Where is the ideal location for a barometric damper when two oil fired units are in series on a single chimney thimble?

My oil fired hot water heater and oil fired hot air furnace share a thimble and flue.

As it is now the HWH is closest to the thimble then the baro then the furnace.

Thoughts?

 
Hoytman
Member
Posts: 6003
Joined: Wed. Jan. 18, 2017 11:30 pm
Location: swOH near a little town where the homes are mobile and the cars aren’t
Hand Fed Coal Stove: Hitzer 354
Coal Size/Type: nut coal
Other Heating: electric, wood, oil

Post by Hoytman » Tue. Apr. 28, 2020 10:52 pm

Hi Scott.

Not sure they would allow that around here. Both would need a separate flue, but if they’d both fit into the same thimble, I’m not sure why they’re require separate flues.

Waiting to read other responses about the baro.

 
User avatar
coaledsweat
Site Moderator
Posts: 13763
Joined: Fri. Oct. 27, 2006 2:05 pm
Location: Guilford, Connecticut
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea

Post by coaledsweat » Wed. Apr. 29, 2020 6:45 am

As far as location, it should be in the middle of a long straight run. And there should be one for each appliance. That said, I don't think you're going to get a 2 into 1 stovepipe deal past inspection. You could power vent one perhaps?

 
User avatar
Rob R.
Site Moderator
Posts: 17980
Joined: Fri. Dec. 28, 2007 4:26 pm
Location: Chazy, NY
Stoker Coal Boiler: EFM 520
Hand Fed Coal Stove: Chubby Jr

Post by Rob R. » Wed. Apr. 29, 2020 6:59 am

I don't see why there would be anything wrong with two oil units in one flue as long as everything was sized appropriately.

Each appliance should have its own baro, and be connected to a common stove pipe that is sized for both appliances.


 
scalabro
Member
Posts: 4197
Joined: Wed. Oct. 03, 2012 9:53 am
Location: Western Massachusetts
Baseburners & Antiques: Crawford 40, PP Stewart No. 14, Abendroth Bros "Record 40"
Coal Size/Type: Stove / Anthracite.
Other Heating: Oil fired, forced hot air.

Post by scalabro » Wed. Apr. 29, 2020 7:40 am

The house passed inspection when it was built this way in 1995.

I’m going to replace my furnace this summer myself and wanted some input.

In my mind the baro would be “after” both units (assuming each requires the same draft) IOW...

Thimble
Pipe
HWH
Pipe
Furnace
Baro

I’ll post a picture this afternoon.

 
User avatar
coaledsweat
Site Moderator
Posts: 13763
Joined: Fri. Oct. 27, 2006 2:05 pm
Location: Guilford, Connecticut
Stoker Coal Boiler: Axeman Anderson 260M
Coal Size/Type: Pea

Post by coaledsweat » Wed. Apr. 29, 2020 7:59 am

You aren't regulating chimney draft, you want to regulate the draft on an individual appliance. Here's a link to Field Controls contractors info. Scroll down and click on the PDF.

https://www.google.com/url?sa=t&source=web&rct=j& ... 8161442485

 
scalabro
Member
Posts: 4197
Joined: Wed. Oct. 03, 2012 9:53 am
Location: Western Massachusetts
Baseburners & Antiques: Crawford 40, PP Stewart No. 14, Abendroth Bros "Record 40"
Coal Size/Type: Stove / Anthracite.
Other Heating: Oil fired, forced hot air.

Post by scalabro » Wed. Apr. 29, 2020 2:38 pm

coaledsweat wrote:
Wed. Apr. 29, 2020 7:59 am
You aren't regulating chimney draft, you want to regulate the draft on an individual appliance. Here's a link to Field Controls contractors info. Scroll down and click on the PDF.

https://www.google.com/url?sa=t&source=web&rct=j& ... 8161442485
Perfect...thank you! When I install the ne w furnace I’m going to re-pipe both units so I’ll install a baro for the HWH as well.