honeywell controls.

They will have to earn my respect as standby controls first.


-Don
My Digital Anthrastat "equivalent" did not replace anything made by Honeywell.
But test away!

 
ziggy87
Member
Posts: 312
Joined: Sat. Oct. 25, 2014 11:22 am
Location: Halifax, Pa
Stoker Coal Boiler: axeman anderson 130
Coal Size/Type: Pea

Post by ziggy87 » Thu. Oct. 18, 2018 11:20 am

StokerDon wrote:
Wed. Oct. 17, 2018 7:08 pm
I took a quick look through the parts list but didn't see it. Here it is so you can look for yourself.
parts list-1.pdf
The solenoid is pretty simple, slug, spring and sleeve. The slug and sleeve could ware causing binding. The spring could get weak or brake.

And there is the 115 volt / 60Hz coil. If that doesn't work. it's smoked.

-Don
I was told by Pete that they sell a rebuild kit if memory serves me correctly. I don't think it was listed in the parts book. It was the guts I do believe. Not the coil.

 
User avatar
StokerDon
Site Moderator
Posts: 7496
Joined: Mon. Nov. 11, 2013 11:17 am
Location: PA, Southern York County!
Stoker Coal Boiler: Gentleman Janitor GJ-5, Van Wert VA-600, Axeman Anderson130 X3.
Hand Fed Coal Furnace: Harman SF3500 reduced down to 3 grates connected to its own plenum
Coal Size/Type: Rice, Chestnut and whatever will fit through the door on the Harman
Other Heating: Noth'in but COAL! Well, Maybe a little tiny bit of wood

Post by StokerDon » Fri. Oct. 19, 2018 5:40 pm

!!!GREMLINS!!!

Yah, I know. Right after I open my big mouth about how wonderful old Honeywell controls are, yesterday morning I looked at the boiler before going to work and the temperature was 120 Degrees. But it was not running???

I checked the ON/OFF switch and it was ON. After trying to measure a couple things, it came on by itself. I figured we had an intermittent connection or part and I figured it was most likely in the HI Limit aquastat since it has some questionable wiring in it. I bypassed it, lit the fire and went to work.

When I got home from work yesterday, the boiler was down under 100 degrees!

I decided to just replace the Honeywell triple aquastat with a different one from the "Good" pile.

Now it's Friday evening and well is well!

-Don

Speaking of "Gremlins", I am having trouble uploading pictures. The "Attachments" tab is not working. I used the "Options" tab and uploaded them just as "Attachments" but doing it that way does not allow you to put the pictures where they need to be.
Sorry.