So...........getting ready to install a furnace and air system. hasn't been one here for 20 yrs but wanted to do it before i retire next year.
had a heat loss survey done, the results were pretty much what i expected but threw the guy that ran it for a loop. seems we loose a total of 135,000 BTUH in the winter in this uninsulated bucket. no problem for FRANK running 24/7, it's still 70* in here even at -20 OAT so who cares.
the bigger issue is that if we go ahead without insulating it will take 11 tons to cool this thing in the summer. hasn't been a problem i have never lived in an air conditioned house and don't like it much in motels either but i'm not paying for that or a split zone heat system.
getting the insulation done via injection foam, will have R18 sidewalls and R14 joist ends and inside of foundation to under grade. 3 days of work starting 6-9.
so with that done i will be transferring about 54,000 BTUH and need just 4 tons of air conditioning. that's in the low average for a 2 story with 1360 total SF of conditioned space in this area.
second Soooooooooooo, i guess i may be looking for a 12" pot globe style base burner or some other little stove to heat with cause the furnace is just in case we "have" to be away sometime ( both of our remaining parents are 90+ ) and / or so it's there if we decide to down size.
the rest of this years projects are water softener, tear out the hard pipe and install pex thru out and a new water heater, 11 more replacement windows on the sun porch and of course the 3 entry doors replaced.
good thing i had this planned and don't need to look for the money.
had a heat loss survey done, the results were pretty much what i expected but threw the guy that ran it for a loop. seems we loose a total of 135,000 BTUH in the winter in this uninsulated bucket. no problem for FRANK running 24/7, it's still 70* in here even at -20 OAT so who cares.
the bigger issue is that if we go ahead without insulating it will take 11 tons to cool this thing in the summer. hasn't been a problem i have never lived in an air conditioned house and don't like it much in motels either but i'm not paying for that or a split zone heat system.
getting the insulation done via injection foam, will have R18 sidewalls and R14 joist ends and inside of foundation to under grade. 3 days of work starting 6-9.
so with that done i will be transferring about 54,000 BTUH and need just 4 tons of air conditioning. that's in the low average for a 2 story with 1360 total SF of conditioned space in this area.
second Soooooooooooo, i guess i may be looking for a 12" pot globe style base burner or some other little stove to heat with cause the furnace is just in case we "have" to be away sometime ( both of our remaining parents are 90+ ) and / or so it's there if we decide to down size.
the rest of this years projects are water softener, tear out the hard pipe and install pex thru out and a new water heater, 11 more replacement windows on the sun porch and of course the 3 entry doors replaced.
good thing i had this planned and don't need to look for the money.
-
- Member
- Posts: 673
- Joined: Sun. Nov. 17, 2019 2:17 pm
What about the ceiling insulation amount? Minimum I would want is R39
-
- Member
- Posts: 4837
- Joined: Wed. Apr. 03, 2013 1:24 pm
- Location: Elkhart county, IN.
- Hand Fed Coal Stove: 1 comforter stove works all iron coal box stove, seventies.
- Baseburners & Antiques: 2014 DTS C17 Base Burner, GW #6, GW 113 formerly Sir Williams, maybe others at Pauliewog’s I’ve forgotten about
- Coal Size/Type: Nut Anth.
- Other Heating: none
Since I had all the knob and tube wiring removed in January I can take are of the attic insulation on my own
These four square houses were very popular back in the 20’s when it was built. Being uninsulated and having wide soffits keeps the roof clear of snow and no ice on the eaves or gutters. You don’t hear of roof problems on these unless branch’s fall on them. probably add some up there this year and see how it goes and add or modify later
These four square houses were very popular back in the 20’s when it was built. Being uninsulated and having wide soffits keeps the roof clear of snow and no ice on the eaves or gutters. You don’t hear of roof problems on these unless branch’s fall on them. probably add some up there this year and see how it goes and add or modify later
- mntbugy
- Member
- Posts: 2043
- Joined: Fri. Dec. 23, 2016 2:36 pm
- Location: clearfield,pa
- Hand Fed Coal Stove: D S 1500, Warm Moring 400
- Baseburners & Antiques: Art Garland 145,GW114 ,Clarion 115, Vestal 20 Globe,New Royal22 Globe, Red Cross Oak 56,Acme Ventiduct 38,Radiant Airblast 626,Home Airblast 62,Moores #7,Moores 3way
- Coal Size/Type: stove and nut and some bit
- Other Heating: Propain
Nice globe-y in Texas. One in Nova Scotia. Two more that will hurt your wallet. Missed two Yesterday, CHEAP.
-
- Member
- Posts: 673
- Joined: Sun. Nov. 17, 2019 2:17 pm
Here is a great link for insulation.
IMO if the company will air seal the attic for you it will be really good money spent. Then I would use rock wool batts in the attic. Fiberglass is not the best choice today in any attic, but home builders need to make profits so they still use it because it’s cheap. Fiberglass allows way to much air movement. Your heat loss will greatly improve from rockwool if you are spray foaming the walls.
https://www.energy.gov/sites/prod/files/guide_to_ ... lation.pdf
IMO if the company will air seal the attic for you it will be really good money spent. Then I would use rock wool batts in the attic. Fiberglass is not the best choice today in any attic, but home builders need to make profits so they still use it because it’s cheap. Fiberglass allows way to much air movement. Your heat loss will greatly improve from rockwool if you are spray foaming the walls.
https://www.energy.gov/sites/prod/files/guide_to_ ... lation.pdf
- McGiever
- Member
- Posts: 10130
- Joined: Sun. May. 02, 2010 11:26 pm
- Location: Junction of PA-OH-WV
- Stoker Coal Boiler: AXEMAN-ANDERSON 130 "1959"
- Hand Fed Coal Boiler: BUCKET A DAY water heater
- Hand Fed Coal Stove: Warm Morning 414A
- Coal Size/Type: PEA,NUT,STOVE /ANTHRACITE
- Other Heating: Ground Source Heat Pump and some Solar
True, and Canada has known this for a.long time....we might catch on eventually.
-
- Member
- Posts: 2344
- Joined: Wed. Feb. 04, 2009 7:13 am
- Location: Fair Haven, VT
- Stoker Coal Boiler: Hybrid Axeman Anderson 130
- Baseburners & Antiques: Sparkle #12
- Coal Size/Type: Pea, Buckwheat, Nut
- Other Heating: LP Hot air. WA TX for coal use.
So you guys are saying to foam the top side of your ceiling to stop air infiltration then rockwool over that for the best heat savings?
- lsayre
- Member
- Posts: 21781
- Joined: Wed. Nov. 23, 2005 9:17 pm
- Location: Ohio
- Stoker Coal Boiler: AHS S130 Coal Gun
- Coal Size/Type: Lehigh Anthracite Pea
- Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75
I seriously question your heat loss studies derived need for heat, because I seriously question Frank's ability to adequately satisfy anything close to such a high demand for heat.
Frank would need to be burning on the order of 15.7 lbs. of anthracite per hour, or 377 lbs. per day to meet such a heat demand.
When Frank has kept your house warm on the coldest days you have ever experienced, how much coal was Frank burning? If Frank is meeting the need, that is your homes present state heat demand (heat loss).
Frank would need to be burning on the order of 15.7 lbs. of anthracite per hour, or 377 lbs. per day to meet such a heat demand.
When Frank has kept your house warm on the coldest days you have ever experienced, how much coal was Frank burning? If Frank is meeting the need, that is your homes present state heat demand (heat loss).
-
- Member
- Posts: 4837
- Joined: Wed. Apr. 03, 2013 1:24 pm
- Location: Elkhart county, IN.
- Hand Fed Coal Stove: 1 comforter stove works all iron coal box stove, seventies.
- Baseburners & Antiques: 2014 DTS C17 Base Burner, GW #6, GW 113 formerly Sir Williams, maybe others at Pauliewog’s I’ve forgotten about
- Coal Size/Type: Nut Anth.
- Other Heating: none
Bingo thanks Larry
The primary issue here is that I will never be able to sell this house without insulation and a modern heat system so I’m doing that
All I know for sure is that there is no insulation in this house and FRANK keeps it 70 down stairs and 72-74 up no matter what
I’ll get different survey done in a couple weeks and go from there for furnace selection
Thanks
steve
The primary issue here is that I will never be able to sell this house without insulation and a modern heat system so I’m doing that
All I know for sure is that there is no insulation in this house and FRANK keeps it 70 down stairs and 72-74 up no matter what
I’ll get different survey done in a couple weeks and go from there for furnace selection
Thanks
steve
- lsayre
- Member
- Posts: 21781
- Joined: Wed. Nov. 23, 2005 9:17 pm
- Location: Ohio
- Stoker Coal Boiler: AHS S130 Coal Gun
- Coal Size/Type: Lehigh Anthracite Pea
- Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75
I'd say that Frank has been doing your heat loss survey. Pay zero attention to Frank's BTUH rating, which is meaningless and totally irrelevant. Pay 100% attention to the amount of fuel Frank is burning on the very coldest of days. And on first approximation, assume 12,275 BTU's per pound for typical anthracite, and 70% efficiency for Frank.KingCoal wrote: ↑Fri. Jun. 05, 2020 6:11 amBingo thanks Larry
The primary issue here is that I will never be able to sell this house without insulation and a modern heat system so I’m doing that
All I know for sure is that there is no insulation in this house and FRANK keeps it 70 down stairs and 72-74 up no matter what
I’ll get different survey done in a couple weeks and go from there for furnace selection
Thanks
steve
- Rob R.
- Site Moderator
- Posts: 17981
- Joined: Fri. Dec. 28, 2007 4:26 pm
- Location: Chazy, NY
- Stoker Coal Boiler: EFM 520
- Hand Fed Coal Stove: Chubby Jr
Even blown in cellulose would be a huge improvement compared to no insulation. Foam would do the best job at air sealing, but may require the use of some kind of air exchange system. Roughly 50% of a home's heat loss is due to air leakage into the attic. Considering how much you are spending to insulate the rest of the house, I think you would get a much better return on your $$ if the attic was insulated as well.KingCoal wrote: ↑Thu. Jun. 04, 2020 5:47 amSince I had all the knob and tube wiring removed in January I can take are of the attic insulation on my own
These four square houses were very popular back in the 20’s when it was built. Being uninsulated and having wide soffits keeps the roof clear of snow and no ice on the eaves or gutters. You don’t hear of roof problems on these unless branch’s fall on them. probably add some up there this year and see how it goes and add or modify later
-
- Member
- Posts: 673
- Joined: Sun. Nov. 17, 2019 2:17 pm
What are they using for a heat loss calculator? I hope its at least Manual J and D and not a best guess.
- lsayre
- Member
- Posts: 21781
- Joined: Wed. Nov. 23, 2005 9:17 pm
- Location: Ohio
- Stoker Coal Boiler: AHS S130 Coal Gun
- Coal Size/Type: Lehigh Anthracite Pea
- Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75
Even for 'Manual J' it is ultimately a case of garbage in, garbage out. That's why for this case I place my faith in Frank and in Steve's testimony that even on the coldest days Frank has kept the house comfortably warm.Holdencoal wrote: ↑Fri. Jun. 05, 2020 7:33 amWhat are they using for a heat loss calculator? I hope its at least Manual J and D and not a best guess.
An old ballpark rule of thumb for typically insulated all-electric (resistance) heated homes (in my area, which is not all that different from Steve's) was 10 Watts per hour per Sq-Ft. I believe I recall where Steve once stated that his home has on the order of 900 Sq-Ft. being heated.
10 Watts/Hr. x 900 Sq-Ft. x 3.412 BTU/Watt = 30,708 BTUH (as output).
That is a far cry from 135,000 BTUH (as output).
Last edited by lsayre on Fri. Jun. 05, 2020 8:02 am, edited 1 time in total.
- lsayre
- Member
- Posts: 21781
- Joined: Wed. Nov. 23, 2005 9:17 pm
- Location: Ohio
- Stoker Coal Boiler: AHS S130 Coal Gun
- Coal Size/Type: Lehigh Anthracite Pea
- Other Heating: Resistance Boiler (13.5 KW), ComfortMax 75
30,708 BTUH for coal would be roughly:
30,708 / 0.70 / 12,275 = 3.574 Lbs./Hr.
3.574 x 24 ~= 86 Lbs. per day
Is Frank burning about 86 pounds per day on the coldest couple days of the year?
30,708 / 0.70 / 12,275 = 3.574 Lbs./Hr.
3.574 x 24 ~= 86 Lbs. per day
Is Frank burning about 86 pounds per day on the coldest couple days of the year?
-
- Member
- Posts: 673
- Joined: Sun. Nov. 17, 2019 2:17 pm
Larry, I Agree 110% with you. I see a lot of guys over size boilers and AC units just on how the wallet is doing and what supply house has the best deal. What’s an extra ton .
Homes in northern Worcester were build in the 70-80’s and most of the time with electric ceiling (Radiant) heat between two layers of drywall.
Homes in northern Worcester were build in the 70-80’s and most of the time with electric ceiling (Radiant) heat between two layers of drywall.